Aspire Aqua Hot runs out of hot water, anyone else have a similar problem?
I have a 2013 Aspire. The Aqua Hot in the Aspire is the electric/propane system.
For the three months since delivery we have experienced the following problem.
If we run the hot water, with electric and propane heaters both in the "on" position for a couple of hours, the hot water runs out after 4/5 minutes. However, if you leave the faucet/shower to continue to run, after 3/4 minutes of cold water the temperature rises back up, and we have continual hot water.
But, if we don't use the hot water for a couple of hours we have to repeat the process again.
My son and I have identical units, and both experience varying degrees of the same problem.
We have both had LazyDays check them out TWICE, and last week we had a different authorized Aqua Hot dealer check them out. He replaced the thermostat in each unit, to no avail.
Is anyone else experiencing this problem? And if so, has anyone successfully solved this problem?
__________________
Jeff and Anne
2013 Entegra Aspire 43DLQ
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-04-2013, 01:34 PM
|
#2
|
Community Moderator
Join Date: Aug 2011
Posts: 6,199
|
Quote:
Originally Posted by JeffK
I have a 2013 Aspire. The Aqua Hot in the Aspire is the electric/propane system.
For the three months since delivery we have experienced the following problem.
If we run the hot water, with electric and propane heaters both in the "on" position for a couple of hours, the hot water runs out after 4/5 minutes. However, if you leave the faucet/shower to continue to run, after 3/4 minutes of cold water the temperature rises back up, and we have continual hot water.
But, if we don't use the hot water for a couple of hours we have to repeat the process again.
My son and I have identical units, and both experience varying degrees of the same problem.
We have both had LazyDays check them out TWICE, and last week we had a different authorized Aqua Hot dealer check them out. He replaced the thermostat in each unit, to no avail.
Is anyone else experiencing this problem? And if so, has anyone successfully solved this problem?
|
Do you hear the propane burner kick on during that initial 5 minutes when you are getting hot water?
|
|
|
05-04-2013, 02:06 PM
|
#3
|
Senior Member
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,695
|
Most of us are not used to a demand hot water heater (I lived with this in Turkey in a previous life). So when we turn the shower on after lighting the burner (diesel in this case) I get hot water fairly quickly, but it lasts about 3-4 minutes. Then the demand exceeds the supply, but it is working hard.
So i tend to rinse, turn the nozzle off, lather up (probably TMI), then hit the hot water by turning the nozzle back on (the small amount of water coming out while it is closed seems to signal continued heating required) and it seems to have plenty for the soap rinse as well as washing the hair. That second shot of hot water seems to last longer.
Don't know why...just learning to live with it.
__________________
Dave and Beth
2015 Cornerstone 45J
2020 Ford F-150 Lariat
|
|
|
05-04-2013, 04:07 PM
|
#4
|
Senior Member
Join Date: Apr 2004
Location: Stillwater, Ok
Posts: 4,812
|
It is an ongoing problem with aqua hot and aqua hot is not manning up and accepting responsibility and it is industry wide, not just in Entegras. Entegra is trying to solve the problem in a variety of ways, installed one of the latest on my coach and we will see if it is fixed. Precision told me they are having a lot of issues with this in numerous brands. Hoping somebody gets this figured out.
__________________
2020 New Aire 3543
2018 Lincoln MKX
|
|
|
05-04-2013, 04:15 PM
|
#5
|
Member
Join Date: Jan 2012
Posts: 49
|
Yes, the burner kicks on. Three different Aqua Hot technicians have observed the whole process, with cover off, and took temps at the Aqua Hot and at the water coming out of the faucet.
Dave, I hear what you say, but I don't believe that's how the system is supposed to work. It's supposed to give continual hot water, non stop, for as long as you need it.
The old propane tank system was more efficient than this, you knew you had 20+ gallons of hot water, more than enough for a good shower.
In three months I have had only two or three showers when the hot water did not run out after 3/5 minutes.
I believe that you should not have to turn off the water after a few minutes to "lather up", just my opinion.
I don't believe that for $15,000 that this is what is expected!
__________________
Jeff and Anne
2013 Entegra Aspire 43DLQ
|
|
|
05-04-2013, 04:35 PM
|
#6
|
Senior Member
Tiffin Owners Club
Join Date: Oct 2012
Posts: 197
|
aqua hot customer service /support
[QUOTE=JeffK;1555922]Yes, the burner kicks on. Three different Aqua Hot technicians have observed the whole process, with cover off, and took temps at the Aqua Hot and at the water coming out of the faucet.
Dave, I hear what you say, but I don't believe that's how the system is supposed to work. It's supposed to give continual hot water, non stop, for as long as you need it.]
I felt your pain - I have the model 450 diesel Aquahot in a 2013 Zephyr and experienced similar painful no hot water experiences coupled with no heat either. The nozzle was replaced twice, entire burner was replaced, the control board was replaced. Still from trip to trip hot water was unreliable. Stumped all the field technicans and then I experienced diesel leaks inside the AH unit with fumes spreading to the basement and coach while driving. I was very frustrated and angry - went to corporate AH and simply stated - you build these units to work , if it doesnt then it needs to be taken care professionally
Aquahot was very professional in their customer service/satisfaction department. Call the main number, ask for their customer service department AH stepped up and pulled my original AH unit and replaced it with a brand new one.
Their units do work ; I now have unlimited hot water and no I dont need to turn the shower off which I agree is unnecessary with these units.
AH is really one of the best equipment providers for service out there so give them a chance. They will want to fix it for you
__________________
Rudy
2013 Tiffin Zephyr LZ-ver C towing 2016 Caddy Escalade
|
|
|
05-04-2013, 06:40 PM
|
#7
|
Senior Member
Entegra Owners Club
Join Date: Oct 2009
Posts: 2,193
|
Well - now and then we have a chance to contribute a positive experience in the face of issues. We picked up our Anthem on March 19 and have had zero issues with hot water. When it isn't cold, we turn off the diesel and we can take a decent shower without doing the Navy thing. If we are both showering, we turn the diesel on and then the Aquahot can keep up.
If there are units which can't keep up, it seems like there is clearly an issue since (for once) ours proves that they can work as we expect them too. In fact we have to be careful not to use straight hot or things can be very uncomfortable.
And please understand we are ecstatic with our coach. It's just nice to know not every coach is likely to have every issue - law of averages says some will have almost none and others will seem to have 'em all. I'm not a patient guy so I guess it is good ours tends toward the "few" side.
__________________
Cheryl and Emerson missing Rascal but loving our new buddy, Winston
Sadly Coachless
|
|
|
05-04-2013, 06:44 PM
|
#8
|
Registered User
Join Date: Mar 2013
Posts: 175
|
Low temp thermostate on back or mixing valve. Call Roger Burke. If he can't fix it, it can't be fixed.
|
|
|
05-04-2013, 07:27 PM
|
#9
|
Senior Member
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,695
|
Hmmmm...."when we are both showering"....no, I won't go there. I knew there was a problem with the size of my DEQ shower compared to those bath and a half models
__________________
Dave and Beth
2015 Cornerstone 45J
2020 Ford F-150 Lariat
|
|
|
05-04-2013, 08:34 PM
|
#10
|
Senior Member
Newmar Owners Club
Join Date: Jan 2012
Location: Polk City, FL
Posts: 3,368
|
Not Hot Aqua Hot
I've had similar lack of hot water problems. At first I thought it was my lack of knowledge about Aqua Hot. Both my DW and I are not "shower lingering folks" but my Aqua Hot gets uncomfortable in about 6-7 minutes with either/both heat sources on. I called Entegra and also Aqua Hot. The Aqua Hot guy said they have been having trouble with the Aqua hots on the Entegras. Their opinion was it is the anti-scalding valve in the shower. The Aqua Hot guy said to take a shower, wait until the water gets cold, then try the sink to see if it still provides hot water. If the sink is cold the problem is in the Aqua hot control, burner setting or whatever. If the water in the sink is still hot, it's a shower problem. I called Entegra and they said it was either the shower mixing valve or the lack of a water conservation disk in the end of the shower hose. I am still tracking mine down. I think mine is the mix valve in the shower control.
I must say my old Monaco had a 10 gal Atwood heater that never run out of hot water for numerous showers.
__________________
Dave & Debbie
2021 Newmar DutchStar 4369
2016 Ford Edge&2019 Ford F-150 toads
|
|
|
05-05-2013, 06:42 AM
|
#11
|
Senior Member
Entegra Owners Club
Join Date: Oct 2010
Location: East Greenwich, RI
Posts: 2,300
|
Same here, first full shower, after a few minutes no more hot water. Stopped the water, (despite no water shutoff valve on the showerhead), let the AH catch up and was able to finish the shower. Switched to the fine setting on the spray pattern and seemed like AH could keep up a little better. May be a flow rate issue? Glad to hear some have a properly functioning unit. Attwood 10 gal on last coach gave us all the HW we needed and that was on electric only. We are on our way back to Middlebury to get our floor heat loop fixed so another item for the punch list.
|
|
|
05-05-2013, 07:18 AM
|
#12
|
Senior Member
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
|
Quote:
Originally Posted by voltdoc
Same here, first full shower, after a few minutes no more hot water. Stopped the water, (despite no water shutoff valve on the showerhead), let the AH catch up and was able to finish the shower. Switched to the fine setting on the spray pattern and seemed like AH could keep up a little better. May be a flow rate issue? Glad to hear some have a properly functioning unit. Attwood 10 gal on last coach gave us all the HW we needed and that was on electric only. We are on our way back to Middlebury to get our floor heat loop fixed so another item for the punch list.
|
I suspect an issue with the tempering valve which is inside the AquaHot case and is the first fitting where the hot waster comes out of the boiler. It's also called the mixing valve and mixes the hot coming out of the boiler with cold water to reduce the temp going into the coach. It's a wax valve and it sometimes needs to be exercised by rotating the valve to each direction.
I have also found, counter intuitive as it is, that low water pressure will have the same symptoms.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
|
|
|
05-05-2013, 08:53 AM
|
#13
|
Senior Member
Entegra Owners Club
Join Date: Oct 2009
Posts: 2,193
|
Quote:
Originally Posted by DSL417
Hmmmm...."when we are both showering"....no, I won't go there. I knew there was a problem with the size of my DEQ shower compared to those bath and a half models
|
Hey - it's a lot more fun than saving water the Navy way...
Maybe I should have said "take showers back to back" - nah That wouldn't have helped.....
;-)
__________________
Cheryl and Emerson missing Rascal but loving our new buddy, Winston
Sadly Coachless
|
|
|
05-05-2013, 09:02 AM
|
#14
|
bnb1313@aol.com
Monaco Owners Club
Join Date: Feb 2008
Location: Western Montana on the Divide
Posts: 1,561
|
I had a similar issue with my 450DE Aqua-Hot unit. I replaced the stir pump with a newer more efficient model (say Roger Berke) and disassembled the mixer valve and cleaned it and problem solved. It's been three years since the fix and it's still working perfect. The mixer valve can be disassembled and cleaned even though I was told the opposite.
__________________
Bob Retired Army Traveling alone now, had to put Charlie the Beagle down :(.
2008 Camelot 40 PDQ 4 slides ISL400 towing a 2020 1500 GMC Sierra Denali 4x4 Crewcab
Western MT in summer, AZ, NV in winter
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|