Old 07-16-2008, 02:43 AM   #1
Junior Member
 
Join Date: Feb 2006
Location: Frederick, Maryland
Posts: 25
I have an 02 Fleetwood Bounder, 2 roof ac units. Sometimes, on either unit, the fan will blow but the compressor will not come on. If I turn it off and back on again, sometimes several times, it comes on. And I can only run one ac unit at a time or neither unit will come on. It has a powermanagement system built into the thermostat and I think it has something to do with that system. Can I eliminate the power management system and install two thermostats for the ac units directly? Thanks.
mxman132 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-16-2008, 02:43 AM   #2
Junior Member
 
Join Date: Feb 2006
Location: Frederick, Maryland
Posts: 25
I have an 02 Fleetwood Bounder, 2 roof ac units. Sometimes, on either unit, the fan will blow but the compressor will not come on. If I turn it off and back on again, sometimes several times, it comes on. And I can only run one ac unit at a time or neither unit will come on. It has a powermanagement system built into the thermostat and I think it has something to do with that system. Can I eliminate the power management system and install two thermostats for the ac units directly? Thanks.
mxman132 is offline   Reply With Quote
Old 07-16-2008, 03:44 AM   #3
Senior Member
 
Workhorse Chassis Owner
Join Date: Sep 2007
Location: st.charles mo.
Posts: 1,482
Do you have a 30AMP or 50AMP service. With a 30AMP service you need the managment system because there is not enough power to start both compresors at the same time. It is posible that your other A/C unit or somthing else in the MH is using to much power to let the other A/C compresor start.
speed racer is offline   Reply With Quote
Old 07-16-2008, 04:06 AM   #4
Junior Member
 
Join Date: Feb 2006
Location: Frederick, Maryland
Posts: 25
30 amp service. I thought of that. With the generator running, and no other loads on the system, should there be enough power to run both ac's?
mxman132 is offline   Reply With Quote
Old 07-16-2008, 05:38 AM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
Since you have a 30A coach, odds are you also have an Energy Management System (probably Intellitec)that prevents both a/c's from running simultaneously. It will let the fans run, but usually won't allow both compressors to cycle at the same time. That's because 30A is not sufficient to handle the starting load of a second a/c while the first is running.

Usually such coaches are wired so that the generator can supply both a/c's and run them both. The generator capacity is usually greater than 30A and one 20A circuit from the generator will supply the rear a/c while the main 30A circuit powers the rest of the coach, including the front a/c.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Long Time Lurker, First Time Poster fncampn New Member Check-In 6 05-21-2008 01:12 AM
Winter Time is Pork Time Kebamo RV Gourmet 1 12-20-2007 05:05 AM
Water pump cycles from time to time. RobG RV Systems & Appliances 10 10-31-2007 12:51 PM
Part Time Work Lee and MaryJane Full-Timers 7 02-16-2007 12:10 PM
The New W16/18 Workhorse Makes Big-Time Power Easy for 1st-Time Class A Buyers DriVer RV Industry Press 6 04-08-2006 03:18 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.