Old 05-19-2018, 03:59 PM   #15
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by LJowdy View Post
Shore power 50 amp service isn't 240 volt but rather (2) separate 120 volt circuits theoretically (1) 30 amp line and (1) 20 amp line .
50 amp service is 2-120 volt lines, L1 and L2. Each with a 50 amp breaker so you can potentially draw 100 amps @ 120 volts.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-19-2018, 04:02 PM   #16
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by Shawn6596 View Post
50 amp shore power is 50 amps @ 240v. Yes the RV only uses 120v appliances, but the wiring and service is 240v. Here is a video that explains it.
Your statement "(2) separate 120 volt circuits" is exactly how 240v is achieved. 120v from the A phase, and 120v from the B phase create 240v.

Not always!! Some high end coaches use 240 for a cooktop or dryer. Mine has a 240 volt dryer.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 05-19-2018, 04:10 PM   #17
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
yes, that's why it's 240v coming thru your Shore Cord, but your breaker panel setup determines whether any of your breakers are designed to use the 240v power, like for a dryer, or whether everything is 'split' onto either side of the panel for only 120v power, which is the typical RV setup.

yes, 50amp RV service can easily be suggested as two different 120v 50amp lines, and it's easy to swallow it that way when describing it, but it's actually still 240v service from a 'full power' standpoint. I also sometimes describe it to those who are new as two separate 50amp hot lines of 120v service, but that's just to 'ease' the conversation and understanding of why you have a double-pole breaker, and not a single breaker, like on a 30amp outlet.

it's when someone describes RV 50amp Service as the same as a 30amp breaker and a 20amp breaker combined, I cringe. It may seem that way when you just 'say' 50amp service, but when you look at the double-pole breaker, you have to assume something much different.
MisterT is offline   Reply With Quote
Old 05-19-2018, 04:14 PM   #18
Senior Member
 
Join Date: Jul 2014
Posts: 35,442
Quote:
Originally Posted by LJowdy View Post
Shore power 50 amp service isn't 240 volt but rather (2) separate 120 volt circuits theoretically (1) 30 amp line and (1) 20 amp line .
That's not true. 50 amp shore power is 50 amp 240 volt service. The RV uses it as 2, 50 amp, 120 volt lines.
twinboat is offline   Reply With Quote
Old 05-19-2018, 04:16 PM   #19
Senior Member
 
Join Date: Dec 2017
Posts: 245
thank you folks. those were the answers I was looking for. just wanted to be sure there wasn't anything RV specific I should be concerned with. I have traced all the wires from the panel through the transfer switch and back to the generator. everything appears to be wired in a very standard 240v configuration. I only asked to be sure there weren't any traps I should be looking for. again thanks guys
__________________
97' Overland Ospery 4012, 42' long, 41,000 miles, 8.3 cummins, 6 speed allison, freightliner chassis, pulling a 24' enclosed trailer.
Shawn6596 is offline   Reply With Quote
Old 05-19-2018, 04:18 PM   #20
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
congrats, and if you follow thru with your plan, let us know how it works out.... others may be interested in the very same idea : )
MisterT is offline   Reply With Quote
Old 05-19-2018, 04:23 PM   #21
Senior Member
 
Join Date: Jul 2014
Posts: 35,442
If you set up your 8000 watt generator for 240 volts, you will only have 33 amps per leg.

One of your legs will probable need more then that to run one AC and your water heater. At 50 amps, that will work, at 33 amps, it will trip a breaker.

With the generator outputs combined as 120 volts, as it is now, you have 66 amps shared between both legs. You can pull more then 33 amps on the leg that handles the high amp draw items.
twinboat is offline   Reply With Quote
Old 05-19-2018, 04:29 PM   #22
Senior Member
 
Join Date: Jun 2017
Posts: 2,807
Quote:
Originally Posted by LJowdy View Post
Shore power 50 amp service isn't 240 volt but rather (2) separate 120 volt circuits theoretically (1) 30 amp line and (1) 20 amp line .
Absolutely wrong!

But I see i was beat to it.......Several times.


Hard to believe with all the 120 VAC/240 VAC 30 Amp, 50 Amp, 100 Amp threads on this forum there are still people who propagate incorrect information. It's OK to be misinformed: just don't spread your misinformation.
aether_one is offline   Reply With Quote
Old 05-19-2018, 04:34 PM   #23
Senior Member
 
Join Date: Jun 2017
Posts: 2,807
Quote:
Originally Posted by twinboat View Post
If you set up your 8000 watt generator for 240 volts, you will only have 33 amps per leg.

One of your legs will probable need more then that to run one AC and your water heater. At 50 amps, that will work, at 33 amps, it will trip a breaker.

With the generator outputs combined as 120 volts, as it is now, you have 66 amps shared between both legs. You can pull more then 33 amps on the leg that handles the high amp draw items.
This answers my would-be question of why it was wired for 120 VAC in the first place.
aether_one is offline   Reply With Quote
Old 05-19-2018, 04:51 PM   #24
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
Smile

Quote:
Originally Posted by Mr_D View Post
50 amp service is 2-120 volt lines, L1 and L2. Each with a 50 amp breaker so you can potentially draw 100 amps @ 120 volts.

hey Mr D! I just thought of something... send us a picture of your breaker panel... getting eyeballs on your 240v double-pole breaker for your dryer will be a help in all of us understanding the 240v vs 120v disagreement.

My understanding is this: just like your home's breaker panel(go look and see), you have two 'sides' of breakers, just like your RV, though since your RV's box might be set up horizontally, you might not think it looks the same, but it really is.
Electricians have to manually decide how the box is 'separated' by the number of breakers needed, and must install them for an 'equal' share of the power. So, if one side has 100amps of breakers, in total, the other side will have a similar or same number of amps. RV Factories do the same, only on a smaller scale, 50amps, or so, on each 'side'. All 'single' breakers will be 120v since they only use one 'side' of the incoming power, or one 'leg' of 240v, which is 120v.

Now, whenever you see a 'Double-pole' breaker(such as 2 30amp breakers with a shared 'handle'), you are actually seeing a true 240v circuit, which will go to something such as a dryer, which requires higher power for all of the heat that it generates. Ultimately, this is like 60amps totals to the dryer, not just 30, since it's 'two' separate 30amp 120v lines, but going to a single source, with a shared neutral.
Most of our coaches do not have a double-pole breaker within our panel because we don't have any 240v appliances... though, Mr D does!

If 50amp RV service wasn't really 240v service, just like your home, then Mr D could not use his dryer...that would make for a sad wife! : /
MisterT is offline   Reply With Quote
Old 05-19-2018, 05:20 PM   #25
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,704
Quote:
Shore power 50 amp service isn't 240 volt but rather (2) separate 120 volt circuits theoretically (1) 30 amp line and (1) 20 amp line .
Even without the inevitable 120 vs 240 arguments, that's just plain wrong! At the very least it would be 2 x 120v/50A circuits. Standard RV 50A delivers up to 12,000 watts of power.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 05-19-2018, 05:28 PM   #26
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by twinboat View Post
If you set up your 8000 watt generator for 240 volts, you will only have 33 amps per leg.

One of your legs will probable need more then that to run one AC and your water heater. At 50 amps, that will work, at 33 amps, it will trip a breaker.

With the generator outputs combined as 120 volts, as it is now, you have 66 amps shared between both legs. You can pull more then 33 amps on the leg that handles the high amp draw items.

35 amp genset breaker(s)?
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 05-19-2018, 05:30 PM   #27
Senior Member
 
Join Date: Dec 2017
Posts: 245
Quote:
Originally Posted by twinboat View Post
If you set up your 8000 watt generator for 240 volts, you will only have 33 amps per leg.

One of your legs will probably need more than that to run one AC and your water heater. At 50 amps, that will work, at 33 amps, it will trip a breaker.

With the generator outputs combined as 120 volts, as it is now, you have 66 amps shared between both legs. You can pull more than 33 amps on the leg that handles the high amp draw items.
You have a very fair point, but the water heater is gas/electric. I have no intention of using it on electric portion of the water heater unless I am on shore power. That being said I may investigate changing it over to 240 if I go that route. also the breakers on the generator are 35 amps.
__________________
97' Overland Ospery 4012, 42' long, 41,000 miles, 8.3 cummins, 6 speed allison, freightliner chassis, pulling a 24' enclosed trailer.
Shawn6596 is offline   Reply With Quote
Old 05-19-2018, 05:36 PM   #28
Senior Member
 
Join Date: Jul 2014
Posts: 35,442
[QUOTE=MisterT;4197531]hey Mr D!



. Ultimately, this is like 60amps totals to the dryer, not just 30, since it's 'two' separate 30amp 120v lines, but going to a single source, with a shared neutral.
Most of our coaches do not have a double-pole breaker within our panel because we don't have any 240v appliances... though, Mr D does!
--------------------------------------------------------''--------


It is a true 240 volt circuit, but it doesn't share a neutral, it doesn't us a neutral at all. The heater coils are 240 volt.

If you double the voltage, the amp draw is halved. That makes it a 30 amp, 240 volt circuit.

The dryer does use some 120 volts for the motor and control but that's the only reason the neutral is there.
twinboat is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 amp 120v or 240v Jamesdl MH-General Discussions & Problems 103 04-16-2018 03:26 PM
50A 120V/240V distribution panel - what uses 240V? CountryB Monaco Owner's Forum 27 10-13-2017 07:53 PM
120v/240v compressor plumbed into DP air system ElvistheKing Class A Motorhome Discussions 23 07-19-2017 04:10 AM
30 amp at 120v or 240v gboyle Class C Motorhome Discussions 29 04-21-2014 05:45 PM
Water heater element, 240V vs. 120V? lwgmc77 iRV2.com General Discussion 17 01-06-2014 09:07 AM