03-22-2012, 05:29 PM
|
#1
|
Senior Member
Join Date: Feb 2011
Posts: 514
|
Gen. will not hold 2 a/c's
My owners manual says my 5000 watt Koehler gen. will operate my 2 a/c's When I put the second A/C online the voltage goes from 120 V to less than 100 V.I have a 30 amp system and I know you cant run 2 a/c's on shore power but your supposed to be able to when on Generator. Obviously you cant. The genny runs perfect and put out 120 V with one a/c but start the other and it drags it way down.. Any suggestions ?
__________________
Don and Maxine McQueen
1996 Damon Intruder
F53 Chassis 33 ft
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-22-2012, 05:39 PM
|
#2
|
Senior Member
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 5,927
|
Sounds like the governor needs adjustment. The engine should speed up and handle the second AC. Your unit is rated to run two airs.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2014 Honda CRV toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
|
|
|
03-22-2012, 07:26 PM
|
#3
|
Moderator Emeritus
Ford Super Duty Owner
Join Date: Aug 2000
Location: Bryan, TX when not traveling.
Posts: 22,945
|
Unless it is an inverter style generator, the generator will not speed up. The 60 hz output is controlled by the engine speed and it runs at a constant speed. The additional A/C will put additional load on the generator, the voltage will sag a bit and the governor on the generator will increase the throttle to maintain 60 hertz and bring the voltage back up.
Now a more expensive inverter generator, will run at reduced or increased speed to handle the load and voltage. The frequency is controlled electronically and is not dependent on generator speed.
Ken
__________________
Amateur Radio Operator (KE5DFR)|No Longer Full-Time! - 2023 Cougar 22MLS toted by 2022 F150, 3.5L EcoBoost Tow Max FX4 Lariat Travel with one Standard Schnauzer and one small Timneh African Gray Parrot, retired mechanical engineer
|
|
|
03-22-2012, 07:38 PM
|
#4
|
Senior Member
Join Date: Mar 2011
Posts: 151
|
I would double check if you can run both a/c units. I don't think my 5500 Onan will run both of my a/c units (15000 & 13500). I just run the a/c unit I need at that time.
|
|
|
03-22-2012, 07:43 PM
|
#5
|
Senior Member
Fleetwood Owners Club Mid Atlantic Campers Workhorse Chassis Owner
Join Date: Apr 2010
Location: Locust Grove, Virginia
Posts: 345
|
Does the generator engine slow significantly when the second A/C comes on line? If so it could be a restricted fuel filter. Has it ever pulled both A/C's?
__________________
Wayne, Diane, & Bentley (our 22 lb. alarm system) 02 Pace Arrow 37A-Workhorse, 01 Jeep Wrangler toad
|
|
|
03-22-2012, 07:48 PM
|
#6
|
Registered User
Monaco Owners Club
Join Date: May 2009
Posts: 3,198
|
I'd expect a 5500 to run both. The one in my old pace arrow did. spray the carb linkage / governer linkage with carb cleaner, change the oil and filter and fuel filer, and just flatt run her for a while.
|
|
|
03-22-2012, 08:01 PM
|
#7
|
Senior Member
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,731
|
Quote:
Originally Posted by TGR
I would double check if you can run both a/c units. I don't think my 5500 Onan will run both of my a/c units (15000 & 13500). I just run the a/c unit I need at that time.
|
I guess mine must both be 13,500W, cause my 5.5KW Generac has no trouble running both .
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
|
|
|
03-22-2012, 08:26 PM
|
#8
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Jul 2010
Location: Anderson,IN
Posts: 407
|
Runs one or two air conditioners with power to spare.5500 onan,mine has 2 30amp breakers,
Air conditioner starting: One 13500 Btu air
conditioner with 3000 W base load or two 11000 Btu air
conditioners with 1500 W base load
So if you start the 13500 first then start the other.I can run both at the same time.
A 15000 btu roof air is only 2000 watts,and a 13500 btu air is about 1500 watts,so a 5500 watt generator should run both with no problem.
|
|
|
03-23-2012, 06:55 AM
|
#9
|
Senior Member
Monaco Owners Club
Join Date: Mar 2012
Location: Angola State Prison - Murder
Posts: 4,230
|
Quote:
Originally Posted by 96 Wideglide
I guess mine must both be 13,500W, cause my 5.5KW Generac has no trouble running both .
|
My 5500 Generac runs both of mine which is a no brainer as my 30amp coach runs both on shore power. Both on low fan pulls about 24-26amps
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
|
|
|
03-23-2012, 07:16 AM
|
#10
|
Senior Member
Join Date: Feb 2011
Posts: 514
|
Quote:
Originally Posted by JimM68
I'd expect a 5500 to run both. The one in my old pace arrow did. spray the carb linkage / governer linkage with carb cleaner, change the oil and filter and fuel filer, and just flatt run her for a while.
|
I did all that except I didnt spray the linkage with carb cleaner I'll try the carb cleaner today. With one a/c going the volt meter reads 120 Kick on the other a/c and it immediately drops to 100 V or lower. I use one of those meters that plugs directley into a 110 resceptical. and you just leave it there plugged in. I agree that it should hold both a/c's but the second one will drag it down in no time at all. Both a/cs keep going ok but that low of a voltage scares me and I shut one off immediately..
__________________
Don and Maxine McQueen
1996 Damon Intruder
F53 Chassis 33 ft
|
|
|
03-23-2012, 07:27 AM
|
#11
|
Senior Member
Monaco Owners Club
Join Date: Mar 2012
Location: Angola State Prison - Murder
Posts: 4,230
|
Just a thought. Have you tried alternating which AC you turn on first? Perhaps the capacitor is bad in one of them?
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
|
|
|
03-23-2012, 07:33 AM
|
#12
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
What else are you trying to run on electricity when attempting to run the 2 A/Cs? The water heater? Refrigerator? Coffee pot? Hair dryer? Microwave? Any of these are current hogs and, especially if several are in use, could affect the ability of your generator to handle the 2nd A/C unit.
Rusty
|
|
|
03-23-2012, 07:42 AM
|
#13
|
Senior Member
National RV Owners Club Workhorse Chassis Owner
Join Date: Apr 2011
Location: Federal Way, Wa.
Posts: 2,901
|
The manual presumes your generator has been cared for in the perscribed manner during it's life time, particulaly when it comes to fuel. You do not say if this is a generator original to you. If it is then you know the answer.
If it is the same vintage as your MH, and you are not the original owner; has it ever handled two AC's since you aquired the MH? If not then it could just be the build up of the dreaded shellac in the fuel system which occurs with inactivity. It may need a more complete cleaning of the fuel system. At least it could use a good workout.
Your generator evidently has the capacity if running well, not at idle but under load.
__________________
I do all my own stunts
03 Dolphin LX 6355, Workhorse W22, 8.1 vortec, 04 CR-V, Blue Ox, Brake Pro----Norm, Barb and
Doc(He's a PhD)
|
|
|
03-23-2012, 07:56 AM
|
#14
|
Senior Member
Join Date: Nov 2006
Location: Oswego, NY
Posts: 483
|
If all the wiring isn't original, you might check that each AC is on separate breakers - Most 5500 Watt generators have a 30 amp & 20 amp breaker; if both ACs ended up on the same generator output that would cause your problem. Try shutting off the breakers at the generator one at a time to check...
__________________
Jon Vermilye
|
|
|
|
|