Old 12-12-2011, 08:26 PM   #15
Senior Member
 
bstark's Avatar
 
Join Date: Aug 2004
Location: Fergus, Ontario, Canada
Posts: 110
Isn't anyone going to mention the difference in the wiring itself from the incoming receptacle to the paanel? To get the dual leg 50 amp benefits you'd also need to change that wiring to 4 wire from 3 wire.

30 amp 115 v service: 1 green ground wire, 1 white neutral wire and 1 black positive 115v feed wire.

50 amp 115/240 v service: 1 green ground wire, 1 white neutral wire, 1 black positive 115v positive feed wirte, 1 red 115v positive feed wire.

This is if you're going for the full magilla 230v service with separate legs.

The benefits of 50 single leg service would be fairly simple to duplicate with running that separate 20 amp extension to another small service box with a single breaker and dedicated to your washing machine, microwave or another motor driven appliance such as a second roof A/C.

I would prefer to have that line come into a totally separate service box so they aren't sharing a neutral in the rig but back at the park's service feed pedestal instead. That's just me being finicky though.
__________________

__________________
2004 International 4400LoPro DT530E 310Hp/950FtLbs ExtCab Harley Doghouse RV Hauler
2005 Mobile Suites 38RL3
bstark is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-12-2011, 08:51 PM   #16
Senior Member
 
mrschwarz's Avatar
 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
Join Date: Jul 2006
Posts: 876
Send a message via Skype™ to mrschwarz
Quote:
Originally Posted by bstark View Post
Isn't anyone going to mention the difference in the wiring itself from the incoming receptacle to the paanel? To get the dual leg 50 amp benefits you'd also need to change that wiring to 4 wire from 3 wire.

30 amp 115 v service: 1 green ground wire, 1 white neutral wire and 1 black positive 115v feed wire.

50 amp 115/240 v service: 1 green ground wire, 1 white neutral wire, 1 black positive 115v positive feed wirte, 1 red 115v positive feed wire.

This is if you're going for the full magilla 230v service with separate legs.

The benefits of 50 single leg service would be fairly simple to duplicate with running that separate 20 amp extension to another small service box with a single breaker and dedicated to your washing machine, microwave or another motor driven appliance such as a second roof A/C.

I would prefer to have that line come into a totally separate service box so they aren't sharing a neutral in the rig but back at the park's service feed pedestal instead. That's just me being finicky though.
Not only do you require 4 wires instead of 3, but they are bigger wires, too. Between the wire coming into the coach and the load center will require a new cable. While a second circuit for the second air conditioner would be sufficient, would it handle the rest of the load in the RV?
__________________

__________________
Michael
2017 Allegro Bus 45OPP, Cummins ISL 450, Allison 3000
mrschwarz is offline   Reply With Quote
Old 12-12-2011, 09:31 PM   #17
Senior Member
 
Wizard's Avatar


 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Mar 2007
Location: Home on the hill in Georgia
Posts: 2,458
I found that the easiest thing for me to do was buy a 50Amp extension cord and cut the female end off, then use that for power cord. That way I had a molded male plug.
__________________
Jerry & Patsy Potter, Taz & Jake Jr.
2000 Winnebago Journey
2006 Ford Explorer 4X4
Wizard is offline   Reply With Quote
Old 12-12-2011, 10:11 PM   #18
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 13,712
Quote:
Originally Posted by ronspradley View Post
I bought a 50amp extension cord today for my 30amp motorhome. Need to upgrade because want to run both roof air conditioners at once. It is a Texas summer kind of thing........ron
If the main breaker in your service panel is 30A, nothing else matters, 30A is all that is available for use.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 12-12-2011, 10:26 PM   #19
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 13,712
Quote:
Originally Posted by JohnITG View Post
A Newbie here (2000 Itasca 35U)...

The current shore line cable is a 30Amp cable, it has a 50Amp Generator which means it has a 50Amp bus and inverter. The transfer switch is rated at 50Amp's. Is there any reason not to change the shore line to a 50Amp cable? ... Or is there more to this than I think?

Any ideas!

Thanks!

John
Are you sure you have a 12,000 watt generator? That is what is required to provide "50A"RV service.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 12-13-2011, 07:30 AM   #20
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 18,085
If you now have the Intellitec power manager (Winnie sometimes labels it "Powerline"), you need to upgrade it to the 50A model. That model checks the incoming power for 50A vs 30A and turns itself off when 50A service is available. Otherwise it would always limit consumption to 30A, which sort of defeats the purpose of the 50A upgrade. The 50A model can also determine if the generator is operating and shut itself off.

You also need to think about how much power your generator puts out and how it is wired into the system. Most 30A coaches have a generator that is larger than 30A (3600 watts) and have an alternate path to support a second a/c unit. If you upgrade to 50A, you may want to wire it differently.
__________________
Gary Brinck
Former owner of 2004 American Tradition
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 12-13-2011, 09:29 PM   #21
Senior Member
 
mrschwarz's Avatar
 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
Join Date: Jul 2006
Posts: 876
Send a message via Skype™ to mrschwarz
Quote:
Originally Posted by Gary RVRoamer View Post
If you now have the Intellitec power manager (Winnie sometimes labels it "Powerline"), you need to upgrade it to the 50A model. That model checks the incoming power for 50A vs 30A and turns itself off when 50A service is available. Otherwise it would always limit consumption to 30A, which sort of defeats the purpose of the 50A upgrade. The 50A model can also determine if the generator is operating and shut itself off.

You also need to think about how much power your generator puts out and how it is wired into the system. Most 30A coaches have a generator that is larger than 30A (3600 watts) and have an alternate path to support a second a/c unit. If you upgrade to 50A, you may want to wire it differently.
When I upgraded my Suncruiser, all of the components were rated at 50 amps. All I needed was a new cable between the transfer switch and load center, a new 50 amp breaker in the load center, and a new cable. Like a previous poster, I bought an extension cord and cut the female end off. The was a whole lot of rewiring involved, though.
__________________
Michael
2017 Allegro Bus 45OPP, Cummins ISL 450, Allison 3000
mrschwarz is offline   Reply With Quote
Old 12-13-2011, 10:03 PM   #22
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,515
Quote:
Originally Posted by Wizard View Post
Depends a lot on what type of controls you have. On my Winnebago, I have the Intelletec panel with load sheading capabilities. When I connect my 50 amp cable to a 30 amp shore power, the panel will recognize to 30 amp and shed loads to keep the current under 30 amp. When on 50 amp, I can't use enough power to overload it.
That's because on 30 amps you have 3,600 watts available, on 50 amp you have 12,000 watts available.
120V X 30 amps = 3,600 watts
120V X 50 amps X 2 (two hot leads) = 12,000 watts
__________________

__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Reply

Tags
service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Guaranty RV in Junction City Oregon - Service Wayne M iRV2.com General Discussion 25 12-17-2012 03:43 PM
Redlands Truck and RV Awarded Top Customer Service Award DriVer RV Industry Press 0 03-21-2009 01:08 PM
Running 50 Amp coach on 30 Amp service Higgins RV Systems & Appliances 7 11-26-2008 05:46 AM
Wondering if I can use a 50 amp converter cord with my 30 amp service? luke_vardanian Travel Trailer Discussion 12 11-10-2008 04:34 AM
Can heatpump run on 20/30 amp service? sunnydays RV Systems & Appliances 14 12-11-2007 07:05 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:08 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.