Number eight won’t go any higher than your six panels, unless you wire them in strings of three.
The spec used for determining wire gauge and circuit protection is the Isc (short circuit amperage) Each string will add voltage...and current will remain the same. The number of strings you have will multiply amperage...
I believe the standard safety factors for planning wire size and circuit protections are...
>= Isc x 1.56
>= Voc x 1.2
And string fuse of Iz
So if you had and Isc for each string of 9.77a
If I get you correctly, you said parallel-series...
If you did three strings of two...the numbers would be...
3 x 9.77 x 1.56 = 45.7 amps for wire and fuse planning... closest fuse/breaker will be 50 most likely...and 8ga wire with 75 degree or better insulation will work. In the two panel string configuration this is maxed out for Your 8 gauge wire. No room to expand unless you keep the number of strings to 3...and place more panels on each string in series.
Let’s assume the Voc is 24.06v
You have two panels in each string so your voltage rating for the wire and fuse or breaker would need to be..
2 x 24.06 x 1.2 = 57.74v. Most wire is rated for 600v but when you get to higher voltages you have to be more selective for protection devices.
The inline string fuse should be paired to the Iz rating which I would guess is 15a.
So, if you want to go bigger in the future...and you insist on 6 gauge wire...the next logical step would be three strings of 3...
3 x 24.06Voc x 1.2 = 86.62v Rating or better.
So, plan you protective device for the higher voltage. Which will probably make you choose Solar specific products...
180w x 6 / 14.4v (nominal Absorbtion voltage). = 75A of Charge on a perfect STC rated panel day. Which is what I would plan for...but not what you should expect. Expect about 80 - 83 % of that. Like 60 amps of charge...
If you go to three strings of three... 180 x 9 x / 14.4 = 112.5 A... I believe you could still get away with a 150/100 Controller...but Inthink the 150/85 is too small.
For wire and protection on the battery side...
Amp x 1.25 is what they use for 100% rated breakers.
75 x 1.25 = 93.75. So, 100A protection 3awg wire...
If you go with the other ...logically the 150/100 Controller will limit you to 100a... so 100 x 1.25 = 125a. 125A protection and 2 awg wire if wire and terminations are rated for 90degrees or better...otherwise 1awg wire if 75 degree rated...
Here’s a link to a planning page...
http://www.cooperindustries.com/cont...-app-guide.pdf
If you have AGM or Lithium...charge rate is not something to worry about. Flooded Lead Acid batteries...you do.
My interstates require a max of C/10 where C is the back capacity.
If you have 4 6v batteries rated at 225aH for example and wired to make 2 12v battery equivalent...
Your capacity would be 2 x 225 = 450 aH
C/10. Would be 450/10=45.0 AH. Max rate.
This doesn’t mean you need to stop adding Solar at 45A...it just means that that’s all the battery can handle.
If you stick with Flooded Lead Acid...and have no way to regulate charge controller output based on actual battery shunt measurement. The 85a controller would be good enough...until you upgrade to AGM batteries.
I have the SmartSolar MPPT 150/100-TR with 8x 180w...and eight 232 aH FLA batteries. I have a 92.8A max rate for my FLA batteries. With an STC rating of 100A of Solar charge...I rarely see more than 86 amps...so no problem there.