Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > iRV2.com COMMUNITY FORUMS > iRV2.com General Discussion
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 06-27-2011, 01:05 PM   #1
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Automatic Transfer Switches-Caution

After speaking with the technical support staff of Iota Engineering and Parallax Power Supply the consensus is that we may be using our transfer switches incorrectly. Neither manufacturer recommends switching while under load as contact pitting will occur resulting in loss of switch life. Their 50 amp. rating is for normal current carrying capability not switching current. They each recommend turning off all inside load before switching power sources. However when pressed they did say that switching 5 or 6 amps will probably not cause a problem. Inductive loads are the worst load type to cause contact damage. The normal operating current of the motors coupled with the inductive inrush currents can cause contact bounce resulting in even more loss of contact/switch life and early failure.


The switch is normally wired so the generator has priority. When the switch senses power from the generator the switch's control board takes 120 volts from the black wire from the generator where it is converted to 110 volts DC and is applied to the relays as control power to close the contacts. Before the contacts are closed however, the control board goes thru a timing sequence to allow the generator to get up to speed before it's asked to carry load. If the generator is running when connected to shore power the generator will continue to supply power to the coach until it is shut off. At that point control power will be lost and the contact will immediately switch to shore power. This is where the most damage is possible to the contacts especially if a motor load is running in the coach. Since AC power is sinusoidal if the power cycle is on the increase at the time the generator was shut down and the incoming shore power is also increasing the voltages will combine and a high voltage will be fed into the coach in the form of a spike. Hopefully, surge protection will dissipate it to ground with no effect.


So what can we do to prevent transfer switch damage. Before we start our generators we should turn off all motor loads such as air conditions and fans and reduce the total load to about 5 – 6 amps. Once the generator is started and available for load servicing the power configuration in the coach can return to normal.


Typically we run our generators while on the road to power the air conditioners so when we arrive at our site the generator is normally running while we hook up. Before turning on the 50 amp breakers at the power pedestal, turn off all air conditioning load and turn off the generator. Then turn on the breaker.


This should help eliminate problems associated with transfer switches and extend its service life saving us inconvenience and money.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-27-2011, 01:20 PM   #2
Senior Member
 
Join Date: Mar 2011
Posts: 133
Thanks for the headsup

Not really off subject, well maybe a little. I have been wondering about running the generator when driving to run AC. The load center and transfer switch on the MH delays connection of the generator for 10 seconds after starting but the generator manual says to let it run for two minutes before adding a load. Here is the problem, if I start out in the morning not needing AC and later in the day want to run the generator and AC, should I already have the thermostat set so that as soon (10 seconds) as the generator comes on line the AC will start or should I stop and wait 1 or 2 minutes then turn on the AC? The thermostat is some 20 feet behind the driver's seat.
I realize that the second choice would be best for the system but does that make the extra stop worth it?
__________________
Bill
Peddler is offline   Reply With Quote
Old 06-27-2011, 01:26 PM   #3
Moderator Emeritus
 
RickO's Avatar


 
Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 10,530
Great info... thanks RJay!

I guess it's another case of "just because we can... doesn't mean we should."

rick
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
RickO is offline   Reply With Quote
Old 06-27-2011, 02:36 PM   #4
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Hi Bill,


The 10 second delay before the switch closes is to allow the generator to stabilize after start. I believe the 1 to 2 minutes the manual requires is for warm up. If I'm not mistaken there is always a delay after you turn on the thermostat to when the air conditioners comes on. So you would be able to turn on your thermostat before you leave and just turn on the generator when you need the air and you wouldn't have to stop. The objective is you don't want to switch the A/C load or loads over 5-6 amps.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 06-27-2011, 03:13 PM   #5
Senior Member
 
Join Date: Mar 2011
Posts: 133
Quote:
Originally Posted by RJay View Post
Hi Bill,


The 10 second delay before the switch closes is to allow the generator to stabilize after start. I believe the 1 to 2 minutes the manual requires is for warm up. If I'm not mistaken there is always a delay after you turn on the thermostat to when the air conditioners comes on. So you would be able to turn on your thermostat before you leave and just turn on the generator when you need the air and you wouldn't have to stop. The objective is you don't want to switch the A/C load or loads over 5-6 amps.
Thanks,

I ran 100 miles home from Tampa last week by myself and the dash air obviously didn't quite do the job.(97 degrees outside). In the future I'll do as you suggested. It was one of those things where I convinced myself that home was "just around the corner" and I really wouldn't sweat to death before I got there.
You've got to love Florida in the summer.
__________________
Bill
Peddler is offline   Reply With Quote
Old 06-27-2011, 03:33 PM   #6
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
As someone who is presently in Texas I feel your pain. Even a couple of hours at that temp is not fun!
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 06-27-2011, 08:00 PM   #7
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
One thing I forgot to mention in my original post is Iota is no longer producing their switch. They said the depressed RV market and other suppliers undercutting their price caused them to get out of the RV market.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 06-27-2011, 08:03 PM   #8
Senior Member
 
mrschwarz's Avatar
 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
Join Date: Jul 2006
Posts: 929
Send a message via Skype™ to mrschwarz
I have seen Iota switches for sale. How long have they been out of the business?
__________________
Michael
2017 Allegro Bus 45OPP, Cummins ISL 450, Allison 3000
mrschwarz is offline   Reply With Quote
Old 06-27-2011, 08:11 PM   #9
KIX
Senior Member
 
KIX's Avatar
 
Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 3,595
Quote:
Originally Posted by Peddler View Post
if I start out in the morning not needing AC and later in the day want to run the generator and AC, should I already have the thermostat set so that as soon (10 seconds) as the generator comes on line the AC will start or should I stop and wait 1 or 2 minutes then turn on the AC? The thermostat is some 20 feet behind the driver's seat.
Isn't that what Cruise Control is for?
__________________
KIX
'02 Ultimate Advantage 40J Spartan MM - Cummins ISC
2013 Jeep Rubicon JK Unlimited
KIX is offline   Reply With Quote
Old 06-27-2011, 08:14 PM   #10
Senior Member
 
keninvic's Avatar
 
National RV Owners Club
Newmar Owners Club
Triple E Owners Club
Join Date: Feb 2010
Location: VICTORIA, BC
Posts: 246
Quote:
Originally Posted by mrschwarz View Post
I have seen Iota switches for sale. How long have they been out of the business?
They are still in business. I stopped in at IOTA Engineering at their plant in Tucson. I was looking to buy a transfer switch. They did not have any and there was no immediate plan to re-tool and manufacture a new batch. Security seemed abnormally high; made me wonder if they have a secret military contract that is keeping them busy.
__________________
2004 DOLPHIN 5320
2001 Dodge Dakota 4x4 Toad
keninvic is offline   Reply With Quote
Old 06-27-2011, 08:31 PM   #11
Senior Member
 
pkmesser's Avatar
 
Workhorse Chassis Owner
Join Date: Oct 2010
Location: Tehachapi, Ca
Posts: 560
Quote:
Originally Posted by Peddler View Post
Thanks for the headsup

Not really off subject, well maybe a little. I have been wondering about running the generator when driving to run AC. The load center and transfer switch on the MH delays connection of the generator for 10 seconds after starting but the generator manual says to let it run for two minutes before adding a load. Here is the problem, if I start out in the morning not needing AC and later in the day want to run the generator and AC, should I already have the thermostat set so that as soon (10 seconds) as the generator comes on line the AC will start or should I stop and wait 1 or 2 minutes then turn on the AC? The thermostat is some 20 feet behind the driver's seat.
I realize that the second choice would be best for the system but does that make the extra stop worth it?

The Newmar products have a 90 second delay from AC power on before the compressor powers up, I would expect recent vintage Winnebago products to do something simular. If it does not appear in your manual, try it at home. Turn your breakers off, turn the thermostat to cool, throw the breakers on, and then time how long before the air conditioner comes on. Should be the same time for the generator power.
__________________
PKMesser
2005 KSCA 3778 on 04 W22 with Koni FSD
Banks Headers, 503 CID
pkmesser is offline   Reply With Quote
Old 06-27-2011, 08:44 PM   #12
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Quote:
Originally Posted by mrschwarz View Post
I have seen Iota switches for sale. How long have they been out of the business?
When I spoke with them today they said they were no longer making them. They probably still have some in stock? They are not going our of business they just stopped making the transfer switch.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 06-28-2011, 07:12 AM   #13
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Quote:
Originally Posted by pkmesser View Post
The Newmar products have a 90 second delay from AC power on before the compressor powers up, I would expect recent vintage Winnebago products to do something simular. If it does not appear in your manual, try it at home. Turn your breakers off, turn the thermostat to cool, throw the breakers on, and then time how long before the air conditioner comes on. Should be the same time for the generator power.
According to my Iota manual for the switch it states there is a 20-30 second delay before the switch is connected to the generator. I know there is a delay after the thermostat is turned on to when the air conditioner comes on but I couldn't find it in the Comfort Control manual. I'm sure someone out there knows.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 06-28-2011, 08:31 AM   #14
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
I think the "Wait 2 minutes before applying load" is a bit... Over cautious.

But as noted, the 30 seconds the ATS waits (normally it's about that long) plus the time delay before the compressor kicks in.. Should cover it.

I don't like firing up the generator with big loads already on line.. but to be honest, there is no inductive "kick" when the switch closes.. Only when it opens. So you should now SWITCH under load, but turn is ok.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Best Automatic Transfer Switch fishinfool RV Systems & Appliances 1 06-27-2011 05:38 AM
Automatic Transfer switch kducat Class A Motorhome Discussions 18 03-31-2011 05:20 AM
installing an automatic transfer switch campclan RV Systems & Appliances 2 03-27-2011 03:18 PM
Automatic Transfer Switch leeines RV Systems & Appliances 3 08-10-2010 10:16 AM
Automatic Transfer Switch Blue74 RV Systems & Appliances 3 06-26-2007 03:47 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:12 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.