Power switch on input side of controller?

Hello
I have two Kyocera 140 watt panels wired in parallel up on the roof of my rig. This panel array produces about 21 volts nominal and is wired into a Morningstar "Sun Saver" MPPT charge controller which is mounted inside the coach. The output of the controller is wired into my 4 x 6V battery series / parallel bank and the charge cable servicing the bank is fused with a 25 amp fuse. The system has worked well for the past two years.

The question I have is if it is necessary to install a fuse or some sort of switch on the input side of the controller (between the panels and the controller)? When I want to service the system now, I generally wait until the sun is not out, then disconnect one of the input lines to the controller. Has worked but is not the most elegant solution. Looking for ideas and guidance.

Thanks in advance

Jim
__________________
Jim Brinsfield
07 Fleetwood Excursion
jbrinsfi is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-30-2016, 08:32 AM   #2
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
You are correct. A DC circuit breaker on the input and output of the solar controller allows for isolation and servicing. My system is this way. Recommended.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 04-30-2016, 01:18 PM   #3
Senior Member
 
Fleetwood Owners Club
Join Date: May 2012
Posts: 181
Thanks Vince for your response to my questions. I suppose a fuse or in your case apparently, a re-settable breaker used on the input side to the charge controller, is only really being used as a switch isolator to conviently remove power from the charge controller. I don't really see how these devices would enhance safety in the installation in any way. A short or current overload between the fuse or breaker and the solar array is not going to be protected by this design and since these devices would be located near to the charge controller, there is not much there to protect. So I would think a simple DC switch would provide the same function as a fuse or breaker.
__________________
Jim Brinsfield
07 Fleetwood Excursion
jbrinsfi is offline   Reply With Quote
Old 04-30-2016, 01:49 PM   #4
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
You are correct that a breaker or fuse rated above the output would never blow.

Breakers become nessessary at the junction box, when multiple panels can backfeed 1 shorted panel above the amp capacity of its wire.

A simple switch is all that's needed.
twinboat is offline   Reply With Quote
Old 04-30-2016, 04:19 PM   #5
Senior Member


 
Join Date: Aug 2015
Posts: 6,911
An option, from handybob's site:

Quote:
I use the 250V cartridge type commercial fuses & holders. One of the folks I sent this to came up with a brilliant suggestion for fusing the solar leads; a two pole fused air conditioner electrical box with a pull-out disconnect. They are available 30 & 60 amp and have #4 lugs for the big wires we need to use. Connect the input from the panels to the controller on one side & the output from the controller to the batteries on the other. Disconnecting the entire solar system is then one simple motion. They are dependable and cheap, however the cheap one available at the box stores will not hold up to a constant DC load over about 25 amps, so look for a Midwest or GE.
__________________
Mark
2008 Holiday Rambler Admiral 30PDD (Ford F-53 chassis)
2009 Honda Fit Sport
l1v3fr33ord1 is online now   Reply With Quote
Old 05-01-2016, 07:48 AM   #6
Senior Member
 
Fleetwood Owners Club
Join Date: May 2012
Posts: 181
I have purchased a marine grade battery isolation switch which I will use at the input to the charge control. Its a bit more elegant than just disconnecting the lead from the array to the controller when I need to service the system but it serves the same function. Thanks for your responses and suggestions

Jim
__________________
Jim Brinsfield
07 Fleetwood Excursion
jbrinsfi is offline   Reply With Quote
Old 05-08-2016, 06:22 AM   #7
Member
 
Mustang65's Avatar
 
Join Date: Nov 2014
Location: Clearwater, FL
Posts: 40
When I set up my system I installed a breaker between the SOLAR and the Morningstar MPPT 60 SOLAR charge controller and one between the SOLAR charge controller and the batteries. More so for the convenience of isolating each of them when I need to trouble shoot a problem.

One point to remember is that Morningstar's documentation stresses that you disconnect the MPPT controller from the batteries before disconnecting the SOLAR panels, to avoid possible electrical damage to the MPPT controller.

I may eventually remove the breaker between the MPPT controller and replace it with a disconnect switch..

Don
__________________
2013 Jayco Eagle 284BHS,2012 Ford F150XLT, EcoBoost w/3.73, 250Watt Grape Solar Panel, MorningStar MPPT 60 Charge Controller, Trojan T145 Batteries (260Ah), 1500 Watt Ramsond PSI, EnGenius WI-FI extender
Mustang65 is offline   Reply With Quote
Old 05-09-2016, 06:30 AM   #8
Senior Member
 
Fleetwood Owners Club
Join Date: May 2012
Posts: 181
Quote:
Originally Posted by Mustang65 View Post
When I set up my system I installed a breaker between the SOLAR and the Morningstar MPPT 60 SOLAR charge controller and one between the SOLAR charge controller and the batteries. More so for the convenience of isolating each of them when I need to trouble shoot a problem.

One point to remember is that Morningstar's documentation stresses that you disconnect the MPPT controller from the batteries before disconnecting the SOLAR panels, to avoid possible electrical damage to the MPPT controller.

I may eventually remove the breaker between the MPPT controller and replace it with a disconnect switch..

Don
With the SunSaver MPT 15 controller, there is no such limitation regarding the order of disconnect. In fact on page 21 of the operators manual there is a specific note that states "The controller will not be damaged regardless of the sequence of connections". The recommended connection order suggests that you first install the load fuse (I do not use the "load" feature on my unit so no fuse there), then install the battery bank fuse to power up the controller, then connect the solar array input power. I believe this is more of a safety issue and a best practice sort of thing. In any event, I appreciate your note.

Jim
__________________
Jim Brinsfield
07 Fleetwood Excursion
jbrinsfi is offline   Reply With Quote
Old 05-11-2016, 08:08 PM   #9
Community Moderator
 
CountryFit's Avatar


 
Join Date: Sep 2011
Location: Between the Oceans
Posts: 8,026
Blog Entries: 4
interesting topic on connect/disconnect sequences... for my midnite controller, i always connect the battery to it first; when disconnect, i disconnect the solar to it first. that is based on the manual and verbal verification with their tech support.
__________________
Steven & Polly
2000 Country Coach Intrigue 40' ISC 350
2018 Ford Explorer 4WD
CountryFit is offline   Reply With Quote
Old 05-12-2016, 06:36 AM   #10
Senior Member
 
Fleetwood Owners Club
Join Date: May 2012
Posts: 181
Quote:
Originally Posted by CountryFit View Post
interesting topic on connect/disconnect sequences... for my midnite controller, i always connect the battery to it first; when disconnect, i disconnect the solar to it first. that is based on the manual and verbal verification with their tech support.
i think the sequence you outlined above is probably the best practice and is how I usually would operate my system.... battery is last off, first on.
__________________
Jim Brinsfield
07 Fleetwood Excursion
jbrinsfi is offline   Reply With Quote
Old 05-22-2016, 10:42 AM   #11
Member
 
Mustang65's Avatar
 
Join Date: Nov 2014
Location: Clearwater, FL
Posts: 40
Quote:
Originally Posted by Mustang65 View Post
When I set up my system I installed a breaker between the SOLAR and the Morningstar MPPT 60 SOLAR charge controller and one between the SOLAR charge controller and the batteries. More so for the convenience of isolating each of them when I need to trouble shoot a problem.

One point to remember is that Morningstar's documentation stresses that you disconnect the MPPT controller from the batteries before disconnecting the SOLAR panels, to avoid possible electrical damage to the MPPT controller.

I may eventually remove the breaker between the MPPT controller and replace it with a disconnect switch..

Don
I apologize for this... I can not believe that I said to disconnect the battery(s) first. The MPPT is powered by the batteries, and the SOLAR panels should always get disconnected first... I must have been having a real bad day when I wrote that... I normally read everything over and over and over again before hitting submit. Again I apologize for it

Don
__________________
2013 Jayco Eagle 284BHS,2012 Ford F150XLT, EcoBoost w/3.73, 250Watt Grape Solar Panel, MorningStar MPPT 60 Charge Controller, Trojan T145 Batteries (260Ah), 1500 Watt Ramsond PSI, EnGenius WI-FI extender
Mustang65 is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bounder: Location of Brake Controller Plug to install aux controller Heavy-13 Fleetwood Owner's Forum 2 04-30-2015 12:58 PM
Looking for Input on Side vs Rear Radiator XCR Chassis Pusherdiva Freightliner Motorhome Chassis Forum 13 12-10-2013 07:32 PM
Can this controller be sub'd for that controller? wildbill001 RV Systems & Appliances 2 09-06-2012 08:36 PM
Kelsey brake controller, any input on using it. partsman01 5th Wheel Discussion 8 03-05-2009 03:17 PM
Brake Controller Install/Windstar - Voltage on low side of stoplight switch camperjohn Pop Up, Tent Trailer and Teardrop Topics 11 04-27-2006 05:09 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:04 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.