Old 05-18-2015, 08:04 PM   #1
Junior Member
 
Join Date: May 2015
Posts: 9
'93 Itasca Sundancer--no 110v power

First of all, warm greetings to the forum from the Yukon! I am new to RV'ing and having fun playing with and learning about my '93 Itasca Sundancer 500.

But I have run into a puzzle and hope there is some wisdom in the community to help me diagnose the problem. Here are the details: While replacing the house batteries, in spite of thinking I was being careful, I shorted the terminals for a brief moment. Sparks flew, the terminal wingnut fused to the stud, but otherwise over quickly and straightforward to start over with more care...

Once the batteries were installed all seemed in good order, all systems go. I then started the on-board Onan genset, which started fine. But no 110 power to the system. So I checked the breakers--all working fine. I then checked the 30 amp breaker in the battery bay. It had not tripped and was working properly.

I notice that there is a solenoid (isolator?) in the battery bay--Winnebego PN 8188-01-000. So my question: Is it possible that my shorting the battery might have fried the solenoid? And, if the solenoid was fried, would this produce the symptoms I am experiencing?

I have not checked voltage going into the batteries to see if they are charging when the Onan (or the RV engine) is running. I can do this, but am curious if there is anything else I should check?

Thank you to the community for making wisdom and experience available!

Onfoot.
__________________

__________________
Onfoot is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-18-2015, 08:08 PM   #2
Senior Member
 
Join Date: May 2013
Location: Aransas Pass, TX
Posts: 251
Have you checked the breakers ON the generator? There will be one or two together, on or near the control panel depending on what model you have. The gennie will fire up and run with breakers off, but not deliver any power until they are on.

The isolator switch is designed to automatically switch from shore power to gennie power when you start the generator; it often takes a few minutes before the switchover.

I can think of no scenario where a short in the battery would affect the generator. The gennie will start from the batteries, but it is unlikely it will directly charge them. The normal configuration is for 110 power to go to the converter, which in turn converts the 110v to 12 volt; the converter then charges the house batteries from a built-in charger, usually a pretty terrible one.
__________________

__________________
HoneyBadger is offline   Reply With Quote
Old 05-18-2015, 08:22 PM   #3
Senior Member
 
CJ7365's Avatar
 
Tiffin Owners Club
Join Date: Mar 2015
Location: Southern NM
Posts: 1,524
As Honey Badger said, check the breaker (s) located on the gen set.
__________________
CJ7365 is offline   Reply With Quote
Old 05-18-2015, 08:23 PM   #4
Senior Member
 
Franka548's Avatar
 
Freightliner Owners Club
Retired Fire Service RVer's
Join Date: Apr 2011
Location: N E Ohio
Posts: 3,465
Does your unit have an automatic transfer switch? Some units you have to pysically plug the shore power cord into the generator outlet plug. If you have the transfer switch then I agree with HoneyBadger, check the breakers on the genset itself.
Frank
__________________
05 Alfa Gold 40' Motor Home "Goldie" 03 Malibu Toad towing 4 down
03 Silverado cclb 3500 drw, D/A, Reese 22k hitch
07 Alfa SeeYa Gold 30RL,2 slides,power everything Above for sale PM me for details
Franka548 is offline   Reply With Quote
Old 05-18-2015, 09:07 PM   #5
Junior Member
 
Join Date: May 2015
Posts: 9
Wow--thanks for the quick replies! Would be lovely if it was simply the Genset breaker. I do appreciate the advice. So far as I can judge, there is one 30A breaker. It did not appear to be tripped. In any event, I started the genset and tried the breaker in both positions (not being sure which was on and which was off). In made no difference. While the gen was running, I also tested the current to the batteries. 12.44v with gen on, 12.44v with gen off. I.e., no charge coming from the generator.

This leads me back to wondering about the solenoid? It is possible that the short was actually against one of the terminals on the solenoid. It was out of view when the short happened. There was no physical evidence of such, but might have been very brief.

Thoughts?

And thanks!
__________________
Onfoot is offline   Reply With Quote
Old 05-18-2015, 09:58 PM   #6
Junior Member
 
Join Date: May 2015
Posts: 9
Now wondering which is on and which is off position on the genset breaker switch. It is on the RH side of the control panel, facing forward in a tight space. Impossible to view any labeling and the manual does not have a diagram or a description that reveals if on is towards me or away from me. (If I was looking directly at the switch, 'towards me' would be to the left and 'away from me' would be to the right. Not sure now which is on...
__________________
Onfoot is offline   Reply With Quote
Old 05-18-2015, 10:16 PM   #7
Junior Member
 
Join Date: May 2015
Posts: 9
Quote:
Originally Posted by Franka548 View Post
Does your unit have an automatic transfer switch?
Thanks for your help, Frank. There is an automatic transfer switch--or at least I presume there must be, as I have never had to plug shore power into the receptacle to charge the batteries or to have 110 power in the RV. For what it's worth, genset was providing 110 power just fine prior to my doing the battery replacement.
__________________
Onfoot is offline   Reply With Quote
Old 05-18-2015, 10:30 PM   #8
Senior Member
 
Join Date: Dec 2013
Location: Plantation, Fl
Posts: 1,072
I have a 2001 Sundancer which doesn't have an automatic transfer switch. You might want to check again for an outlet, to plug your power cord into, in your utility bay.
__________________
2014 Itasca Spirit 31K
2016 Mazda CX5, on an Acme tow dolly, 4 trips 5800mi
Now 2017 RWD F 150 with a drive shaft disconnect
Mich F is online now   Reply With Quote
Old 05-18-2015, 10:36 PM   #9
Junior Member
 
Join Date: May 2015
Posts: 9
Newbie Confessions--

Frank nailed the problem. There is NOT an automatic transfer switch. To use the genset for 110v, the shoreline power cable DOES need to be plugged into the genset receptacle. Since I had never had occasion to use shoreline power, I had not experienced making the transfer. But after replying confidently to Frank that I must have an auto transfer switch, a niggle of doubt prompted me to research the manual, where I discovered the need for making the manual connection. (Not for lack of reading the manual up til now--just had not been noticing that paragraph for some reason...)

Mind you, I am still scratching my head as to how the generator would have been providing 110v a week ago and then ceased when I changed the batteries--as I had no occasion at all to visit the compartment with the shoreline connector and genset receptacle. I can only imagine that it must have been only barely plugged in and somehow vibrated loose.

Be that as it may, it is now firmly plugged in and the genset provides 110v and the batteries show a charge coming in. (Very slight, mind you--only 12.79v, but perhaps the charge controller is showing the batteries as nearly fully charged and has largely backed off.)

Anyway, thank you to all for your patience with my newbie learning curve!!!
__________________
Onfoot is offline   Reply With Quote
Old 05-18-2015, 10:39 PM   #10
Junior Member
 
Join Date: May 2015
Posts: 9
Quote:
Originally Posted by Mich F View Post
I have a 2001 Sundancer which doesn't have an automatic transfer switch. You might want to check again for an outlet, to plug your power cord into, in your utility bay.
Yep. You're very gracious, Mich F.
__________________
Onfoot is offline   Reply With Quote
Old 05-19-2015, 02:04 AM   #11
Senior Member
 
mohamer's Avatar
 
Join Date: Jul 2013
Location: Exeter, MO
Posts: 111
Onfoot,
Keep plugging away mate!!
__________________
mohamer is offline   Reply With Quote
Old 05-19-2015, 06:57 AM   #12
Senior Member
 
Franka548's Avatar
 
Freightliner Owners Club
Retired Fire Service RVer's
Join Date: Apr 2011
Location: N E Ohio
Posts: 3,465
Onfoot,
Glad that it was a simple fix, there seems to be no rhyme or reason which units have auto transfer switches and which units don't. My 88 Southwind had one. My 07 Alfa 5er does not.
That solenoid might be for the emergency start switch that allows you to start the engine off the house batteries if the chassis battery goes dead.
Frank
__________________
05 Alfa Gold 40' Motor Home "Goldie" 03 Malibu Toad towing 4 down
03 Silverado cclb 3500 drw, D/A, Reese 22k hitch
07 Alfa SeeYa Gold 30RL,2 slides,power everything Above for sale PM me for details
Franka548 is offline   Reply With Quote
Old 05-20-2015, 09:50 PM   #13
Junior Member
 
Join Date: May 2015
Posts: 9
Thanks, guys.

I will indeed keep pluggin'... But that is one awful pun! Seriously, grateful for the advice and help. Great community support, guys. Almost wishing I had more questions to ask--but now just wanting to do some camping.
__________________

__________________
Onfoot is offline   Reply With Quote
Reply

Tags
itasca, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Switching Power Sources on an 85 Mallard wolf_7669 Vintage RV's 4 10-28-2014 03:16 PM
Adding more power vs safety to engine Smitty77 Cummins Engines 15 10-13-2014 09:06 AM
2003.Discovery help no ignition power Alanboss Class A Motorhome Discussions 3 03-28-2014 07:05 AM
No power to coach unless RV is running dvleemin Class A Motorhome Discussions 9 03-27-2014 08:33 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.