Old 05-10-2014, 09:37 PM   #43
Member
 
Join Date: Dec 2011
Posts: 35
Quote:
Originally Posted by Alan_Hepburn View Post
Doesn't clearly answer the question. If you connect to a 30A shore supply you will have 30A service - no matter if your RV is set up for 30A service, 50A service, or 100A service. The question was "How is your RV built?" Most manufacturers try to match the generator to the incoming supply as best as they can, so a 30A coach would have a 3500W generator while a 50A coach would have a 5500W generator.
Well, my coach has a 3 pronged powercord so I've always assumed it's a 30 amp rig. I wonder if it has the wrong cord installed? My owner's manual (copied from internet) say my year/model coach is supposed to have 50 amp service and I know I have a 5500W generator. Hmmmm.....
__________________

__________________
MikeLeonard is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-10-2014, 09:56 PM   #44
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Mike,

Trust me you would need more than a 5500 KW generator to run a 50 amp coach.

My 50 amp 2002 Monaco came with a 7500 KW Onan which is small compared to the 8000 KW Onan's that were put into the later model Windsor and Camelots.

Some of the bigger 50 amp coaches with 3 A/C's have the 10000 or 12000 KW Onan's.

If you have a three prong plug on your shore power cable then it is a 30 amp coach.

You should also be able to tell by looking at your main electrical panel to see how the circuit breakers are arranged.

Dr4Film ----- Richard
__________________

__________________
Dr4Film is offline   Reply With Quote
Old 05-11-2014, 07:31 AM   #45
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by Dr4Film View Post
You should also be able to tell by looking at your main electrical panel to see how the circuit breakers are arranged.
Dr4Film ----- Richard
Richard
Correct
The "main breaker", in the electrical panel of my "50A coach", is a double pole 50A breaker.
(My earlier "30A class C" had a single pole 30A main breaker).
Mel
'96 Safari
__________________
mel s is offline   Reply With Quote
Old 05-11-2014, 07:47 AM   #46
Senior Member
 
Join Date: Dec 2013
Posts: 471
45.8amps would be the rating for a 5500watt generator.

I=P/E
__________________
HuntingHawk is offline   Reply With Quote
Old 05-11-2014, 08:21 AM   #47
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Onan Generator Specs

And again 45 amp would be what you would find in a typical 30 amp coach. That is why people with 30 amp coaches with 2 A/C's have no problem running both A/C's along with anything else that want to that needs 120 VAC power.

Attached is a brochure listing the manufacturer specs of the 6000 KW, 7500 KW and the 8000 KW Onan generators.

You can decide what is what.

Dr4Film ----- Richard
Attached Files
File Type: pdf Cummins Onan HDKAT Features & Benefits.pdf (152.4 KB, 31 views)
__________________
Dr4Film is offline   Reply With Quote
Old 05-11-2014, 10:21 AM   #48
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,206
Quote:
Originally Posted by Dr4Film View Post
Hooligan,
Your drawing IS correct and IS only using one Leg of the 50 amp plug.
Dr4Film ----- Richard
Communications---Must be my southern accent---Yes- It is only using one leg of the plug, therefore it does not use the other leg of that plug. My plug is still half full...
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 05-11-2014, 01:22 PM   #49
Senior Member
 
Brockx's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: Punta Gorda FL.
Posts: 2,631
My apology to anyone who read my screwed up version of the 50/30 adaptor plug wiring. It was explained to me that way by an electrician, the same one who wired 220V to the plug he installed in his garage for his MH.
__________________
2008 Bounder 38P F53 24/30K V10, 2013 Kia Soul Basic 6 speed manual, Ready Brake Elite tow system (previous equipment 1996 Pace Arrow Vision w/Acme Dolly)
Brockx is offline   Reply With Quote
Old 05-14-2014, 03:37 PM   #50
Senior Member
 
Alan_Hepburn's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Feb 2000
Location: San Jose, Ca, USA
Posts: 1,045
Quote:
Originally Posted by Dr4Film View Post
Mike,

Trust me you would need more than a 5500 KW generator to run a 50 amp coach.
A 30 Amp coach will generally NEVER use more than 3600 Watts - so there is no issue with the manufacturers cutting corners by not installing more generator than can be used by the coach. On the other hand, a 50A coach is capable of consuming 12KW of power, but most 50A gas coaches are delivered with a 5500W generator, mostly because it's cheaper, and the coach CAN get by on a total of 50A since the manufacturer sets it up so that most of the load is supplied by one side of the generator, and the second AC is supplied from a second winding in the generator. Of course, high end coaches, both gas and diesel, come equipped with 7500W, 12KW, or even 15KW generators because their electrical needs are greater - most of them have all-electric appliances, large inverters, and other electricity hogs so the extra power is appreciated by the owners.

Running a 50A coach on a 5500W generator is NOT impossible - we've had both ACs running, the water heater, fridge, TV, DirecTV receiver, laptops, hotspot, and other loads running in ours and the generator had no problem keeping up with the demand.
__________________
Alan Hepburn - San Jose, Ca
2007 Bounder 35E being pushed by a 2008 smart fortwo Passion
Good Sam Member #566004 * FMCA Member #F431612
Alan_Hepburn is offline   Reply With Quote
Old 05-15-2014, 08:12 AM   #51
Member
 
Join Date: Dec 2011
Posts: 35
All I want to know is how to keep my rig cool in the summer, especially this summer in the American Southwest. I have 30 amp service when plugged in. Our rig never got cool last summer during the day when plugged in on our trip to the Florida Keys.

Do most RV parks let you run your generator when parked? If so, do I need to buy a snorkle?

I'd much rather not have to run my generator. Can I simply put my fridge on gas power thus freeing up more power for both AC's? Do I need to turn off all othe electrical loads?
__________________
MikeLeonard is offline   Reply With Quote
Old 05-15-2014, 08:45 AM   #52
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Mike,

You have been given some good ideas how to accomplish your task.

However, if you plan to run your generator in order to run your two A/C's you won't be staying in any RV Park or campground.

You will need to find a secluded location where you can dry camp and run your generator anytime you choose.

Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 05-15-2014, 09:00 AM   #53
Member
 
Entegra Owners Club
Join Date: Mar 2012
Posts: 74
I had this problem on a previous RV. I spliced the supply wire for one AC behind the breaker box with standard male/female 120v plugs. Then when I needed more juice, I unplugged the AC and plugged it into a heavy duty extension cord and plugged into the extra 120v plug on pedastal. I ran extra romex where the AC plug was in basement and easy access when I needed to run extension cord. James
__________________
James and Diana
2014 Entegra Coach Aspire 44B
jherrin99 is offline   Reply With Quote
Old 05-22-2014, 07:03 PM   #54
Member
 
Join Date: Mar 2014
Posts: 38
I have 2008 Fleetwood Fiesta with 30amp shore power and I can run both AC's at the same time. It has some type of power management system that allows 1 air conditioner to start 1st, and then the second AC starts up about 30 seconds later and if I turn on the Microwave one AC shuts off and when the Microwave is done it starts right back up again. With both ac's running at full it is pulling about 26amps, so 30amps is more than enough power.
__________________
mgjessop is offline   Reply With Quote
Old 05-22-2014, 07:41 PM   #55
Senior Member
 
dvmweb's Avatar
 
Join Date: Sep 2010
Location: MI
Posts: 982
We had a gasser with 50 amp cord and a 5500 watt generator that would run everything fine. 2 AC's and every once in a while the microwave.
__________________
dvmweb is offline   Reply With Quote
Old 05-22-2014, 10:31 PM   #56
Member
 
williame's Avatar
 
Vintage RV Owners Club
Join Date: Oct 2010
Posts: 38
Blog Entries: 9
I ran both airs in my old 83 sportscoach no problem, it was. 30 amp.
__________________

__________________
williame is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Water Heater does Not Work Unless Plugged Into Shore Power jimfryar Newmar Owner's Forum 4 03-23-2014 11:23 PM
Install 2nd shore power connector wincrasher Travel Trailer Discussion 1 03-18-2014 10:50 PM
15/20 Amp Shore Power Rehbergl Roadmaster Motorhome Chassis Forum 4 03-05-2014 07:07 PM
Question About Chassis Battery Charging on Shore Power TandCplusRV RV Systems & Appliances 15 02-05-2014 11:57 AM
Bounder: Shore Power issue Tom Dufresne Fleetwood Products Owner's Forum 10 08-26-2013 07:03 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:18 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.