Inverter/ House GFI Tripping

MY RV has been plugged into a house 15amp GFI for 6 months with a 12ga X cord when we are not on the road. Only use is to keep batteries charged. Just this last week its been popping the GFI. Now it does it in about 10 seconds. I replaced the ext cord and GFI. Took a AMP reading and got 5.4 amp draw on the ext cord when plugged in. The only thing on is the inverter which charges the 6 volt batteries which I have to say seem to go dry every two months. Seems they are being over charged and drying out. I can hear them bubbling when being charged.Im thinking the inverter has something to do with the house outlet gfi tripping. Any thoughts ?
ffpmdefi is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-12-2017, 06:49 PM   #2
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Use Google to look for a manual for your inverter/charger. Sounds like it's not working properly. You will destroy your batteries and that bubbling is creating hydrogen gas, very explosive and you could have serious problems if you allow it to continue. The bubbling is also releasing sulphuric acid in vapor form which can cause much damage to the battery compartment.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 08-13-2017, 06:18 AM   #3
Community Moderator
 
Spdracr39's Avatar


 
Monaco Owners Club
Join Date: Jul 2016
Location: Central, Arkansas
Posts: 11,283
Disconnect the batteries and see if it stops blowing the GFI. It is the Converter not the inverter that charges the batteries. They may be all in one unit though.
__________________
2004 Beaver Monterey Laguna IV
Cummins ISC 350HP Allison 3000 6 speed
2020 Chevy Equinox Premier 2.0t 9 speed AWD
Spdracr39 is offline   Reply With Quote
Old 08-14-2017, 05:27 AM   #4
Junior Member
 
Join Date: Oct 2016
Posts: 28
Thanks, Ill try that as soon as I get home today. I've disconnected until I figure it out. Plus i've sent an E mail to Xantrex customer service. Let you know what I find out.
ffpmdefi is offline   Reply With Quote
Old 08-14-2017, 03:17 PM   #5
Member
 
Join Date: Aug 2017
Posts: 49
My GFI in bathroom was doing the same thing. Turns out my fridge ice maker valve busted during the winter and water was crossing the contacts. Odd that fridge was on GFI in the first place. I replaced it with a 20 A "smart GFI" from Home Depot and it would trip or error out while on inverter and kill the fridge (Samsung residential). Worked fine on genset and shore power. I'm ended up moving the fridge feed from the load side to the line side to keep the fridge from losing power. No idea why it isn't happy with the inverter and haven't investigated the root cause yet with an o'scope and checking the grounding and bonding. My best guess is that the inverter isn't really clean and the GFI is so sensitive that it detects it and trips/errors out. '02 Bounder 39z mostly stock.
atroph is offline   Reply With Quote
Old 08-16-2017, 10:27 AM   #6
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,659
The GFCI trips when something in the RV has a ground fault. That's a short between a 120v hot or neutral wire and the RV frame or the electrical ground wire.

Your battery charging problem is the amount of 12v DC current current the inverter/charger is applying to the batteries. You didn't mention the inverter brand/model, but most of them are pretty sophisticated these days. They will, however, overcharge if one of the batteries has either an internal short or high resistance, aka a "bad battery". I suspect that's your problem, but please tell us more about the charger and the battery size/age/condition.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 08-16-2017, 03:28 PM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Have you run the electric water heater, without water in the heater, just before this problem appeared ?

A burnt heater element will still heat water, but trip a GFCI .
twinboat is offline   Reply With Quote
Old 08-17-2017, 12:20 PM   #8
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,659
Quote:
A burnt heater element will still heat water, but trip a GFCI .
Conceivable, I guess, but surely unlikely. An element that was partially destroyed could still heat a little, but tripping the GFCI while doing so is at best a slim chance. That would only happen if a piece of the element dangled and touched the tank wall, shorting slightly.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 08-17-2017, 01:12 PM   #9
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Element*- The element consists of an inner wire surrounded by filler material enclosed in a sheath of copper or stainless steel. The thermostat allows electrical current to flow through the inner wire, and from the wire's resistance, creates heat, which is transferred through the filler material to the outer sheath and is then absorbed by the water.

When they get too hot, they burn thru the outer sheath. If not on to long, they stil conduct power. Problem is the current is leaking to ground. That trips any GFCI.

Here is an article, there are many.

http://www.everything-about-rving.co...l-outlets.html

When water heater elements fail, they cause a neutral fault to ground wether they are in use or not. Turning them off at the switch or breaker changes nothing because the problem is a correctly sensed neutral to ground fault, not a voltage or load fault. This is the primary purpose of a GFCI device, to detect said faults. Remove the white wire from your water heating element and tape it off. Now try plugging into a GFCI source. If electrical system now works, go buy a new heater element, and a new heater tank cathode and change them (flush the crap out of the tank too).
twinboat is offline   Reply With Quote
Old 08-17-2017, 02:42 PM   #10
Member
 
Join Date: Aug 2017
Posts: 49
Weird. Is it common for the WH to be on a gfci?
atroph is offline   Reply With Quote
Old 08-17-2017, 03:27 PM   #11
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Quote:
Originally Posted by atroph View Post
Weird. Is it common for the WH to be on a gfci?
Absolutely not ! The OP and many other plug into GFCI outlets in their houses.

There seems to be a trend of some state parks installing 30 amp GFCI outlets. That's causing some issues.
twinboat is offline   Reply With Quote
Old 08-17-2017, 04:15 PM   #12
Senior Member
 
Workhorse Chassis Owner
Join Date: Jun 2006
Location: Northwestern Montana
Posts: 3,513
I would suspect a bum battery or a faulty inverter/ charger. Boiling the batteries is not normal, nor desirable.
__________________
Dieselclacker
dieselclacker is offline   Reply With Quote
Old 08-18-2017, 04:09 AM   #13
Junior Member
 
Join Date: Oct 2016
Posts: 28
Its a Xantrax RV 2012 GS. I think you may be on track with the bad battery. I talked to the xantrax tech guy and found out that if a battery is low in the bank when the charger first turns on it can pull up to 16.5 amps. Going to check batteries today with a hydrometer. That would explain why I have not had this problem in the past. The only thing that changed is mabie a bad battery. Tech guy also reminded me I can change the shore power AC input level on the xantrax control board from 50amp to 15 amp so it knows not to exceed that amount. Thanks
ffpmdefi is offline   Reply With Quote
Old 08-18-2017, 08:12 AM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Quote:
Originally Posted by ffpmdefi View Post
Its a Xantrax RV 2012 GS. I think you may be on track with the bad battery. I talked to the xantrax tech guy and found out that if a battery is low in the bank when the charger first turns on it can pull up to 16.5 amps. Going to check batteries today with a hydrometer. That would explain why I have not had this problem in the past. The only thing that changed is mabie a bad battery. Tech guy also reminded me I can change the shore power AC input level on the xantrax control board from 50amp to 15 amp so it knows not to exceed that amount. Thanks
A GFCI trips due to a ground fault. Current flowing on the hot line, does not equal the current flowing on the neutral line. Its leaking some to ground. You may be in that leaking path.

A circuit breaker trips due to a current overload. When you draw more current then the wiring can safely handle, it cuts the hot line.

Unless you have a combined Breaker/GFCI, in your panel, one problem won't trip the other.
twinboat is offline   Reply With Quote
Reply

Tags
inverter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inverter/converter tripping GFI jwcgc629 RV Systems & Appliances 49 05-15-2023 09:55 AM
GFI tripping, with inverter and transfer switch pokgunner RV Systems & Appliances 4 05-30-2015 02:50 PM
Tripping a GFI? Automobilist Winnebago Industries Owner's Forum 4 07-08-2011 05:52 PM
Tripping 20Amp GFI? rdalcanto Fleetwood Owner's Forum 11 06-20-2011 02:43 PM
GFI keeps tripping?? little help please FLYING BUTCH Monaco Owner's Forum 12 05-21-2011 11:09 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.