We recently bought a MH that requires or has 50 AMP service. My question is and I'm sure it has been asked many times.
Will a cheater box work on the same electric panel breaker box mounted on a single campground site post that does not have 50 amp service but has a 30 and 20 amp service?
Mathematically it should work. Math I understand, electricity ahhhh.... different story.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
01-09-2017, 08:29 AM
|
#2
|
Senior Member
Outdoors RV Owners Club
Join Date: Oct 2016
Posts: 1,804
|
Quote:
Originally Posted by badrad
We recently bought a MH that requires or has 50 AMP service. My question is and I'm sure it has been asked many times.
Will a cheater box work on the same electric panel breaker box mounted on a single campground site post that does not have 50 amp service but has a 30 and 20 amp service?
Mathematically it should work. Math I understand, electricity ahhhh.... different story.
|
Cheating electricity is cheating death.
__________________
2018 ORV 24KTS 30,000+miles
2017 Ford 3.5 TwinTurbo w/MaxTow
640 Watts solar/600 Ahr
|
|
|
01-09-2017, 08:33 AM
|
#3
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,451
|
Welcome to iRV2.
A 50 amp RV site plug has two hot legs of 50 amp power .100 amps total.
The cheater box will combine 30 amp and 20 amp ( 50 amps total) then split ( depending on the way it's wired ) into 25 amps per hot leg , OR feed 30 amps to one leg in the coach and 20 amps to the other . Your still only getting 1/2 the power the coach needs to operate all it's systems.
NOTE; a 50 amp RV can operate on 30 amp power provided you manage your power use carefully .
Only one Air conditioner, water heater on propane , don't use microwave and A/C at the same time, etc.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
01-09-2017, 08:37 AM
|
#4
|
Senior Member
Excel Owners Club Winnebago Owners Club Ford Super Duty Owner
Join Date: Aug 2014
Location: Santa Fe, NM
Posts: 6,809
|
Yes this is fine and its done everyday. There are solutions from many places, this link is from eTrailer for example: Power Grip RV Power Cord Adapter w/ Handles - 125V - 50 Amp Female to 30 Amp Male Camco RV Wiring CAM55185
I would not really call it a cheater box, simple conversion pigtail or something similar. When used properly electricity is a good friend, cheat on the rules and standards and your mileage will vary!!
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & Coach House 272XL E450
2007 RAM 3500, Diesel, 6Spd Auto, SWD, 4x4, CC & LB
[SIGPIC][/SIGPIC]
|
|
|
01-09-2017, 08:37 AM
|
#5
|
Registered User
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
|
it may, if you have the space for a dbl pole 50a breaker
I did this in the house we are wintering in for my coach parked next door... there was already room in the breaker box, I already had the dbl pole 50a breaker, the wiring required, and the 50a plug/box ... now the coach has full 50a(100a total) service
|
|
|
01-09-2017, 09:08 AM
|
#6
|
Junior Member
Join Date: Oct 2016
Posts: 18
|
WOW....Thanks for all the quick replies.
I think I will do the one A/C and run the water heater on propane route. Seems the safest way for now.
Thanks again
|
|
|
01-09-2017, 09:13 AM
|
#7
|
Registered User
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
|
you can purchase a 'dog bone' RV adapter that may allow you to use both the 30a plug and the 15/20a plug at your site, given the outlet is not a GFCI type.
this would give you a total of 45or50amps instead of only 30
(some residential outlets are 20amps, others are only 15amps)
Camco 55025 Power Grip Series™ 50-Amp Power Maximizer 15-Amp Male & 30-Amp Male
|
|
|
01-11-2017, 12:08 AM
|
#8
|
"Formerly Diplomat Don"
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 24,090
|
"MisterT" noted the one exception. You can use both outlets, as long as the 15/20 amp one is not GFCI protected. If it is, it will just trip. We used a cheater for years for a specific campground, but rarely see campgrounds now that DON't have a GFCI in the second outlet.
If there is an empty campsite next to you, you can use both 30's if you have a long enough cord.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
|
|
|
01-11-2017, 11:24 AM
|
#9
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
Will a cheater box work? Some times but generally NO!
The theory: You can draw 30 amps on on e leg and 20 on the other for a total of 50 amps.
The problems: First. By code any new installation since a specific date (Varies from state to state) the 20 amp outlet MUST BE GFCI. and I have been in parks where the 30 amp was also GFCI. 1.5 of them (one park only selected outlets are GFCI) Now These boxes will trip a properly working GFCI 100% of the time, no exceptions if it does not trip the GFCI is defective.
Now I have used it where I could snag a pair of 30 amp NON GFCI, and where the 20 amp was NON GFCI, but anywhere you have a GFCI, no joy, never, nada.
Problem 2: 50 amps is 50 amps PER LEG, the cheater box at most can do 30 amps per leg. So even if you can use it you will have limited power
Problem 3: IF both legs are the same.. The Neutral can be hauling 60 amps. This is 20% over the wire's rating and may cause issues.
__________________
Home is where I park it!
|
|
|
01-11-2017, 11:27 AM
|
#10
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,678
|
In addition to the likely GFCI problem, be aware that the 20A and 30A outlets will be tied to the same wire and power source, and that source will be designed for 30A. Don't be surprised if another breaker elsewhere in the park trips when you exceed 30A, or if wires get hot.
I've also had some parks tell me that this is not allowed after they noticed my cheater box. One refused me even though I offered to pay the same rate as a 50A site (they didn't have any available for me to rent).
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
01-12-2017, 04:04 PM
|
#11
|
Junior Member
Join Date: Oct 2016
Posts: 18
|
Thanks for all the good advice.
If I end up at a 30 amp site I'll mind power usage. Run 1 A/C or the microwave not both.
I just bought a surge protector (PI EMS-PT50C). So hopefully I don't end up with fried electrical circuits. Bought that from the advice I read on this site.
Thanks
|
|
|
01-12-2017, 04:17 PM
|
#12
|
Senior Member
Join Date: Oct 2015
Location: Brighton, MI
Posts: 775
|
If your MH has a power management panel it will manage the loads for you. I can run both ACs on 30 amps. If I start using other devices it will shut down the 2nd AC, and the electric water heater and the fridge and finally switch the AC fan from high to low. Even if you don't have power management you shouldn't fry anything. Maybe pop a breaker, that's what they're for but not fry any circuits.
__________________
Hank & Lynda
2003 Winnebago Adventurer 35U, Workhorse W22
|
|
|
01-12-2017, 05:22 PM
|
#13
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
Regarding that surge protector.. Good choice, I like the HW 50C better but the reason is convenience, not function.. Both operate identically save for the need to plug one of them in every time.
__________________
Home is where I park it!
|
|
|
07-08-2018, 10:14 AM
|
#14
|
Member
Join Date: Mar 2012
Location: Stamping Ground,Ky
Posts: 33
|
Electric cheater box
Another thought is to break the connection to one AC unit and install a pigtail using a short 12/3 extension cord cut in half. This allows me to run both AC units. Haven’t tried a GFCI circuit yet. It might work being the ground wire will also be a separate run to the GFCI outlet. Use at your own risk. I do not accept any liability.