Old 01-20-2006, 01:13 PM   #1
Senior Member
 
Join Date: Aug 2003
Location: Worcester, MA
Posts: 340
I run my MH and genrator for an hour every month while not in use. I am having trouble getting the generator to start. I sometimes have to try it 4 or 5 times before it will start. It seems like it not getting gas. Anyone else having trouble? Scotty.
__________________

__________________
2005 FourWinds 24T motorhome, 23' Stratos walk around, 1991 FXRS + 1994 XL 1200, 3 Springer spaniels and wife.
Fxrscotty is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-20-2006, 01:13 PM   #2
Senior Member
 
Join Date: Aug 2003
Location: Worcester, MA
Posts: 340
I run my MH and genrator for an hour every month while not in use. I am having trouble getting the generator to start. I sometimes have to try it 4 or 5 times before it will start. It seems like it not getting gas. Anyone else having trouble? Scotty.
__________________

__________________
2005 FourWinds 24T motorhome, 23' Stratos walk around, 1991 FXRS + 1994 XL 1200, 3 Springer spaniels and wife.
Fxrscotty is offline   Reply With Quote
Old 01-20-2006, 02:38 PM   #3
Senior Member
 
antlerz's Avatar
 
Join Date: Dec 2005
Location: Missouri
Posts: 115
HI FXrScotty,
Just had that problem about a month ago , we have a Onan 7k gas genset it had a partial clogged fuel filter, it looked good looked as if gas was really going good too, but it wasn't
changed the fuel filter and now cranks about 2 times and runs great, So fuel filter and air cleaner may need to be changed almost forgot there is a winter and summer setting for ours too. It adjust the air going into the carb.

hope that helps

antlerz
Craig & Linda
Oscar the Dog
__________________
1994 Holiday Rambler Endeavor LE 32 CB F53 chassis

2007 Toyoata Prius Hybrid
antlerz is offline   Reply With Quote
Old 01-20-2006, 04:21 PM   #4
Senior Member
 
Kirk's Avatar
 
Join Date: Jan 2000
Location: Livingston, Tx., US
Posts: 162
I had the hard start, multi try problem with an Onan some years back followed by a fuel pump failure.
__________________
Good travelin! ......Kirk
URL: www.1tree.net/adventure/
Kirk is offline   Reply With Quote
Old 01-20-2006, 05:35 PM   #5
Senior Member
 
Join Date: Mar 2005
Location: Phoenix, AZ
Posts: 1,029
My Onan starts "faster" now that I know how to prime it first with the local or remote switch.
__________________
abarkl is offline   Reply With Quote
Old 01-22-2006, 01:50 PM   #6
Senior Member
 
Webster's Avatar
 
Join Date: May 2005
Location: Jamestown, California
Posts: 330
You didn't say you had an Onan so I don't know much about those. I have a Generac and it wouldn't start at all. My repair shop checked the solenoid and that solved the problem.
__________________
<font color="#0000ff">George Eldridge

Cynthia Totten</font>
Webster is offline   Reply With Quote
Old 01-22-2006, 04:00 PM   #7
Senior Member
 
Dougmyers's Avatar
 
Join Date: Jan 2006
Location: TEXAS
Posts: 177
My Onan would not start one time and I changed fuel pump and filter fixed it for about two months. Then when it would not stay running I found it was sucking air on the fuel line at a rubber connector, changed that and runs fine now.
__________________
Doug & Diane Myers

DFW, Texas
Dougmyers is offline   Reply With Quote
Old 01-22-2006, 04:26 PM   #8
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,150
Blog Entries: 21
We had a 1999 Minnie Winnie with a Onan Microlite 4.0 that was hard to start from day one. You had to crank several times if it set for more than a day or two. It always started, but did take some cranking. Onan would do nothing except charge you for a tune up and the thing started no differently than before they lightened your wallet.

It acts as it does not get fuel and you have to reprime it after a day or two. I wonder if a check valve in the fuel line would help it.

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 01-22-2006, 04:55 PM   #9
Member
 
Join Date: Jun 2003
Location: Hogtown, Va.
Posts: 93
I believe that the gas does not stay right at the fuel pump for that period of time. My generator does the same thing as you stated. If I go out the next day it starts fine. In your Onan manual they describe how to prime your generator before starting if it has been sitting. It recommends to hold the switch in the stop position for a few seconds to prime the unit.
__________________
dawg is offline   Reply With Quote
Old 01-23-2006, 02:12 PM   #10
Senior Member
 
Join Date: Aug 2003
Location: Worcester, MA
Posts: 340
Thanks to all that replied. I will look and see if there is a prime switch. It is a generac 4000 gardian. Scotty.
__________________
2005 FourWinds 24T motorhome, 23' Stratos walk around, 1991 FXRS + 1994 XL 1200, 3 Springer spaniels and wife.
Fxrscotty is offline   Reply With Quote
Old 01-24-2006, 01:43 PM   #11
Senior Member
 
Join Date: Aug 2003
Location: Worcester, MA
Posts: 340
I pulled the panel and there is a primer switch. Why it there isn't a remote to the inside of the coach is beyond me. My last two slide ons had remotes! go figure. Scotty.
__________________
2005 FourWinds 24T motorhome, 23' Stratos walk around, 1991 FXRS + 1994 XL 1200, 3 Springer spaniels and wife.
Fxrscotty is offline   Reply With Quote
Old 01-24-2006, 03:14 PM   #12
Senior Member
 
Webster's Avatar
 
Join Date: May 2005
Location: Jamestown, California
Posts: 330
The primer on my Generac is on the generator. Don't have a remote. I will try the holding down stop and see if that improves the starting.
__________________
<font color="#0000ff">George Eldridge

Cynthia Totten</font>
Webster is offline   Reply With Quote
Old 01-25-2006, 02:16 PM   #13
Senior Member
 
Join Date: Aug 2003
Location: Worcester, MA
Posts: 340
Webster, my last two had seperate switches for the primer on the panel. Smae brand go figure. I am curious to know if holding the stop switch works. it doesn't make sense that it would but the older I get the less stuff makes sense! Scotty.
__________________
2005 FourWinds 24T motorhome, 23' Stratos walk around, 1991 FXRS + 1994 XL 1200, 3 Springer spaniels and wife.
Fxrscotty is offline   Reply With Quote
Old 03-31-2006, 11:02 AM   #14
Member
 
Swannee's Avatar
 
Damon Owners Club
Join Date: Jun 2005
Location: Jacksonville Fla.,USA.
Posts: 77
Hay,Fxrscotty
Ditto, we have a 31 ft. 2004 Chateau by four winds, the problem started last trip. I have probably put 40 hrs on gen-set since we bought the rig. Tried it last week for grins and it was worse than before it finally started.
Going to track fuel line as Dougmyers said this is most logical action to me. It runs good once it starts sounds like having to pull full line of fuel to re-crank.
Once again I have learned something from this site.............
thanks in advancce
MIke
__________________

__________________
MIke & Karen

Swannee is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
hard starting burnsy MH-General Discussions & Problems 3 08-26-2008 08:36 AM
Hard starting kt38 Newmar Owner's Forum 7 03-21-2008 04:43 PM
Hard starting generator Fxrscotty MH-General Discussions & Problems 2 03-03-2006 02:16 PM
Hard Starting? htg3 Alpine Coach Owner's Forum 3 01-30-2006 10:46 AM
hard starting New Member Check-In 3 12-31-1969 07:00 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.