Old 01-26-2019, 07:45 AM   #1
Senior Member
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 137
Maximum Recommended PV Array Voltage

I am getting quotes from different PV installation folks for a PV array I want to put on my RV roof. The last installer has quoted me an 8 panel system of 170W per panel for a total of 1360W. He has recommended wiring all of the panels in series which would result in 182V/9.32A (Voc/Isc) and 155V/8.79A (Vmpp/Vimpp). The Victron Energy 250/100 charge controller can support these high voltages just fine and deliver approximately 95A @ 14.6V to the battery bank (12V/840AH AGMs). I have 6AWG prewired to the roof.

My question is about safety. At 182V, we're not fooling around here. Everything will be fused and there will be breakers before and after the charge controller, but I'm wondering about the wisdom of this design.

What do people think? I don't know the electrical code recommendations here... and Googling hasn't helped. Input appreciated!
__________________

__________________
Steve & Karen Upp
2019 Newmar New Aire 3341
2019 Jeep Wrangler Unlimited Rubicon (4 cyl Turbo)
SteveUpp is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-26-2019, 08:08 AM   #2
Senior Member
 
Itinerant1's Avatar
 
Join Date: May 2017
Location: Itinerant
Posts: 434
It sounds like that guy does house installs and doesn't understand possible shading issues on an rv. Why not series/ parallel or parallel? What's his reasoning for such high voltage? Plenty of us out here with similar amount solar and not pushing high voltage and living as if we're plugged in to the grid but out in the bush.
__________________

Itinerant1 is offline   Reply With Quote
Old 01-26-2019, 09:07 AM   #3
Senior Member
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 137
Quote:
Originally Posted by Itinerant1 View Post
It sounds like that guy does house installs and doesn't understand possible shading issues on an rv. Why not series/ parallel or parallel? What's his reasoning for such high voltage? Plenty of us out here with similar amount solar and not pushing high voltage and living as if we're plugged in to the grid but out in the bush.
The installer is an RV installer... I think the argument is that if you have 8 panels, and 1 panel is shaded, isn't it just as likely as 2 panels shaded and unluckily shading panels on the separated series strings?

My rig has awnings up on the roof that are about 8 inches high. I'm going to have a racking system installed so the panels are completely in the clear of anything on the roof (e.g. A/Cs, antennas) that could shade any panel. So it is only external shading..which is entirely random and changes throughout the day.

Decisions .. decisions
__________________
Steve & Karen Upp
2019 Newmar New Aire 3341
2019 Jeep Wrangler Unlimited Rubicon (4 cyl Turbo)
SteveUpp is offline   Reply With Quote
Old 01-26-2019, 09:35 AM   #4
Senior Member
 
Timon's Avatar
 
Join Date: Jul 2014
Location: Tustin, CA
Posts: 1,008
Quote:
Originally Posted by SteveUpp View Post
I am getting quotes from different PV installation folks for a PV array I want to put on my RV roof. The last installer has quoted me an 8 panel system of 170W per panel for a total of 1360W. He has recommended wiring all of the panels in series which would result in 182V/9.32A (Voc/Isc) and 155V/8.79A (Vmpp/Vimpp). The Victron Energy 250/100 charge controller can support these high voltages just fine and deliver approximately 95A @ 14.6V to the battery bank (12V/840AH AGMs). I have 6AWG prewired to the roof.

My question is about safety. At 182V, we're not fooling around here. Everything will be fused and there will be breakers before and after the charge controller, but I'm wondering about the wisdom of this design.

What do people think? I don't know the electrical code recommendations here... and Googling hasn't helped. Input appreciated!
Since it's over 60VDC as long as they run the cables in conduit from the roof to the charger it's OK.

However I would suggest split the panels into two 4 panel strings which would keep the voltage down to under 100VDC then use two smaller Victron MPPT chargers. That way if you ever have a charger failure you only loose half of your panels.

Bottom line is that either will work just fine and don't worry about shading issues, see my comments below, as it seems your installer understand shading.

Quote:
Originally Posted by Itinerant1 View Post
It sounds like that guy does house installs and doesn't understand possible shading issues on an rv. Why not series/ parallel or parallel? What's his reasoning for such high voltage? Plenty of us out here with similar amount solar and not pushing high voltage and living as if we're plugged in to the grid but out in the bush.
I'm so tired of people repeating the falsehood that one should parallel series strings or run all panels parallel because it's totally the wrong way to do it. What they want to do it TOTALLY right.

Too many people, there are some here that do get it, here think that if a panel gets shaded in a series string you will loose the entire string. This is not correct, you only loose the one panel and in some cases on part of the panel.

The reason is that each group of cells, there are usually 2 or 3 groups in each panel, has a bypass diode which allows the other cells to keep producing power.

So if one panel gets shaded in a series string the other panels still produce power because the power flows through the bypass diode.

However, if you parallel two series strings and one panel gets shaded then you will loose that entire string because its total voltage drops below the other series string which has full sun. This is why it's best for each series string to have it's own MPPT controller.

The installers for home solar understand this. They typically have 20 or more panels in series but if some of the panels gets shaded the others still produce power. They also know that you should never parallel series strings so they will run an inverter per series string.

So flat out the best way to install panels is in series with each series string feeding it's own MPPT charge controller. You then parallel the outputs of the MPPT charge controllers.

FYI, Being an engineer and I understand this, it's basic electrical theory, so I challenge anyone to prove me wrong.
__________________
John (N6BER), Joyce, Lucas (Golden Retriever mix), Bella (Great Pyrenees) and Lance (Great Pyrenees).
Tustin, CA
Timon is offline   Reply With Quote
Old 01-26-2019, 10:19 AM   #5
Senior Member
 
Join Date: Jul 2018
Posts: 1,116
Quote:
Originally Posted by Timon View Post
Since it's over 60VDC as long as they run the cables in conduit from the roof to the charger it's OK.

However I would suggest split the panels into two 4 panel strings which would keep the voltage down to under 100VDC then use two smaller Victron MPPT chargers. That way if you ever have a charger failure you only loose half of your panels.

Bottom line is that either will work just fine and don't worry about shading issues, see my comments below, as it seems your installer understand shading.


I'm so tired of people repeating the falsehood that one should parallel series strings or run all panels parallel because it's totally the wrong way to do it. What they want to do it TOTALLY right.

Too many people, there are some here that do get it, here think that if a panel gets shaded in a series string you will loose the entire string. This is not correct, you only loose the one panel and in some cases on part of the panel.

The reason is that each group of cells, there are usually 2 or 3 groups in each panel, has a bypass diode which allows the other cells to keep producing power.

So if one panel gets shaded in a series string the other panels still produce power because the power flows through the bypass diode.

However, if you parallel two series strings and one panel gets shaded then you will loose that entire string because its total voltage drops below the other series string which has full sun. This is why it's best for each series string to have it's own MPPT controller.

The installers for home solar understand this. They typically have 20 or more panels in series but if some of the panels gets shaded the others still produce power. They also know that you should never parallel series strings so they will run an inverter per series string.

So flat out the best way to install panels is in series with each series string feeding it's own MPPT charge controller. You then parallel the outputs of the MPPT charge controllers.

FYI, Being an engineer and I understand this, it's basic electrical theory, so I challenge anyone to prove me wrong.
Exactly right, many years ago, panels did not have bypass diodes and you could lose a complete panel , and if in series, the whole string if any of them were partially shaded. I am running two strings of 3 panels ea in series to two mppt controllers. If one panel in either string is partially shaded, my voltage and current may fall a bit, but the non shaded areas and panels will still produce full power.
__________________
Foretravel tag axle 40 ft. 500 hp/1550 ft/lbs ism 1455 watts on the roof. 600 a/h's lithium down below.
jcussen is offline   Reply With Quote
Old 01-26-2019, 03:17 PM   #6
Senior Member


 
Monaco Owners Club
Join Date: Mar 2018
Location: Blairsville, GA & WPB, FL
Posts: 1,731
Send a message via ICQ to Ivylog
OP, you may want to look into my “800W solar install” posted here as I have the raised rails for the awnings and came up with a simple way of tilting them.
__________________
This post is my opinion, worth what you paid for it.
04 Dynasty 42 Sold in 2018 after 14 great years.
My New ride...08 HR Navigator 45
Ivylog is online now   Reply With Quote
Old 01-28-2019, 06:04 AM   #7
Member
 
Join Date: May 2018
Posts: 35
Series is the way to go. The higher voltage means you can use smaller wires which will be cheaper and easier to run. 180 volts really isn't anything unusual. I mean a lot of the world uses 240 ac for their domestic wiring and the insulation on the wire is probably rated for 600 volt. As long as the charge controller is good for it just treat it the way you would any of your 120 volt wiring and don't worry about it.
biohazard is offline   Reply With Quote
Old 02-18-2019, 12:36 PM   #8
Senior Member
 
Join Date: Jul 2016
Posts: 571
I am not sure if it matters or not, but a very common DC breaker used in solar installs are the midnight solar units.

These breakers are actually made by a different company, and relabeled by a number of sellers. At $20, the are a bargain.

IIRC, they are rated for 150 volt DC, which I think is based on the assumption of Voc at lowest expected temperature.

If you go down a technical path that will only work with one brand of components, it can be potentially troublesome in the future.

IMHO, it is worth the effort to wire the system in a way that it can stay within the 150 VDC limit.

Perhaps I am being too conservative.
__________________
Pleasanton, CA
harryn is offline   Reply With Quote
Old 02-18-2019, 08:21 PM   #9
Senior Member
 
Freightliner Owners Club
Join Date: Apr 2004
Location: Foothills, Yuma, Az
Posts: 958
see my signature -
__________________
Dale&Susan, 08 Alfa Gold, DaGirlsRv Blog
2015 F-150XLT_1600W Solar_880 AmpHr
Magnum_MSH 3812 & PT100
gatorcq is offline   Reply With Quote
Old 02-18-2019, 08:33 PM   #10
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 14,319
If system components are rated at XX then it's best not to exceed XX. There are times you can oversubscribe if its known the usage senario will not exceed.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 02-18-2019, 08:39 PM   #11
Senior Member
 
Join Date: Jul 2018
Posts: 1,116
Some home grid tie systems run to 600 volts in series. I run 120 volts on a 150 volt solar controller with no problems.
__________________
Foretravel tag axle 40 ft. 500 hp/1550 ft/lbs ism 1455 watts on the roof. 600 a/h's lithium down below.
jcussen is offline   Reply With Quote
Old 02-18-2019, 10:40 PM   #12
Senior Member
 
Timon's Avatar
 
Join Date: Jul 2014
Location: Tustin, CA
Posts: 1,008
I’d just stick with inline fuses located at the panel. Remember the fuse it to protect the wire so you want it at the source. Less expensive and more reliable. Use one per series string. If your rightunning more than one string don’t parallel the strings but use a MPPT controller for each series string.

https://www.amazon.com/Renogy-30-Wat.../dp/B00YG2IAQ4
Timon is offline   Reply With Quote
Old 02-18-2019, 11:54 PM   #13
Senior Member
 
Join Date: Jul 2016
Posts: 571
Quote:
Originally Posted by Timon View Post
Id just stick with inline fuses located at the panel. Remember the fuse it to protect the wire so you want it at the source. Less expensive and more reliable. Use one per series string. If your rightunning more than one string dont parallel the strings but use a MPPT controller for each series string.

https://www.amazon.com/Renogy-30-Wat.../dp/B00YG2IAQ4
I have never really been impressed with the renogy components, but it is still amazing to me that a company can sell a fuse holder and still have multiple complaints about quality. Look at the amazon reviews. Unbelievable.
__________________
Pleasanton, CA
harryn is offline   Reply With Quote
Old 02-19-2019, 08:57 AM   #14
Senior Member
 
Join Date: Jun 2004
Posts: 973
Quote:
Originally Posted by harryn View Post
I have never really been impressed with the renogy components, but it is still amazing to me that a company can sell a fuse holder and still have multiple complaints about quality. Look at the amazon reviews. Unbelievable.
I'm not a Renogy fan but 86% positive is a pretty good rating. After reading the other 14% I would chalk up most to purchaser issues.
__________________

__________________
2014 Southwind 32VS
2013 Nissan Xterra PRO-4X
PbdBlue is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using Renology 100 Watt Flexible Panels For Portable Array astrocamper Going Green 7 09-11-2018 07:35 AM
Limiting charge current for an oversized solar array? fadec RV Systems & Appliances 8 12-14-2016 07:20 PM
Limiting charge current for an oversized solar array? fadec RV Systems & Appliances 4 11-12-2016 06:45 AM
Solar array cahollister Alpine Coach Owner's Forum 3 11-17-2014 12:39 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:28 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.