30a outlet at the RV dock.

So, here's my thought:
I want to run 120vac/30a service out to my RV dock.

Plan:
1. replace a 15A CB in the panel with a 30A,
2. run 10ga. wire to a small CB box where the 15A CB will be relocated to,
3. reconnect the house wiring back to the 15a breaker,
4. split off a 10ga. run from the small CB box buss out to the 30a receptacle at the dock.

The 30a breaker will protect the line out to the dock and the 15a breaker will protect the house wiring as before. I have the power to use, just not the CB panel room.


Any holes in this plan?
__________________

__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-09-2016, 06:54 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 12,351
I'll have to break out my " sub panel " wiring regulations , but right off the top of my head , I think to meet code you have to put a 30 amp and the 15 amp into the sub panel, you're not allowed to make wiring connections in a sub panel unless they are through a C/B.
30 amp C/B in the main will allow up to 60 amps total C/Bs in the sub.

If I find anything different in the regulations I'll re-post.

Edit : How long is the wiring run from the sub panel to the RV plug going to be , wiring size for the length of run there may be an issue.
__________________

__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 07-09-2016, 08:51 PM   #3
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 12,697
Quote:
Originally Posted by grumpy_g View Post
So, here's my thought:
I want to run 120vac/30a service out to my RV dock.

Plan:
1. replace a 15A CB in the panel with a 30A,
2. run 10ga. wire to a small CB box where the 15A CB will be relocated to,
3. reconnect the house wiring back to the 15a breaker,
4. split off a 10ga. run from the small CB box buss out to the 30a receptacle at the dock.

The 30a breaker will protect the line out to the dock and the 15a breaker will protect the house wiring as before. I have the power to use, just not the CB panel room.


Any holes in this plan?
Sounds like it's doable, just make sure you use the correct wire size for all runs.electrician calculators
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 07-10-2016, 04:44 AM   #4
Member
 
Join Date: May 2016
Posts: 35
Thanks, guys.
Skip - the run will be a max of 60 feet, and judging by the calculators that Ray sent, very handy Ray, the voltage drop will be about 3.8% or about 115 at the load based on 120vac to begin with.
__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Old 07-10-2016, 04:48 AM   #5
Member
 
Join Date: May 2016
Posts: 35
So Skip, you're saying that I have to treat this little box as a sub panel and run a line from the main panel buss to it without coming off a breaker in the main panel, and then have my 30a and 15a breakers in the small box? (there is room for two breakers but I thought lines coming off the main should be protected when they leave)
__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Old 07-10-2016, 06:35 AM   #6
Senior Member
 
Dr4Film's Avatar


 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,208
I am installing a 30 amp RV receptacle box at the rear of my property where an older one was installed when the property was being built by the original owner who lived in a small trailer. My main panel inside my garage has a 30 amp CB.

The conduit that was there had outdoor 10/2 gauge wire plus ground from one end to the other but because it is about 90 feet long I am removing the 10 gauge and installing 2 - 6 gauge single wires (black/white) plus ground to minimize the voltage drop.

I am assuming that I do not need a CB at the RV receptacle box plus there isn't any such area in the new box that I purchased from Lowe's to install one.

30 amp RV Receptacle Box

It is my understanding that if you plan to use a sub-panel it has be protected at the main panel with a CB. Then your sub-panel should have CB's to protect whatever circuits you are splitting off in the sub panel to their destination. It would seem logical to me that the cable size going to the sub-panel needs to be sized for the combined circuits that are being split off at the sub-panel.

Disclaimer: I am not a licensed electrician, only one that can be very dangerous at times to myself.

I yield to the knowledge of experienced and licensed electricians.

Dr4Film ----- Richard
__________________
2002 Monaco Windsor PBT 40Ft. (R HOME) - 30Ft. 2006 Pace Trailer (R JUNK). Trailer Has 06 VUE (R TOWD) 04 Victory Alen Ness Edition (R RYDE). Full-Timer for 14 Yr's BUT now a Part-Timer. Cummins ISC-350 With Banks Power Pack and Upgraded PRXB PacBrake.
We are at our Winter Home in Flagler Beach FL
Dr4Film is offline   Reply With Quote
Old 07-10-2016, 07:14 AM   #7
Member
 
Join Date: May 2016
Posts: 35
That sounds reasonable, so I should install a 60a breaker on the main panel with #6 wires going to the 2-breaker sub-panel and from there reconnect the house wiring to the 15a breaker and the #10 wiring out to the RV drop from the 30a breaker.

Does that sound right?
__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Old 07-10-2016, 07:24 AM   #8
Senior Member
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,790
I assume all of your breaker slots are full.....

Why not replace a breaker with two skinny or a dual breaker?
This would be much simpler as far a no changes to the existing 15A circuit.

You can buy a dual 15A breaker, and replace an existing 15A breaker....then remove the "target" 15A and move that wire to the new extra breaker....now you have an open slot for your new 30A circuit.

Regards,

Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2014 Jeep Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -South Orange County Ca.
dpinvidic is offline   Reply With Quote
Old 07-10-2016, 07:37 AM   #9
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 4,143
Quote:
Originally Posted by Dr4Film View Post
I am installing a 30 amp RV receptacle box at the rear of my property where an older one was installed when the property was being built by the original owner who lived in a small trailer. My main panel inside my garage has a 30 amp CB.

The conduit that was there had outdoor 10/2 gauge wire plus ground from one end to the other but because it is about 90 feet long I am removing the 10 gauge and installing 2 - 6 gauge single wires (black/white) plus ground to minimize the voltage drop.

I am assuming that I do not need a CB at the RV receptacle box plus there isn't any such area in the new box that I purchased from Lowe's to install one.

30 amp RV Receptacle Box

It is my understanding that if you plan to use a sub-panel it has be protected at the main panel with a CB. Then your sub-panel should have CB's to protect whatever circuits you are splitting off in the sub panel to their destination. It would seem logical to me that the cable size going to the sub-panel needs to be sized for the combined circuits that are being split off at the sub-panel.

Disclaimer: I am not a licensed electrician, only one that can be very dangerous at times to myself.

I yield to the knowledge of experienced and licensed electricians.

Dr4Film ----- Richard
You are correct. But don't give licensed electricians too much credit. Many of them look at a RV recpt. and automatically think 230 volts. I was called to a 4th of July fireworks show on the 3rd. They had a electrician wiring a recpt. for a travel trailer. I walked over and saw he was hooking the recpt. up to 230 volts. I said you better check the writing on the recpt. You will find it says 30 amp 125 volts travel trailer use only. He looked at it and said thank you, I have never seen this before. He wasn't dumb, just not used to RV wiring.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2012 Honda Civic toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is offline   Reply With Quote
Old 07-10-2016, 08:03 AM   #10
Member
 
Join Date: May 2016
Posts: 35
Quote:
Originally Posted by dpinvidic View Post
I assume all of your breaker slots are full.....

Why not replace a breaker with two skinny or a dual breaker?
This would be much simpler as far a no changes to the existing 15A circuit.

You can buy a dual 15A breaker, and replace an existing 15A breaker....then remove the "target" 15A and move that wire to the new extra breaker....now you have an open slot for your new 30A circuit.

Regards,

Dan
Yes, the panel is full. That's a good idea and I would but they are not square-D and I am having trouble finding them. Zinsco or something. I did see a 120vac double 30a online at Amazon for around $56.
__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Old 07-10-2016, 08:10 AM   #11
Senior Member
 
Spk64's Avatar


 
Join Date: Apr 2014
Location: Floyds Knobs, In.
Posts: 795
30a outlet at the RV dock.

Something I have read and heard on true sub-panels is the handling of grounds. Depending on how it is installed determines the ground path setup. Sometimes there is a separate ground rod and ground connection. I had to do this on my shop that was split off from the meter box. If a sub-panel is coming from the main panel then you generally share the ground and run a ground wire from main like my sub-panel in our basement.
With that said I am not sure an RV box/outlet would be considered a sub-panel but should have a ground wire coming from main panel.
As to having a circuit breaker at the outlet, I did the same as you are describing Richard except 50 amp. Having a breaker at the box would be nice if you want to kill the power to the outlet before disconnecting. I just shut down everything inside coach then disconnect.

I too am not a licensed electrician so take my information lightly.🤓


Steve
__________________
Spk64 is offline   Reply With Quote
Old 07-10-2016, 08:36 AM   #12
Senior Member
 
Rockwood27's Avatar
 
Winnebago Owners Club
Nor'easters Club
Workhorse Chassis Owner
Join Date: Jun 2012
Location: Freedom, NH
Posts: 856
I'm not an electrician and I'm not certain about separate ground rods at the subpanel. The ground and neutral wires have to be separated at the subpanel. I don't know if you can buy a 120V subpanel. They may be 240V only. This might require a Double CB at the main panel and fed to the subpanel with a 3 conductor with ground cable.
__________________
Fran, Mary & Zoey (silver Cocker)
2006 Itasca Sunrise 35A, 2005 W-22, Allison 1000 5 speed
'13 Ford Focus ST or '10 Prius on Master Tow Dolly 80THD-SB or '00 Jeep Cherokee 4-down
Rockwood27 is online now   Reply With Quote
Old 07-10-2016, 08:43 AM   #13
Senior Member
 
Dr4Film's Avatar


 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,208
Steve,

I believe a sub-panel requires a ground rod buried in the ground whereas an outlet box does not. However, the location where the old outlet was happens to have a ground rod too which I will use since it is there but it will be grounded at the ground buss in my main panel in the garage too. No need to have a CB in the receptacle box as that circuit will be off unless it is being used by a guest staying at the house. A little walking never hurt anyone.

I am wiring a 50 amp box to my RV carport area located under my elevated beach house where my coach will be parked. That is only about 25 paces from the main power box inside the garage. No need to have extra CB's like what they usually have at RV Parks.

Dr4Film ----- Richard
Attached Thumbnails
Click image for larger version

Name:	214487_27.jpg
Views:	120
Size:	98.6 KB
ID:	132589  
__________________
2002 Monaco Windsor PBT 40Ft. (R HOME) - 30Ft. 2006 Pace Trailer (R JUNK). Trailer Has 06 VUE (R TOWD) 04 Victory Alen Ness Edition (R RYDE). Full-Timer for 14 Yr's BUT now a Part-Timer. Cummins ISC-350 With Banks Power Pack and Upgraded PRXB PacBrake.
We are at our Winter Home in Flagler Beach FL
Dr4Film is offline   Reply With Quote
Old 07-26-2016, 04:01 PM   #14
Member
 
Join Date: May 2016
Posts: 35
I seem to have gotten a bit lost. (Also not an electrician)
If I install a 30a breaker in place of a 15a on my main panel, then install a small sub panel, connected by #6/2 wire, with a 15a for the displaced main, and a 30a for the dock power, with the home depot 30a rv power outlet with breaker, do I ground the dock box or is the ground coming from the breaker panel with the #10/2 wire enough?
__________________

__________________
2004 Gulf Stream B-Touring Cruiser - 5230 on a Ford E450 chassis, V10
1999 Road King
grumpy_g is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Use of 50A Surge Protector with 30A Pigtail for 30A Shore Power hugh37 Newmar Owner's Forum 9 07-08-2016 01:14 PM
For you electricians - 30A outlet install questions Steverino iRV2.com General Discussion 35 12-02-2013 09:31 PM
Will 50A RV Work W/30A Outlet? born free 28 Class A Motorhome Discussions 12 09-19-2012 10:39 AM
Can A 30A MH Plug Into A 50A Outlet (with a plug converter of course) Ceratto's Grotto MH-General Discussions & Problems 10 07-08-2012 04:15 PM
Need some electrical help with running a new 30A outlet schupaul iRV2.com General Discussion 23 10-01-2010 08:06 AM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:38 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.