Watch Out For This!!!

I found my 15 Amp breaker for my power plug to the coach at the house tripping and started to check for the problem and I found it.

I went to the power bay and on going to unplug, found that my 10 ga. power cord plugged to the 30-15amp reducer was melted together. Could have been catastrophic!

I watched a video on RV Travel that mentioned the small reducers as inferior. Now I know it to be true. I went out and purchased a 30-15Amp Camco "dogbone" one and everything is fine.

My advise, if you've got one of these small reducers....get rid of it!!!

Click image for larger version

Name:	ImageUploadedByiRV2 - RV Forum1414416913.530335.jpg
Views:	212
Size:	298.9 KB
ID:	77585
__________________

__________________
Les (RVM12), Bonnie, Morgan and 4 leggers Bella & Bruce
2010 Forest River Cardinal 3450RL 40' Full Body Paint- 2015 Ram 3500 Laramie 6.7 ltr Turbo Diesel, 68RFE Trans. 4x4 SRW SB Pullrite 2900 18K FMCA-420438 Good Sam
Dogpatch is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-27-2014, 08:45 AM   #2
RVM #74
 
PushedAround's Avatar


 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
Les, which is the part that burned up, the cylindrical adapter on the left?
__________________

__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 10-27-2014, 08:56 AM   #3
Senior Member
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Jan 2013
Location: michigan-tip of the mitt
Posts: 1,382
Those legs on your power cord end need to be cleaned to a shiny surface or you will always have elec. issues. I use the small adapter when I am at the S&B with no issues.
__________________
HR 29 fks TT, 1 slide, Chevy Silverado
Next stop?
t55watson is offline   Reply With Quote
Old 10-27-2014, 09:10 AM   #4
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by dogpatch View Post
I found my 15 Amp breaker for my power plug to the coach at the house tripping and started to check for the problem and I found it.
I went to the power bay and on going to unplug, found that my 10 ga. power cord plugged to the 30-15amp reducer was melted together. Could have been catastrophic!
dogpatch
That "melting" is NOT the fault of the electrical adapter/reducer.
It's caused by using more than 15-20 AMPs of power in the coach when connected to a 15 AMP receptacle via an extension cord.
Common sense energy management will prevent that from happening.
Mel
'96 Safari
__________________
mel s is offline   Reply With Quote
Old 10-27-2014, 09:24 AM   #5
Senior Member
 
monkey's Avatar
 
Join Date: Sep 2011
Location: Arkansas
Posts: 2,250
I use one of those 'type' adapters to keep the rv plugged in the garage... But the only drain really is the convertor to keep the batteries up.. No problems yet,,, but I do check it from time to time... Not like we would try to run the AC or something off of it...
__________________
Monkey, pilot of a Great Dane hauler,
2015 Silverado 2500 Duramax/Alison 4x4 CrewCab 2016 Cougar 28SGS
1ST CAV
monkey is offline   Reply With Quote
Old 10-27-2014, 09:30 AM   #6
Senior Dude
 
Dogpatch's Avatar


 
Forest River Owners Club
Join Date: Sep 2010
Location: Somewhere, BC.
Posts: 5,584
Blog Entries: 8
Quote:
Originally Posted by PushedAround View Post
Les, which is the part that burned up, the cylindrical adapter on the left?
It was the joint itself that overheated.

Quote:
Originally Posted by mel s View Post
dogpatch
That "melting" is NOT the fault of the electrical adapter/reducer.
It's caused by using more than 15-20 AMPs of power in the coach when connected to a 15 AMP receptacle via an extension cord.
Common sense energy management will prevent that from happening.
Mel
'96 Safari
I agree, I found my electric switch for my Aqua Hot on when I started looking for possibilities of cause.

I still believe those all in one reducers to be inferior. The "dogbone" style is the recommended.

Here's what I bought.

http://www.amazon.ca/Camco-55165-12-...xp_grid_pt_1_1
__________________
Les (RVM12), Bonnie, Morgan and 4 leggers Bella & Bruce
2010 Forest River Cardinal 3450RL 40' Full Body Paint- 2015 Ram 3500 Laramie 6.7 ltr Turbo Diesel, 68RFE Trans. 4x4 SRW SB Pullrite 2900 18K FMCA-420438 Good Sam
Dogpatch is offline   Reply With Quote
Old 10-27-2014, 09:37 AM   #7
RVM #74
 
PushedAround's Avatar


 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
Quote:
Originally Posted by dogpatch View Post
It was the joint itself that overheated.
I am aware of that, see it all the time. Your picture answered my question though, it was a failing (overheating) connection on the cylindrical adapter that was potentially at fault.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 10-27-2014, 09:38 AM   #8
Registered User
 
Join Date: Sep 2014
Posts: 2,322
Luckily we have 12 Awg/ 20 amp breakers. The connection to the extension cord still was getting warm if the AC was running. I made a 12 gauge extension cord out of romex and an outlet and this connection stays room temp. (using IR to test for heat)
Using any extension cord to run the AC can be problematic. The "melting" was proof that the weakest link gets the hottest. With brand new adapters it would likely be very difficult to melt with 10 gauge extension cord and 15 amp breaker. Still not the best solution if you want to run the AC.
__________________
okcnewbie is online now   Reply With Quote
Old 10-27-2014, 11:02 AM   #9
Senior Member
 
Join Date: Sep 2014
Location: Newcastle West, Ireland
Posts: 392
Quote:
Originally Posted by okcnewbie View Post
Luckily we have 12 Awg/ 20 amp breakers. The connection to the extension cord still was getting warm if the AC was running. I made a 12 gauge extension cord out of romex and an outlet and this connection stays room temp. (using IR to test for heat)
Using any extension cord to run the AC can be problematic. The "melting" was proof that the weakest link gets the hottest. With brand new adapters it would likely be very difficult to melt with 10 gauge extension cord and 15 amp breaker. Still not the best solution if you want to run the AC.
10 gauge cable at 30 amps is good for max 50 feet but that 15 amp adapter will heat if you overload it no matter how good the connection and the dog-bone is still only 15 amps at one end and subject to the same heating, you are asking for trouble when overloading them.
__________________
'98 Southwind 34L, too many cameras, old hat, young heart.
May the light be with you.
Mentor is offline   Reply With Quote
Old 10-27-2014, 11:06 AM   #10
Senior Dude
 
Dogpatch's Avatar


 
Forest River Owners Club
Join Date: Sep 2010
Location: Somewhere, BC.
Posts: 5,584
Blog Entries: 8
Typically I only have the fridge and inverter/charger in use in my driveway.
__________________
Les (RVM12), Bonnie, Morgan and 4 leggers Bella & Bruce
2010 Forest River Cardinal 3450RL 40' Full Body Paint- 2015 Ram 3500 Laramie 6.7 ltr Turbo Diesel, 68RFE Trans. 4x4 SRW SB Pullrite 2900 18K FMCA-420438 Good Sam
Dogpatch is offline   Reply With Quote
Old 10-27-2014, 11:50 AM   #11
Senior Member
 
mrt_1111's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
iRV2 No Limits Club
Join Date: Oct 2012
Location: Colorado Springs, CO
Posts: 974
Quote:
Originally Posted by dogpatch View Post
Typically I only have the fridge and inverter/charger in use in my driveway.
Add up all the amps from the fridge/inverter/light/fan/heater/everything and and I think you will find the reason it melted. I wonder if they make a 15 amps power protector thingie for people who plug in to their garage. Or maybe put a gfi outlet.
__________________
Mark
1999 Bounder 32H Ford V10, 2012 Ford Focus, Pretty DW, 1 cat. Retired USAF
mrt_1111 is offline   Reply With Quote
Old 10-27-2014, 12:00 PM   #12
RVM #74
 
PushedAround's Avatar


 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
If it is pulling more than 15 amps on a consistent basis, the S&B circuit breaker should have tripped. A deteriorating connection between the plug and receptacle blades will cause a heat buildup and the observed problem even though the current draw may have been within acceptable operating parameters i.e. 80% of the maximum circuit rating.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 10-27-2014, 12:07 PM   #13
Senior Dude
 
Dogpatch's Avatar


 
Forest River Owners Club
Join Date: Sep 2010
Location: Somewhere, BC.
Posts: 5,584
Blog Entries: 8
Quote:
Originally Posted by mrt_1111 View Post
Add up all the amps from the fridge/inverter/light/fan/heater/everything and and I think you will find the reason it melted. I wonder if they make a 15 amps power protector thingie for people who plug in to their garage. Or maybe put a gfi outlet.
Never had a problem in 4 years with only fridge and inverter/charger on. As mentioned, I forgot to turn off the Aqua Hot Electric switch.
__________________
Les (RVM12), Bonnie, Morgan and 4 leggers Bella & Bruce
2010 Forest River Cardinal 3450RL 40' Full Body Paint- 2015 Ram 3500 Laramie 6.7 ltr Turbo Diesel, 68RFE Trans. 4x4 SRW SB Pullrite 2900 18K FMCA-420438 Good Sam
Dogpatch is offline   Reply With Quote
Old 10-27-2014, 03:58 PM   #14
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,831
First: There are two common causes of the failure you photographed.

One is dirty contacts, Often we let those get kind of tarnished and do not polish them up before we plug 'em in.

But in this case, let me ask,,, the breaker that feeds the outlet where you plugged in , 15 or 20 amps?

Duplex outlets come in two common flavors,, one has two parallel slots, it has holes (or slots) that accept 14ga wire and it is rated 15 amp

The other has one straight slot (The hot) and one "T" shaped (Neutral) and has no holes for the wire, you bend the 12ga (or larger) wire around a screw and tighten well. This is a 15/20 amp outlet and is often fed with a 20 amp breaker.

The puck and the cord end were both 15 amp rated. Pulling 20 (or even 15) can melt them.
__________________

__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where to watch fireworks in OR? emeraldlake Northwest Region 5 07-06-2014 01:42 AM
How much data to watch movie S-n-L Technology: Internet, TV, Satellite, Cell Phones, etc. 19 05-08-2014 05:54 PM
DW and I are trying to watch a DVD need help Dawg44b Entegra Owner's Forum 11 05-04-2014 09:10 PM
Stronger Beer! Watch This! Dogpatch Just Conversation 12 07-16-2013 09:38 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:12 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.