Old 07-10-2013, 11:13 AM   #15
Member
 
Bosty's Avatar
 
Thor Owners Club
Join Date: Nov 2011
Location: Chandler, AZ
Posts: 73
How about with a propane gen? All my previous RV had gas gens which I can understand the issues with varnishing and so forth. But a propane is a different animal. Anyone have any advice here?
__________________

__________________
Bosty is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-10-2013, 11:18 AM   #16
Senior Member
 
Sky_Boss's Avatar


 
Newmar Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,068
Quote:
Originally Posted by Bosty View Post
How about with a propane gen? All my previous RV had gas gens which I can understand the issues with varnishing and so forth. But a propane is a different animal. Anyone have any advice here?
I don't THINK there is any different recommendations. Part of the purpose of exercising the genny is to remove humidity/moisture from the components that generate the electricity itself. So, while fuel age/condition may not be as big of a problem for propane, the other side of it still needs to be worked.
__________________

__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 DSDP 4320, Spartan MM IFS, 2013 CR-V, Blue Ox Avail, SMI AF1, Samsung 197R Refer.
Sky_Boss is offline   Reply With Quote
Old 07-10-2013, 11:59 AM   #17
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by Sky_Boss View Post
I don't THINK there is any different recommendations. Part of the purpose of exercising the genny is to remove humidity/moisture from the components that generate the electricity itself. So, while fuel age/condition may not be as big of a problem for propane, the other side of it still needs to be worked.
True.
The slip rings, brushes and other 120VAC generating components are the same on the Gas and LP Onans, as are the throttle linkage etc.

I know the should be exercised regularly, however, I don't do it very often, (often enough).

Mel
'96 Sahara, 132k miles
17 year old 6.3kw LP Onan
(360 total hours)
__________________
mel s is offline   Reply With Quote
Old 07-10-2013, 12:58 PM   #18
Senior Member
 
sc3283's Avatar
 
Join Date: Aug 2011
Posts: 1,126
mine is LP...it starts no differently during day to day usage as it does fall until next spring(after sitting all winter)
__________________
96 Dynasty 36' that does NOT wander, thanks to RuppParts.com and their superior "poly" suspension bushings
sc3283 is offline   Reply With Quote
Old 07-10-2013, 01:15 PM   #19
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Since the coach is R HOME, it is quite easy to routinely exercise the generator. During the summer months, I pick a day when I have both A/C's in use to run the generator approximately 1.5 - 2 hours. During the winter we usually have two Lasko Ceramic electric heaters running on a cold day and I will run the generator about the same amount of time each month.

The more the generator is used the better I feel about having it work correctly when I REALLY need it especially when traveling from Point A to Point B when it is used the most.

Dr4Film ----- Richard
__________________
Dr4Film is offline   Reply With Quote
Old 07-10-2013, 01:39 PM   #20
HHg
Registered User
 
Join Date: Nov 2010
Location: Austin, Texas
Posts: 413
My Onan 10k generators owners manual says to keep warranty in force, it must be exercised 2 hours per month under at least 1/2 load. That is what I do.

Hhg
__________________
HHg is offline   Reply With Quote
Old 07-10-2013, 01:43 PM   #21
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,461
I turn on both heat pumps, one on heat the other on cool, in about ½ hr I switch them around.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is online now   Reply With Quote
Old 07-10-2013, 01:46 PM   #22
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,461
Quote:
Originally Posted by sc3283 View Post
mine is LP...it starts no differently during day to day usage as it does fall until next spring(after sitting all winter)
But that's not the point of "exercising" the gen. The generator windings collect moisture which needs heat to "burn" it off or they can short out. So, while a propane powered engine doesn't need the "exercise" the generator itself does.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is online now   Reply With Quote
Old 07-10-2013, 01:55 PM   #23
Senior Member
 
Mike_Harriet's Avatar
 
Join Date: Jan 2013
Posts: 776
We currently live on our 42' trawler. Our gen is a diesel Westerbeke. Same high quality construction as the Onan/Cummins. At 4211 hrs I finally had to overhaul it. It's 18 years old and ran like top until starting to lose compression on #2 cyl. New rings, head gasket, bearings and its 413 hrs since rebuild. Those small diesels are meant to run. Start them up, load them up (60% at least) once a month and they will out last the coach.
__________________
Mike_Harriet is offline   Reply With Quote
Old 07-10-2013, 10:48 PM   #24
Senior Member
 
spritz's Avatar


 
Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Mar 2013
Location: c above
Posts: 4,952
Cool

Quote:
Originally Posted by Old Scout View Post
WOW--360 hrs on a 1996 genset--so what are you saving it for???? Lots of opinions here and some facts. Seems like once a month for 30 minutes, at 1/2 load is about right--key is warm up the components and drive off any moisture that has accumulated. Not sure how cold "too cold" is but winter and storage is the prime time to exercise your genset. Having it set for months in cold weather is not good for the engine or the generator.....just saying

OBOY, 1982 Pace Arrow genny has under 200 hours, I just don't stay anywhere where there isn't hookups. I just have to start BOONDOCKING
Another reason to go RVing!!!!! Lets go go go.
__________________
1982 Pace Arrow 30ft.
KarKaddy SS, Toad: 1999 Deville Concours
Lilly and Rubie Our 4 legged Kids & Tim & Joe
spritz is offline   Reply With Quote
Old 07-11-2013, 05:32 AM   #25
Senior Member
 
HD4Mark's Avatar
 
Winnebago Owners Club
Coastal Campers
Join Date: Oct 2009
Location: Marathon, Florida
Posts: 2,894
Quote:
Originally Posted by HHg View Post
My Onan 10k generators owners manual says to keep warranty in force, it must be exercised 2 hours per month under at least 1/2 load. That is what I do.

Hhg
I guess it would be easy for them to see if you used the genny 2 hours by the hour meter but not so sure how they could tell what load it was under. Of course now days when everything seems to have a computer in it the generators might be keeping track. Big Brother Onan
__________________
Mark & Nancy
2004 Winnebago Vectra 40KD
Shep dog, R.I.P. Kenzie dog Toad 2015 Jeep Wrangler Willys Wheeler
HD4Mark is offline   Reply With Quote
Old 07-11-2013, 02:19 PM   #26
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,799
Summertime, When I change campgrounds (About an hour's drive) I fire up ye old air conditioning.

Winter time when I change campgrounds (About a 30 minute drive) the space heaters.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 07-11-2013, 03:44 PM   #27
Senior Member
 
Join Date: Jun 2013
Location: Osoyoos, BC
Posts: 123
Gets pretty cool in Canada during the winter. I'm looking at purchasing a MH, and the dealer told me that in the winter, top up the fuel tank and add a a gas treatment to the tank. This will avoid problems when you start up rhe generator come summer.
__________________
Bruceeb is offline   Reply With Quote
Old 07-11-2013, 04:03 PM   #28
Senior Member
 
14 Cornerstone's Avatar
 
Entegra Owners Club
Join Date: May 2013
Location: Scottsdale, AZ/Saugatuck, MI
Posts: 105
We live in Arizona and when driving I fire up the generator for the A/C. Our coach is 10 years old and we have over 955 hrs on the gen. You know the old saying, use it or lose it! Ours fires up every time. I have had no problems at all. When in storage (outside under cover) I fire up the gen turn on the AC and take a nap. LOL Damn life is hard.
__________________

__________________
T/R
Arizona
"2014 Entegra Cornerstone”
14 Cornerstone is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.