Question 50 amp down to 15 amp for use in shed

Greeting all, I have my 1986 HR Imperial hooked into a 50 amp outlet dropped down to 30 on a regular residential lot. There is a second 50 amp outlet that is not in use. I want to use that outlet to run extension cord/cords to a portable shed I have on this lot. I do not want to hardwire the electric due to that would require permits, ect.. I just want to run lights,radio and basic shop tools in the shed. Would it be feasable to drop all the way down from the 50 to the 15 without hurting anything in the shed,and how many cords could I run off the 30 amp end? Would this setup cause to much heat in the cords? Inquiring minds want to know
__________________

__________________
SEMPER FI MAC
steelbreezzz is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-22-2015, 08:38 PM   #2
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,416
Yep, no problem. But I'd limit the draw to 20 amps at the most and then only with good extension cords of no more than 50'
__________________

__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 05-22-2015, 08:40 PM   #3
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 14,970
Ok , assuming this an RV 50amp, plug , not a 220v 50 amp welder plug.
If you adapt the 50amp down to a 30 amp , down to a 15amp cord, you will have 100amps, ( or 50 depending on the adaptor) available on a 15 amp cord. Very easy to overheat the cord , and create a fire, or shock, hazard.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-22-2015, 08:47 PM   #4
Junior Member
 
steelbreezzz's Avatar
 
Join Date: Jan 2015
Location: monahans tx
Posts: 13
Yes it is a regular 50 amp RV outlet. They were going to put 2 RV's on this lot but the city would not allow them to do it. Could I wire the 50 straight into a wall mounted panel and then wire the shed like a regular garage? If the power is plugged into the pole I can argue that it is still not hardwired (technicality, but I want to play with my stuff)
__________________
SEMPER FI MAC
steelbreezzz is offline   Reply With Quote
Old 05-22-2015, 08:51 PM   #5
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 14,970
Quote:
Originally Posted by steelbreezzz View Post
Could I wire the 50 straight into a wall mounted panel and then wire the shed like a regular garage?)

That would be the safe way , 50 amp plug into a sub panel with a pair ( or more ) of 15amp breakers, and outlets, then run your cords from there.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-22-2015, 10:34 PM   #6
Senior Member
 
Join Date: Feb 2010
Posts: 4,492
Inspectors are wonderful folks...

If it plugs in it is a consumer device or appliances...thus off limits.

In a previous home had garage wiring with plugs as the inspector was measuring the distance between staples...

Put plugs on and he was not happy but powerless....

Go to the store and get a premade range cord with the correct style end, see what the number on the face of your outlet is and match it.

While there look through the selection of subpanels as they have many and most come with a handfull of breakers.

Have someone help you to open the package and make sure 2 ground busses...one tied to neutral and one tied to the case...many of these only have one.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 05-22-2015, 11:23 PM   #7
Junior Member
 
steelbreezzz's Avatar
 
Join Date: Jan 2015
Location: monahans tx
Posts: 13
I saw on a video about a green screw that has to be removed from a sub panel. gonna have to go back and watch them again to make sure.
__________________
SEMPER FI MAC
steelbreezzz is offline   Reply With Quote
Old 05-22-2015, 11:24 PM   #8
Senior Member
 
Join Date: Sep 2013
Posts: 596
What is a 50 amp outlet dropped down to 30A? How many tools do you need to run at once in the shed? How far is the shed from the post? What you could do is go to your local electrical contractor, give them the length of the run, what plug you need at the post and they'll build you an extension cord with either a single or twin duplex outlets. These outlets will have their own circuit breaker. It's just like running a sub panel in the shed but in this case it's temporary. Very common in the construction industry.
__________________
marcham is online now   Reply With Quote
Old 05-22-2015, 11:58 PM   #9
Senior Member
 
garbonz's Avatar
 
Join Date: Aug 2013
Posts: 620
Quote:
Originally Posted by marcham View Post
What is a 50 amp outlet dropped down to 30A? How many tools do you need to run at once in the shed? How far is the shed from the post? What you could do is go to your local electrical contractor, give them the length of the run, what plug you need at the post and they'll build you an extension cord with either a single or twin duplex outlets. These outlets will have their own circuit breaker. It's just like running a sub panel in the shed but in this case it's temporary. Very common in the construction industry.
Yep, that's the solution. Please note that the 50Amp RV plug at the house is still a 220 volt plug, it is at the RV end that it becomes two 110v legs. So if you don't use pre-wired adapter to your shed that will only run off one leg, then make sure you keep this in mind when wiring up your sub-panel or your duplex outlet(s).
__________________
2005 Bigfoot 1500C8.2 Truck Camper; MANY mods, to many to list
2007 Chevy 2500 Duramax Std Bed Ext Cab
garbonz is offline   Reply With Quote
Old 05-23-2015, 07:26 AM   #10
Senior Member
 
Join Date: Sep 2013
Posts: 596
Technically, all households have a 3 wire single phase 120V service You could not use 120V appliances if you had 240V service from the utility. Because your neighbourhood transformer is center tapped (neutral conductor) , you get half of the output on each leg, but each leg is still 120V from neutral. By using both hot legs together (no neutral), you are tied in to the outside taps of the transformer thus have 240V available.
__________________
marcham is online now   Reply With Quote
Old 05-24-2015, 12:01 AM   #11
Junior Member
 
steelbreezzz's Avatar
 
Join Date: Jan 2015
Location: monahans tx
Posts: 13
thanks all. in the shed i plan on using LED's for lighting. and then shop wise just basic stuff like a bench grinder and small drill press. the compressor is just a small 100 gal. model that just plugs into a normal outlet. I will not have anything that needs a larger outlet. nothing like a dryer or welder. The shed will actually be closer to the pole than the RV. about 10 ft away.
__________________
SEMPER FI MAC
steelbreezzz is offline   Reply With Quote
Old 05-24-2015, 09:26 AM   #12
MPH
Senior Member
 
MPH's Avatar
 
Join Date: Aug 2014
Location: Somewhere on the Rainbow. Fulltiming and lovin' it!
Posts: 2,036
Quote:
Originally Posted by Skip426 View Post
Ok , assuming this an RV 50amp, plug , not a 220v 50 amp welder plug.
If you adapt the 50amp down to a 30 amp , down to a 15amp cord, you will have 100amps, ( or 50 depending on the adaptor) available on a 15 amp cord. Very easy to overheat the cord , and create a fire, or shock, hazard.
Should I be worried??? My MH is plugged in at the covered storage unit this way. I took the 50 amp cord down to a 30 amp adapter and then took that down to a 15 amp adapter from which I run a heavy gauge extension cord that is plugged into the wall at the storage unit. We keep the 8 cubic ft residential frig running this way. Is this a safe setup? We've been doing it for 8 mos with no problem so far.

Thanks,

Mel
__________________
MPH is offline   Reply With Quote
Old 05-24-2015, 09:40 AM   #13
Senior Member
 
Qwert66's Avatar
 
Newmar Owners Club
Join Date: Nov 2011
Location: Michigan
Posts: 762
Send a message via Skype™ to Qwert66
Your case is different because you are fed from a breaker protecting the outlet you are plugged into. Probably 15 or 20 amp. If your fridge is the ONLY thing using the juice then no problem. If you are connected to a 20 amp breakered outlet AND using a small extension cord rated at 15 amps AND using more than 15 amps then there could be a problem.

The earlier post would be protected by a 50 amp breaker only and could push 50 amps thru a 15 amp necked cord which could cause problems and not be to code.


The difference is he would be plugged into a 50/100 amp line and you would be plugged into a 15/20 amp line.
__________________
1999 Newmar Mountain Aire MADP 4080, Cummins ISC 8.3L, Allison, Spartan MM IFS, Howard Power Center, Chev Trailblazer LTZ Towed w/ BlueOx rigging, Segway X2.
www.shaw11.com
Qwert66 is offline   Reply With Quote
Old 05-24-2015, 06:42 PM   #14
Senior Member
 
dvmweb's Avatar
 
Join Date: Sep 2010
Location: MI
Posts: 982
Build a small 50 amp to 20 amp power distribution box. You can buy one at home despot. Spendy but very handy. It has a marine twist type connector. I have seen a regular rv plug adaptor for this.

I had one built. I use it for parties to power outdoor lights, electric cookers/crockpots/roasters. I also use it for powering our bands sound system and amps.


2013 FleetWood Expedition 38B
__________________

__________________
dvmweb is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
20 amp Stay-in-play fuse keeps blowing Donut lover Toads and Motorhome Related Towing 11 03-19-2015 07:00 AM
Dutch Star Gas Cooktop Hidden Fuse Dutch Star Don Newmar Owner's Forum 2 03-10-2015 07:16 PM
Norcold 1200 W/ Amish CU Intermittent Fuse Blow ProjectPro RV Systems & Appliances 1 03-02-2015 05:41 PM
Fuse for roof lights ?? caheath Workhorse and Chevrolet Chassis Motorhome Forum 3 02-21-2015 09:30 PM
I found the fuse harleychief Newmar Owner's Forum 6 05-14-2014 11:18 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.