01-21-2020, 09:59 PM
|
#15
|
Senior Member
Join Date: Jul 2018
Posts: 4,925
|
Quote:
Originally Posted by cavie
|
^^THIS, although Code says the bond must be "at the point of service." That could be the meter base or the first service disconnect.
For those interested, it's in Article 250 of the National Electrical Code, NFPA70.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
01-21-2020, 10:49 PM
|
#16
|
Senior Member
Winnebago Owners Club Workhorse Chassis Owner
Join Date: May 2016
Location: Kamloops, BC, 60 miles from the Center of the Universe according to the Rinpoche, of the SF monks.
Posts: 7,397
|
Not saying my idea would be to code.
IF the current ground wire is the same size and insulation as the others, it will work.
Anyone ever been to India or any of many countries in Africa? You would think my suggestion would be super safe compared to that wiring system!
Put a GFI in the sub panel by the 50 amp outlet and be happy.
Happy Glamping.
__________________
Happy Glamping, Norman & Elna. 2008 Winnebago Adventurer 38J, W24, dozens of small thirsty ponies. Retired after 40 years wrenching on trucks! 2010 Ford Ranger toad with bicycles or KLR 650 in the back. Easy to spot an RVer, they always walk around with a screwdriver or wrench in one hand!
|
|
|
01-21-2020, 10:59 PM
|
#17
|
Senior Member
Alpine Owners Club
Join Date: Oct 2019
Location: Hoodsport Wa
Posts: 3,147
|
Convert it to 30a with existing.
Anything else is a dig up and new 4 wire svc.
Personally I like easy, and never had the need for 50a at home.
__________________
2000 Alpine 36 FDS #74058
04 Jeep Wrangler TJ
"On the road to find out..."
|
|
|
01-22-2020, 01:05 AM
|
#18
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Keep in mind that converting it to 120 volt 30 amps will mean you can no longer use it as a welder outlet. There will no longer be 240 volts available at that outlet.
|
|
|
01-22-2020, 05:01 AM
|
#19
|
Senior Member
Join Date: Jul 2018
Posts: 3,165
|
Quote:
Originally Posted by Unplanned
Not saying my idea would be to code.
IF the current ground wire is the same size and insulation as the others, it will work.
Anyone ever been to India or any of many countries in Africa? You would think my suggestion would be super safe compared to that wiring system!
Put a GFI in the sub panel by the 50 amp outlet and be happy.
Happy Glamping.
|
3rd World Country wiring.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
|
|
|
01-22-2020, 05:21 AM
|
#20
|
Registered User
Join Date: Oct 2016
Posts: 2,078
|
Interesting to follow
Prior to the 90's dependent on what area of the country you were in you didn't find ground wires on anything
Lot of dryers and as mentioned by the OP welder receptacles still in use with three wires and?
In many places based on building dates they are exempt from current codes until renovations
Same goes for GFCI
I am sure many grey beards can remember hot skin tingles on old (new at the time) RV'S
Sure the new and improved circuit wiring has saved a few shocks and maybe worse but we survived a lot of years without the ground wire
Using the properly installed ground rod is certainly a safe option even if it isn't bonded
What about sub panels?
|
|
|
01-22-2020, 06:01 AM
|
#21
|
Senior Member
Join Date: Sep 2018
Posts: 1,944
|
A note about ground rods - most normally installed grounding electrodes like ground rods can't pass enough current at 120V to trip even a 15A breaker. In fact, in addition to the prohibition mentioned by others above about the earth not being relied upon to pass fault current to open a breaker (or fuse) to clear the fault, there is a requirement for single electrodes (like a ground rod) to have a resistance to ground of 25 ohms or less, and if not, a second one has to be added at 6 ft spacing or more. And there is no performance requirement for those two rods or other made electrode system at that point.
At 120V, 25 ohms will only pass 4.8A. You could put a live conductor on that rod and do nothing but (maybe) chase a few night crawlers out. And it's difficult to measure the impedance to ground anyway, so most folks just drive a pair of rods and call it good.
Grounding electrodes are there for many reasons, specifically lightning, voltage stabilization, and to hold all things grounded to the same potential as the earth in that immediate vicinity, but working alone as a 'safety ground' is not actually one of them, and the NEC is quite clear on that point and has been since before my time.
__________________
Tom & Jeri
2018 Coachmen Galleria 24T Li3
|
|
|
01-22-2020, 10:46 AM
|
#22
|
Senior Member
Join Date: Jan 2009
Posts: 5,399
|
From the information at hand, converting to 30 amp service sounds like the best plan. I'll add that if it were me, I'd wrap white electrical tape around both ends of the relocated (from hot to neutral) wire so that there was no mistaking it as now being neutral.
__________________
03 Itasca Sunova, Workhorse P32 with the 8.1 and 4L85-E
|
|
|
01-22-2020, 11:13 AM
|
#23
|
Senior Member
Join Date: Jul 2011
Posts: 1,144
|
Don't, under any circumstances, connect that 220v plug to your RV. You will start a fire. I think you already know that. Rv's are wired differently. In a 50A system, they use two hots, like in house wiring, but they are connected through a box that separates the two hots so that it is not possible to get 220v power...only two 110v 50A lines.
It is possible to change your existing 30A plug to a 30A RV compatible 120v plug. You would leave the wire attached to the brass screw where it is. That will be your 110v hot. You would remove the wire from the silver screw. This will become your new neutral wire for the 30A 110v service. Now, the code says this must be a white insulation colored wire. You can wrap the wire insulation (inside the box) with white electrical tape to satisfy the code. Then disconnect the same wire from the breaker at the panel. Again, wrap it with white electrical tape in the panel box. (The panel should be turned off for this). Then you will connect this wire to the neutral bus. Now, at the other end, you will have a receptacle that has a hot, a neutral, and a ground. Test each plug terminal with your meter to check that you have 110v from hot to neutral, and 110v from hot to ground. No digging, not much work. You are done!
By the way, you did not say what size you wire is coming into the 3-way wall receptacle. It must be able to carry 30A. If not, then you need to dig and install wire of the correct size or change the plug to a standard 120v receptacle. If you are leaving the RV plugged in just to keep the batteries charged, you may be able to get away with this. If you are planning to use more power, you are back to considering putting in larger gage wire.
FYI...a neutral is a current-carrying wire. It is required to complete a circuit. A ground NEVER carries current unless there is a short somewhere. This was the original idea to protect people from getting shocked or electrocuted.
Good luck. Above all, be careful! If any of this scares you or you aren't comfortable with wiring, you may want to call an electrician.
__________________
2004 Tiffin Allegro 27.5 ft. P32 18,000 lb. GVW. 8.1 liter. Workhorse chassis built May 2002. 35,500 miles. 2012 Jeep Liberty Toad. RVi2 brake unit.
|
|
|
01-22-2020, 11:27 AM
|
#24
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Quote:
Originally Posted by Full.Monte
Rv's are wired differently. In a 50A system, they use two hots, like in house wiring, but they are connected through a box that separates the two hots so that it is not possible to get 220v power...only two 110v 50A lines.
.
|
A box that seperates the hots ?
Since the neutral is the same gauge as the hots, you can not seperate the hots without adding another neutral. Neutral only carries the difference between the 2 hots, nothing if draw is equal on both.
If you have a 50 amp RV, it will have 2 main breakers. If you measure the voltage between them it will read 240 volts.
http://www.myrv.us/electric/Pg/50amp_Service.htm
|
|
|
01-22-2020, 11:40 AM
|
#25
|
Senior Member
Join Date: Jul 2011
Posts: 1,144
|
Quote:
Originally Posted by twinboat
A box that seperates the hots ?
Since the neutral is the same gauge as the hots, you can not seperate the hots without adding another neutral. Neutral only carries the difference between the 2 hots, nothing if draw is equal on both.
If you have a 50 amp RV, it will have 2 main breakers. If you measure the voltage between them it will read 240 volts.
The 50-amp 120/240-volt 3 pole 4
|
The main 50A breaker has two 110v sides to it. Yes, they will measure 220v across the two hot sides of that breaker. But the whole thing is designed so you cannot put two breakers side-by-side to give 220v like you can in house wiring.
Yes, the neutral is the same size as the two hots, but since they are out of phase with each other, the neutral wire will actually be carrying less current than the total current coming through the two hot wires. If you imagine that the two hots were carrying the same current 180 degrees out of phase, there would be no current measured in the neutral wire. Since the wires are not carrying current at 180 degrees phase shift, but 120 degrees, there is some current being carried in the neutral wire, but not zero. From your comment, i think you understand this.
__________________
2004 Tiffin Allegro 27.5 ft. P32 18,000 lb. GVW. 8.1 liter. Workhorse chassis built May 2002. 35,500 miles. 2012 Jeep Liberty Toad. RVi2 brake unit.
|
|
|
01-22-2020, 12:17 PM
|
#26
|
Senior Member
Join Date: May 2019
Posts: 2,392
|
Quote:
Originally Posted by Full.Monte
The main 50A breaker has two 110v sides to it. Yes, they will measure 220v across the two hot sides of that breaker. But the whole thing is designed so you cannot put two breakers side-by-side to give 220v like you can in house wiring...
|
There are RVs which have 240v appliances and 240v circuits. It's not the most common way to do it, but there are those that do. Our first coach had a JennAir grill/range which ran on 240v.
__________________
Richard
1994 Excella 25-ft (Gertie)
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser
|
|
|
01-22-2020, 12:20 PM
|
#27
|
Senior Member
Join Date: Apr 2005
Posts: 4,461
|
Interesting enough Tesla sells an adapter for use with that receptacle. Of course the EVSE/car charger is a balanced 240 volt load. Unlike an RV.
|
|
|
01-22-2020, 12:41 PM
|
#28
|
Senior Member
Join Date: Jul 2011
Posts: 1,144
|
Quote:
Originally Posted by richard5933
There are RVs which have 240v appliances and 240v circuits. It's not the most common way to do it, but there are those that do. Our first coach had a JennAir grill/range which ran on 240v.
|
Yes, I've heard that. Those RV's are less common. The RV-style distribution boxes are 120v at each outlet or appliance. I've not had an RV that has 220 volt panel, but where they exist, there wouldn't be much difference from your main house panel. I guess the wisdom here is that you have to understand what you have before you start wiring something that could get you in trouble. That's why I have a Surge Guard to protect me from shade-tree electricians that may have wired the receptacles in RV campgrounds!
__________________
2004 Tiffin Allegro 27.5 ft. P32 18,000 lb. GVW. 8.1 liter. Workhorse chassis built May 2002. 35,500 miles. 2012 Jeep Liberty Toad. RVi2 brake unit.
|
|
|
|
|