Old 04-11-2019, 11:37 AM   #57
Senior Member
 
Fiesta48's Avatar
 
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Nov 2010
Location: Texas
Posts: 4,283
Lots of good info and theory. Easiest solution is...
No post/shore power with GFCI.
__________________
Full Timers.
2015 Fleetwood Discovery 40E on a Freightliner XCS chassis with a Cummins ISL9 pulling 1 and/or 2 motorcycles, '07 Honda Accord OR a 17' Runabout Boat.
Fiesta48 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-11-2019, 11:50 AM   #58
Senior Member
 
Join Date: Jul 2018
Posts: 4,920
Quote:
Originally Posted by Fiesta48 View Post
Lots of good info and theory. Easiest solution is...
No post/shore power with GFCI.

In the latest revision of the National Electrical Code (NFPA70), 30 and 50 amp services outdoors are to be GFCI protected. Private campgrounds and parks will be slow to convert but new construction (and government-owned sites) will have them.


It's better to figure out why you have a ground fault than simply treat the symptom.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 04-11-2019, 12:03 PM   #59
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Ground faults are dangerous. Possibly deadly. Not a theory but a fact. If you have them you need to fix them.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Old 04-11-2019, 12:17 PM   #60
Senior Member
 
J Birder's Avatar
 
Join Date: Feb 2012
Location: Lake County, IL
Posts: 1,584
Quote:
Originally Posted by hohenwald48 View Post
Ground faults are dangerous. Possibly deadly. Not a theory but a fact. If you have them you need to fix them.

That is a very misleading statement.



The GFCI shuts down when the current flowing in the hot line is not equal to the current flowing in the neutral. The only possible cause of such an imbalance, is that some current is returning as leakage to ground.


If that leakage is flowing through a person, then it might be deadly. However, when there is no person involved, then there is some other leakage path, which is almost certainly harmless.


Joel
__________________
Retired electronics engineer. Avid paddler & birder.
2011 Silverado 2500HD, diesel, 4x4,crew cab, 8' bed
Palomino Puma 253FBS (27' 5er) & '94 19' Class B
J Birder is offline   Reply With Quote
Old 04-11-2019, 12:42 PM   #61
Senior Member
 
Join Date: Mar 2019
Posts: 246
Many (not all) inverters come factory wired with ground neutral bonded.


If you have an inverter check it out could be bonded.
garry1p is offline   Reply With Quote
Old 04-11-2019, 01:28 PM   #62
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Quote:
Originally Posted by J Birder View Post
However, when there is no person involved, then there is some other leakage path, which is almost certainly harmless.
Joel
Unless it's thru the skin of the RV which will eventually be touched by a person on the ground. Maybe a barefooted kid, who knows. Fix ground faults.

I don't understand why so many are willing to try to defend a potentially dangerous and improper wiring situation and simply shrug it off. Weird. I've had my say. Do as you please.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Old 04-11-2019, 01:29 PM   #63
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Quote:
Originally Posted by garry1p View Post
Many (not all) inverters come factory wired with ground neutral bonded.

If you have an inverter check it out could be bonded.
Might be true of a cheap WalMart inverter but most inverters of any quality will have a relay to bond or not bond depending on shore power status.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Old 04-11-2019, 01:59 PM   #64
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by hohenwald48 View Post
Ground faults are dangerous. Possibly deadly. Not a theory but a fact. If you have them you need to fix them.
Quote:
Originally Posted by J Birder View Post
That is a very misleading statement.

The GFCI shuts down when the current flowing in the hot line is not equal to the current flowing in the neutral. The only possible cause of such an imbalance, is that some current is returning as leakage to ground.

If that leakage is flowing through a person, then it might be deadly. However, when there is no person involved, then there is some other leakage path, which is almost certainly harmless.
The current leakage pathway hohenwald48 refers to is a ground fault, and the current is technically called fault current. The ground fault circuit interrupter (GFCI) opens to clear the fault. Just a matter of semantics, but it's the language of the NEC. So as he said, if you have a ground fault, you need to fix it.
KanzKran is offline   Reply With Quote
Old 04-11-2019, 03:22 PM   #65
Member
 
walt_embree's Avatar
 
Join Date: May 2009
Posts: 60
Quote:
Originally Posted by KPC View Post
RV has been fine using campground 50 amp power posts but when plugged into a friends house with a 50 amp GFI protected outlet the breaker pops .
Are campground posts GFI protected? Anyone know what could cause this?
My Samsung residential fridge compressor failed, and that’s what started the GFI to start tripping, although it worked fine for almost 3 years. During the investigation into repair procedures, it was noted by information and the repair person that a fridge should never be plugged into a GFI. Not sure why, but sure enough, dedicated outlet for the house fridge is not GFI’d. So, first step, if Res Fridge, turn it off as part of your isolation strategy. If NOT residential, then proceed as other posters have described in isolating your trouble source. Keep in mind that it might take some time to trip, so when activating circuits, allow some time (many minutes...several hours??) to see how the GFI responds.
walt_embree is offline   Reply With Quote
Old 04-11-2019, 03:30 PM   #66
Junior Member
 
Fleetwood Owners Club
Join Date: Dec 2018
Location: North Bend, OR
Posts: 15
Gary RV Roamer is right on. The only thing that will trip a GFCI is an unbalance of current between the line and neutral on the circuit (4-5ma). I've seen some people, even electricians, wire a GFCI receptacle, shove it back into the box and have the bare ground just barely touch the neutral and the GFCI won't work because just enough of the neutral current will go back on the ground trip the device. Also a likely source could be that fridge ac heater element with a high resistance short, bleeding off to ground.. Follow the troubleshooting path Gary has for you, you'll find it!
powerpro is offline   Reply With Quote
Old 04-11-2019, 04:23 PM   #67
Senior Member
 
Join Date: Apr 2010
Posts: 661
All the Ground Fault Protection Devices are much more protective than the actual danger posed. Your bathroom device is set to 4-6 mA. Your underground swimming pool lights have a GFCI type device set to 30 mA.

So, if you touch a faulty device with a wet hand in your bathroom, when you can quickly pull away, you're allowed to get 4-6 nA. If you're totally immersed in the water, in the deep end and find a faulty light fixture leaking electricity, you can get up to 30 mA before it trips. Weird huh??
bucks2 is offline   Reply With Quote
Old 04-11-2019, 05:03 PM   #68
Tug
Junior Member
 
Join Date: Apr 2009
Location: Roundup MT
Posts: 14
It’s called Kirchoff’s Law ⚡️⚡️

Ok GFI 50 circuit breakers on shore power have caused and is causing big problems in the marina industry. The same for RV’s .
It has to do with current return on the neutral wire.
Grounding or not is not the issue. Refer’s, inverters,battery chargers, microwaves, block heaters, water heaters and so on.
The Only Solution has been to install a isolation transformer on boat or RV side. Such as a Charles..
The input is two hots and a ground. Transformer outlet is two hots, a neutral, and a isolated ground..
You cannot believe the service outfits that are screwing over the public on this. Everybody is a expert until shtf....
Tug is offline   Reply With Quote
Old 04-11-2019, 05:21 PM   #69
Senior Member
 
Bullitt6283's Avatar
 
Join Date: Nov 2018
Location: Shrewsbury, PA
Posts: 202
If I had a GFCI trip, I would want to know... for sure... what the ground fault problem really is. Just plugging into a non-protected power source is not a remedy.

When I worked in a factory building air conditioners, part of the UL testing was a high-potential test of the wiring to see if anything was close to being grounded. The windings of the compressor were excluded from that high voltage test (1500 volts) because the insulation of the wires in the compressor motor is very thin enamel and could be compromised. The same is true of refrigerator compressors. It is somewhat normal that you could have a small amount of hot-to-ground current leakage in refrigerator and air conditioner compressor motors.

As GFCI pedestals become more prevalent, we will be seeing more of these issues.
__________________
Ron and Dagmar, Retired
2016 Jayco Greyhawk 29MV.... 2000 Jeep TJ Toad
2009 Mustang GT (DW's DD)...2009 Mustang Bullitt (My Toy)
Bullitt6283 is offline   Reply With Quote
Old 04-11-2019, 05:44 PM   #70
Senior Member
 
Piros1's Avatar
 
Join Date: Dec 2015
Location: Dittmer, MO 63023
Posts: 1,123
Quote:
Originally Posted by twinboat View Post
No, all campgrounds are not GFCI protected but some are starting to be.

Reading complaints from people tripping them in State CGs. It will probably take years before private CGs switch over.

If switching off breakers, one at a time, doesn't isolate the problem, you may need to start removing the neutral of each item to isolate the leak to ground.

Could also be a surge guard doing its test thats causing the trip.
If you remove the neutral from each circuit please make sure you turn the circuit off before doing so. This is very dangerous, besides the arc flash which may be minor you never want to be in the path of a hot neutral circuit. once the neutral is open you can turn back on to check
__________________
2005 CC Affinity 770, 2006 Jeep TJ
2015 Newmar Essex 4553 2022 Jeep Gladiator.
Piros1 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onboard ground fault conflicts with campground ground fault skatebus80 Country Coach Owners Forum 3 07-15-2017 12:42 PM
Norcold tripping ground fault on shore power rjdelapp RV Systems & Appliances 10 01-26-2012 08:08 PM
Water heater element tripping Ground Fault burfurd RV Systems & Appliances 10 06-20-2011 09:13 AM
Ground fault A/C plug in bathroom of 83 Pace Arrow kartvines Fleetwood Owner's Forum 1 02-06-2011 10:57 PM
Where's the ground fault for the fridge? glashalful Class A Motorhome Discussions 9 01-08-2011 03:02 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:27 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.