Very temporary power cut-out
Old 10-15-2011, 08:12 PM   #1
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
On the last 3 RV sites that we have visited we have experienced very short power cut-outs, and because this has happened on 3 different RV sites, we assume that this is down to our RV rather than a campground faulty power supply.

What happens is this: Power will disappear for a fraction of a second and then return. It happens at a time where we have a 50 amp connection and not having loaded this with any more than say 5 or 7 amps max.

As mentioned, the power disappears for a fraction of a second. That means that everything comes back straight away, except the DirectTv box that will now start to reset itself (very annoying in the middle of your favourite program BTW).

We have a hard-wired Progressive surge protector in our rig and this doesn't disconnect our electric supply when the fall-out appears.

Could this be down to a inverter malfunction? Is the inverter "in charge" of the 110V supply to the effect that a malfunction here would cause a fall out as described?

__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-15-2011, 08:22 PM   #2
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,653
The inverter usually will only control certain but not all circuits. So my guess is that it's not the inverter.
My best guess is that you have a loose neutral connection somewhere. I found one recently inside my ATS. With inverter off and shore power disconnected you could tighten every electrical connection in the ATS and power distribution panel including the breaker outputs. Tightening these connections is a periodic maintenance task.

__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 10-15-2011, 08:42 PM   #3
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
Thx KIX

I will get my spanner out and see what I can find, but it may be a "tall order" for an electrical idiot like myself.

Fortunately I will have good friends from England over on a visit next week, and as it happens he is a former electrician in the BBC. I think I may put him to work once the jet-lag is gone.

Happycarz works for cookies - my friend works for red wine
__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Old 10-15-2011, 08:50 PM   #4
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,653
Pretty easy to tighten all the lugs.......even a caveman can do it.
Just make certain all electrical is discoed then remove panel covers and tighten the screws that hold the wires in the connection. There are 4 wires in 50 amp circuits. green = ground, red = 120 volt, black = 120 volt and white = neutral. My guess is your problem is with the white connections. Ignoring this issue can lead to electrical shock.....don't put this off.
__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 10-16-2011, 11:09 AM   #5
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
Took the lid off the ATS (automatic transfer switch).

Everything looks good (no scorched connections) and none of the connections could be tightened any further.

Problem must be lying somewhere else.
__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Old 10-16-2011, 01:19 PM   #6
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,653
Have you checked all the connections inside the shore power distribution panel?
__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 10-16-2011, 02:11 PM   #7
BCooke is online now
Senior Member
BCooke's Avatar
Join Date: Aug 2011
Posts: 491
Sounded like connections as I read it also. Either at supressor or circuit breaker panel. Last bad cord.... good luck finding that if it is. Tighten all screws while unplugged, a little better than snug.
Oh yea, have seen bad connection at main breaker also.
__________________
  Reply With Quote
   
Old 10-16-2011, 10:47 PM   #8
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,621
Have you checked the load center connections inside coach?
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 10-16-2011, 11:50 PM   #9
Arch Hoagland is offline
Senior Member
Arch Hoagland's Avatar


Workhorse Chassis Owner
Join Date: Aug 2002
Location: Clovis, CA, USA
Posts: 993
Are you seeing any fault codes on the Progressive Surge protector?

Open neutral and open ground conditions are supposed to be detected by that unit according to their webpage info. Are any codes displayed by the microprocessor readout panel?

If you don't find anything obvious I would suggest wiring around the surge protector and see if the problem disappears.
__________________
2004 Monaco La Palma 36DBD, W22, 8.1
7.1 MPG based on fuel used over 60,000 miles
2000 LEXUS RX300 FWD 22MPG 4020 LBS
  Reply With Quote
   
Old 10-17-2011, 08:40 AM   #10
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
Quote:
Originally Posted by "007" View Post
Have you checked the load center connections inside coach?
Not yet, but this is my next move.

Would a lose connection in one of my 110V sockets cause the same problem?
__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Old 10-17-2011, 08:42 AM   #11
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
Quote:
Originally Posted by Arch Hoagland View Post
Are you seeing any fault codes on the Progressive Surge protector?

Open neutral and open ground conditions are supposed to be detected by that unit according to their webpage info. Are any codes displayed by the microprocessor readout panel?

If you don't find anything obvious I would suggest wiring around the surge protector and see if the problem disappears.
No fault codes are displayed at the surge protector and the brief lack of power doesn't trip it ( it doesn't reset itself).
__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Old 10-17-2011, 09:01 AM   #12
puttin is online now
Senior Member
puttin's Avatar


Winnebago Owners Club
Ford Super Duty Owner
Join Date: Dec 2009
Posts: 544
I just want to clarify...The three rv sites are all in separate rv parks, right? If not, have you checked with anyone else close by? Second, if everything in the rig is affected, the problem must be very close to the output of the surge protector, or between that point and the main panel. Also, do you have an e.m.s? It may be possible that it's malfunctioning-although I think this would be way down the list of possibilities.
__________________
  Reply With Quote
   
Old 10-17-2011, 09:11 AM   #13
The Danes Are Coming is offline
Senior Member
The Danes Are Coming's Avatar


Monaco Owners Club
Texas Boomers Club
Join Date: Feb 2008
Location: Denmark and US
Posts: 946
Send a message via Skype™ to The Danes Are Coming
Quote:
Originally Posted by puttin View Post
I just want to clarify...The three rv sites are all in separate rv parks, right? If not, have you checked with anyone else close by? Second, if everything in the rig is affected, the problem must be very close to the output of the surge protector, or between that point and the main panel. Also, do you have an e.m.s? It may be possible that it's malfunctioning-although I think this would be way down the list of possibilities.
Yes - 3 seperate parks, and no one else I spoke to had noticed any problems.

Yes - everything is effected at the same time. Everything disappears at the same time and only very very brief.

Yes - I have got a "Smart EMS" by Intellitec.
__________________
The Great Dane
2007 Monaco Diplomat PAQ - 2007 Saturn Vue
Living in Denmark - visiting the US whenever possible. Honorary Texas Boomer
www.monacocoach.dk

  Reply With Quote
   
Old 10-17-2011, 09:41 AM   #14
Triker56 is offline
Senior Member
Triker56's Avatar


Fleetwood Owners Club
Join Date: Jun 2009
Posts: 988
It is more then a short brief cut off, if the DirecTV receiver goes through a reset.

Where I am at there are a few short cut offs 2-3 times a week. Only thing they affect is the front TV will shut off and has to be restarted. The DirecTV attached to it comes back on and still working.

The DirecTV does go through a reset if power is off long enough to put the surge guard into it's 2 minute reset mode. Also then the Micro clock & coffee maker clock need to be reset when power comes back. But never after the quick shut offs.

__________________
99 Discovery 34Q ISB with Banks PowerPack
HHR Toad
Fulltime Since "99"
  Reply With Quote
   
Reply

Tags
power


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No ac power from pole dennis46c Monaco Owner's Forum 6 06-01-2011 08:28 PM
Pure Power opens Navistar engine research center in South Carolina DriVer Navistar MaxxForce Engine Forum 0 01-26-2010 03:02 PM
Shore Power: Breaker Off before Connecting or Disconnecting Batman_777 MH-General Discussions & Problems 18 11-13-2009 04:10 PM
Generator Power Cutting In and Out nosnovi MH-General Discussions & Problems 7 09-29-2008 09:58 PM
50A Power and Amperage Workshop Excel Owner's Forum 16 01-17-2008 05:48 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 07:19 AM.