30 amp 240 receptacle

At my storage building I have a 30 amp 120 volt receptacle. I have blown the 30 amp fuse on the buss that it is connected to a few times, so I want to add more power. The easiest option is to pull in one more wire and connect another leg to get 240 and change the receptacle to a 50 amp. The wire will only be rated for 30 amps so it will only have 30 amp fuses installed. This basically doubles my current capacity and should eliminate any blown fuses.
Changing the wire and disconnect box to get a full 50 amps is much more involved.

Thoughts?
__________________

__________________
rssnape is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-05-2013, 12:21 PM   #2
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,389
Quote:
Originally Posted by rssnape View Post
At my storage building I have a 30 amp 120 volt receptacle. I have blown the 30 amp fuse on the buss that it is connected to a few times, so I want to add more power. The easiest option is to pull in one more wire and connect another leg to get 240 and change the receptacle to a 50 amp. The wire will only be rated for 30 amps so it will only have 30 amp fuses installed. This basically doubles my current capacity and should eliminate any blown fuses.
Changing the wire and disconnect box to get a full 50 amps is much more involved.

Thoughts?
That will work. I'm sure no code authority would be happy. If you are dealing with a fuse box that must be an old installation.
__________________

__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 09-05-2013, 12:50 PM   #3
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 330
It's coming off a box on a 400 amp buss bar. The fuses will match the rating of the lowest rated item, in this case the wire in the conduit. Yes it is about 40 year old industrial set up.

Thanks
__________________
rssnape is offline   Reply With Quote
Old 09-05-2013, 01:32 PM   #4
Senior Member
 
Melmoses's Avatar
 
Tiffin Owners Club
Join Date: Aug 2010
Location: Montgomery, AL
Posts: 1,196
I guess you are aware that your MH is 120v so a 50 amp box should be wired as such. If you connect a 50 amp 240 dryer type box you will fry everything inside.
__________________
Mel (Melanie) and Harry
2009 Tiffin Phaeton 40QTH
2014 Jeep Wrangler Sport
Melmoses is offline   Reply With Quote
Old 09-05-2013, 01:37 PM   #5
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 330
Yep, 3 pole 4 wire receptacle. 14-50R
__________________
rssnape is offline   Reply With Quote
Old 09-05-2013, 01:39 PM   #6
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
It will work fine and there is no difference between 50 amp 4 wire socket as far as
wiring. Not so on the 30 amp sockets.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Old 09-05-2013, 02:36 PM   #7
Senior Member
 
ShapeShifter's Avatar


 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Feb 2010
Location: Buffalo, NY
Posts: 1,632
Quote:
Originally Posted by rssnape View Post
At my storage building I have a 30 amp 120 volt receptacle. I have blown the 30 amp fuse on the buss that it is connected to a few times, so I want to add more power. The easiest option is to pull in one more wire and connect another leg to get 240 and change the receptacle to a 50 amp. The wire will only be rated for 30 amps so it will only have 30 amp fuses installed. This basically doubles my current capacity and should eliminate any blown fuses.
Changing the wire and disconnect box to get a full 50 amps is much more involved.

Thoughts?
Your idea has some merit, and should increase the amount of available power. If you have an energy management system that detects the type of power, and automatically sheds loads to keep it under the available limit, it will be confused by this arrangement. There will be nothing that prevents it from allowing more than 30 amps per leg (other than the breaker feeding the outlet.) Not likely to be a serious issue, but something to be aware of, since you will have to do your own load management and rely on your management system.

So it should work, but is it legal? You say you want to pull an extra wire. Are the existing wires in conduit, and you are adding an extra single conductor? If so, is the conduit large enough to handle the extra power from the added conductor? Is there enough volume in the junction boxes to legally allow the addition of another conductor?

If the existing circuit is not in conduit, and is using jacketed non-metallic cable (Romex), then is it legal to run another cable in parallel to it? I would doubt that it would be legal to run a single non-jacket extra conductor outside of conduit. And does the junction box for the socket have enough volume to support the extra conductor?

Finally, while it's obviously bad to put a 30 amp socket on a 50 amp circuit, is it legal to put a larger socket on a smaller circuit? When you get right down to it, the breaker doesn't instantly trip when it goes over 30 amps, it may be possible to draw 35 or 40 amps on that wire for a while - will that be enough to heat things up and cause problems before the breaker trips?

And it doesn't hurt to say that the second hot line must be on the opposite supply phase from the existing hot line, because you will overload the existing neutral line if it isn't. But I think you know this since you're mentioning 240 volts.

I don't have the answers to all of these questions, but they should be answered before you do anything. It's so tough to give definitive suggestions without seeing the actual conditions, so it's always a good idea to get the a professional opinion from someone who can actually see the job conditions, even if you are planning on doing the work yourself. Often times, your local building inspector is willing to talk to a homeowner about planned work and give advice about what is an isn't safe and legal.

Theoretically, your idea will give more power to the RV, and your RV will be happier. But will it be legal, and more importantly safe? It would be better to find that out before doing the work rather than finding out the hard way.

Now, with all of this said, if you're going to be pulling new wire(s), why not just do it right and pull a new 50 amp 240 volt circuit and not have any issues? It's a little more up-front money and work, but in the end it's the right thing to do.

Quote:
Originally Posted by Melmoses View Post
I guess you are aware that your MH is 120v so a 50 amp box should be wired as such. If you connect a 50 amp 240 dryer type box you will fry everything inside.
As long as that 50 amp 240 volt dryer socket is a standard four prong socket, there will not be an issue. A 50 amp RV uses the exact same plug and socket as the modern 50 amp 120/240 volt 3 pole 4 pin dryer socket. The four pins consist of two hots, one neutral, and a ground.

If it's an older socket with only three pins (no neutral) then it would be a very bad thing to connect to, whether it be 30 amps or 50 amps.
__________________
Adam and Sue, and a pack of little furballs
2007 Holiday Rambler Endeavor 40PDQ Limited Edition - Cummins ISL 400
2013 Ford F-150 FX4 toad - USGear Unified Tow Brake, Roadmaster Blackhawk II Tow bar, Blue Ox baseplate
Home base near Buffalo NY, often on the road to a dog show
ShapeShifter is offline   Reply With Quote
Old 09-05-2013, 04:00 PM   #8
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 330
It is in conduit and the box is a 2 gang handy box. The problem is the conduit likely would not handle wire rated for 50 amp and it is a clamp on disconnect onto the 400 amp buss not sure we have a 50 amp.
My only concern is the phase. It is 3 phase, but my maintenance guy says he can give me another leg to make 240. My question/ concern is the second phase 180 degrees out? I don't understand 3 phase completely, but my guy has never done me wrong in the 30 years he's worked for me.
Attached Thumbnails
Click image for larger version

Name:	image-2407318344.jpg
Views:	59
Size:	445.5 KB
ID:	45482  
__________________
rssnape is offline   Reply With Quote
Old 09-05-2013, 04:20 PM   #9
Senior Member
 
Steve N Sal's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 5,614
I have a question. In the picture you have provided, the cord that is plugged into that receptacle, is it a 50 to 30 adapter cord or is it the actual feed cord from the coach?
__________________
Steve & Sally / HiTee & Hudson Our Little Poms / Heidi & Houston Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert
Michigan (Summer) Michigan (Winter For Now)
Steve N Sal is offline   Reply With Quote
Old 09-05-2013, 06:02 PM   #10
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 330
Quote:
Originally Posted by Steve N Sal View Post
I have a question. In the picture you have provided, the cord that is plugged into that receptacle, is it a 50 to 30 adapter cord or is it the actual feed cord from the coach?
50 to 30 dog bone
__________________
rssnape is offline   Reply With Quote
Old 09-05-2013, 07:05 PM   #11
Member
 
Busyteach's Avatar
 
Join Date: Oct 2012
Posts: 85
Actually, in a true 3 phase, it is 120 degrees out but that actually will not be a problem. I assume your maintenance guy knows this but voltages will also need to be correct.

Since the bus already has a 120v leg fed from it, it will likely be what the industry calls a 208 Y connection or a 240V Delta connection. The concern would be that if it is a grounded delta, you will have 240V 3 phase with a neutral. What this means to you is that there are only 2 of those phases you can connect to a single phase load ( your 50A 240v receptacle). You or your maintenance man will need to be careful in identifying which leg of the 3 phase is "wild" and not use it. You can use the other 2 phases with no problem.

If the 3 phase is a Y it will actually be a grounded 208/120 volt system. The beauty here is that all phases to ground here are 120V so there is no "wild" leg and you can use any 2 of the 3 phases off the buss duct. Drawback is that it is actually 208 volts single phase. I am not sure the 50 amp wired coaches have moved to 240v appliances and ac or not but I doubt it since many parks still only offer 30a 120v. If in fact the loads in a 50a coach are still only 120v then you would never know the difference. I also could not answer the problems with the inverters but I assume they are also still fed with 120V.

I agree with others that as long as your overcurrent protection is lower than the wire and device capacity, you will be OK as far as safety from overcurrent and heating. I also cannot answer what load shedding devices in your coach might do but I suspect they are also using 120v circuits and they will only act if the current is too high. You are fused under that so you should blow the fuses if you are loaded too heavy. I think the trip curve issue mentioned earlier with fuses and especially breakers would be the same or worse with an actual 50 amp rated circuit rather than your 30A rated circuit. You may have to monitor loads to avoid tripping your overcurrent device.

If you or your maintenance man do not understand this I would recommend finding an electrician who does. You could cause a lot of costly damage if you get it wrong. Hope this helps.
__________________
Busyteach is offline   Reply With Quote
Old 09-06-2013, 02:39 AM   #12
Senior Member
 
stink's Avatar
 
Join Date: Apr 2012
Posts: 1,414
I did the same thing only with single phase. can run both a/c s and ref no problem.
__________________
Dave and Laura & two cats
02 Discovery with Accord toad
retired auto rv tech and teacher, wife rt nurse
stink is offline   Reply With Quote
Old 09-06-2013, 05:25 AM   #13
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 330
Quote:
Originally Posted by Busyteach View Post
Actually, in a true 3 phase, it is 120 degrees out but that actually will not be a problem. I assume your maintenance guy knows this but voltages will also need to be correct.

Since the bus already has a 120v leg fed from it, it will likely be what the industry calls a 208 Y connection or a 240V Delta connection. The concern would be that if it is a grounded delta, you will have 240V 3 phase with a neutral. What this means to you is that there are only 2 of those phases you can connect to a single phase load ( your 50A 240v receptacle). You or your maintenance man will need to be careful in identifying which leg of the 3 phase is "wild" and not use it. You can use the other 2 phases with no problem.

If the 3 phase is a Y it will actually be a grounded 208/120 volt system. The beauty here is that all phases to ground here are 120V so there is no "wild" leg and you can use any 2 of the 3 phases off the buss duct. Drawback is that it is actually 208 volts single phase. I am not sure the 50 amp wired coaches have moved to 240v appliances and ac or not but I doubt it since many parks still only offer 30a 120v. If in fact the loads in a 50a coach are still only 120v then you would never know the difference. I also could not answer the problems with the inverters but I assume they are also still fed with 120V.

I agree with others that as long as your overcurrent protection is lower than the wire and device capacity, you will be OK as far as safety from overcurrent and heating. I also cannot answer what load shedding devices in your coach might do but I suspect they are also using 120v circuits and they will only act if the current is too high. You are fused under that so you should blow the fuses if you are loaded too heavy. I think the trip curve issue mentioned earlier with fuses and especially breakers would be the same or worse with an actual 50 amp rated circuit rather than your 30A rated circuit. You may have to monitor loads to avoid tripping your overcurrent device.

If you or your maintenance man do not understand this I would recommend finding an electrician who does. You could cause a lot of costly damage if you get it wrong. Hope this helps.
It is 208 3 phase. And yes my maintenance man understands this much better than I. He maintains all our equipment. 5 air compressors, numerous process heaters, dc rectifiers, builds process controls from scratch, plumbing, mechanical, you name it he can do it.

My coach is a 1997 and I'm pretty sure there is no load shedding device.

Thanks for your detailed reply!
__________________
rssnape is offline   Reply With Quote
Old 09-06-2013, 05:48 AM   #14
Senior Member
 
BCooke's Avatar
 
Join Date: Aug 2011
Posts: 1,523
Quote:
Originally Posted by rssnape View Post
At my storage building I have a 30 amp 120 volt receptacle. I have blown the 30 amp fuse on the buss that it is connected to a few times, so I want to add more power. The easiest option is to pull in one more wire and connect another leg to get 240 and change the receptacle to a 50 amp. The wire will only be rated for 30 amps so it will only have 30 amp fuses installed. This basically doubles my current capacity and should eliminate any blown fuses.
Changing the wire and disconnect box to get a full 50 amps is much more involved.

Thoughts?
How long is that run from the main box?
As you mentioned a storage shed, I am curious is your wire is under sized for the length of the run. While #10 is normal, longer runs (I add runs that will have constant loads) need to be up sized.
__________________

__________________
2017 F350 Lariat Diesel Dually, White, Hitch Kit.
2013 Dutchman Voltage 3200 Epic II 5th wheel.
BCooke is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.