Not being a pro at this . Should I not use that ? I ask because id like to know what is meant here "The split to 120 volts is taken care of in the MHs circuit breaker panel. " That circuit i mention has a twist outlet which I recentlly purchased a twist plug that accepts a 30 amp plug .
|
Journey cat, if it doesn't have a 4 wire service do not use it. Your coach needs a neutral and a ground to operate, since the loads on the 2 legs are never equally balanced.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
02-18-2017, 07:28 PM
|
#44
|
Senior Member
Join Date: Jul 2014
Posts: 35,317
|
Quote:
Originally Posted by Journey cat
Not being a pro at this . Should I not use that ? I ask because id like to know what is meant here "The split to 120 volts is taken care of in the MHs circuit breaker panel. " That circuit i mention has a twist outlet which I recentlly purchased a twist plug that accepts a 30 amp plug .
|
The split is taken care of when using the properly wired MATCHING outlet.
You can't just adapt any outlet to your RV.
Did you read the article I referenced ?
|
|
|
02-18-2017, 07:43 PM
|
#45
|
Senior Member
Join Date: Jun 2016
Posts: 611
|
Quote:
Originally Posted by twinboat
The split is taken care of when using the properly wired MATCHING outlet.
You can't just adapt any outlet to your RV.
Did you read the article I referenced ?
|
Not thoroughly . I will take some time for me to absorbe it
But thanks for that Its whats needed !
|
|
|
02-19-2017, 04:09 AM
|
#46
|
Senior Member
|
Quote:
Originally Posted by Vicr
Tim, if your panel is 240 then using a two pole breaker gives you 240 volts. A phase is 120v, B phase is 120v so one pole of the breaker is A phase and the other pole of the breaker is 120v but they are opposing phases which gives you 120/240v, the coach uses 240 volts.
|
Exactly. I thought JourneyCat was asking if he could supply 240 v to the RV. That would mean no neutral in which case he would be supplying all his RV appliances and outlets with 240 volts. So as you described above he needs to supply the RV with 2 120 volt legs and if the coach has a 240 volt outlet and it is wired correctly he will be able to use it.
So technically he is supply 240 volts to the RV, but just be aware like your house it is split between 2 120 volt legs which are 180 degree's out of phase thus giving you the opportunity to obtain 240 volts.
I believe we are all on the same page.
__________________
Tim
Leesburg, FL '07 American Tradition 40Z Cummins 400 ISL
Towing a '14 Honda CRV Both sold
2021 Vanleigh Beacon 41LKB 5th wheel
|
|
|
02-19-2017, 05:02 AM
|
#47
|
Senior Member
Join Date: Jun 2015
Posts: 244
|
Here another one for discussion. An older camp ground we visit was originally wired with just 120v 30a outlets. When they started having more guests that required 50a service they had a guy come in and changed the 30a outlets to 50a. He simply changed the outlet and ran a jumper wire from L1 to L2. These outlets do not have 220v available. Both legs of our coach have power and our surge protector and power management system read it as 30a.
|
|
|
02-19-2017, 05:43 AM
|
#48
|
Senior Member
Join Date: Jun 2016
Posts: 113
|
Quote:
Originally Posted by gcamper
Here another one for discussion. An older camp ground we visit was originally wired with just 120v 30a outlets. When they started having more guests that required 50a service they had a guy come in and changed the 30a outlets to 50a. He simply changed the outlet and ran a jumper wire from L1 to L2. These outlets do not have 220v available. Both legs of our coach have power and our surge protector and power management system read it as 30a.
|
*Shakes head and cringes*
|
|
|
02-19-2017, 08:02 AM
|
#49
|
Senior Member
Join Date: Jun 2016
Posts: 611
|
Its all clear to me now . Lucky was smart enough not try that old circuit .
Next time up there ill see what I can do to correct it Thanks to all !
Thats sure is a valuable electric artical
|
|
|
02-19-2017, 12:20 PM
|
#50
|
Senior Member
Join Date: Feb 2017
Posts: 182
|
Quote:
Originally Posted by Vicr
Tim, if your panel is 240 then using a two pole breaker gives you 240 volts. A phase is 120v, B phase is 120v so one pole of the breaker is A phase and the other pole of the breaker is 120v but they are opposing phases which gives you 120/240v, the coach uses 240 volts.
|
I know what you are trying to say, but there are not two phases. Residential service is single phase.
__________________
'17 Montana 3950BR
|
|
|
02-19-2017, 12:48 PM
|
#51
|
Senior Member
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
|
Quote:
Originally Posted by Todd727
I know what you are trying to say, but there are not two phases. Residential service is single phase.
|
Us non electrical professionals get caught saying two phase even when we know it's not. Makes more sense to us somehow. I have a layman's knowledge of 120/240 power on the consumer side of a weather head but very fuzzy about the power company side. I've heard linemen talk about "center tapped neutral" and have a simplistic notion of L1 coming off the top half of the sine wave and L2 off the bottom or vice-versa. Don't really know how that translates to what's happening up on the transformer.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
|
|
|
02-19-2017, 01:07 PM
|
#52
|
Senior Member
Join Date: Dec 2016
Location: Fortuna Foothills, AZ
Posts: 189
|
Quote:
Originally Posted by Todd727
I know what you are trying to say, but there are not two phases. Residential service is single phase.
|
[moderator edit] Single phase 120/240 systems do have two phases A and B. I design and build electrical systems for a living and well, I'm an expert at this.
Vicr
IBEW Local 46
Seattle, WA
34 years in the trade.
|
|
|
02-19-2017, 04:49 PM
|
#53
|
Senior Member
Monaco Owners Club National RV Owners Club Workhorse Chassis Owner
Join Date: Dec 2013
Location: St. Charles MO
Posts: 4,920
|
Todd must be using verbage thinking of single phase verses 3 phase and there not being a 2 phase.
__________________
2002 Monaco Windsor 40PST 2019 Equinox 1.5L, Blue OX Aventa LX tow bar, Roadmaster EZ5 baseplate, SMI Stay-In-Play Duo, TireSafeGuard TPMS
|
|
|
02-19-2017, 06:28 PM
|
#54
|
Senior Member
Join Date: Oct 2006
Location: Rochester NY
Posts: 2,706
|
Vicr is (obviously) correct. We're getting wrapped around the axle on the terminology. Residential wiring IS single phase, but there are 2 legs on the panel which are 180 degrees out of phase which each other, which cancels current on the neutral. This is known as phase A and phase B.
Contrast this discussion with 3 phase electrical for industrial applications. Not found in residential applications.
Hope this helps.
__________________
Don
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank, Safe-T-Plus
'07 HHR Toad, SMI AFO, Blue OX
|
|
|
02-19-2017, 11:08 PM
|
#55
|
Senior Member
Newmar Owners Club Freightliner Owners Club
Join Date: Oct 2008
Location: SE Louisiana
Posts: 199
|
Some people who have responded are a little off track about residential single phase electric service so I thought I would try to resolve any confusion. As for my credentials, I am an electrical engineer and worked over 40 years for the local electric utility.
Most residential homes receive single phase, 120/240 volt service from their electric utility. Single phase means there is only one phase on that service. The transformer serving the house has two coils inside. One, the primary coil, is connected to the high voltage side with one end connected to the high voltage wire (for example, 7960 volts at the utility I worked for) and the other end connected to ground. This means there is 7960 volts across the primary coil. The other coil, the secondary coil, has three connections. The middle of the coil is connected to ground and is also connected to the neutral wire going to the house. The two outside ends of the coil are connected to the two "hot" or energized wires going to the house. The turns of wire in the secondary coil are designed to produce 120 volts in each HALF of the coil. Therefore one measures 120 volts from each hot leg to neutral or ground. The measurement from one hot wire to the other hot wire is 240 volts because half of the secondary coil adds voltage to the other half of the secondary coil (120v + 120v). Another way to look at it is there is 240 volts across the entire length of the secondary coil and 120 volts across half of it. Electric voltage on both hot wires have the same sine wave so they are the same phase.
Hopefully this helps.
------ Jim
__________________
Jim & Debbie
2017 Newmar Ventana LE 3436
1987 Ford Bronco II or 1974 VW Beetle
|
|
|
02-20-2017, 09:19 AM
|
#56
|
Senior Member
Join Date: Feb 2010
Posts: 4,654
|
There is 2 phase power delivery in some eastern areas but that is a whole nutter thing.
Pay attention to the pros who do this as they have the good information.
Our suggestion is to wire the 50 amp outlet for the rv as such using the correct wire size as if you had 50 amps available as the cost is not much more for materials and labor same.
Less voltage drop and someday if you upgrade the supply you only need to change breaker.
Given following restrictions.
Main supply is 40 amps
Main supply is distance at minimum wire size
We suggest using the 30 amp dual breaker as there is some loss in the wiring that could cause issues if you run too many things that may cause excess draw.
The ac runs about 12 to 15 amps and if 2 installed usually one on each side so you should be fine.
This also gives cushion for other loads of 10 amps as you suggested.
There also may be something in the NEC regarding circuit size related to supply size but that is best left to the pros.
__________________
Tony & Lori
1989 Country Coach Savannah SE
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|