For you electricians - 30A outlet install questions

Hi all,

One of my winter projects is to install an outdoor shore power outlet (load center) near our RV parking spot (like this one GE 30 Amp Temporary RV Power Outlet-U013P at The Home Depot).

I'm planning to run the wire from my breaker panel out through the shop wall & inside pvc conduit (outdoor rated) along our deck to the deck-mounted outlet. Total wire run will be about 32 feet. I want to comply with current code. Now the questions:

1. What type of wire do I need? Based on what I'm reading, should I use THHN/THWN?

2. Do I need to use a GFCI circuit breaker on this since the outlet itself isn't GFCI?

Other advice welcome too…

Thanks in advance!
__________________

__________________
Steve & Carol

2000 Jayco 3230K Designer
Steverino is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-30-2013, 11:23 AM   #2
Senior Member
 
Theberrys's Avatar


 
National RV Owners Club
Join Date: Jun 2009
Posts: 2,605
Here is a document with the required wiring. Look at the bottom for correct wire sizes.
https://skydrive.live.com/?cid=ae67f...=WordPdf&wdo=1

Dick
__________________

__________________
1999 Tradewinds 7372 Cat 3126
Albuquerque, NM
Theberrys is offline   Reply With Quote
Old 11-30-2013, 11:27 AM   #3
Senior Member
 
MattC's Avatar
 
Join Date: Feb 2012
Location: SE Michigan
Posts: 459
Steve,

As it will be in pipe, 10AWG would pass, but price 8 before you buy. And, 6 for that matter, you may want to go to 50A someday and you might as well buy the copper now.

The breaker should be a GFCI if the receptacle is outdoors. That is current code just about everywhere.

I don't do building electrics anymore, but ampacities and NEC codes have not changed much, but some local/states have added things.

Matt
__________________
A lifelong waterman and his bride going dry places for as long as the fuel money lasts.
MattC is offline   Reply With Quote
Old 11-30-2013, 12:55 PM   #4
Senior Member
 
Steverino's Avatar
 
Ford Super Duty Owner
Join Date: Jun 2012
Location: Central PA
Posts: 257
Thanks to you both - very helpful! Am I right about the wire type (THWN) for outdoor use?
__________________
Steve & Carol

2000 Jayco 3230K Designer
Steverino is offline   Reply With Quote
Old 11-30-2013, 01:30 PM   #5
Senior Member
 
Join Date: Mar 2013
Location: Langley. BC, Canada
Posts: 677
Excellent project and well worthwhile!

Not sure why that call the outlet "temporary". Electrical products are never designed to be "temporary", but that's good 'ol HD... I like that design because when you have the plug in, the hood over the outlet will keep rain off. Some weatherproof receptacles don't keep rain out when plugged in and the flap is open.

I highly recommend that you also install a disconnect switch at the outlet. You should never plug in live because it will cause pitting and damage to the plug blades and outlet. Use a "motor rated" switch because it is designed to make/break connection on high inrush current. That's what I did for ours. You'll need the appropriate outlet box size in series with the conduit and under the outlet. An nice option would be to hardwire in an "on" indicating light of some kind.

For 32' you should be fine, but you need to consider the overall length from outlet to wherever the panel is. You could easily have another 50' or more. Unless you want to be able run a full 30 amps at home (with AC and other stuff on) and you have a long wire run, #10 should be fine. The ground wire can be a #14. If you buy the wire at HD, just ask for wire that is rated for underground use or a wet location - needs to have an underground "U" or wet "W" rating on it and will be printed on the jacket, as in say, TWU.

I would use 1" conduit even though 3/4" or even 1/2" (would have to look in NEC table) would be okay by code. 1" will be so much easier to pull through and gives you spare capacity to add more wire if ever needed for something else (yard light, weed eater plug, etc.). If that's a possibility, install a spare pull string for future use.

Do NOT install a GFCI otherwise you'll end up with GFCIs in series which is not good. Do not install a separate ground rod at the remote outlet.

If you are going to all the work to dig a trench, you might want to think about putting in a spare conduit. You could always use that for CATV to the RV for when kids or visitors want to use it.

Tip: when you do install this and want your fridge to run on 120V, do NOT forget to make sure the power is on inside your unit. It is possible to have all your food spoil...
__________________
Gil & Deb & Dougal the Springer Spaniel
2014 KZ Spree 262RKS & Ford F250 supercab V10 4x4 LB
Langley, B.C.
myredracer is offline   Reply With Quote
Old 11-30-2013, 03:12 PM   #6
Senior Member
 
rgvtexan's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Oct 2009
Location: NE WA or S TX
Posts: 2,239
It is called temporary, as it is a receptacle for a plug. If it were permanent, it would be hard wired.
__________________
04 Horizon QD, 12 Ford Flex, Excalibar, Brakemaster, Winter Texan, RVin! since 1974
Norm, Donna & Tinker Kat 74 MGB-GT, 75 MGB, 01 Z3
Life is a Timed Event, you only get One Go Around!
rgvtexan is offline   Reply With Quote
Old 11-30-2013, 04:05 PM   #7
Community Administrator
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,617
I agree that GFCI is not used for RV service.

Quote:
Originally Posted by myredracer View Post

Do NOT install a GFCI otherwise you'll end up with GFCIs in series which is not good. Do not install a separate ground rod at the remote outlet.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is offline   Reply With Quote
Old 11-30-2013, 04:07 PM   #8
Senior Member
 
Steverino's Avatar
 
Ford Super Duty Owner
Join Date: Jun 2012
Location: Central PA
Posts: 257
Wait - so I DON'T need a GFCI breaker for this, despite the outdoor location?
__________________
Steve & Carol

2000 Jayco 3230K Designer
Steverino is offline   Reply With Quote
Old 11-30-2013, 04:27 PM   #9
Just south of Twin Cities
 
Cooperhawk's Avatar


 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jun 2013
Location: 5 miles south of Lakeville, Mn
Posts: 1,588
Have you got the document for a 50 amp outlet?
__________________
Retired FAA ATC,
VFW AL, VVA, NRA
2002 Journey DL 36, 3126 Cat 330hp
2015 Ford Explorer Blue Ox tow bar, AF1
Cooperhawk is offline   Reply With Quote
Old 11-30-2013, 04:29 PM   #10
Member
Commercial Member
 
Join Date: Jan 2011
Posts: 53
Be sure it's wired for 120 volt not wired 220 volt. It's very very common if you call a electrician to wire a 30 amp receptacle for you they will wire it as a 220 volt receptacle, since the most needed wired item for the electrician is 220 volt for 30 amp service, but not your RV. If you plan to at a later date go with a 50 amp box you will need to have 4 wires and the 30 amp will only need wires. Go ahead an pull 4 wires through for future needed service.
__________________
http://rvcoolingunit.com/
dforce1 is offline   Reply With Quote
Old 11-30-2013, 04:30 PM   #11
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 13,712
This NEC wire size calculator removes those mistakes from installing wiring.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 11-30-2013, 04:38 PM   #12
Senior Member
 
palehorse89's Avatar


 
Newmar Owners Club
Join Date: Oct 2009
Posts: 7,751
Quote:
Originally Posted by Route 66 View Post
I agree that GFCI is not used for RV service.
Quote:
Originally Posted by Steverino View Post
Wait - so I DON'T need a GFCI breaker for this, despite the outdoor location?
No GFCI needed for a RV 50 amp. or 30 amp. outdoor outlet, It must be in a enclosed covered box w/a lid that opens.
Stop and think of what a power pedestal looks like inside when you lift the lid to plug in....... only the 15-20 amp. plug is a GFCI.
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 11-30-2013, 04:41 PM   #13
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,821
Just one thing you need to remember.

This is a 120 volt outlet.. Just like a common 15 amp duplex outlet in the wall of your house.. Other than bigger wire, and bigger breakers it wires up exactly the same way.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 11-30-2013, 04:53 PM   #14
Senior Member
 
Join Date: Mar 2013
Location: Langley. BC, Canada
Posts: 677
Quote:
Originally Posted by rgvtexan View Post
It is called temporary, as it is a receptacle for a plug. If it were permanent, it would be hard wired.
In all my years as an electrical engineer, I've never heard of that definition before. I could maybe see saying it's for temporary use of your RV when parked at home, but even then it'd be a stretch. Wouldn't that be like saying every receptacle in your house is temporary?
__________________

__________________
Gil & Deb & Dougal the Springer Spaniel
2014 KZ Spree 262RKS & Ford F250 supercab V10 4x4 LB
Langley, B.C.
myredracer is offline   Reply With Quote
Reply

Tags
install



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:24 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.