Hughes AutoTransformer fail/fix
06-18-2011, 09:50 PM
|
#1
|
|
Senior Member
Monaco Owners Club
Join Date: Oct 2006
Posts: 734
|
The Hughes unit failed me this past week. Thought about shipping it back for repair (4-years old) but decided to do a look-see first. Drilled out the pop rivets and lifted the lid. Turns out that the plug-in (female 50-amp) had a burned out slot. $6.87 for a new receptacle and a couple of hours of labor ( I work slow) and she is good as new.
__________________
1998 Monaco Dynasty
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-18-2011, 11:36 PM
|
#2
|
|
Senior Member
Join Date: May 2011
Location: Vancouver, WA
Posts: 4,294
|
We have one, it's the 30 amp unit with 50 amp plugs that CW sold for a while. I used it on a 50 amp circuit once and blew it up. Had a friend that was into electronics, he took it and found a blown resistor and replaced it. Still have the unit but have pretty much quit using it. In fact it's not even in the rig now.
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
|
|
|
|
| |
|
06-19-2011, 03:12 PM
|
#3
|
|
Senior Member
Workhorse Chassis Owner Damon Owners Club
Join Date: Mar 2009
Posts: 8,085
|
I thought Hughes sold a genuine 30 and a genuine 50, it was the other company that sold a 30, a 30.30 and a 50.50
That is a 30 amp, straigt
A 30 amp dual with 50 amp plug and socket
and a true 50 amp (Which is always a dual)
I have a hughes hidden next to my ATS, which Damon hid. I know where it's at, but you'd need luck or skill to find it.. This means the odds of it growing legs in the hight.. Kind of low.
And if someone tried. The odds of them ... Well let's say I sit next to that thing often IT's in my Radio Room.
__________________
Home is where I park it!
|
|
|
|
| |
|
06-19-2011, 07:34 PM
|
#4
|
|
Senior Member
Monaco Owners Club
Join Date: Oct 2006
Posts: 734
|
I had one of the other units (Franks?) that was a 35-amp with 50-amp connectors. It did not fare well when I had to load it up. Never understood why they marketed it like that. Worked great as long as only 30-amps or less was required.
The Hughes is built like an anvil. SOLID piece of gear. I suspect that my male plug had a corroded spot or some such and just over heated the neutral connection. Sure was glad I didn't pay $30 bucks to ship it back for repair.
Know what you mean about them growing legs and walking away. I use a braided cable and lock to help keep honest men honest.
"Gun control means hitting what you aim at".
__________________
1998 Monaco Dynasty
|
|
|
|
| |
|
06-20-2011, 08:59 AM
|
#5
|
|
Senior Member
Workhorse Chassis Owner Damon Owners Club
Join Date: Mar 2009
Posts: 8,085
|
There are other advantages to the "Install" kit
For one I plugged it in ONE TIME, I will likely never plug it in again so long as I own this rig. For another I recall one time when I was "Overnighting" in a campground next door to a wind farm Winds that night 90 sustaind with 110 gusts (plenty, in fact too much wind for the wind farm)
Voltage at the post .... 90
Since I was overnighting, and had not yet installed the Hughes, I'd not drug it out (Anval's are HEAVY don't you know)
Plus a few places I've parked had a "NO Autoformers" rule.
So, now.. I don't worry about plugging it in, I don't have to drag it out, No problem at all and the "No Autofomer Police" won't see a thing. Even if they open every cabinet and compartment they will not see a thing. I need screwdrivers to look at it.
__________________
Home is where I park it!
|
|
|
|
| |
|
09-08-2011, 12:41 PM
|
#6
|
|
Senior Member
Workhorse Chassis Owner
Join Date: Jan 2000
Location: Healdsburg, CA
Posts: 296
|
This might be a  dumb question. I've been reading the posts on the surge protectors and see I may need one. I've been living the russian roulette myself for the past 30+ years  .
So, my question is.. if I have one of the Hughes 50A Autoformers.. Will I still need one? I'd guess the answer might still be yes. I'd think the transformer would absorb the spikes but, won't protect me from "way low" or "way high" voltages. I've used it in Mexico where one park was lower than the limit on the HA.. and the voltage in the coach was still low. Never had a "too high" condition.
Anyhow, any thought clarifying would be beneficial to me.
__________________
Bill Splaine, Healdsburg, CA N6GHG
2006 37' Holiday Rambler Admiral Se, '96 Harley FLHTCUI, and recumbent bikes and trikes
Brewin' 'n Que'n
|
|
|
|
| |
|
09-08-2011, 12:53 PM
|
#7
|
|
Senior Member
Join Date: May 2011
Location: Vancouver, WA
Posts: 4,294
|
Quote:
Originally Posted by wa8yxm
I thought Hughes sold a genuine 30 and a genuine 50, it was the other company that sold a 30, a 30.30 and a 50.50
|
Nope, it's a true Hughes brand unit, 50 amp plugs in and out but only 30 amp (3,600 watt) internals.
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
|
|
|
|
| |
|
09-08-2011, 12:55 PM
|
#8
|
|
Senior Member
Join Date: May 2011
Location: Vancouver, WA
Posts: 4,294
|
Quote:
Originally Posted by wa8yxm
Plus a few places I've parked had a "NO Autoformers" rule.
|
Obviously they don't understand how they work, if they did they would welcome them!!
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
|
|
|
|
| |
|
09-11-2011, 12:32 PM
|
#9
|
|
Senior Member
Monaco Owners Club
Join Date: Sep 2011
Location: Alaska 6 months out of the year, as for the other 6, somewhere in the Lower 48
Posts: 2,632
|
Quote:
Originally Posted by wa8yxm
There are other advantages to the "Install" kit
For one I plugged it in ONE TIME, I will likely never plug it in again so long as I own this rig. For another I recall one time when I was "Overnighting" in a campground next door to a wind farm Winds that night 90 sustaind with 110 gusts (plenty, in fact too much wind for the wind farm)
Voltage at the post .... 90
Since I was overnighting, and had not yet installed the Hughes, I'd not drug it out (Anval's are HEAVY don't you know)
Plus a few places I've parked had a "NO Autoformers" rule.
So, now.. I don't worry about plugging it in, I don't have to drag it out, No problem at all and the "No Autofomer Police" won't see a thing. Even if they open every cabinet and compartment they will not see a thing. I need screwdrivers to look at it.
|
Never saw a No Autoformer Policy, what is the logic behind this policy?
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers.org, NRA and VFW Life Member, AK EMT.
If you are coming to AK let me know. Love it here and love sharing AK with others.
2009 Safari Cheetah 40 SKQ
|
|
|
|
| |
|
09-12-2011, 01:25 AM
|
#10
|
|
Senior Member
Winnebago Owners Club Workhorse Chassis Owner
Join Date: Sep 2007
Location: KAPOLEI, HAWAII AND VANCOUVER, WASHINGTON
Posts: 1,847
|
Quote:
Originally Posted by sdennislee
Never saw a No Autoformer Policy, what is the logic behind this policy?
|
using an autoformer, the amperage draw on the park pedestal increases commensurate with the voltage increase inside your rv. this can cause more problems for cg owners who should fix the low voltage problem in the first place.
like everything else, fixing electrical problems costs money.
__________________
01 WINNEBAGO 35U W20.8.1L SW Wa, Hi. Good Sam, SKP. AMSOIL fluids. BANKS ecm program. SCAN GAUGE II w/ Ally temp. 2 LIFELINE GPL-6CT AGM Batts on their sides. TST tptts. K&N panel air filter. AERO mufflers. TAYLOR plug wires. ULTRA POWER track bar. KONI fsd shocks
|
|
|
|
| |
|
09-12-2011, 05:27 AM
|
#11
|
|
Senior Member
Monaco Owners Club
Join Date: Oct 2009
Location: Anchorage, AK
Posts: 1,200
|
Quote:
Originally Posted by GreatWhite
This might be a  dumb question. I've been reading the posts on the surge protectors and see I may need one. I've been living the Russian roulette myself for the past 30+ years  .
So, my question is.. if I have one of the Hughes 50A Autoformers.. Will I still need one? I'd guess the answer might still be yes. I'd think the transformer would absorb the spikes but, won't protect me from "way low" or "way high" voltages. I've used it in Mexico where one park was lower than the limit on the HA.. and the voltage in the coach was still low. Never had a "too high" condition.
Anyhow, any thought clarifying would be beneficial to me. 
|
The setup that I have and recommend would be the PowerMaster Voltage Booster with 3580 Joules of SURGE protection followed with the Progressive Industries EMS HW-50C system with another 3580 Joules of Surge protection.
The Hughes autoformer will work in place of the PowerMaster but I believe it only goes up to a maximum of 10% boost. I think that it has some SURGE protection but I don't know how much.
The Progressive Ind. EMS system provides the most protection for your coach as it monitors ALL aspect of the incoming electrical supply from the pedestal.
Read this Blog to better understand ALL of the benefits of the Progressive Industries EMS HW-50C unit.
120 Volt Electrical Protection: Part I - Progressive Industries EMS - iRV2 Forums
Quote:
Originally Posted by wa8yxm
Plus a few places I've parked had a "NO Autoformers" rule.
|
Any place that I pull into, if they have posted a notice of No Autoformers allowed, that would be my first clue to turn and drive away quickly. It is a CLEAR message that their power supply SUCKS and they do not want to invest in upgrading it to code.
If I had to stay there for whatever reason, they would not know I even have one as mine is enclosed in a secure compartment protected and hidden. However, I would more than likely choose NOT to stay there and would probably take my chances at a local church parking lot, Wal-Mart or the mall for one night.
I have been in only one RV park where the voltage was TOO high and my Progressive Industries EMS HW-50C cut-off power because of excessive voltage. That was in TOK Alaska, I did NOT want to disconnect my PowerMaster, therefore I simply used my 30 amp dog-bone and the 30 amp outlet for the night.
Dr4Film ----- Richard.
__________________
2002 Monaco Windsor PBT 40Ft. (R HOME) - 26Ft. 2006 Pace Trailer (R JUNK).
Trailer Has 06 VUE (R TOWD) 04 Victory Alen Ness Edition (R RYDE) & Junk.
Full-Timer 9 Yr's & Still Lov'n It. Now in Anchorage Alaska for Two Months.
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|