Join CruisersForum Today
Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
AC/DC
Old 07-17-2010, 03:30 PM   #1
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
OK I am new to motorhomes and today I plugged it into shore power to test the AC/DC.

Everything that worked before hand stills works, I was hoping to get the other non working items to work once the shore power was connected.

I called the previous owner and so far I have been unable to reach him, so I guess I must now float that question to this board.

My new Motorhome is a used 83 Pace Arrow model G31, at the time I tested some of these items before we bought it I was told by the owner that it must be a fuse, something that I hate hearing because it tells me nothing. So here is my question, it seems as if none of the AC plugs work, I used both a test lamp and a drill to verify it, and a lot of the DC items also do not come on, so where are these fuses, and what else should I be looking for and checking to be able to see if it is indeed a fuse or a real problem that I must now try and repair. Also I ran the roof air conditioner for about a half hour on shore power before it blew the breaker on the control panel in the bedroom.

Please provide me with some feed back and guild lines on what I can now do to determine if I bought a problem or it is just a fuse.

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-17-2010, 03:56 PM   #2
TXiceman is offline
Moderator Emeritus
TXiceman's Avatar


Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Cypress, TX
Posts: 11,983
Sorry you are having a problem. You did not give a lot of information. Do you have the RV plugged into 120 VAC (volts A/C)? Next, do you have a volt ohm meter?

You need to find the breaker box and check the power in the breakers for the 120 VAC.

Have you checked to see if there is power at the plug that the RV is plugged to.

__________________
Amateur Radio Operator|Practicing for our retirement! 2008 Cameo 35SB3 - 2002 7.3L Crew Cab Dually w/ a SCMT - Max Brake - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
  Reply With Quote
   
Old 07-17-2010, 04:26 PM   #3
F&D ABQ is offline
Senior Member
Alpine Owners Club
Join Date: Jan 2005
Location: Albuquerque
Posts: 182
Quote:
Originally Posted by kartvines View Post
OK I am new to motorhomes and today I plugged it into shore power to test the AC/DC.

Everything that worked before hand stills works, I was hoping to get the other non working items to work once the shore power was connected.

I called the previous owner and so far I have been unable to reach him, so I guess I must now float that question to this board.

My new Motorhome is a used 83 Pace Arrow model G31, at the time I tested some of these items before we bought it I was told by the owner that it must be a fuse, something that I hate hearing because it tells me nothing. So here is my question, it seems as if none of the AC plugs work, I used both a test lamp and a drill to verify it, and a lot of the DC items also do not come on, so where are these fuses, and what else should I be looking for and checking to be able to see if it is indeed a fuse or a real problem that I must now try and repair. Also I ran the roof air conditioner for about a half hour on shore power before it blew the breaker on the control panel in the bedroom.

Please provide me with some feed back and guild lines on what I can now do to determine if I bought a problem or it is just a fuse.
My answer is generic - I'm not familiar with the PA - but here goes:
1. Newer motorhomes have an automatic transfer switch (ATA) that connects to either the generator or shore power, never both at once. If the ATA malfunctions, nothing works except maybe what's powered by the inverter.
2. The inverters in newer motorhomes also have a transfer switch built into them; those too have been known to go bad. If that is the problem, you may be able to reset the inverter's circuit breaker and fix nearly everything.
3. I'm assuming you do have a generator and some kind of a transfer system (on my previous MH I simply plugged the shore power line into an outlet box from the generator; worked every time, unlike the ATA). Have you tried powering the coach from that? With what result?
4. Are your batteries good? Should measure about 12.5 volts if not recharged real recently.

Also, you said your roof air breaker quit after half an hour. Was the line voltage low? If not, either the A/C was drawing too much power or the breaker is old and weak. If the A/C was cooling well, I'd suspect the breaker.

The more tests you run and the more different power sources you try, the easier it will be to diagnose your specific situation.
__________________
Franklin & Dessa
2001 Alpine 34 FDDS
Tow a 2002 CR-V
  Reply With Quote
   
AC/DC
Old 07-17-2010, 05:55 PM   #4
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
Yes the 30 amp cord is plugged in to my home supply and it is reaching the RV, and I checked the plugs on the inside that they are not powered, either is the plug on the outside by the door, the only one that seem to power is the plug the inverter . [the one outside] is plugged into, I guess I can just start pulling fuses to see what is good and or bad, I just don't know where to start, I guess this will be trail by doing. Could it be a breaker?

Do I even have to be concerned with the fused under the dash, being they are just for the chassis, isn't that correct.

Quote:
Originally Posted by TXiceman View Post
Sorry you are having a problem. You did not give a lot of information. Do you have the RV plugged into 120 VAC (volts A/C)? Next, do you have a volt ohm meter?

You need to find the breaker box and check the power in the breakers for the 120 VAC.

Have you checked to see if there is power at the plug that the RV is plugged to.
__________________
  Reply With Quote
   
Old 07-17-2010, 07:38 PM   #5
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,085
If you are in the proper part of Michigan (Flint area) I can do house calls.. Otherwise tracking down fuses or breakers ... Some companies I think HIDE the things.

Basically open every door, compartment or panel that can be opened and look.
__________________
Home is where I park it!
  Reply With Quote
   
Old 07-17-2010, 08:27 PM   #6
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
Thank you, being I live in the San Gorgonio Pass of the Inland Empire, California I am a bit farther than Michigan, so I will begin my search and open every , door , panel and cubbyhole until I discover what I seek. Now I have toned D/C power line to detriment their path, but I think that even trying to do so with A/C would be deadly being I do not have a clue to where all of the power sources are connected to. I guess I could pull all of the batteries and disconnect all power source and try to trace these wired with a toning device but that will or may create as many problems as it could solve, but none the less I have a place to start.
__________________
  Reply With Quote
   
Old 07-18-2010, 04:56 AM   #7
NeilV is offline
Senior Member
Join Date: Nov 2005
Posts: 1,910
Start at the power source where it enters the RV and follow the power.

On some of the older coaches there is no transfer switch so you have to manually remove a plug from the generator and then plug it into the power cord.

Check the cabinetry inside your RV near the location where the power cord is attached outside and start looking for false panels etc.

You could also give the manufacturers customer service line a call which I believe is Fleetwood at: 800-322-8216.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
  Reply With Quote
   
Old 07-18-2010, 07:54 AM   #8
bigskymt is offline
Senior Member
bigskymt's Avatar
Newmar Owners Club
Join Date: Apr 2010
Posts: 453
What converter do you have? There are several DC fuses and AC breakers in some of the converter boxes. Depending on your model Fleetwood may have installed yours under the bed.
I have a lot of docs remaining from my 84 SouthWind.
__________________
  Reply With Quote
   
Old 07-18-2010, 08:47 AM   #9
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,606
It doesn't sound to me like a fuse or breaker problem. And the a/c worked, so he has shore power (at least for awhile).

There may be a GFCI tripped - that would stop power to the 120vac outlets. Check the bathroom outlet - it is typically the one with the GFCI function.

How are the batteries? Have you checked the voltage there? And the converter/charger (you probably don't have an inverter, or at least it wasn't standard equipment)? You should show 13.3-13.6v at the battery when plugged to shore power and at least 12.6 when not.
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 07-18-2010, 09:59 AM   #10
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
Thanks Gary, being I did not see any GFI, I did not even think about one being the the bathroom, I have the same problem in our 1955 Crown, so that will be the very first thing I check and I hoe it is the problem, if so that will solve the AC side. I will report back once I have been able to test it. The batteries I am not sure I kow one is a new one, but I will have to do a voltage test.

I also guess i will have to check the power panel in the bedroom, all of the fused look goo,d but I guess if power is not being delivered to the fuses, it tell me nothing.

I will check out both today as long as the California heat spell doesn't make being inside unbearable.
__________________
  Reply With Quote
   
Old 07-18-2010, 02:39 PM   #11
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
Gary
You were right on in regards to a GFI in the bathroom being tripped, I corrected that and now all of my AC is currently working, So next I tested all of the 12 volt coming into my Progressive Dynami Power Converter, and discoverd everything was working with the exception to one black wire that was not powered, so I went ahead and jumped it with another wire from one of the lugs with power and all of my DC begin to work so as of today all of the things I was worried about is now working, So now the question will this jumper wire cause any other probelms? I thought I woud buy a fused wire connector and fuse it just under the correct amp just in case of a over load so I woud not burn out that cirucut. Can anyone provide me with their feed back in this matter, I was emailed some wiring diagrams from another board and I will see what this black wire is and where it is coming from to see if I can just replace it, but I am unsure what I will see once I take the face off of this converter in the bedroom area. Has anyone rewired one of these on a 1980-83 fleetwood, and if so can you provide me with some input on how and what you did? I am comfortable with working with 12 volt being I do it all of the time but I do not want to begin something that could create more or other problems.
__________________
  Reply With Quote
   
Old 07-23-2010, 08:22 PM   #12
ralper is offline
Senior Member
Join Date: Apr 2010
Location: Full Timer / Vagabond
Posts: 567
One thing that comes to my mind is that with the age of your unit you should go through it and tighten all electrical connections. PLEASE do it with the power OFF. Even the connections in your vent fans and A/C units. Every connection in the rig. I am not saying this is your problem but it may be. No matter what the problem is the connections should be tightened. I did it on my 5'er when it was new and I found some loose ones.

Fuses blow due to old age and breakers do get old and will not pass the power they are rated for. I would consider replacing all fuses and replacing breakers as needed.
__________________
Ralph & Snickers
2006 3500 Chevy Dually - 8.1 - Allison
2006 30' New Horizon - Solar
  Reply With Quote
   
Old 07-23-2010, 08:46 PM   #13
kartvines is offline
Senior Member
kartvines's Avatar


Vintage RV Owners Club
Fleetwood Owners Club
Join Date: Aug 2008
Location: Beaumont, Calif.
Posts: 436
Thank you I will take this into consideration each time I take something apart I always make sure that the connection is solid
__________________
  Reply With Quote
   
Old 07-25-2010, 09:29 PM   #14
nbounder is offline
Senior Member
Join Date: May 2009
Posts: 306
Ralper has a good point. Also, realize that breakers and fuses will 'pop' at below rated current if the ambient temperature is high - a condition you described earlier. There's very little you can do against this. Some folks have left the cover off the 'fuse box' to aid in cooling the breakers, other have had to add a cheapie fan to do the same thing. In a month or so, it should cool down and the prob goes away.

__________________
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC/DC Relationship Question Jackm MH-General Discussions & Problems 4 10-11-2009 03:25 AM
KVH R4SL voltage problem Gary RVRoamer Technology: Internet, TV, Satellite, Cell Phones, etc. 4 06-20-2008 04:10 AM
National 6355 coach wiring diagrams for AC/DC LIDR National RV Owner's Forum 5 03-20-2008 10:04 AM
AC/DC Issues Harleygirl MH-General Discussions & Problems 5 05-31-2007 06:27 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 11:07 PM.