240v dryer
I am trying to find out if i am able to install a 240v bosch stackable washer dryer. I have the room but not sure about the power. I have a 2009 hr scepter with a 120v combo washer dryer. Thanks for any help. Brunter
__________________
Vilano 375fl
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-13-2010, 02:32 PM
|
#2
|
Senior Member
Join Date: Apr 2008
Location: Freeport, ME
Posts: 4,707
|
If you have a 50 amp service plug then you have 240 available in the circuit breaker panel. Do you have two adjacent blanks in the main 110v circuit breaker panel, one above or below the other? Not crosswise.You will probably not be able to run the dryer with any of the AC units turned on. Does the book with the dryer tell you how many amps it needs on a circuit breaker?
__________________
Mike Canter
"Gunner" USN Retired, Airdale
2004 Monaco Signature 44' Conquest. Detroit 60
|
|
|
03-14-2010, 05:57 AM
|
#3
|
Moderator Emeritus
Country Coach Owners Club Appalachian Campers Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
|
If you have an inverter generator like an Onan 7.5 - 8 kw generator;l you will not be able to operate the 240 vac dryer as these generators do not put out 120/240 vac. Only two 120 vac circuits. Like Mike has said you will need to use a double pole 30 amp circuit breaker and four, 10 gage wires, to properly supply power for this dryer. It has been done in these kinds of coaches before.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
|
|
|
03-14-2010, 09:17 AM
|
#4
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
|
Many 240v dryers can be converted to 120v operation, but the drying time is much longer.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
03-16-2010, 01:45 PM
|
#5
|
Moderator Emeritus
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,644
|
Tiffin initially used a 240 volt drier in the Allegro Bus when they first offered the stackable units back in 2006. Shortly thereafter they went to the 120 volt stackables.
The 240 volt drier is nice because it has some serious wattage and dries fast. However, it requires 240 volts to operate. That's fine if you are on a 50 amp shore power pedestal. Everything operated just fine that way. However, you are dead in the water if on 30 amp. Also, the Onan quiet power generator sets are strictly 120 volts up through 8,000 watt. The larger 10,000 watt and up generator sets are 120/240 though. The 10KW gensets only came on the longer tag axle coaches with three air conditioners but the 40' coach only had two air conditioners so it got the 7500 watt Onan.
Eventually Tiffin decided to just stay with 120 volt stackables to end the confusion and limitations of not having enough power. They do take a bit longer to dry though.
If starting out from scratch, I'd probably just go with the 120 volt Splendide stackable units. So far they look like the best choice available.
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
|
|
|
03-17-2010, 08:49 PM
|
#6
|
Registered User
Monaco Owners Club
Join Date: May 2009
Posts: 3,198
|
Hope this isn't too far off the topic, but why have I never heard of running a gas dryer in an rv?
We have a maytag stack in my Mom's apartment in our basement, 32" wide, almost has the capacity of a full size machine, washes and dries fast, and runs on 115 and natural gas. Could something like this be used in an RV?
I imagine the burner can be rejetted for propane?
|
|
|
03-18-2010, 02:45 AM
|
#7
|
Moderator Emeritus
Country Coach Owners Club Appalachian Campers Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
|
One could very easily install a gas dryer as long as the area it is installed in has the minimum clearances required and enough air flow through the door(s). If you have to pay for all of your electric it might be more efficient depending on what you have to pay for propane vs price of kw hours. If you are in a campground that electric is included, then you are using up a lot of propane needlessly; although it would do a nice job of drying your clothes and quickly.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|