Electrical Problem at Park

We have a 2011 Class A 43 ft. We just came from 6 months on the road without an electrical problem. We pulled into this park and hooked to the 50 amp post. Power came on saying we have 50 amp power on our Energy Management System. About 15-30 seconds later “NO SERVICE” shows on EMS and AC shut off. 15-30 seconds later power comes back on plus AC. Then again “NO POWER”. Park changed the breaker but same thing happened so we tried another pole next to us in same area. Same thing happened. What’s going on or happening? Anyone know?
__________________

rml1998 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-19-2018, 04:07 PM   #2
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Winnebago Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 33,195
Check the voltage at the service pole. Probably low so the EMS is shutting power off to protect your appliances.
__________________

__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is online now   Reply With Quote
Old 05-19-2018, 04:13 PM   #3
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 16,997
Anyone nearby having issues ? Park crowded ?
Sure sounds like an intermittent low supply voltage triggering the EMS to shut down.
Did the park worker check voltage or just throw another breaker in?
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-19-2018, 04:18 PM   #4
Senior Member
 
sdennislee's Avatar


 
Monaco Owners Club
Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,322
I assume you don't have a Progressive Industries EMS-HW50C or similar with display which will show error codes. If you do what error codes are being shown.

Can you start your generator and run with out interruptions, this could help you isolate whether or not its the pedestal or coach.

I'd suggest unplugging from the pedestal and remain unplugged until you check the pedestal for over/under (is my bet) voltage, open ground, open neutral & reverse polarity. If you don't have or are not comfortable with a multi-meter call an electrician or perhaps the park has a maintenance guy.

If your coach has not had issues seems like the issue is being caused by the pedestal.

Dirty power from a pedestal has ruined more than one coach worth of sensitive electronics.
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
sdennislee is offline   Reply With Quote
Old 05-19-2018, 05:35 PM   #5
Member
 
rml1998's Avatar
 
Join Date: Jun 2010
Posts: 99
Worker just replaced the 50amp breaker and same problem. We disconnected from shore and are paying premium site price for no power. Generator working fine so maybe “dirty” power. The marina next to us was having some issues also. Don’t know about others mostly 30 ampers. Our coach has a progressive system hard wired in so we think is doing its job. Another thought .. Could it be the transfer switch? Moving to a different park tomorrow. We are in a hellacious rain storm currently here West of Nashville on the Tennessee River.
rml1998 is offline   Reply With Quote
Old 05-19-2018, 05:41 PM   #6
Member
 
rml1998's Avatar
 
Join Date: Jun 2010
Posts: 99
Quote:
Originally Posted by Skip426 View Post
Anyone nearby having issues ? Park crowded ?

Sure sounds like an intermittent low supply voltage triggering the EMS to shut down.

Did the park worker check voltage or just throw another breaker in?


Yes the Resort park on the Tennessee River is packed. 86 units mostly 30 ampers. Worker just put in a new breaker and he checked power with a big Camco Surge Protector which indicated both legs showing blue lights and power light showing green. ????
rml1998 is offline   Reply With Quote
Old 05-19-2018, 05:45 PM   #7
Senior Member
 
sdennislee's Avatar


 
Monaco Owners Club
Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,322
Quote:
Originally Posted by rml1998 View Post
Our coach has a progressive system hard wired in so we think is doing its job.
Is it the EMS-HW50C, if it is there should be a remote display that will show you the error code.
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
sdennislee is offline   Reply With Quote
Old 05-19-2018, 05:46 PM   #8
Member
 
rml1998's Avatar
 
Join Date: Jun 2010
Posts: 99
Quote:
Originally Posted by sdennislee View Post
I assume you don't have a Progressive Industries EMS-HW50C or similar with display which will show error codes. If you do what error codes are being shown.

Can you start your generator and run with out interruptions, this could help you isolate whether or not its the pedestal or coach.

I'd suggest unplugging from the pedestal and remain unplugged until you check the pedestal for over/under (is my bet) voltage, open ground, open neutral & reverse polarity. If you don't have or are not comfortable with a multi-meter call an electrician or perhaps the park has a maintenance guy.

If your coach has not had issues seems like the issue is being caused by the pedestal.

Dirty power from a pedestal has ruined more than one coach worth of sensitive electronics.


Generator started and is running with no issues at all so suspect the pedestal or park has issues.
All 86 sites full with mostly 30 ampers. A few 50 of us folks but they are on a different circuit line area than me.
rml1998 is offline   Reply With Quote
Old 05-19-2018, 05:53 PM   #9
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
can u make use of the 30amp outlet if u have an adapter?
MisterT is offline   Reply With Quote
Old 05-19-2018, 06:19 PM   #10
Member
 
rml1998's Avatar
 
Join Date: Jun 2010
Posts: 99
Quote:
Originally Posted by MisterT View Post
can u make use of the 30amp outlet if u have an adapter?


Tried the double 30 pigtail to 50. Same results. Power then no power. Tried 30 alone same results.
rml1998 is offline   Reply With Quote
Old 05-19-2018, 06:55 PM   #11
Moderator Emeritus
 
smlranger's Avatar


 
Country Coach Owners Club
Freightliner Owners Club
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 7,723
Blog Entries: 1
As noted, most likely low voltage on at least one leg of the circuit. I had same issue at my storage unit recently. Owner added 50 amp for my coach but any time I tried to use an AC unit, my surge guard would shut off power. Checked voltage and one leg had 123VAC and the other was at 108VAC. That lower voltage on one leg caused my surge guard/EMS to shut down.



The tester with blue lights is not actually showing the voltage.
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA
smlranger is offline   Reply With Quote
Old 05-19-2018, 06:59 PM   #12
Member
 
rml1998's Avatar
 
Join Date: Jun 2010
Posts: 99
Thanks that sound just like what is happening. Moving to another park tomorrow and will see we still have issues. Hopefully not.
rml1998 is offline   Reply With Quote
Old 05-19-2018, 07:09 PM   #13
Senior Member
 
sdennislee's Avatar


 
Monaco Owners Club
Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,322
Progressive Industries will shut down at less than 104 volts for low voltage protection. The display on the remote for the EMS HW50C or on the unit for the LCHW 50 will show E4 for line 1 or E6 for line 2
Attached Images
 
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
sdennislee is offline   Reply With Quote
Old 05-20-2018, 04:52 AM   #14
Senior Member
 
Join Date: Oct 2016
Location: Rendon, Texas
Posts: 282
Am curious...Did the worker check the incoming power using a voltmeter? If so what was the voltage?
__________________

txcpl is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stuck in Yosemite National Park (electrical issue) efstewart Class A Motorhome Discussions 50 08-26-2017 08:31 AM
Word of caution - Nehalem Bay State Park electrical service ME for Maine Camping Locations, Plans & Trip Reports 0 07-18-2017 10:02 AM
No electrical power at one lug (3) Left Front Electrical Center RobRoy Monaco Owner's Forum 18 03-31-2017 11:59 AM
RV Park electrical hook up dvkiel Class A Motorhome Discussions 11 08-24-2014 12:38 PM
Sat Dome Problem or Electrical Problem?? fansill Technology: Internet, TV, Satellite, Cell Phones, etc. 5 04-25-2011 11:34 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:19 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.