50 amp service for RV

Have existing 42 x 60 ft building to be used to house 4023 dsdp. My problem is that it presently has sufficent wiring for lights and a few recept. I would like to up grade to a 50 amp rv service. I now have number 6 copper. The meter with 200 amp service is 420 ft away. Can someone tell me what size of direct bury I can run for this distence (alum)? Thanks in advance. Roger
__________________

__________________
Rog1965char is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-15-2014, 11:10 PM   #2
Senior Member
 
dsbear's Avatar
 
Join Date: Jan 2013
Posts: 628
Roger,

I'm in the process of building an RV garage and have been looking into electric and I have about a 200 ft run. What I have discovered is its much less expensive to have a second meter set.
__________________

__________________
dsbear is offline   Reply With Quote
Old 05-15-2014, 11:57 PM   #3
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 3,329
There are many charts on the web for this. If your current wiring is in a 2" conduit, then it would be an easy retro. Pull the old wire out with a mule tape attached, then pull the new wire in. Much easier if you have a pull box or two in the middle.

I used #6 copper. I am slightly beyond the outer limits on length for #6 (165'), but I will never come close to using 50A on either leg.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Trojan T-105's
2014 F150 4x4 Crew Cab Platinum 157" WB
Roadmaster Blackhawk 2, RVI2 Brake System
Scottybdivin is offline   Reply With Quote
Old 05-16-2014, 12:22 AM   #4
Senior Member
 
stink's Avatar
 
Join Date: Apr 2012
Posts: 1,414
You say you want to run that in aluminum? Might need 0 or 00 for that distance. I would check with your local building inspector office.
__________________
Dave and Laura & two cats
02 Discovery with Accord toad
retired auto rv tech and teacher, wife rt nurse
stink is offline   Reply With Quote
Old 05-16-2014, 11:00 AM   #5
Senior Member
 
Join Date: Jan 2000
Location: Castle Rock Co USA
Posts: 381
Seems I ran 0 aluminum wire to feed my sub panel-direct bury is the way to go,save a lot over copper.For your area check local laws,some are a pain.
__________________
2011 Montana-3400RL
Towed by[B]'99 F-350 SD PSD DRW Lariat
RichR is offline   Reply With Quote
Old 05-16-2014, 11:05 AM   #6
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 11,773
Do you really need 50a service there? Only if planning to run multiple air conditioning on the coach.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is online now   Reply With Quote
Old 05-16-2014, 11:58 AM   #7
Senior Member
 
Retired and Happy's Avatar
 
Join Date: Feb 2004
Location: Stone Mountain, GA
Posts: 941
Running my 50A coach on a 30A circuit and both A/C's have been running at times. Of course the power company came by this week and told me my meter had self-reported overheating. If I didn't resolve the problem, they would have to disconnect the meter due to fire danger. I think I will turn off one AC and raise the temp on the other to ease the draw. I also had my S&B A/C cleaned yesterday and the draw from that went down. We'll see how it helps when the outside temp goes back up. It's cold here today.
__________________
Ken, Judy, and the Angels--2005 Fleetwood Southwind--2008 Cargo Trailer--2003 EZGO Golf Cart
Retired and Happy is offline   Reply With Quote
Old 05-16-2014, 11:59 AM   #8
Senior Member
 
lanerd's Avatar
 
Tiffin Owners Club
Join Date: Apr 2009
Location: Home in warm Sou Calif for the winter.
Posts: 1,399
You must, of course, go with the local, county, state building codes. Whatever they require, that's what you need.

I too, would just replace the existing wire with new (larger) if at all possible. If you know where the current conduit is located, you can measure off 100' increments and install pull boxes to help with the new wire .

I recently built my rv garage (30x50) and supplied 50amps to it but only used a 30amp breaker for the mh's power. The rest I use for 20amp outlets and lots of lights. I ran new conduit (abs) wire (#6 copper) about 75'. I also keep my truck and two quads in the garage and have them on battery minders for the five months we are gone.

Ron
__________________
Ron, Sandie and Lilly
2013 Tiffin Phaeton 42LH 400 ISL | 2011 GMC Terrain SLT-2
Roadmaster All Terrain | US Gear Unified Brake System | Pressure Pro
lanerd is offline   Reply With Quote
Old 05-16-2014, 12:52 PM   #9
Senior Member
 
Join Date: Feb 2010
Posts: 4,492
Make tge trip to the inspectors office and ask about installeng a sub panel and how large you can go.

Panels are dirt cheap and cost of wire for bigger panel not as much more considering you will never need to do this again.

Labor biggest expense here and a trench is a trench...

The inspectors office can advise exactly what wire and panel size then you can get proper quotes without having some gc charge you for engineering that may not be correct


We installed 200 amp sub panel because it was only 77 bucks with a good selection of breakers, it does not have main breaker inside so main disconnect at main panel.

You may need a disconnect at the panel thus needing to visit the inspector.

NEC the n is for national but local jurisdictions often have additional requirements and the expense here due to distance simply is not worth trusting any opinion other than the inspector.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 05-16-2014, 01:14 PM   #10
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,614
Most if not all inspector offices or city engineering offices will NOT give you any instruction on what is needed. You may be able to apply for a home owners permit but usually the minute you start asking questions as how to do the job or what do I need, they'll probably tell you to hire a licensed contractor. If you don't know this on your own I suggest hiring an electrical contractor to do the job. A city inspector is not going to make himself or his office liable for something that you install wrong by maybe not understanding what they're explaining to you. Hire it done and all will be safe.
__________________
Steve & Sally / HiTee & Hudson Our Little Poms / Heidi & Houston Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Old 05-16-2014, 01:26 PM   #11
Senior Member
 
BCooke's Avatar
 
Join Date: Aug 2011
Posts: 1,523
Quote:
Originally Posted by Rog1965char View Post
Have existing 42 x 60 ft building to be used to house 4023 dsdp. My problem is that it presently has sufficent wiring for lights and a few recept. I would like to up grade to a 50 amp rv service. I now have number 6 copper. The meter with 200 amp service is 420 ft away. Can someone tell me what size of direct bury I can run for this distence (alum)? Thanks in advance. Roger
As mentioned get a local electrician/elect eng.

Generally, with out all of the required calculations (software is expensive, and I am not a engineer), you are looking somewhere around a #1 wire. The 420 feet kills it.
A 120 volt 50 amp through #6 at 420 feet you are looking around 20 volt drop.
__________________
2017 F350 Lariat Diesel Dually, White, Hitch Kit.
2013 Dutchman Voltage 3200 Epic II 5th wheel.
BCooke is offline   Reply With Quote
Old 05-16-2014, 03:16 PM   #12
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
NECMichigan National Electrical Code Update 2005 2008 2011

The above link will help you but as others have posted check your local requirements.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Old 05-16-2014, 07:48 PM   #13
Senior Member
 
Join Date: Sep 2013
Location: Az
Posts: 130
50 amp service for rv

First of all I would like to thank everyone for all the input on this matter. I had the utility co out today to locate the underground service from transformer to meter which they did. He would not locate any other wires that I had trenched in, stating that they are only responsible for the main service and that any future work that I did would be up to me. I have my own equipment such as backhoe and trencher but want to make sure that I am up to code since many things has changed over the last 5- 10 years. This being said I will contact a license electrician and pay him for his advice and guidance on this. At this point I am leaning toward using 00 alum (direct bury) and maybe upgrading my pedestal (meter socket and panel so that I will have more room for additional breakers. Again thanks for all the help. Roger
__________________
Rog1965char is offline   Reply With Quote
Old 05-17-2014, 07:30 AM   #14
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 3,329
For the life of me, I don't know why anyone would place direct bury electrical wire unless it is low voltage control wiring. Often times, the additional shielding drives the price higher than the cost of pvc conduit. If anything ever happens to it, you are stuck. I recently added a 2500 gal storage tank and booster pump at one of my water wells. Wiring was too small for the 1 HP booster pump and well pump together. Pulled the old wire out and installed the larger wire (350'). If I hadn't used conduit, I would have had to start over again. The 8 year old wire was in perfect shape and most of it has been reassigned.
__________________

__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Trojan T-105's
2014 F150 4x4 Crew Cab Platinum 157" WB
Roadmaster Blackhawk 2, RVI2 Brake System
Scottybdivin is offline   Reply With Quote
Reply

Tags
service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where Did the 15 -20 amp Outlet Go? Bigd9 iRV2.com General Discussion 7 04-06-2014 08:48 AM
Service??? Bespos Class A Motorhome Discussions 18 01-30-2014 11:30 AM
Weak House Batteries after Service Mystery Class A Motorhome Discussions 13 01-11-2014 07:36 PM
RV Service Contract Companies golden iRV2.com General Discussion 2 01-04-2014 11:12 PM
20 amp service question............ Fred420 Class A Motorhome Discussions 13 09-19-2013 07:49 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:53 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.