Join CruisersForum Today
Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
RV Power Cord Extension Voltage Drop
Old 03-28-2009, 12:10 PM   #1
oldpa is offline
Senior Member
Join Date: Apr 2006
Location: Homestead,FL
Posts: 126
Here’s the scenario, you back in to your site and find the sweet spot, door lines
up with the pad, an opening in the trees for the satellite dish and you’re level.
Then you pull out your 25 foot built in cable and it’s anywhere from 2 to 5 feet short of the pedestal.
You could just back up but don’t want to do that. You do have a 25-foot extension but what about line loss?
What I’m thinking of doing is to make up an 8-foot extension just to have on hand if needed.
Now for my question, would the line loss difference between an 8-foot or 25 foot extension be significant?
I do have a piece of 3/10 30 amp. cable with a male end on it, so all I’ll need is a female end.

Greg

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-28-2009, 12:23 PM   #2
Route 66 is offline
Community Administrator
Route 66's Avatar


Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,896
I haven't found that to be a problem with my 25' extension cord.

The 8 footer would be more convenient, though.

__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV


  Reply With Quote
   
Old 03-28-2009, 04:21 PM   #3
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
Dirk and I are the same. I have an extension cord, mounted to a SurgeGuard, which stays in the electrical bay. This means I am always using the extension cord. I've never had a bit of trouble.
__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 03-28-2009, 04:30 PM   #4
becks is offline
Senior Member
becks's Avatar
Winnebago Owners Club
Join Date: Sep 2006
Location: SE Minnesota
Posts: 614
I to have never had a problem using my 25 ft ext, and I seem to need it often. But the idea of having a 8 ft does sound good because you are correct one seldom needs more than 5 or 6 ft. Just may have to make one of those up.
__________________
  Reply With Quote
   
Old 03-28-2009, 04:40 PM   #5
yogi154 is offline
Senior Member
yogi154's Avatar
Join Date: Mar 2009
Location: Peotone ILL
Posts: 100
Oldpa

Voltage drop off the pedestal in whith a hundred foot cord the voltage drop would be none. As long as the cords has good ends ( tight connections ) and the cord is the same gauge as the trailer cord 30 or 50 amp. That is as long as the voltage is up to snuff ( 120 volts ) at the pedestal but less volts more power loss.

Hope this helps Wayne
__________________
Wayne & Marti , Yogi spoiled rotten dog & Blackie the cat.
Ford 08 F350 PSD the Black Pig, Jayco Designer 37 RQLS 2010
Peotone , Illinois NAM VET 1st CAV 70-71
  Reply With Quote
   
Old 03-28-2009, 05:28 PM   #6
JC2 is offline
JC2
Senior Member
JC2's Avatar


Newmar Owners Club
Texas Boomers Club
Join Date: Dec 2003
Location: Mo
Posts: 1,829
I bought the 15ft 50A extension cord from CW when it was on sake for $99.00 so I could also have our portable surge guard locked in the storage area. We have not seen any power reduction.
__________________
2004 Newmar DSDP 4015-370hp Cummins-Spartan Chassis-2008 Saturn Vue-Texas Boomers Member-FMCA #402879
  Reply With Quote
   
Old 03-29-2009, 02:27 PM   #7
Clay L is offline
Senior Member


Workhorse Chassis Owner
Join Date: Jun 2003
Location: Full Timer - Sioux Falls, SD
Posts: 1,937
The 8 feet of 10 gauge wire will have a maximum 0.629 volt drop when you are drawing 30 amps. That's not very significant.

25 feet of 10 gauge would have a 1.967 volt drop at 30 amps. Again that's not very much even when added to the voltage drop across the existing cable on your RV.

As I recall, appliances are designed to operate at 120 vac plus or minus 10% or 132 vac to 108 vac.

Unless the pedestal voltage is low you should be okay with either 8 feet or 25 feet of extra 10 gauge cord .
__________________
Clay WA5NMR - Fulltiming- 2004 Winnebago Sightseer 35N Workhorse chassis. Honda Accord toad.
  Reply With Quote
   
Old 03-29-2009, 05:21 PM   #8
dirko is offline
Senior Member


Ford Super Duty Owner
Join Date: Dec 2002
Posts: 467
Hi Ho: Voltage drop in extension cords follows Ohm's Law which is simply that the voltage (Volts) is the current (amps) times resistance (ohms). For example if you use 10 AWG copper wire, resistance is 0.00118 ohms/ft. If you have a 30 amp load and a 25 foot cable, then the voltage drop is 0.00118 times 30 times 25 or 0.89 volts. If you add another 25 foot extension cord you get another 0.89 volt drop. A total voltage drop of about 2 volts is normally not a problem unless the voltage is too low to begin with.

If you want to play around with different wire sizes and load currents, here is a simple web site: http://www.stealth316.com/2-wire-resistance.htm

Another concern for RVers is that the connectors become corroded or don't make good contact with the wires in the cables. When you disconnect pay attention that the plug is not hot, especially when using A/C or other large loads.

Good luck and happy miles, Dirk
__________________
  Reply With Quote
   
Old 03-29-2009, 05:38 PM   #9
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
Quote:
Originally Posted by Dirk Ostermiller View Post
Another concern for RVers is that the connectors become corroded or don't make good contact with the wires in the cables.
Now that is one of the real problems out there!!! This same corrosion/bad-contact problem also extend to the condition of the receiving prongs in the pedestal. We've all seen burned up pedestals and plugs or the black residue on a pedestal that's been fixed (hopefully) all over the place!
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-29-2009, 07:07 PM   #10
hamguy is offline
Senior Member
hamguy's Avatar


Workhorse Chassis Owner
Join Date: Nov 2003
Location: Mesa, AZ USA
Posts: 1,572
We were at a cmpground in Carlock, IL a few years ago. when I pplugged in at the brand new 50A pedistal, I found the voltage to be under 108 volts with only one AC running.

I talked to the owner and he told me with a big, proud smile that his buddy on the local police force was an expert and they had rewired the park from a new big transformer.

He took me over to the transformer (over 300' from my site) which certainly looked to be big enough and said it had cost him a bundle to run the #10 ALUMINUM wires to each double site.

Can you imagine? 100A for 2 RVs? On a 300' #10 run? Nothing could disuade him from his position.

OH, the low voltage took out my AC control board.
__________________
Wretched excess is just barely enough.

2002 Itasca Suncruiser - WH Chassis - 35U - 2006 Jeep Liberty
  Reply With Quote
   
Old 03-29-2009, 08:30 PM   #11
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
Quote:
Originally Posted by hamguy View Post
Can you imagine? 100A for 2 RVs? On a 300' #10 run? Nothing could disuade him from his position.
Don't you just love that type of DIYer? A double whammy eh? 1) that they did it and 2) nothing could convince him of the utter error/saftey hazard!!!!

So, the NEC rates #10 AL in 3wire configuration at 25amp at 25degrees C. They further rate it as fusing at 247amp. So either these guys are basically running a 300ft fuse for your protection (how nice of them LOL) or you are getting a line loss at 240v at ONLY 25amps of nearly 30V so each 120v leg is delivering only (240-30=210/2) or 105v at 25a/leg!!! And they are thinking that 2 * 50amp power hogs will plug into the same #10 line? Run Toto, run!!!

Oh, I get it now, that CG wired by those DIYers is really multi-tasking - they are in a snowy area and they use the wire heat to melt the drievway snow right?
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-29-2009, 08:42 PM   #12
Ray,IN is offline
Senior Member
Ray,IN's Avatar


Join Date: Aug 2001
Location: North America somewhere
Posts: 4,925
Great reply Dirk! Excellent advice.
Hamguy, this is a solid reason to always have a line voltage monitor plugged in where it is easily seen_and frequently. One model costs <$20, very cheap considering the cost of A/C repair.
__________________
"As nightfall does not come at once, neither does oppression. In both instances there is a twilight where everything remains seemingly unchanged. And it is in such twilight that we all must be aware of change in the air - however slight - lest we bec
  Reply With Quote
   
Old 03-29-2009, 10:17 PM   #13
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
Quote:
Originally Posted by Dirk Ostermiller View Post
Hi Ho: Voltage drop in extension cords follows Ohm's Law which is simply that the voltage (Volts) is the current (amps) times resistance (ohms). For example if you use 10 AWG copper wire, resistance is 0.00118 ohms/ft. If you have a 30 amp load and a 25 foot cable, then the voltage drop is 0.00118 times 30 times 25 or 0.89 volts. If you add another 25 foot extension cord you get another 0.89 volt drop. A total voltage drop of about 2 volts is normally not a problem unless the voltage is too low to begin with.

If you want to play around with different wire sizes and load currents, here is a simple web site: http://www.stealth316.com/2-wire-resistance.htm
Sorry to say, but in taking a closer look there is a slight, but common, oversight in the calculation given above and of that used on the particular web site listed.

Ohms law as used in both these cases applies to a single wire, not a paired wire. Hence, in a paired wire situation (120vAC) the entire circuit length is twice the extension cord length (the hot PLUS the neutral return). Therefore, for a 25ft cord, the circuit length is actually 50ft. This means the voltage loss for each 25foot #10 copper extension cord operating loaded at 30amps is 1.8v (double the 0.89v above). Round that up to about 2v per cord used and that loss is from the voltage at the pedestal (which is the correct voltage to plug into Ohm's law as used here as well).

This is a common oversight and is frequently used incorrectly in many DIY web site calculators where they use all the correct NEC tables (as the steath316.com site does) but make the incorrect assumption about total circuit length in the examples (like the stealth316.com site does). If you use a web calculator you must verify exactly what assumption they use to calculate wire length. Seldom do the non-industry web sites identify their wire length assumption in their calculator which means you are likely to get erroneous results. All the industry web sites are clear about this assumption. Of course, you can always just use Ohm’s law yourself with the correct circuit/wire length as indicated above and the correct starting voltage. Also note that lower voltage (like 12v landscape lights and other 12v car/RV calculations) will have different wire factors than those for higher voltages. Losses at low voltage are significantly higher than at higher voltages.
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-30-2009, 08:14 AM   #14
Clay L is offline
Senior Member


Workhorse Chassis Owner
Join Date: Jun 2003
Location: Full Timer - Sioux Falls, SD
Posts: 1,937
RVDude is correct about the length. Also there should be some derating for temperature increase of the cable. In addition the ohms per foot tables out there are usually for solid cable while the cables used are stranded and some de-rating should be applied for the "lay" of the cable. That is since the cable is not solid there will be a smaller actual cross section for the stranded cable than for the solid thus a higher oms per foot.

I wrote a program some time back that takes these things into account as well as makes it clear that the total run length must be used.
If anyone is interested it can be downloaded at http://www.rvforum.net/index.php?opt...=289&Itemid=63

__________________
Clay WA5NMR - Fulltiming- 2004 Winnebago Sightseer 35N Workhorse chassis. Honda Accord toad.
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Cord Reel Pete & Cynthia Alpine Coach Forum 4 09-16-2008 09:28 PM
30 Amp Extension Cord okay? cabindog Winnebago Industries Owner's Forum 9 06-26-2008 09:19 AM
Toshiba AC power cord GG1 Technology: Internet, TV, Satellite, Cell Phones, etc. 9 04-23-2008 12:07 PM
Fleetwood Power Lift Recall Beer Belly Pop Up Discussion 2 11-12-2007 02:13 PM
Low voltage in camp grounds Donald Norder sr. MH-General Discussions & Problems 27 08-16-2006 08:13 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 03:13 AM.