50A Outlet Box Ground?

I'm installing a 50A outlet box out where I park the motorhome. I have two 6 gauge hots going out there and one 6 gauge neutral. Should I run a ground wire from the box directly to a ground stake? Or should I run a ground wire 150 feet back to the source? Does it really matter?

Thanks.
__________________

__________________
Craig M is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-22-2010, 03:40 PM   #2
Administrator in Memoriam
 
Hitchhiker's Avatar


 
Appalachian Campers
Join Date: Jan 2000
Location: Buladean, NC
Posts: 8,127
If I were doing it I'd run a ground all the way back to the box that supplies the power. As an extra, a second ground rod located near where the outlet is located won't hurt but it should be also connected to the ground at the power box. But, I'm not a licensed electrician.
__________________

__________________
'11 GMC Acadia SLT AWD
'11 GMC Sierra 1500 4x4 Extended Cab
Hitchhiker is offline   Reply With Quote
Old 10-22-2010, 03:43 PM   #3
Community Administrator
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,622
Back to the box,

Details here.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is offline   Reply With Quote
Old 10-22-2010, 05:01 PM   #4
Member
 
Join Date: Oct 2010
Posts: 36
What size wire for the ground? Would 10 gauge solid be enough for the ground?
__________________
Craig M is offline   Reply With Quote
Old 10-22-2010, 05:20 PM   #5
iRV2 Marketing
 
DriVer's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Coastal Campers
Carolina Campers
Join Date: Jan 2000
Location: Conway, SC
Posts: 23,304
Blog Entries: 70
Quote:
Originally Posted by Craig M View Post
I'm installing a 50A outlet box out where I park the motorhome. I have two 6 gauge hots going out there and one 6 gauge neutral. Should I run a ground wire from the box directly to a ground stake? Or should I run a ground wire 150 feet back to the source? Does it really matter?
You must establish that you have 120Volts only on L1 & L2 to the Neutral. The Neutral wire needs to be the same size as the L1 & L2 wires in this case you are OK with a #6. You also need a GREEN wire or bond wire between the metal boxes from the service to the 50A receptacle panel you're installing outside. Minimum size is a #8.

If you measure the voltage between L1 & L2 you should get 220V. Only use the receptacle that you installed if both L1 & L2 to the Neutral lug measure 120 volts.

Do not tie the bond and the neutrals together on the same bus bar. The Neutral is a current carrying conductor while the bond is not.

There are 4 lugs on a 50A plug (cord cap). L1 & L2, Neutral and Ground (Bond).
__________________
03 Adventurer 38G, Workhorse W22
F&R Track Bars, Safety+ , Ultrapower, Taylor Extremes, SGII
TST 507, Blue Ox, SMI, Koni FSD, CrossFire
RV/MH Hall of Fame - Lifetime Member
DriVer is offline   Reply With Quote
Old 10-22-2010, 06:16 PM   #6
Senior Member
 
National RV Owners Club
Join Date: Nov 2006
Posts: 288
I ran 165 ft from the feeder panel to my garage. Electrical inspector told me to ground to the ground rod in the garage since it was so far back to the feeder panel. You can pick up a copy of the NEC at the library, or ask your local inspector to be sure. He's the one who will sign it off when you are done.
__________________
USN, Retired
2002 Tradewinds LTC Founders Ed
2004 Tundra Double Cab toad, 2007 Honda Goldwing
Submustang is offline   Reply With Quote
Old 10-22-2010, 06:39 PM   #7
Senior Member
 
vermilye's Avatar


 
Join Date: Nov 2006
Location: Oswego, NY
Posts: 380
Blog Entries: 1
Send a message via Skype™ to vermilye
Quote:
Originally Posted by Craig M View Post
Should I run a ground wire from the box directly to a ground stake? Or should I run a ground wire 150 feet back to the source? Does it really matter?

Thanks.
It does matter. One of the main purposes of the ground wire is to trip the circuit breaker(s) feeding the receptacle if there is a fault between a hot & ground. Although driving a stage sounds like you are making a ground, the earth is likely to have enough resistance between the new stake & the bond at the service entrance panel that a ground fault won't trip the breaker. In almost all cases, a ground wire must be run along with the neutral & hots. In some cases, the local authority will also require a driven ground rod at the receptacle connected to the ground only (no neutral connection).
vermilye is offline   Reply With Quote
Old 10-22-2010, 07:27 PM   #8
Senior Member
 
Tallyrver's Avatar


 
Heartland RV Club
Join Date: Mar 2010
Posts: 695
I Installed a 50 amp box for my rig,the line was 90 ft. from the main electrical panel. I used 4 wire 6 ga. 2 hot 1 neutral and 1 ground.
__________________
Wayne and Debbie
2014 Gateway 3650BH
2008 F350 dually diesel .
www.mudflapscampingclub.com
Tallyrver is offline   Reply With Quote
Old 10-22-2010, 08:31 PM   #9
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,150
Blog Entries: 21
I had my 50 amp installed when we built the garage and the ground is back to the main power panel, plus it has an 8' copper clad rod driven in the ground at the garage and at the shop.

ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 10-23-2010, 06:22 PM   #10
Member
 
Join Date: Oct 2010
Posts: 36
Thanks for all the help! It's been very helpful.
__________________
Craig M is offline   Reply With Quote
Old 10-25-2010, 01:45 PM   #11
Senior Member
 
alvinc's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 658
To summarize: There must be 4 wires going from your new receptacle back to the main panel. Two hots, one neutral, and one ground. At your receptacle box, the neutral and ground MUST NOT be connected together. This can only be done at the main panel.

Whether a local ground rod is required is up to the the electrical inspector.
__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
alvinc is offline   Reply With Quote
Old 10-25-2010, 02:06 PM   #12
Member
 
Join Date: Oct 2010
Posts: 36
Quote:
Originally Posted by alvinc View Post
To summarize: There must be 4 wires going from your new receptacle back to the main panel. Two hots, one neutral, and one ground. At your receptacle box, the neutral and ground MUST NOT be connected together. This can only be done at the main panel.

Whether a local ground rod is required is up to the the electrical inspector.
Good summary. That is how I am doing it. At this point, I am not going to bother grounding at the new box.

Copper wire sure is expensive. I was looking at aluminum, but decided to stick with copper. The RV is my wife's hobby. Last night I showed her the installed box and told her it was an early Christmas present.

This will sure make getting ready for our cold Feb. Disney trips easier....
__________________
Craig M is offline   Reply With Quote
Old 10-26-2010, 05:56 AM   #13
Senior Member
 
Tallyrver's Avatar


 
Heartland RV Club
Join Date: Mar 2010
Posts: 695
RV Electric

Here is a site I found on here, If you are going to do the work yourself or hire someone ,this is important.
__________________
Wayne and Debbie
2014 Gateway 3650BH
2008 F350 dually diesel .
www.mudflapscampingclub.com
Tallyrver is offline   Reply With Quote
Old 10-26-2010, 02:11 PM   #14
Member
 
Join Date: Oct 2010
Posts: 36
Quote:
Originally Posted by Tallyrver View Post
RV Electric

Here is a site I found on here, If you are going to do the work yourself or hire someone ,this is important.
Yup, yup, that was linked earlier in the thread. "Open Neutrals" got me a little nervous. I shared that info with my dad.
__________________

__________________
2011 Forest River Georgetown 350, 36 ft, 3 slides and bunk beds for our 2 boys.
RVing since 2002.
Craig M is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dash Pod Ground Bar Don The Ham Winnebago Industries Owner's Forum 13 03-08-2017 04:29 PM
Bedroom Window Box Jim A Alpine Coach Owner's Forum 4 06-12-2009 02:33 PM
short box vs long box wakamicamper Trailer Towing and Tow Vehicles Discussion 13 12-04-2008 06:44 AM
50a Voltage Boosters Robin_M MH-General Discussions & Problems 2 09-11-2007 07:01 AM
Extended Pin Box Mod chevyrod 5th Wheel Discussion 8 08-24-2005 05:18 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:58 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.