Old 11-23-2015, 05:42 PM   #71
Senior Member
 
Join Date: Oct 2015
Location: Brighton, MI
Posts: 633
Quote:
Originally Posted by cb1000rider View Post
Thanks for all the discussion guys. Here's the plan:
  • rock saw the trench
  • pull a length of #8 copper cables ~100 ft, 4 of them
  • encase in 3/4" gray PVC conduit
  • 30A double-pole breaker on the break box
  • Run into a standard 50A RV-style outlet (outdoor, wet use), labelled "30 A limit".


Should run 2 ACs + no problem.

I appreciate the discussion and suggestions.

Sounds like a good plan. Hope there isn't another 5 pages saying your plan sucks because there's nothing wrong with it.
__________________

__________________
70ChevelleSS is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-23-2015, 11:00 PM   #72
Senior Member
 
Timon's Avatar
 
Join Date: Jul 2014
Location: Tustin, CA
Posts: 982
Do your self a favor and run 1" or 1 1/4" PVC. The cost difference is minor and it will be easier to pull cable through and lots easier if you later change your mind and repull 3 #6s and 1 #8. Remember wire you can repull but you can't change the conduit easily.

If you ever think you might want to run any sort of data or phone lay a 3/4" PVC 6" above the power conduit and just cap the ends. It will be there if you need it.

One last thing, get a roll of that yellow caution tape and lay it in the trench after you've put about 8 or 12" of fill over the conduit then fill the rest of the trench. If someone is digging they'll hit the tape long before they hit the conduit.

Even if you have an electrician do the work you will likely save money if you dig the trench. You can rent a DitchWitch for a day normally for less than $100 or so.

Have fun digging.
__________________

__________________
John (N6BER), Joyce, Lucas (Golden Retriever mix), Bella (Great Pyrenees) and Lance (Great Pyrenees).
Tustin, CA
Timon is offline   Reply With Quote
Old 11-23-2015, 11:18 PM   #73
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,477
Yep, I'd oversize the conduit as above. Not much more cost and you might be surprised if you have to rewire.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 11-25-2015, 07:50 PM   #74
Member
 
Flyerpicker's Avatar
 
National RV Owners Club
Newmar Owners Club
Join Date: Dec 2010
Posts: 41
Voice of experience here....I plugged my Newmar DP into a 30 amp/220 volt circuit, BECAUSE a decal in the power compartment said "110/220". So I assumed the internal power logic would figure it all out, and magically reduce the voltage. NOT.

That flawed thinking caused me to replace 2 televisions, a Keurig coffee maker, one roof top air conditioner motherboard, the circuit board in the microwave, an X-Box game controller, and a hand full of smaller items.

Just Sayin'
__________________
Carolyn, Jim, and Clara Allen
'05 Newmar Dutch Star
Fisherville, KY
Flyerpicker is offline   Reply With Quote
Old 11-25-2015, 07:53 PM   #75
Member
 
Flyerpicker's Avatar
 
National RV Owners Club
Newmar Owners Club
Join Date: Dec 2010
Posts: 41
Voice of experience here....I plugged my Newmar DP into a 30 amp/220 volt circuit, BECAUSE a decal in the power compartment said "110/220". So I assumed the internal power logic would figure it all out, and magically reduce the voltage. NOT.

That flawed thinking caused me to replace 2 televisions, a Keurig coffee maker, one roof top air conditioner motherboard, the circuit board in the microwave, an X-Box game controller, and a hand full of smaller items.

Just Sayin'
__________________
Carolyn, Jim, and Clara Allen
'05 Newmar Dutch Star
Fisherville, KY
Flyerpicker is offline   Reply With Quote
Old 11-25-2015, 08:35 PM   #76
Senior Member
 
dabrooks's Avatar
 
Tiffin Owners Club
Join Date: Sep 2012
Location: Maryland
Posts: 1,000
Quote:
Originally Posted by Flyerpicker View Post
Voice of experience here....I plugged my Newmar DP into a 30 amp/220 volt circuit, BECAUSE a decal in the power compartment said "110/220". So I assumed the internal power logic would figure it all out, and magically reduce the voltage. NOT.

That flawed thinking caused me to replace 2 televisions, a Keurig coffee maker, one roof top air conditioner motherboard, the circuit board in the microwave, an X-Box game controller, and a hand full of smaller items.

Just Sayin'
The OP was not asking or intending on plugging into a reg 30 amp 220 circuit with an adapter. He was asking about using a standard 50 amp RV outlet but using lighter gauge wire and 30 amp 2 pole breaker instead of a 50 amp 2 pole breaker. At least that's what I got when I read his question.
__________________
dabrooks is offline   Reply With Quote
Old 11-26-2015, 06:44 AM   #77
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 3,934
WOW--76 posts but think we got this one solved! New rule--you cant comment unless your have read the previous 76 posts. Notwithstanding local and national codes--the issue from the beginning was making sure you didnt cross a 120v leg onto the rigs neutral leg [240 volts] or reverse polarity--both/either will cause the "magic smoke." Given the declining state of many old campgrounds these days, the need for a high-end surge-protector like Progressive Industries is more important than ever.
__________________
Old Scout
2003 40' MDTS
Garden Ridge, Texas
Old Scout is offline   Reply With Quote
Old 11-26-2015, 06:49 AM   #78
Senior Member
 
Rockwood27's Avatar
 
Winnebago Owners Club
Nor'easters Club
Workhorse Chassis Owner
Join Date: Jun 2012
Location: Freedom, NH
Posts: 949
Or....for entertainment. ...start reading from the most recent post and go to the beginning. See how long it takes you to figure out what the OP's question wss!
__________________
Fran, Mary & Zoey (silver Cocker)
2006 Itasca Sunrise 35A, 2005 W-22, Allison 1000 5 speed
'13 Ford Focus ST or '10 Prius on Master Tow Dolly 80THD-SB or '00 Jeep Cherokee 4-down
Rockwood27 is offline   Reply With Quote
Old 11-26-2015, 08:56 AM   #79
Senior Member
 
CJ7ole's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 968
Yes a good surge protector will save your equipment, but you must not have the key in bypass mode. That error almost cost me my RV. 220 volts in equipment designed for 110 volts can and has (in my case) caused a fire.
__________________
Ole and Anne Anderson, Highland, Michigan
'02 Adventurer 32V, Ford F-53, ours since 4/08,Goodyears, Konis, SeeLevel, CHF
'84 CJ-7 , 5.3 Chevy, 3" lift, 33's, Detroit Locker, Fiberglas tub, winch, hi-lift
CJ7ole is offline   Reply With Quote
Old 12-01-2015, 02:27 PM   #80
Registered User
 
Join Date: Aug 2013
Posts: 307
Quote:
Originally Posted by Timon View Post
Do your self a favor and run 1" or 1 1/4" PVC. The cost difference is minor and it will be easier to pull cable through and lots easier if you later change your mind and repull 3 #6s and 1 #8. Remember wire you can repull but you can't change the conduit easily.

If you ever think you might want to run any sort of data or phone lay a 3/4" PVC 6" above the power conduit and just cap the ends. It will be there if you need it.

One last thing, get a roll of that yellow caution tape and lay it in the trench after you've put about 8 or 12" of fill over the conduit then fill the rest of the trench. If someone is digging they'll hit the tape long before they hit the conduit.

Even if you have an electrician do the work you will likely save money if you dig the trench. You can rent a DitchWitch for a day normally for less than $100 or so.

Have fun digging.

How about......dig a 2 foot deep ditch, pour about 8" of concrete in it, lay.....oh...just for grins & giggles.....1-1/2" pvc in it then, fill the rest of the ditch with concrete.
Naw, lets' go 3' deep, 2' wide, & center the pipe.
<edit> almost forgot.....fill the ditch with concrete
__________________
malexander is offline   Reply With Quote
Old 12-01-2015, 04:55 PM   #81
Senior Member
 
Join Date: Feb 2010
Posts: 4,493
Why concrete?

The yellow tape is fine and the utilities can map the wire just with current passing.

Do contact usa by calling 811 before any digging as it Could save your butt.

While talking with them as how to submit your drawings so it can be registered...not sure how that works as we had another department that handled that back in the day.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 12-01-2015, 09:41 PM   #82
Senior Member
 
Timon's Avatar
 
Join Date: Jul 2014
Location: Tustin, CA
Posts: 982
Quote:
Originally Posted by TQ60 View Post
Why concrete?

The yellow tape is fine and the utilities can map the wire just with current passing.

Do contact usa by calling 811 before any digging as it Could save your butt.

While talking with them as how to submit your drawings so it can be registered...not sure how that works as we had another department that handled that back in the day.
I agree, no need at all for any concrete. The depth and the schedule 40 PVC grey electrical conduit is more than enough.
__________________
John (N6BER), Joyce, Lucas (Golden Retriever mix), Bella (Great Pyrenees) and Lance (Great Pyrenees).
Tustin, CA
Timon is offline   Reply With Quote
Old 12-02-2015, 07:46 AM   #83
Senior Member
 
CJ7ole's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 968
Quote:
Originally Posted by malexander View Post
How about......dig a 2 foot deep ditch, pour about 8" of concrete in it, lay.....oh...just for grins & giggles.....1-1/2" pvc in it then, fill the rest of the ditch with concrete.
Naw, lets' go 3' deep, 2' wide, & center the pipe.
<edit> almost forgot.....fill the ditch with concrete
Trouble recognizing sarcasm guys?

I do pity having to get a rock saw just to get a 2' deep trench though. That must cost a bunch.
__________________
Ole and Anne Anderson, Highland, Michigan
'02 Adventurer 32V, Ford F-53, ours since 4/08,Goodyears, Konis, SeeLevel, CHF
'84 CJ-7 , 5.3 Chevy, 3" lift, 33's, Detroit Locker, Fiberglas tub, winch, hi-lift
CJ7ole is offline   Reply With Quote
Old 12-02-2015, 09:08 AM   #84
Senior Member
 
OLYLEN's Avatar
 
Monaco Owners Club
Join Date: Jan 2008
Location: Olympia, Wa
Posts: 2,337
What I think, how I screwed up, how I heard it was done, now 84 posts to pull 4 wires a 100'. JMO

LEN
__________________

__________________
2004 Clss C 31' Winnebgo
OLYLEN is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50A or 30A?? TheMatrix 5th Wheel Discussion 17 02-17-2015 05:25 PM
Using 30A and 50A service simultaneously: a terrible idea? markaeric RV Systems & Appliances 42 12-21-2014 02:11 PM
30A or 50A to garage mothgrey Class A Motorhome Discussions 31 11-21-2013 05:14 PM
30A to 50A Adapter Causes MH Fire Pusherman Class A Motorhome Discussions 173 09-02-2013 05:33 PM
Bounder: 30A to 50A converting Sonnydale Fleetwood Products Owner's Forum 20 06-11-2013 10:08 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.