Capability of Newmar Solar Prewire

I'm fairly certain my 2006 Newmar has the older 10 gauge prewire, but I will verify that this weekend. I plan on putting 4 Renogy 100w panels on the roof for a total of 400w and about 25 amps maximum down the prewire. At an estimated 30' wire run I only get about 1.5volt drop on the wire to the charge controller.

I read a lot of posts here about upgrading to 6 gauge versus using the older prewire. From all my calculations the 10 gauge is more than capable of handling the 25 amps and the voltage drop is minimal. I do; however, think that is about the maximum that I would feed down the prewire at 5.1 amps per panel.

Am I missing something other than most folks must be putting a lot more than 400w on the roof?
ColoradoBnd is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-21-2017, 07:30 AM   #2
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
Split the panels into two strings, double the voltage and then half the current down the wire. You will need a MPPT controller to handle the higher voltage conversion. This would overall be a better system than four panels in parallel to a PWM controller. Else you should run a larger wire.

I have three strings, each with five 100w panels. Three pair of #10 from the roof.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 07-21-2017, 08:00 AM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
The 1.5 voltage drop is 10% of your voltage. That's a lot in the 12 volt solar world.

On the slightly overcast day when your panels are producing 14 volts, your getting 12.5. That's less then battery voltage of 12.6.

2% or maybe 5% is acceptable with solar.
twinboat is offline   Reply With Quote
Old 07-21-2017, 12:26 PM   #4
Community Moderator
 
CountryFit's Avatar


 
Join Date: Sep 2011
Location: Between the Oceans
Posts: 8,026
Blog Entries: 4
one of my two sets of panels runs on 12 gauge with 720w, but at 126v nominal (3 240w panels at 42v in series). no problem.

your panels are small in foot print. you can arrange them at the space(s) where there will be no shading between 10am to 4pm, in series. you can even install many more panels if you want to.

(the set of wires at 12g was been used prior to my ownership of the coach. when i set up mine, i installed a pair of 6g wires for 6 panels in parallel at 42v for 1440w. then added more panels using the unused pair of 12g for 720w in series. both of my controllers are mppt - one can handle 96a and another can do 60a).
__________________
Steven & Polly
2000 Country Coach Intrigue 40' ISC 350
2018 Ford Explorer 4WD
CountryFit is offline   Reply With Quote
Old 07-22-2017, 05:29 AM   #5
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
Quote:
Originally Posted by vsheetz View Post
Split the panels into two strings, double the voltage and then half the current down the wire. You will need a MPPT controller to handle the higher voltage conversion. This would overall be a better system than four panels in parallel to a PWM controller. Else you should run a larger wire.

I have three strings, each with five 100w panels. Three pair of #10 from the roof.
This sounds like the best way for me. I am going to use the Magnum charge controller which is a MPPT controller. I am quite confident the wire can handle 10amps and the voltage drop goes down to 0.6V or ~2.5%. I really don't want to rewire the solar. I'm worried enough about the conversion from cable to HDMI. LOL. Thanks VSHEETZ.
ColoradoBnd is offline   Reply With Quote
Old 07-22-2017, 05:50 AM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
Here is a site with some info about solar.

http://www.affordable-solar.com/sola...sizing-charts/
twinboat is offline   Reply With Quote
Old 09-11-2017, 06:37 PM   #7
Senior Member
 
Join Date: Sep 2016
Location: SLC, UT
Posts: 1,172
You are correct, there are no issues with 10AWG while running multiple panels in series using a MPPT controller.

With a Renogy 400watt kit with Rover MPPT, I was seeing 72v and less then 6 amps to the controller.

Using an estimated 25' run, we were looking at .4% drop, which basically negligible.

Right now I'm to 600 watts - 2 parallel 300 watt strings - and I'm seeing more like 8-9amps at 56v...voltage drop again is way below 2%, though higher, at .9%.

Here is the site I use to make those calculations:
http://www.rapidtables.com/calc/wire...calculator.htm


There is a group out there that prefers running all panels in parallel @12V (really 18v) and running a PWM controller. As you can imagine with the low voltage, and potentially high amperages, wire size becomes much more important.
__________________
2017 F-350 6.7 Diesel, CCSB SRW - 2005 F350 6.0
2018 Alpine 3660FL - 2005 Alfa SYF30RLIK
--Full time 2016 to 2019-- Seasonal now
mrgrayaz is offline   Reply With Quote
Old 09-12-2017, 05:07 AM   #8
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2017
Location: Eden, UT
Posts: 418
Thanks!
ColoradoBnd is offline   Reply With Quote
Reply

Tags
newmar, solar



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help, absolutely confused w/ Zamp prewire solar stylinlp38 Technology: Internet, TV, Satellite, Cell Phones, etc. 1 06-21-2017 11:10 AM
Solar prewire crah Monaco Owner's Forum 7 12-09-2015 07:05 AM
Solar Prewire on Palazzo tamdle Palazzo Motorhomes 4 10-01-2015 06:57 AM
Solar Panel and/or CB prewire Johnontheroad Monaco Owner's Forum 1 06-10-2009 05:39 PM
Solar prewire KayLarGo Newmar Owner's Forum 16 11-23-2006 04:33 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:04 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.