Old 07-09-2017, 12:18 PM   #1
Junior Member
 
Join Date: Jul 2017
Posts: 4
Another house GFCI tripping nightmare..with a twist..

2008 extreme rpm 23ft 30amp service toy hauler....

no problem running TH a/c plugged into the house using a plug adaptor. Today I was vacuuming with a small box fan on, turned the vacuum off to move some items.... turned it on...SNAP goes the GFCI in the garage...Mind you for years I have never had a issue with popping house GFCI's. What make my situation a horror story is the fact that I can still run the box fan but as soon as I turn on the vacuum pop goes then GCFI....turn the water heater, microwave or a/c on..SNAP it comes. What is odd is that I can turn the ac fan only on and no problem...

I am at wits end.... any help would be greatly appreciated....
Berzerker is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-09-2017, 12:54 PM   #2
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
Welcome to the forum.
Yes indeed balancing electrical needs can be a challenge in RV's. There are usually only a couple circuits that have to share multiple loads. The GFIC is not only a ground safety feature but load protector also. So it's possible the inductive load of the motors is a tad high for the rated amperage. Many vacuums can draw 12+amps and a box fan on high could be 5A or more. When you first turn on a motor the inductive load creates back EMF so in effect the circuit sees an additional 20% increase. You A/C, as well as the micro are often on a separate dedicated or perhaps shared circuit.
Many forget the 12V battery charger / converter has to come out of the mix also and is often an overlooked load ??W, HW 800W, refrig.350W
After numerous trips breakers can often get weaker and may not retain their original rating or time delay.
Best of luck.
__________________
J & J, DRV Suites ES-38RSSA #9679
GM Denali, 3500HD-Max, 4x CC, 8' DRW,
EZGo-TXT, Clubcar Precedent
MtnTrek is offline   Reply With Quote
Old 07-09-2017, 01:28 PM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Quote:
Originally Posted by MtnTrek View Post

The GFIC is not only a ground safety feature but load protector also..
That's not true, here is some reading about GFCIs and a link.

A GFCI receptacle will trip off if you overload it (run too many watts).*This is not true at all. Only the circuit breaker in your electrical panel cares about the amount of load things are using. A GFCI is not at all sensitive to that, but it is very sensitive to electrical leaks AWAY FROM the path that loads (things running) use.

http://www.thecircuitdetective.com/h...ical_myths.htm
twinboat is online now   Reply With Quote
Old 07-09-2017, 01:36 PM   #4
Senior Member
 
Join Date: Jul 2000
Location: Chicago Metro
Posts: 3,965
I'm wondering if the problem might be in the outlet the vacuum is plugged into. try a different outlet and see what happens.
__________________
Rich, Ham Radio, Sport Pilot
Retired 9-1-1 Admin.
rk911 is offline   Reply With Quote
Old 07-09-2017, 01:43 PM   #5
Senior Member
 
MtnTrek's Avatar
 
Join Date: Jul 2015
Location: Currently; SW Cali. Sunny & warm!
Posts: 1,323
Quote:
Originally Posted by twinboat View Post
That's not true, here is some reading about GFCIs and a link.

A GFCI receptacle will trip off if you overload it (run too many watts).*This is not true at all. Only the circuit breaker in your electrical panel cares about the amount of load things are using. A GFCI is not at all sensitive to that, but it is very sensitive to electrical leaks AWAY FROM the path that loads (things running) use.

Home Electrical Myths
Hmm, Square D Homeline 20 Amp Single-Pole GFCI Circuit Breaker-HOM120GFICP - The Home Depot
Surely there are probably exceptions to all blanket statements. The GFCI "receptacles" are also on a breaker protected branch circuit. Many times when folks are resetting, pushing, flipping they may not really know what is being done for sure.
Did you have any theories on the OP?
Be well.
MtnTrek is offline   Reply With Quote
Old 07-09-2017, 05:55 PM   #6
Member
 
Join Date: Aug 2015
Location: SLC, Utah
Posts: 73
At least 2 or 3 times a year I get a call from a general contractor I do work for, crying because his shop vac (you've seen them, drywall mud stuck all over the outside, Sheetrock dust in the motor) keeps tripping the gfi receptacle at a job site.
I can't always reproduce the situation, but I am sure it has something to do with the dirty worn brushes in the vacuum motor.
I have to explain to him that my license and insurance is too important to me to risk removing a gfi where someone else might get hurt, and suggest cleaning and repairing the vacuum might be in order.
You might want to check the vacuum motor make sure it is not overly dirty, and that the brushes are overly worn.
rocketslc is offline   Reply With Quote
Old 07-09-2017, 06:54 PM   #7
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
Quote:
Originally Posted by twinboat View Post
That's not true, here is some reading about GFCIs and a link.

A GFCI receptacle will trip off if you overload it (run too many watts).*This is not true at all. Only the circuit breaker in your electrical panel cares about the amount of load things are using. A GFCI is not at all sensitive to that, but it is very sensitive to electrical leaks AWAY FROM the path that loads (things running) use.

Home Electrical Myths
Quote:
Originally Posted by MtnTrek View Post
Hmm, Square D Homeline 20 Amp Single-Pole GFCI Circuit Breaker-HOM120GFICP - The Home Depot
Surely there are probably exceptions to all blanket statements. The GFCI "receptacles" are also on a breaker protected branch circuit. Many times when folks are resetting, pushing, flipping they may not really know what is being done for sure.
Did you have any theories on the OP?
Be well.
I think you guys are comparing granny smith and fuji apples. A GFCI outlet won't trip if overloaded because its also protected by a circuit breaker. A GFCI breaker will trip for both.

I have a 50 amp GFCI circuit breaker in my detached garage that I plug the motor home into.
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 07-09-2017, 06:59 PM   #8
Moderator Emeritus
 
barmcd's Avatar


 
Monaco Owners Club
Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 13,426
GFCI outlets go bad. Can you plug it into another outlet and see if the problems persist?
__________________
Dennis and Katherine
2000 Monaco Dynasty
barmcd is offline   Reply With Quote
Old 07-09-2017, 07:06 PM   #9
Senior Member
 
Vicr's Avatar
 
Join Date: Dec 2016
Location: Fortuna Foothills, AZ
Posts: 189
Send a message via ICQ to Vicr Send a message via AIM to Vicr
The vacuum probably has voltage leakage from hot to neutral causing the GFCI outlet to trip. It's doing what it is supposed to do. And anyone who thinks a GFCI his an over current protection device just had a whole continent of electricians and engineers laughing. Please don't post electrical advice when you have no clue of what your saying.
Vicr is offline   Reply With Quote
Old 07-10-2017, 07:52 AM   #10
Junior Member
 
Join Date: Jul 2017
Posts: 4
But here is the rub....I attempt to turn on the water heater. . pop.. microwave. .pop...ac unit. .pop.. (each separately)...plug the vacuum directly into the garage gfci..works like a champ.... and just to muddy the waters a but more.. The box fan runs fine in the rv. ..as does the fan only on the ac...simultaneously. .. oh wait there's more... I turn off the converter breaker... turn on the micro wave.. it run fine for a few seconds then just slows down as if not enough juice.. I turned it off after 10 seconds or so...oh wait there's even more... when I went to remove the extension cord from the always tripping gfci in the garage as the box fan was running.. it tripped the gfci in the garage....arrrrrrrrrrgggghhh
Berzerker is offline   Reply With Quote
Old 07-10-2017, 07:56 AM   #11
Junior Member
 
Join Date: Jul 2017
Posts: 4
.. oh yes important tidbit... the shore line is a tad to short to reach the garage gfci outlet. m I an running a 50 ft extension cord..small diameter. ..it has been working fine in the past. ..
Berzerker is offline   Reply With Quote
Old 07-10-2017, 07:58 AM   #12
Senior Member
 
Dupdyke's Avatar
 
Join Date: May 2012
Location: Roseville MN sum / La Feria Tx winter
Posts: 790
Perhaps you should try a different extension cord
__________________
Sheri & Don 2003 Dynasty 42" regal ISL 400
2007 Goldwing Trike Gmc 4X4 w/ autoloader for trike
Lets go we got it all loaded.
Dupdyke is offline   Reply With Quote
Old 07-10-2017, 09:37 AM   #13
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
OK, so you have a ground fault somewhere in the RV. Any of several 120vac loads in the RV can trigger the fault, which the GFCI outlet in the garage then detects. Since the GFCI trips any time the neutral current doesn't match the hot current, all you know at this point is that it has to be something common to all those branch circuits. I'd be looking at the shore cord and the laod center (breaker box in the RV).

And no, it is NOT too much current anywhere (amp overload). That's what circuit breakers do, not GFCIs.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 07-10-2017, 10:51 AM   #14
Senior Member
 
CharlesinGA's Avatar
 
Join Date: Jun 2016
Location: South of Atlanta, Georgia
Posts: 2,141
Sometimes the switch in devices will make my GFCI receptacle in the shop trip. It probably is something like that. Most vacuums are double insulated (two prong cord olug) and as such, a low level internal short "cannot" reach the user, but if the GFCI is tripping, the problem should be found.

Try the vac on another GFCI and also on the same circuit without the extra cords, etc.

Although GFCI circuit breaker combinations in electrical panels are more reliable and less likely to cause problems, they are expensive, and you have no idea if the trip is caused by the GFCI circuitry or an overload of the breaker.

Quality GFCI wall receptacles are best in most cases (and more accessible for a reset) and much cheaper in the event that they need replacing, as they do go bad. Note that code does require a wet location rated receptacle or GFCI if the receptacle is installed out doors (and under the proper rain cover).

Charles

Charles
__________________
'03 Ram 2500 CTD, 5.9HO six speed PacBrake std cab long bed Leer top and 2008 Bigfoot 25B21RB.. Previously, 2008 Thor Freedom Spirit 180, SOLD! 2007 Winnebago View 23H Motorhome, SOLD!
CharlesinGA is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bounder: 2016 Bounder 33C - GFCI keeps tripping (Internal to RV, not house GFCI) nehmia Fleetwood Owner's Forum 8 10-22-2016 07:34 AM
DSI Fault and GFCI circuit tripping Boblevy Class A Motorhome Discussions 9 03-04-2014 08:55 AM
Norcold refriegrator tripping GFCI plug nhcouple RV Systems & Appliances 7 01-04-2014 07:37 PM
GFCI at Vanity keeps tripping NeptuneGator RV Systems & Appliances 6 07-24-2009 08:05 AM