Originally Posted by rssnape View Post
...I guess I should swap one pair of hots to lessen the possibility of all the load being on one leg...Attachment 175716
If you do and they 're all wired the same then you have an unbalanced load. Not much you can do unless you supply the 30 to 50 adapters.
__________________

__________________
Hank & Lynda
2003 Winnebago Adventurer 35U, Workhorse W22
70ChevelleSS is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-08-2017, 05:35 AM   #16
Senior Member
 
SKP Kirk's Avatar
 
Join Date: May 2010
Location: Part-time out of Bass Lake Retirement Community
Posts: 335
Quote:
I have 3- 50 amp RV plugs and 1- 30 amp RV plug.
The double pole breakers are 2 on one side and 1 on the other side of the panel.
In a household electrical distribution box, when you use a double circuit breaker the result is a 240V supply or two 120V hot leads of opposite polarity. You c4an use that to supply a 50a plug just fine as it has 4 pins, L1, L2, neutral, & ground. But a 30a RV plug has only 3 pins and if you use L1, L2, and neutral, there will be no ground and the RV plugged into it will be subjected to 240V and you will do major damage to that RV. Since all 50A RV outlets are technically 240V and get power from both bus bars, it does not matter which side of the box they are on, they all still draw from both busses. All 50a RV outlets are connected to both L1 & L2.

A proper 30a RV outlet has only 3 pins and they are one hot, one neutral and one ground and it is supplied by one single, 30a circuit breaker. If you connect it by using a double breaker you will apply 240V to the 30 a RV. If you wire it properly, then it will have one single circuit breaker of 30a for each outlet and if they are located one above the other they will be on different buses. If you put them directly across from each other at the same level, they will usually be on the same bus but I'd have to look at the interior design of the box to know that for certain.

As stated previously, you need qualified help.
__________________

__________________
Good Travelin! Kirk
Full-time 11 years, now part-time.
Kirk & Pam's Great Adventure!
SKP Kirk is offline   Reply With Quote
Old 09-08-2017, 08:27 AM   #17
Senior Member
 
Join Date: Mar 2013
Posts: 414
No where did he say he wired the 30 amp to a double breaker. Sounds like the op knows more about electricity the most of the "experts" that have tried to "help" him
MotorPro is offline   Reply With Quote
Old 09-08-2017, 09:02 AM   #18
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 13,864
Wire a both 50a and 30a to same double breaker. Then users are not using adapters. You have control of which leg each 30a is connected. Thus requires adding 30a connectors and ensuring they are used as an exclusive or pair. Like each is a pedistal in a CG, only collocated.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 09-11-2017, 11:03 AM   #19
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 338
Quote:
Originally Posted by Old-Biscuit View Post
Power panel should already be split into 2 busses

Every other CB slot is on same buss
SO 1,3,5 etc would be hot from one buss and 2,4,6 etc would be hot from other buss

But as posted above......
You have a 30A breaker feeding a 50A RV Plug?
30A is 1 Hot, 1 Neutral, 1 Ground
50A is 2 Hots, 1 Neutral, 1 Ground


You are feeding subpanel from main panel with 2 hots........correct?


Yes, and if you wire the two pole breakers identically then rotate it to the other side the loads end up on the same busses. If I swap the loads for one breaker it should reduce the possibility of everyone ending up on the same buss. My coach uses a 50 amp 4 prong plug so, I reduce the possibility even more.

Thank you for your help.
rssnape is offline   Reply With Quote
Old 09-11-2017, 01:01 PM   #20
Senior Member
 
olcarguy's Avatar
 
Join Date: Jun 2017
Location: Ontario, Canada
Posts: 339
Neutral and ground are, in a sense the same, as they both are connected to ground.
__________________


“Good judgment comes from experience, and a lotta that comes from bad judgment.”93 Coachmen Pusher 38' 8.3Cummings, 6sp Alison. "Roy"
olcarguy is offline   Reply With Quote
Old 09-11-2017, 11:21 PM   #21
Senior Member
 
DENSHER's Avatar
 
Gulf Streamers Club
Spartan Chassis
Join Date: May 2016
Location: Cookeville, TN
Posts: 200
Simple way to offset the possible load imbalance if 3 50a to 30a adapters are used at same time is move the 2 breakers in one column down one slot on the panel. If one double pole 30 amp and the single were moved down that would change the loads that were on buss #1 to buss #2. Take another single pole breaker and place in that open top slot to fill the open hole in the panel cover.
__________________
1995 Gulfstream Sun Voyager MX 34' DP with 2011 Silverado in tow.
Dennis & Sherry.
DENSHER is offline   Reply With Quote
Old 09-12-2017, 07:56 PM   #22
Senior Member
 
Join Date: May 2017
Posts: 756
Why not just wire in one 50 amp outlet and two 30 amp outlets? Do you really intend to have up to three 50 amp RV's being supplied at the same time? One 50 amp RV and one 30 amp RV from the same load center should be OK. But, if you are expecting three 50 amp RV's and one 30 amp to all be plugged in at the same time, wouldn't you be exceeding the ratings on the feeder breakers to your 100 amp sub panel?
DryCreek is offline   Reply With Quote
Old 09-12-2017, 09:04 PM   #23
Senior Member
 
dwhit's Avatar
 
Join Date: Feb 2013
Location: Lake Hartwell, SC/GA
Posts: 594
Owner of the KOA we're in has similar load problem...his boxes were wired so most RV's were using his L1 providing a vastly overloaded L1 leg. Most RV's are wired L1 as primary buss. I confirmed that with my primary AC unit. Tied to L1 along with fridge & water heater. Most of the heavy users are L1. Not all that much on L2.

His solution was to rewire every ODD box so that the primary conductor is L2.

He says load balance is now better than it was.

On my home pedestal I jus' wired a 30 off of...of course L1.

My issue at home was whether to bond neutral/ground at that third distribution box. My SC code says no, that it's bonded only once at main panel. Everything is working properly as far as I can tell.

Balancing household loads is an art form...doubtful it's ever near equal.
__________________
2019 Sandpiper 379FLOK with the dreaded LG LFCS22520 fridge, F350 Lariat Diesel DRW, NRA Benefactors.
dwhit is offline   Reply With Quote
Old 09-14-2017, 08:41 PM   #24
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 338
Quote:
Originally Posted by DryCreek View Post
Why not just wire in one 50 amp outlet and two 30 amp outlets? Do you really intend to have up to three 50 amp RV's being supplied at the same time? One 50 amp RV and one 30 amp RV from the same load center should be OK. But, if you are expecting three 50 amp RV's and one 30 amp to all be plugged in at the same time, wouldn't you be exceeding the ratings on the feeder breakers to your 100 amp sub panel?


My coach usually pulls right at 30 amps with 2 airs running. Anything additional and a breaker will trip. So let's just say 40 amps total. Divide that across a 2 pole breaker and maybe you are 20-15. So if you figure 30 amp max for each 2 pole breaker and 30 amp max for the single pole breaker, one leg would have 120 amps the other 90. The 2 pole breakers shouldn't get that high so 60-75 for each leg and 30 for the single that's 105 amps.
I understand that you can put up to twice the main breaker amperage in load breakers, although it's better to calculate the load.
Based on what I expect I should be fine on total load, but am concerned about the balance and having everyone running on one leg. That would lead to problems.

Thanks everyone for weighing in and giving me food for thought.
rssnape is offline   Reply With Quote
Old 09-14-2017, 08:58 PM   #25
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 4,771
This is exactly why I don't like seeing adaptors that allow a 30 amp plug to go into a 50 receptacle. First off--you have the potential of putting 50 amps down a 30amp cord. Second, you have a challenge of balancing load at the box. The reverse works perfectly to allow one 30 amp leg to power two 50amp legs to the coach, but you have no idea how two legs from coach to a single 30 amp at the breaker box. If you are only going to have 30 amp legs to begin with, then use a single leg and 30amp receptacle and balance everything at the breaker box. Agree--think the OP has a better command of the subject matter than most of the contributors--but that is the "beauty" of this form--isn't it?????
__________________
Old Scout
2003 40' MDTS
Garden Ridge, Texas
Old Scout is offline   Reply With Quote
Old 09-15-2017, 07:50 AM   #26
Senior Member
 
rssnape's Avatar
 
Join Date: Oct 2011
Posts: 338
Quote:
Originally Posted by Old Scout View Post
This is exactly why I don't like seeing adaptors that allow a 30 amp plug to go into a 50 receptacle. First off--you have the potential of putting 50 amps down a 30amp cord. Second, you have a challenge of balancing load at the box. The reverse works perfectly to allow one 30 amp leg to power two 50amp legs to the coach, but you have no idea how two legs from coach to a single 30 amp at the breaker box. If you are only going to have 30 amp legs to begin with, then use a single leg and 30amp receptacle and balance everything at the breaker box. Agree--think the OP has a better command of the subject matter than most of the contributors--but that is the "beauty" of this form--isn't it?????


What you are missing is that 30 amps on 2 poles is 60 amps total. And on a 50 amp plug the 30 amp cord is protected by the 30 amp breaker in the coach. I have the 50 amp plug down rated to 30 amps as to allow more places to plug up and hopefully run each circuit at less than max by using 2 poles instead of 1. The X factor is any adapters that people might use to adapt a 2 pole to a 1 pole (50-30amp). If they all use L1 and I bond all L1 on the same buss then you get the problem.
Thanks
rssnape is offline   Reply With Quote
Old 09-15-2017, 08:34 AM   #27
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvil", TN
Posts: 975
Quote:
Originally Posted by olcarguy View Post
Neutral and ground are, in a sense the same, as they both are connected to ground.
Yes they are....in the pedestal box! But at the trailer itself, the neutral and ground are not to be bonded together!
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2017 Keystone Fuzion Impact 303
Excessive Payload Capacity is a Wonderful Thing!
xrated is offline   Reply With Quote
Old 09-16-2017, 06:21 AM   #28
Senior Member
 
olcarguy's Avatar
 
Join Date: Jun 2017
Location: Ontario, Canada
Posts: 339
True.
__________________

__________________


“Good judgment comes from experience, and a lotta that comes from bad judgment.”93 Coachmen Pusher 38' 8.3Cummings, 6sp Alison. "Roy"
olcarguy is offline   Reply With Quote
Reply

Tags
panel, power, shore power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plugging into shore power trips shore power breaker BFF Travel Supreme Owner's Forum 8 07-28-2017 11:53 PM
Shore power power not providing power to air conditioner jjhenley RV Systems & Appliances 6 06-21-2016 10:08 AM
Sub panel breaker trips while on shore power. Eric D National RV Owner's Forum 4 10-28-2009 04:57 PM
Which Wire? Brake Light Wire Off Switch mickey53usa Freightliner Motorhome Chassis Forum 2 04-14-2009 04:05 PM
6 wire motorhome, 4 wire toad?? smlranger Toads and Motorhome Related Towing 3 02-27-2005 07:03 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:15 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.