Thumbs up Convert 30 amp to 50 amp and added a 2nd Air Conditioner

Well after a 2 week vacation in 95+ degree weather my mind was made up. I need a second a/c (preferably in the bedroom). Now we are talking about a Winnebago Vista 30t (30 Ft 3 slides) with one Coleman Mach 3 (15k a/c, heat pump) and at 98 degrees outside I could not cool down below low 80's. So I made up my mind to convert from 30 amp to 50 amp service, I also decided to swap out the 4kw Onan for a 5.5kw Onan that I took out of my 5th wheel prior to selling it. So it began, 1st thing I did was start with the transfer switch, then swapped out the breaker box w/converter, I the swapped out the shore power cord and the main line from the transfer switch to the now new breaker box as well as an external convert charger. So now I have a breaker box with two hot lines in (50 amp service achieved) now it was time to tackle the generators. The 4kw's mount was welded in (had to cut it out and grind it smooth, next was to order in the new mount for the 5.5kw. Had my frame reinforced and the new generator mount welded in (the shop that installed it, checked it by placing over 500 pounds of weight in mount). Next was to get the 5.5kw in the mount (placed it on a few wood blocks then backup over the generator so that it was under the RV below the mount) 3 friends and alot of wood blocks, floor jack and jack stands we finally got it into the mount and secured. Hooked up generator to the transfer switch and verified that it worked as it was suppose to. All wire to the transfer switch was 6 gauge wire, 8 gauge from the transfer switch to the breaker panel (ran numerous checks on eletric system, all is good). The last piece of this puzzle was not the hardest, but sure was the most nerve wracking as I had to cut a hole in my roof (14x14 same size as a vent). I then needed to get power to the new a/c through the Styrofoam roof insulation and over to the breaker box. I did get the wires all ran, 2nd thermostat and ducting setup the way I wanted (all the ducted vents forward of the front a/c work on front a/c and I blocked off the rear ducts, then installed duct tunnel from the rear a/c to the ducts to the rear of the front a/c allowing the rear a/c to use the ducts to the rear off the front a/c). I also installed Chill Grills on both front and rear a/c's. Now 98 degrees outside in Lawton Oklahoma about 55% humidity, it's a cool 70 degrees inside my rv. Pics or video to follow once I figure out how to resize.
__________________
Ret. U.S.Army, Comanche County Sheriff's Dept, Lawton Police
Relax and Enjoy the View, Life's to Short
robval1987 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-05-2017, 06:04 AM   #2
Senior Member
 
mikebreeze's Avatar
 
Thor Owners Club
Solo Rvers Club
Mid Atlantic Campers
Ford Super Duty Owner
Join Date: Sep 2012
Location: Manassas, VA
Posts: 755
Congrats! It sounds like you have a good knowledge of electricity to get this done. I'd be curious how much you spent in materials to do this and how much one would expect someone else to do this conversion for them parts and labor wise.
__________________
2006 Four Winds Majestic 23A
mikebreeze is offline   Reply With Quote
Old 08-05-2017, 10:29 AM   #3
Senior Member
 
trx430ex's Avatar
 
Join Date: Jun 2017
Location: Worcester Pennsylvania
Posts: 1,063
Nice upgrade, like the can get it done attitude, safely, and on spec.
Mike, he salvaged much from the 5'er, nice way to do it. Find one that is wrecked, buy it for parts.Things crash everyday.
__________________
2006 Fleetwood Bounder 35E Trek pure Trike, electric, 50 mile range, 7000 ,miles the get everything runner. To be toad list Done, Ford E450 toad. Stay & Play active brakes.
Full-time since 2018. LG 4.5 cu ft washer/dryer.
trx430ex is offline   Reply With Quote
Old 08-06-2017, 11:04 AM   #4
Senior Member
 
Redapple's Avatar
 
Join Date: May 2006
Location: SoCal
Posts: 1,123
Congrats! What you did is no small feat. Great job! Look forward to the pics!
__________________
2020 Grand Design Reflection 315RLTS
2019 GMC Sierra Denali Duramax
Redapple is offline   Reply With Quote
Old 08-06-2017, 11:49 AM   #5
Senior Member
 
trx430ex's Avatar
 
Join Date: Jun 2017
Location: Worcester Pennsylvania
Posts: 1,063
robval1987 had my AC intake down to clean filter, and you made me dig a little deeper because the AC always sounded like it was fighting for flow. So low and behold I pull the cross plenum for output to the front and there is a decal on the top of it??? It was installed upside down!!! creating a 3/4 inch wall of foam on the bottom of that small plenum. Then also the foam between the two ducks was a flat wall air was running into. So I cut the roof foam into a v to deflect the air into the ducks more efficiently. What a difference! That and about 25 pieces of silver tape to seal the intake from the output. Then found leaks from where the 120 line comes in, sealed every little hole with silver tape. System runs 100% more air flow and sounds like it is not struggling.

System still would not have kept up with the heat you were in, but thanks, you made me dig a little deeper.

You may want to revisit the front unit and re-hab it for best flo.Cut the square wall roof foam into a v for more efficient flow.
__________________
2006 Fleetwood Bounder 35E Trek pure Trike, electric, 50 mile range, 7000 ,miles the get everything runner. To be toad list Done, Ford E450 toad. Stay & Play active brakes.
Full-time since 2018. LG 4.5 cu ft washer/dryer.
trx430ex is offline   Reply With Quote
Old 08-07-2017, 04:05 PM   #6
Senior Member
 
Join Date: Jun 2013
Posts: 324
robval1987, Great job! I'd love to see your pictures on this one. I have a Vista 27N and was considering doing exactly the same thing. Solved this one by buying a 30T with dual air conditioners yesterday

Btw, I'm very familiar with Lawton, I grew up there!

David
2013 Vista 27N, soon to be 2017 Sunstar 30T
dwaugh10 is offline   Reply With Quote
Old 08-10-2017, 09:29 AM   #7
Senior Member
 
hilgert's Avatar
 
Join Date: Nov 2014
Location: Somewhere
Posts: 827
I did much the same thing this past weekend on a similarly-sized motorhome. Ripped out the 30A inlet, bypassed the existing 30A transfer switch, and removed the 30A wiring. Replaced with a 50A inlet, 50A transfer switch and ran the 50A cable from one side of the motorhome to the other (very small space to run it).

I also added a 50A Hughes Autoformer (for voltage boost in RV parks with low voltage issues...so pretty much all RV parks) and a Progressive Industries EMS-PT50X 50A EMS (after the autoformer). Both are plug-in units so that I can bypass if either fails.

New AC unit and induction cooktop will be the next big projects (when bank account recovers).
__________________
2019 Fleetwood Discovery LXE 40D
2023 Ford Expedition Limited Stealth Edition Towed
Full-Timers since 2018
hilgert is offline   Reply With Quote
Old 09-01-2017, 10:13 AM   #8
Member
 
robval1987's Avatar
 
Winnebago Owners Club
Join Date: Aug 2017
Posts: 66
Thumbs up pics

Here are the pics for my 30 to 50 amp conversion. I did use the same type of a/c just smaller version, 15,000 btu in living room, 13,500 in bedroom, vents in the living room run from that a/c, vents down the hall, bathroom and bedroom from that a/c, (I blocked off the vents to the rear from inside the living room plenum, small piece of sheet metal and hvac tape.
Attached Thumbnails
Click image for larger version

Name:	2017-09-01 10.37.20.jpg
Views:	134
Size:	142.3 KB
ID:	175145   Click image for larger version

Name:	2017-09-01 10.39.06.jpg
Views:	216
Size:	155.2 KB
ID:	175146  

Click image for larger version

Name:	2017-09-01 10.40.02.jpg
Views:	123
Size:	248.2 KB
ID:	175147   Click image for larger version

Name:	2017-09-01 10.41.05.jpg
Views:	124
Size:	99.5 KB
ID:	175148  

Click image for larger version

Name:	2017-09-01 10.42.00.jpg
Views:	143
Size:	198.9 KB
ID:	175149   Click image for larger version

Name:	2017-09-01 10.42.46.jpg
Views:	121
Size:	133.1 KB
ID:	175150  

Click image for larger version

Name:	2017-09-01 10.43.31.jpg
Views:	132
Size:	183.6 KB
ID:	175151  
__________________
Ret. U.S.Army, Comanche County Sheriff's Dept, Lawton Police
Relax and Enjoy the View, Life's to Short
robval1987 is offline   Reply With Quote
Old 09-01-2017, 10:53 AM   #9
Member
 
robval1987's Avatar
 
Winnebago Owners Club
Join Date: Aug 2017
Posts: 66
Before and After pics

Here are photos of the generators, transfer switch (same switch, it's a dual 30 or 50 amp depending on wiring), breaker boxes, pics of the cutting of the roof and rear a/c install,
I have more pics if needed just PM me or email me for more info.
Attached Thumbnails
Click image for larger version

Name:	654.jpg
Views:	127
Size:	163.2 KB
ID:	175157   Click image for larger version

Name:	2017-09-01 10.37.20.jpg
Views:	112
Size:	142.3 KB
ID:	175158  

Click image for larger version

Name:	583.jpg
Views:	118
Size:	198.2 KB
ID:	175159   Click image for larger version

Name:	2017-09-01 11.30.50.jpg
Views:	125
Size:	198.9 KB
ID:	175162  

Click image for larger version

Name:	2017-09-01-11-01-59.jpg
Views:	112
Size:	356.9 KB
ID:	175169   Click image for larger version

Name:	2017-09-01 10.40.02.jpg
Views:	136
Size:	248.2 KB
ID:	175170  

Click image for larger version

Name:	20170730_102616.jpg
Views:	156
Size:	143.9 KB
ID:	175171   Click image for larger version

Name:	20170730_110836.jpg
Views:	80
Size:	221.5 KB
ID:	175172  

Click image for larger version

Name:	20170730_124625.jpg
Views:	98
Size:	146.6 KB
ID:	175174   Click image for larger version

Name:	20170805_053114.jpg
Views:	101
Size:	145.2 KB
ID:	175175  

__________________
Ret. U.S.Army, Comanche County Sheriff's Dept, Lawton Police
Relax and Enjoy the View, Life's to Short
robval1987 is offline   Reply With Quote
Old 09-01-2017, 01:57 PM   #10
Member
 
robval1987's Avatar
 
Winnebago Owners Club
Join Date: Aug 2017
Posts: 66
Thumbs up 2nd a/c

And yes if you'll look at the pic of the a/c plenum installed you can see the Styrofoam in the ceiling, I did go back an built a wooden fram 1x3.5 (I noticed as i tightened the a/c bolts it began to crush in the Styrofoam) I then covered everything in hvac tape. I did have to drill a hole for the power/thermostat wires as well as the 2x6 inch opening that I cut thru to the duct work for the rear a/c. I also used the new Coleman dump vent/ filter housings on both a/c's to keep the appearance the same and for the function to dump the a/c's directly down and cool off the coach quickly if needed. On my final test day it was 98 degrees outside with a feels like temperature of 111 degrees and I was able to cool the coach down to 70 degrees (the a/c's were actually cycling on and off as needed to keep that temperature, and that was using shore power and then running off the Generator.
__________________
Ret. U.S.Army, Comanche County Sheriff's Dept, Lawton Police
Relax and Enjoy the View, Life's to Short
robval1987 is offline   Reply With Quote
Old 09-09-2017, 02:13 PM   #11
Senior Member
 
Bosunmate's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Jan 2017
Location: South Carolina
Posts: 353
Nice job, mighty nice!!!
__________________
Semper Paratus
KE4TQV
2017 Winnebago Vista 29VE
Bosunmate is offline   Reply With Quote
Reply

Tags
air conditioner, air



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pippi's 30 to 50 amp convert capecodbob iRV2.com General Discussion 0 09-09-2016 07:42 AM
Convert 30 Amp service to 50? beepaj Class A Motorhome Discussions 17 08-21-2013 07:55 AM
2nd Air conditioner install... With pics! EMD_Driver RV Systems & Appliances 7 09-18-2012 01:00 PM
Convert 30 amp to 50 amp GuitarLefty Class A Motorhome Discussions 10 08-06-2012 07:46 PM
2nd air conditioner Roger Watts Excel Owner's Forum 8 02-13-2007 05:26 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:10 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.