Old 07-15-2016, 02:30 PM   #15
Community Administrator
 
Clifftall's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Aug 2009
Posts: 26,499
Let's discuss the topic without discussing each other. Our Community a Rules do not permit this between members.
Thanks, Cliff
__________________

__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
Clifftall is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-16-2016, 09:03 PM   #16
Senior Member
 
1ciderdog's Avatar


 
Join Date: Jun 2010
Posts: 4,299
My thought is it will be OK unless you both need to run air conditioners. Then as mentioned above the amperage may cause problems.
__________________

__________________
Bob, Sandi & Marmaduke the Big Pug
SW OREGON 2004 Journey 39K, 330 Cat
If towing: a 2006 Mini Cooper or 1995 Wrangler
1ciderdog is offline   Reply With Quote
Old 07-18-2016, 07:46 PM   #17
Senior Member
 
Join Date: Jul 2015
Posts: 116
Quote:
Originally Posted by twinboat View Post
If it is a modern and properly wired site, it should be a 100 amp service to it.

The electric code shouldn't allow 3 breakers, that add up to 100 amps, hooked to a wire not capable of carrying it.

What's out there is a totally different thing. Maybe the campground operator can tell you.
Really not true.
Quote NEC section.
42 year, retired IBEW
I hate it when people spout about something the know nothing about.
Look at any typical residential panel and add up the breakers, it will be a lot more than the rated main breaker.
You never use full capacity.

How many of you have ever taken a NEC code class let alone any rely experience in the Trade????
__________________
2008 Dutch Star 4035
Retired IBEW Local 595
Dutchstar08 is offline   Reply With Quote
Old 07-18-2016, 09:52 PM   #18
Senior Member
 
Join Date: Jun 2016
Location: Nine Mile Falls WA / Arizona City AZ
Posts: 437
geez .... Twinboat has the right answer... if the 20, 30 and 50 amp breakers and female plugs are wired correctly they have to be supplied by a 100 amp breaker and corresponding wiring.... this is nothing more or less than a sub panel off a main panel... of course, the park might have just a 50 amp service, expecting you to choose between one of the 3...
__________________
Retired Business Owner, Re-manufacturing HD Clutches, Brake Shoes, Air Compressors, Sales & Installation of PacBrake and other Industrial Friction
jelag is offline   Reply With Quote
Old 07-19-2016, 05:51 AM   #19
Senior Member
 
Join Date: Sep 2012
Posts: 4,712
Actually it is not treated as a sub off a main. It is a main the way you are thinking because it is supposed to have neutral and ground bonded and a ground rod. The RV panel is a sub panel.

Anyone who has looked at how public utility companies provision power or telco services would know that one does not add up the potential usage by counting outlets. They add up the expected loads then factor in a usage model to reduce that number to something less than full usage. As an example a 10 unit park wired with ten 80 Amp boxes (that is how they are termed) would be assumed to use maybe 5 50 amp and 5 30 amp services or 400 Amp total. Then there would be an assumption of say 80% peak usage or 320 Amp supply and the feed sized accordingly. In fact they may also assume a reduction on the use per site as well as another one with a lower occupancy. That probably why a lot of places have power problems for the couple of peak holiday weekends. Ditto crowded telco services telling you a line is not available be it wired or wireless.

This kind of reasoning goes back to when Edison first started selling power in the latter half of the 1800's. It may go back farther in another guise. It significantly alters the number of customers that can be serviced adequately with a given size plant.
__________________
nothermark is offline   Reply With Quote
Old 07-19-2016, 05:59 AM   #20
Senior Member
 
Rockwood27's Avatar
 
Winnebago Owners Club
Nor'easters Club
Workhorse Chassis Owner
Join Date: Jun 2012
Location: Freedom, NH
Posts: 856
Quote:
Originally Posted by jelag View Post
geez .... Twinboat has the right answer... if the 20, 30 and 50 amp breakers and female plugs are wired correctly they have to be supplied by a 100 amp breaker and corresponding wiring.... this is nothing more or less than a sub panel off a main panel... of course, the park might have just a 50 amp service, expecting you to choose between one of the 3...
I would think the max sized breaker would only need to be 80 amps if all 3 outlets are used at once. The cable coming from the main panel only needs to be sized for 80 amps. One conductor would carry a 50 plus 20 amp load. The other conductor would carry the 50 plus 30 amp load. You could have a max of 70A on one hot load and 80A on the other hot side.
__________________
Fran, Mary & Zoey (silver Cocker)
2006 Itasca Sunrise 35A, 2005 W-22, Allison 1000 5 speed
'13 Ford Focus ST or '10 Prius on Master Tow Dolly 80THD-SB or '00 Jeep Cherokee 4-down
Rockwood27 is offline   Reply With Quote
Old 07-19-2016, 06:17 AM   #21
Senior Member
 
Hit_the_Rhod's Avatar


 
Join Date: Oct 2014
Location: Salvisa, KY
Posts: 2,108
Quote:
Originally Posted by twinboat View Post
If it is a modern and properly wired site, it should be a 100 amp service to it.

The electric code shouldn't allow 3 breakers, that add up to 100 amps, hooked to a wire not capable of carrying it.

What's out there is a totally different thing. Maybe the campground operator can tell you.

Actually, the Eaton unmetered box we just ordered is what many campgrounds use for single RV sites. It has a 50 amp RV plug, a 30 amp RV plug, and a 20 amp GFCI standard plug. Box rated for 50 amp maximum draw, and requires 50 amp wiring with disconnect. Bought, installed, and inspected by our county Electrical Inspector. See below:

Eaton Power Outlet Panel - Unmetered-CHU1N7N4NS - The Home Depot

Home depot doesn't actually have them, I had to purchase elsewhere, but their site gives the specs.
__________________
Scot & Laura Kellersberger
Newmar 4 wheel drive Dutch Star 3891, 2005 GMC Canyon. Demco Tow Bar & Baseplate U.S.Army (ret)
1985 - 2006
Hit_the_Rhod is offline   Reply With Quote
Old 07-19-2016, 06:56 AM   #22
Senior Member
 
Join Date: Jul 2014
Posts: 7,310
I'll concede to the experts but if it's wired to a 50 amp breaker at the main and I am drawing 45 amps on the 50 amp outlet and plug in my 15 amp electric grill, out at the pedestal, what purpose would the 3 individual breakers serve.

I now have to find the CG owner and the shed sized panel to reset the tripped breaker.
__________________
twinboat is offline   Reply With Quote
Old 07-20-2016, 08:39 AM   #23
Senior Member
 
Join Date: Sep 2012
Posts: 4,712
If you are drawing 45 Amps and plug in 15 more you will pop the breaker. That is why it is there. That is also the intent of the setup. It is designed and provisioned to supply one of the three sockets at a time. The intent is to supply a large RV, or a small RV or a tent camper.

FWIW you will probably seldom if ever draw 45 amps on one leg of a properly installed 50 Amp setup. Maybe with 3 A/C's running while doing laundry in a stacked washer and dryer, low battery charge and somebody hitting the hair dryer while the microwave heats a cup of water for some tea right after a shower. ;-)
__________________
nothermark is offline   Reply With Quote
Old 07-20-2016, 11:08 AM   #24
Senior Member
 
Join Date: Jul 2014
Posts: 7,310
Quote:
Originally Posted by nothermark View Post
If you are drawing 45 Amps and plug in 15 more you will pop the breaker. That is why it is there. That is also the intent of the setup. It is designed and provisioned to supply one of the three sockets at a time. The intent is to supply a large RV, or a small RV or a tent camper.
You missed the point here. The panel has, as many do, a 50, a 30, and a 20 amp breaker. I don't believe the 20 and 30 are run off the 50.

I have used these panels and only needed the 30 amp breaker on. The 50 was off and I had power.
__________________
twinboat is offline   Reply With Quote
Old 07-20-2016, 11:23 AM   #25
Senior Member
 
Join Date: Sep 2012
Posts: 4,712
They do not need the 50 on at the box. They are provisioned for 50 with the wiring. The 30 and 20 are off the 240 split phase bus. As has been pointed out one does not need to supply the total current of the breaker capacity of the box. OTOH one should put a breaker at the source end of the feed cable. The cable will probably be a #6 protected at the feed with a 50 Amp breaker.
__________________
nothermark is offline   Reply With Quote
Old 07-20-2016, 11:30 AM   #26
Senior Member
 
Join Date: Sep 2012
Posts: 4,712
I am not sure if they are or are not. The point is the box will probably be provisioned with #6 wire protected at the feed end with something between a 50 and 60 Amp breaker. Depending on the source one can get 50, 55, and 60 Amp rated breakers and the wire will handle that safely depending on conductor type and insulation. Provisoning for more power would add significantly to the cost of the wire for a marginal improvement for the end user. In fact it would be a benefit for the park as it would keep usage from exceeding their expectations.
__________________
nothermark is offline   Reply With Quote
Old 07-20-2016, 11:32 AM   #27
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,778
Quote:
Originally Posted by Terryshirley View Post
If I park 2rvs on one site and plug into both the 50 amp and the 30 amp will there be any issues. Don't know how much comes to the site supply box. I want to camp with my sister but they only have room for me to plug in with them on their post
Terryshirley
I don't think it's possible to know whether or not there will be issues with that particular shore power hookup in that particular site unless/until you try it.
Mel
'96 Safari
__________________
mel s is offline   Reply With Quote
Old 07-20-2016, 08:45 PM   #28
Senior Member
 
Join Date: Feb 2010
Posts: 4,384
The small breakers in the sub panel or pedestal are there per NEC as they protect the circuits they serve based on capacity.

A 50 add me breaker may serve or protect the pedestal but the smaller circuits of 30 and 15 or 20 amp are both 120 vac not 240 vac and also smaller capacity so a single pole breaker for each per the circuit design.
__________________

__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Reply

Tags
electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Supply Pump Electrical Problem porpear RV Systems & Appliances 2 11-04-2011 02:49 AM
freezing water supply bandmbrown MH-General Discussions & Problems 5 12-27-2008 07:28 AM
high pressure air supply on Mh Oh-one MH-General Discussions & Problems 9 12-08-2008 03:59 PM
Workhorse springs and supply problems Max Tunnell Workhorse and Chevrolet Chassis Motorhome Forum 14 11-29-2008 12:22 PM
Air supply pressure denwhit Alpine Coach Owner's Forum 7 11-16-2005 03:11 AM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:41 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.