How to HARDWIRE a GP3000HD inverter to TS501

I'll try again, I have a Go Power 3000HD inverter with a Parallax TS-501 transfer switch. Shore Power only.The inverter has 3 wires for hardwire 1 ground-----2 hot 60 volts each installed in the transfer switch. Do I need to put a jumper between those two wires to get 120 volts out the load side to the RV ?
Ronvada is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-16-2013, 07:29 PM   #2
Senior Member
 
Fleetwood Owners Club
Join Date: Dec 2004
Posts: 527
Where did the idea of having two 60 volt wires come from. I looked at the manual and also have not encountered such a thing.
targaboat is offline   Reply With Quote
Old 09-16-2013, 07:39 PM   #3
Senior Member
 
mahon1993's Avatar
 
Join Date: Mar 2010
Location: Fowlerville, Mich.
Posts: 606
60 volts???????????????????
__________________
2000 Monaco Diplomat 40PBD
2012 Grand Cherokee Limited
2008 FatBoy, three spoiled Great Danes and a cat.
mahon1993 is offline   Reply With Quote
Old 09-16-2013, 08:28 PM   #4
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
Yes, it's in the manual. Speaks to phasing and how this is normal for such inverters. The two 60's make 120vac. Connect as if the two wires were hot and neutral, matters not which is which. Grounding per the install instructions.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 09-16-2013, 08:53 PM   #5
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by vsheetz View Post
Yes, it's in the manual. Speaks to phasing and how this is normal for such inverters. The two 60's make 120vac. Connect as if the two wires were hot and neutral, matters not which is which. Grounding per the install instructions.
Yes, they are split phase at 60vac each. DO NOT CONNECT THEM TOGETHER. There is no neutral and each leg is hot ... as mentioned above they are treated as you would connect the "black" and "white" in a conventional home circuit.

Note the caution from the manual regarding bonding:

"The ground wire output is yellow and green, connect this first. The remaining two wires
are split phase at 60 volts each. This means they are both “HOT” and there is no neutral.
This is standard with most mod-sine wave inverters. Inverter operation will be fine for
mobile applications as long as the National Electrical Code is followed by ensuring the
neutral line is not bonded to ground anywhere in the system. See Grounding, Section
4.6."
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 09-17-2013, 04:48 AM   #6
Senior Member
 
mahon1993's Avatar
 
Join Date: Mar 2010
Location: Fowlerville, Mich.
Posts: 606
Quote:
Originally Posted by vsheetz View Post
Yes, it's in the manual. Speaks to phasing and how this is normal for such inverters. The two 60's make 120vac. Connect as if the two wires were hot and neutral, matters not which is which. Grounding per the install instructions.

OK. Now I understand.
__________________
2000 Monaco Diplomat 40PBD
2012 Grand Cherokee Limited
2008 FatBoy, three spoiled Great Danes and a cat.
mahon1993 is offline   Reply With Quote
Reply

Tags
inverter, p30



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.