Electrical help

Looking for some help from our resident electricians.

I am hosting an evening soiree (French for hoe-down) in our backyard. Need some electricity for lights and such, and thinking about the 50 amp outlet I have on side of utility shed. Will this work?

Purchase a 30 ft replacement 50 amp cord (male plug on one end, bare wires on other). Place junction box on bare end. Attach a short length of 10 or 12 gauge wire to the black, white, and green wires. Connect a 20 amp outlet to other end of this pigtail. Connect another pigtail to the red, white, and green wires in the junction box, to another outlet. So two 120v/20 amp outlets powered by the 50 amp cord.

Isn't this essentially what the CB panel inside the MH does? Leg 1 and Leg 2?

Since the neutral and ground wires are common to both outlets, will this result in a dangerous situation?
Should the pigtails be of heavier gauge?
Regular outlets or GFI's?

When the party is over, I can put a replacement female 50 amp plug on the cord, and have a 50 amp extension cord.

Thoughts?
__________________

__________________
2016 Newmar Ventana 4002
2013 Honda CRV
bandcworkhorse is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-13-2019, 06:44 AM   #2
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 1,829
It will work as you described. BUT you must attach the #6 wire to a 20 amp breaker. Use GFI's
__________________

__________________
2011 Keystone Sprinter BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 10-13-2019, 08:12 PM   #3
Senior Member
 
Workhorse Chassis Owner
Join Date: Mar 2006
Location: Columbus, IN
Posts: 164
Thanks for reminding me to protect the branch circuits with appropriate CB's, Cavie. Just thinking (that usually gets me in trouble), to minimize the number of connections, can I temporarily swap the 50 A double pole breaker that is now in the panel, for a 20 A double pole breaker?
Thanks.
__________________
2016 Newmar Ventana 4002
2013 Honda CRV
bandcworkhorse is offline   Reply With Quote
Old 10-13-2019, 09:13 PM   #4
Senior Member
 
Join Date: Jul 2014
Posts: 19,503
That sounds like a great way to cure the big breaker/light gauge wire issue.

Pop a double 20 amp breaker and place of the 50 amp and your safe from short circuits overloading the wires.
twinboat is online now   Reply With Quote
Old 10-13-2019, 09:21 PM   #5
tcg
Senior Member
 
tcg's Avatar
 
Join Date: Aug 2016
Posts: 1,148
Couldn't you just use one of these?

Conntek Y1450520S NEMA 14-50 50-Amp 125/250-volt RV/Generator Y-Adapter Plug to U.S. 15/20-Amp Female Connectors https://www.amazon.com/dp/B00BHGXYRC..._YS9ODb13ZNA5D
tcg is offline   Reply With Quote
Old 10-14-2019, 03:15 AM   #6
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 1,829
Quote:
Originally Posted by tcg View Post
Couldn't you just use one of these?

Conntek Y1450520S NEMA 14-50 50-Amp 125/250-volt RV/Generator Y-Adapter Plug to U.S. 15/20-Amp Female Connectors https://www.amazon.com/dp/B00BHGXYRC..._YS9ODb13ZNA5D
This is the reason as an electrician I think dog bones need to be outlawed. If he uses that and plugs in a 20 amp appliance it will be fused at 50 amps. Not very smart!
__________________
2011 Keystone Sprinter BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 10-14-2019, 04:51 AM   #7
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,664
Quote:
Originally Posted by cavie View Post
This is the reason as an electrician I think dog bones need to be outlawed. If he uses that and plugs in a 20 amp appliance it will be fused at 50 amps. Not very smart!

He could still change the 50amp breaker for a 20amp. JMHO
__________________
Steve & Sally / Hudson Our Little Pom / Heidi, Houston & HiTee Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Old 10-14-2019, 05:23 AM   #8
tcg
Senior Member
 
tcg's Avatar
 
Join Date: Aug 2016
Posts: 1,148
Quote:
Originally Posted by cavie View Post
This is the reason as an electrician I think dog bones need to be outlawed. If he uses that and plugs in a 20 amp appliance it will be fused at 50 amps. Not very smart!
Then get a gfci power strip with a 15a or 20a breaker. The whole thing would come in under a hundred bucks

I would think, unless the OP is an electrician, using a solution that doesn't require building an electrical box would be safer.

I know I wouldn't want to fool with building a 50amp box.
tcg is offline   Reply With Quote
Old 10-14-2019, 06:59 AM   #9
Senior Member
 
Join Date: Jul 2014
Posts: 19,503
Maybe you can rent a " Spider Box " from a local rental place.

It does exactly what you want to do.Click image for larger version

Name:	Capture%2B_2019-10-14-07-58-40.jpeg
Views:	8
Size:	37.1 KB
ID:	263533
twinboat is online now   Reply With Quote
Old 10-16-2019, 09:12 PM   #10
Member
 
Join Date: Sep 2018
Posts: 50
I haven't checked, but #6 into a 20 amp breaker might not fit.
__________________
2015 Silverado CC DRW Duramax
2006 Hitchhiker Champagne
TB673 is offline   Reply With Quote
Old 10-16-2019, 09:30 PM   #11
Senior Member
 
Join Date: Jul 2018
Posts: 1,498
Quote:
Originally Posted by TB673 View Post
I haven't checked, but #6 into a 20 amp breaker might not fit.

It won't. Most 20 amp breakers accept wire sizes up to #10.


For those not familiar: the AWG (American Wire Gauge) numbers get bigger as the wire gets smaller, i.e. #10 is smaller than #4. When you get to Really Big Wires, things change but that's beyond this discussion.


I like the spider box idea - it ticks all the boxes for overcurrent protection (circuit breakers) and ground fault protection. The rental yard probably has cables made up to plug into your 14-50 outlet.


Of all these ideas I most dislike the homeowner changing out his 50 amp, 2 pole breaker for a 20 amp 2 pole breaker. I'd rather have an electrician build a break out box with the appropriate fuses or breakers than have a home owner swapping breakers in his home's hot (energized) panel.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 10-17-2019, 08:45 AM   #12
Senior Member
 
Workhorse Chassis Owner
Join Date: Mar 2006
Location: Columbus, IN
Posts: 164
So many great ideas. Thanks, all, for the inputs.
I had not run across the y-cord in my internet search. That will suffice, and Amazon promises it will be here by Friday.
The spider box would be better, but all the ones I found online and at Sun Rental, use a twist lock input connection. No one had a clue how to adapt to a 4 blade connection.
I have a couple power strips with 15 or 20 amp fuses, so I think I'm good to go. As it turns out, food heating is by Sterno, lighting is a few strings of Christmas tree lights, and the DJ claims he's never started a fire. Oh, and the bouncy house.
My electrician was happy to build a breakout box, but time was an issue. He relayed to me the general idea I posted above. You filled in the details.
When you live in a 110 year old house, you have to become a junior electrician, plumber, plasterer, window glazer, and finish carpenter. All of which I have been in just the past month. Butcha got to know your limitations, thus I have Pro's on my speed dial. And of course, this website, from which I have learned so much.

Thanks again, folks.
BTW, if I'm lucky, I get to spend 60 days a year in my MH. And that's up from what I could before I "retired".
__________________

__________________
2016 Newmar Ventana 4002
2013 Honda CRV
bandcworkhorse is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No electrical power at one lug (3) Left Front Electrical Center RobRoy Monaco Owner's Forum 18 03-31-2017 12:59 PM
Help help help Georgie Boy 1994 start problem BDS52 Ford Motorhome Chassis Forum 13 02-04-2016 11:13 AM
help help help WD9BOB Class A Motorhome Discussions 7 09-08-2012 01:07 PM
Help, Help, Help, Oh Please Help. Possum RV Systems & Appliances 11 04-23-2012 11:35 PM
110V Electrical help needed wagonmaster2 Winnebago Industries Owner's Forum 9 12-03-2008 07:13 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:51 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
×