Old 05-09-2014, 08:23 PM   #29
Senior Member
 
Brockx's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: Punta Gorda FL.
Posts: 2,631
Quote:
Originally Posted by Fl_Richard View Post
Funny... But I use the Fleetwood energy management system that they have been un-successful in using.....
Yeah.....I sure don't have any complaints either............
__________________

__________________
2008 Bounder 38P F53 24/30K V10, 2013 Kia Soul Basic 6 speed manual, Ready Brake Elite tow system (previous equipment 1996 Pace Arrow Vision w/Acme Dolly)
Brockx is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-10-2014, 05:51 AM   #30
Senior Member
 
Triker56's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2009
Posts: 3,950
Quote:
Originally Posted by Alan_Hepburn View Post
Most manufacturers try to match the generator to the incoming supply as best as they can, so a 30A coach would have a 3500W generator while a 50A coach would have a 5500W generator.
Hummmm!! I wonder why Fleetwood would put a over kill LPG 6.5W(54.2AMP) in my 30 AMP MH? It has no problem running a 13.5K & 15K AC's the same time.

And they also had a optional 7.5W diesel for the same model 30 AMP MH's.
__________________

__________________
99 Discovery 34Q ISB
2014 MKS AWD EcoBoost Toad
Fulltime Since "99"
Triker56 is offline   Reply With Quote
Old 05-10-2014, 05:58 AM   #31
Senior Member
 
Brockx's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: Punta Gorda FL.
Posts: 2,631
Quote:
Originally Posted by Triker56 View Post
Hummmm!! I wonder why Fleetwood would put a over kill LPG 6.5W(54.2AMP) in my 30 AMP MH? It has no problem running a 13.5K & 15K AC's the same time.

And they also had a optional 7.5W diesel for the same model 30 AMP MH's.
Mine has a 5.0 more than adequate for running the whole show. Don't understand the earlier 3500 comment, never seen that with 2 airs, but I'm still green.
__________________
2008 Bounder 38P F53 24/30K V10, 2013 Kia Soul Basic 6 speed manual, Ready Brake Elite tow system (previous equipment 1996 Pace Arrow Vision w/Acme Dolly)
Brockx is offline   Reply With Quote
Old 05-10-2014, 06:25 AM   #32
Senior Member
 
Join Date: Dec 2013
Posts: 471
I would not just get a 50amp adaptor for the 30amp without having someone that knows what they are doing to make sure the wiring is capable of 50amps.
__________________
HuntingHawk is offline   Reply With Quote
Old 05-10-2014, 09:24 AM   #33
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by HuntingHawk View Post
I would not just get a 50amp adaptor for the 30amp without having someone that knows what they are doing to make sure the wiring is capable of 50amps.
HuntingHawk
Most, (all?), campground pedestals with a 50A receptacle also have a 30A receptacle .
No adapter is needed to connect a 30A RV to a 30A receptacle.

However, if there is only a 50A receptacle in the pedestal, a 50A male to 30A female adapter is required to connect a 30A RV.
In that case the pedestal breaker may not adequately protect the 30A cord, (but the circuit breakers in the RVs electrical panel will protect the wiring in the RV).

To connect a 50A RV to a 30A receptacle, a 30A male to 50A female adapter is required.
If/when a 50A RV is connected to a 30A receptacle not everything in the RV can be operated with the 30 available amps.

BTW, years ago some 30A RVs with 2 roof airs had a manual "front/rear A/C switch" somewhere in the cabin.

Mel
__________________
mel s is offline   Reply With Quote
Old 05-10-2014, 09:37 AM   #34
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,206
Quote:
Originally Posted by HuntingHawk View Post
I would not just get a 50amp adaptor for the 30amp without having someone that knows what they are doing to make sure the wiring is capable of 50amps.
The 50 amp at the pedestal indicates service available. It will still only provide the current that your system demands. Your electrical system (circuit breakers) still protect your equipment from exceeding 30 amps.
Using the 50 to 30 amp adapter is done to hopefully provide a cleaner connection to the heavier wiring used in the 50 amp pedestal circuit.
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 05-10-2014, 09:48 AM   #35
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 4,383
Quote:
Originally Posted by Alan_Hepburn View Post
Doesn't clearly answer the question. If you connect to a 30A shore supply you will have 30A service - no matter if your RV is set up for 30A service, 50A service, or 100A service. The question was "How is your RV built?" Most manufacturers try to match the generator to the incoming supply as best as they can, so a 30A coach would have a 3500W generator while a 50A coach would have a 5500W generator.
I have worked on thousands of motorhomes and all the motorhomes with two AC's and thirty amps service had a 5500 or 6500 generator to run both AC's at the same time. I have never seen a motorhome with two AC's with a 3500 watt generator.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2012 Honda Civic toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is online now   Reply With Quote
Old 05-10-2014, 09:54 AM   #36
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Quote:
Originally Posted by MikeLeonard View Post

'07 National Surfside Class A motorhome.

When I'm hooked up to 30 amp shore power, I can only get one of my AC's to operate. When I unplug the shore line and turn on my generator, I can get both AC's to operate. I don't want to run my generator. Is there any way to get both AC's to operate from shore power?

Is there any benefit to running the generator while plugged in to shore power? Is it even safe to do so?

Thanks.

Mike
The simplest cheapest and easiest method to run both A/C's is to run one using your regular 30 amp shore power cord. The second A/C can be powered using the 20 amp outlet at the pedestal along with a 12 gauge extension cord.

You would have to run romex from your rear A/C or the A/C sub panel CB to a dedicated junction box at the rear of the coach or whatever compartment your shore cable goes into. Then using the extension cord to plug into the pedestal and the junction box.

You now have power to run your second A/C.

Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 05-10-2014, 10:11 AM   #37
Senior Member
 
anotherone's Avatar
 
Join Date: Jun 2006
Location: brooksville fl
Posts: 662
Quote:
Originally Posted by ga traveler View Post
I have worked on thousands of motorhomes and all the motorhomes with two AC's and thirty amps service had a 5500 or 6500 generator to run both AC's at the same time. I have never seen a motorhome with two AC's with a 3500 watt generator.
when I read that I said oh boy the miss information on the internet is amusing and really can mess things up for the novice. Glad you caught it too.
__________________
2016 f150 4x4, 2 pia horses! 2016 phaeton 40 ah and 2017 harley road glide ultra
anotherone is offline   Reply With Quote
Old 05-10-2014, 11:18 AM   #38
Senior Member
 
Brockx's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: Punta Gorda FL.
Posts: 2,631
Quote:
Originally Posted by HuntingHawk View Post
I would not just get a 50amp adaptor for the 30amp without having someone that knows what they are doing to make sure the wiring is capable of 50amps.

The adaptor does not put 50 amps into the coach. It puts 2 30 amp circuits into parallel, kind of like 2 12 volt batteries in parallel gives you 12 volts not 24. That's not a real great explanation someone else will probably come along and do better.
__________________
2008 Bounder 38P F53 24/30K V10, 2013 Kia Soul Basic 6 speed manual, Ready Brake Elite tow system (previous equipment 1996 Pace Arrow Vision w/Acme Dolly)
Brockx is offline   Reply With Quote
Old 05-10-2014, 12:35 PM   #39
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
50 amp versus 30 amp has been discussed SO many times previously that my fingers are now stubs.

50 amp service is really 100 amps total on two separate out of phase 120 VAC Lines, L-1 and L-2.

A 50 amp to 30 amp dogbone simply takes only ONE of the 120 VAC lines, either L-1 or L-2, NOT both and uses that 120 VAC to power the 30 amp coach.

The 30 amp coach and its CB's are still only 30 amp 120 VAC regardless of how much 120 VAC you try to stuff into the coach.

Another way to look at it is this:

A RV 30 amp 120 VAC supply has 3600 watts of power available to use - 120 x 30 = 3600.

A RV 50 amp 120 VAC supply has 12000 watts of power available to use - (L-1)50 x 120 + (L-2)50 x 120 = 12000.

Here is a web site that you should bookmark that is VERY helpful to RVer's. It will explain EVERYTHING you will ever need to know about RV Electric.

Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 05-10-2014, 01:16 PM   #40
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,206
Richard, saw this diagram, it may help the explanation.. The 30 amp adapter does not use 1 leg of the 50 amp circuit..
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 05-10-2014, 05:31 PM   #41
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Hooligan,

Your post contradicts the drawing that you have posted.

Your drawing IS correct and IS only using one Leg of the 50 amp plug.



Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 05-10-2014, 05:58 PM   #42
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by Dr4Film View Post
Hooligan,
Your post contradicts the drawing that you have posted.
Your drawing IS correct and IS only using one Leg of the 50 amp plug.
Dr4Film ----- Richard
Dr4Film
Correct
His drawing clearly shows only 3 wires:
1 Neutral--(Gray)
1 Ground--(Green)
1 Hot Leg--(Black)
__________________

__________________
mel s is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Water Heater does Not Work Unless Plugged Into Shore Power jimfryar Newmar Owner's Forum 4 03-23-2014 11:23 PM
Install 2nd shore power connector wincrasher Travel Trailer Discussion 1 03-18-2014 10:50 PM
15/20 Amp Shore Power Rehbergl Roadmaster Motorhome Chassis Forum 4 03-05-2014 07:07 PM
Question About Chassis Battery Charging on Shore Power TandCplusRV RV Systems & Appliances 15 02-05-2014 11:57 AM
Bounder: Shore Power issue Tom Dufresne Fleetwood Products Owner's Forum 10 08-26-2013 07:03 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:26 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.