Here is my problem.
when plugged into a 30 amp shore power all my outlets, lights, microwave and ac units work. I have 2 ac units with a switch to run the front or rear. turn switch to front and front ac runs turn to rear and rear ac runs.
when generator is running ac units work but turn switch to front and rear ac runs, turn to rear and front ac runs. also I lose all power to outlets, lights, and microwave.
I also had plugged into shore power and started generator and it seemed to stay on shore power since everything worked normal. when I pulled shore power ac units worked in reverse of switch and no power to outlets, microwave etc.
Whats up???
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
04-07-2007, 04:39 PM
|
#2
|
Junior Member
Join Date: Jan 2007
Posts: 6
|
Here is my problem.
when plugged into a 30 amp shore power all my outlets, lights, microwave and ac units work. I have 2 ac units with a switch to run the front or rear. turn switch to front and front ac runs turn to rear and rear ac runs.
when generator is running ac units work but turn switch to front and rear ac runs, turn to rear and front ac runs. also I lose all power to outlets, lights, and microwave.
I also had plugged into shore power and started generator and it seemed to stay on shore power since everything worked normal. when I pulled shore power ac units worked in reverse of switch and no power to outlets, microwave etc.
Whats up???
|
|
|
04-08-2007, 12:43 AM
|
#3
|
Moderator Emeritus
Country Coach Owners Club Appalachian Campers Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
|
dgren, welcome to iRV2.com. It sounds like you have either a wiring problem between generator and transfer switch or possibly a bad set of contacts in the transfer switch. Are you comfortable in working with elctricity? If not I would recommend you have a qualified individual check this issue out and make neccessary repairs. GOod luck and enjoy the website.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
|
|
|
04-08-2007, 01:17 AM
|
#4
|
Senior Member
Join Date: Nov 2005
Posts: 4,063
|
dgren,
As Mike said plus can you provide the make, model and year of your RV.
Although it may be that someone cross wired something in the transfer switch connections, which is what I found when I first purchased my current coach, it could also be something as simple as one of the breakers built into the generator are tripped. Open up the access panel on the generator and see if one of the breakers or reset buttons inside there are tripped. It could also be a combination of all things mentioned thus far.
It is generally normal for the shore power to override the generator when both are active.
Give us more data and let us know when/how things get worked out.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
|
|
|
04-08-2007, 05:30 AM
|
#5
|
Senior Member
Monaco Owners Club
Join Date: Apr 2002
Location: On top of Windy Hill - Florida
Posts: 141
|
Hello dgren,
As Mike and Neil said, more info on your RV would be helpful. Is this a new problem on an RV you have had for a while or on an RV you just acquired?
If your transfer switch stays on shore power after the generator has been running for more than two minutes then you have, at least, a transfer switch problem. I have had both Fleetwood and Monaco products and on all of them the transfer switch will default to the the generator power, when both generator and shore power are present. You should check your owner's manual for confirmation.
Green lights and soft breezes,
__________________
Roland, Diane & Katie - the furry 4-footed kid
'01 Diplomat - ISC330 - Allison MD3060 - Progressive Ind. EMS-50C - Hughes Autoformer - '06 Jeep Liberty CRD
|
|
|
04-08-2007, 08:21 AM
|
#6
|
Junior Member
Join Date: Jan 2007
Posts: 6
|
Thanks for the help. Found the 30 amp circuit breaker on generator had been triped. reset and all seems to work ok. I still need to plug in to a 30 amp service and see if generator will over ride the shore power.
|
|
|
|