Old 03-04-2014, 08:07 PM   #1
Junior Member
 
Join Date: Mar 2014
Posts: 6
Question Intellitec BD problem? Or...?

#long read warning. Sorry.

So. I have had the apparently not so unusual issue of no 12v power when I unplug from the pedestal and the generator didn't want to start.

This is a 30 amp 2000 Winnebago Minnie 27P and I have the wiring diagrams. http://www.winnebagoind.com/diagram/2000/133784.pdf

The other one I need to look at more closely is here: http://www.winnebagoind.com/diagram/2000/133781.pdf

Anyway, I set about solving my own problem and I got new GC2 coach batteries and built new battery cables for them. (I tested the gravity of the cells on the old marine batteries, and one of them had a bad cell. No great loss, as they were at least 7 years old.)

I know, building battery cables seems extreme, but I wanted a heavier gauge cable (2/0) and copper lugs.

I installed a new Powermax Boondock 4 stage converter because I did not want the old Magnetek single stage thing touching my new batteries.

For grins, I replaced the 12 v fuse block. The new one has it's own fuse protection, and that seemed like a better thing.

I had to install a new power outlet for the converter because the old magnetek didn't plug in. There was one of those fake receptacle boxes right there, so I converted it to a real one.

I was so happy. I was so proud. I did it myself. Everything worked! for ONE TRIP. And then. Back to square one. No 12v and no generator start.

So I had been suspecting for a while that the solenoid and BD under the step would soon need replacing. The posts and nuts were starting to look corroded.

I replaced the solenoid first. Picked up an Echelin ST80 at Napa and installed that. Nope. That didn't fix the problem. It was really difficult to replace that because the bolts holding it on were so corroded. I had to break the bracket that supported it and dremel the bolts off. I had to do the same thing when I removed the BD, but then I also had to drill new holes because the old ones were NOT accessible from the back side to get a nut on them!

I had no reason not to believe that it wasn't the Intellitec thing at this point, and I called the Intellitec support guy, and he helped me troubleshoot it for sure. I got a reading of 12.77v on the coach battery side. I had a reading of 10.83v on the "generator" side (opposite side).
And there was a small <1v reading across those two posts. He said that meant I definitely had to replace the BD. So he shipped me a new one and I installed that today.

Anyway. Now I have 12.65v on the coach battery side. Initially I got 13.6 and then 15.1v on the "generator" side, and again a small <1v reading across those two posts.

When the old one was installed, the rocker switch on the wall still made it go CLUNK. This one doesn't even do that.

But here are the things that have me puzzled. The S and I posts on the front are supposed to have at least 11v to them and there is 0 on both of them. On the wiring diagram those go to a 9 pin connector somewhere, but I haven't been able to find it. Does anyone know where they actually go? On the wiring diagram these are circuits LG and LH. I did JUST notice that the little codes that they annotate on the second diagram are printed on the sheathing of the spaghetti wires, so I will have to go back and look at those again. I think the third skinny wire that goes to the 5 amp fuse operates the rocker switch on the wall. I am actually not convinced that the spade it is making contact with the fuse. I tried both new fuses and the old fuses from the old unit, because they were actually good, but the spade connection doesn't seem to fit well. Which might explain why I have no switching from the rocker switch.

Anyway, I'm real sorry to be so long winded but....does anyone think it seems likely or possible that I got a bad BD from Intellitec right out of the box? Before he sent me the new one he told me that I could troubleshoot it by putting the cables all one lug, but all of the lugs don't actually FIT on one post. He told me that a simple piece of #10 wire was not heavy enough to use as a jumper.

Thoughts?
__________________

BrassBelle is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-05-2014, 02:35 AM   #2
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
Hello and We are glad to have you join us here and we look forward to reading of your adventures and experiences. I am sure you will enjoy our website and forums. Good luck, stay safe and keep us posted.
First off it looks like your problem may have started when you changed the battery bank out. I would suggest you go back and make certain that all the wiring, especially ground connections are correct, clean and tight at the battery and on the frame. Have you trouble shot the BD switch? Please give us as much detail as possible on your findings.
__________________

__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 03-05-2014, 05:29 AM   #3
Junior Member
 
Join Date: Mar 2014
Posts: 6
Thanks for the welcome. No the problem did NOT start when I changed the battery bank out. In fact changing the batteries is one of the things that originally solved the problem. The battery connections are fine and the batteries are fully charged. I gave all that detail up there in my original post. Including the details of troubleshooting the BD. Thanks.

Actually I have enjoyed reading a lot of the forum. I have read a lot of it. But I am an avid "lurker" lol.
BrassBelle is offline   Reply With Quote
Old 03-05-2014, 07:52 AM   #4
Junior Member
 
Join Date: Mar 2014
Posts: 6
Talking Problem solved

It really is a simple thing, but not sure how I am going to ultimately fix it. The spade connector that is supposed to connect to the 5 amp fuse on the new BD was not making contact with the fuse, causing the switch not to operate, causing the contacts on the BD not to make.

Apparently the spade connector is faulty or the wrong one or something and CANNOT reach the fuse. Go figure. I will have to figure out something. But bypassing that fuse got everything working as it should. YAY.

Thanks for all your help. Oh wait....lol!
BrassBelle is offline   Reply With Quote
Old 03-05-2014, 09:18 AM   #5
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 18,632
Glad to hear it was a simple problem. At worst it's a new connector and/or fuse holder.
__________________
Gary Brinck
Former owner of 2004 American Tradition
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 03-05-2014, 10:45 AM   #6
Senior Member
 
Dave78Chief's Avatar
 
Join Date: Jun 2009
Posts: 1,525
Am i reading this correctly that you ended up replacing the ST80 from NAPA with the Intellitec Battery Disconnect solenoid? That's good if you did as the ST80 relay is not designed to be used as a Battery Disconnect relay. The ST80 is designed for continuous operation required for the Battery Mode relay only. For the battery disconnect latching solenoid, to prevent a constant drain on the battery when boondocking, there is only a short pulse applied to the BD (LG & LH) to get it to latch ON. When you place the switch in OFF, another short reverse polarity pulse is applied to the BD (again on LG and LH). There should never be a constant voltage across LG and LH.

The best drawing for you is http://www.winnebagoind.com/diagram/2000/133784.pdf

pdf page 3 shows the BD. Follow circuits LG and LH back to pdf page 2 to the 9 pin connector. As you can see from the drawing that is located below the Galley Range.

Other side of that connector is on pdf page 6, bottom center. Follow LG/LH to pdf page 7 bottom left to BD Switch connector.

Again, the BD switch is a momentary action switch with center off. Only provides a signal when ON or OFF is depressed. Returns to center (no signal) when released. The mechanical latching assembly inside the BD solenoid keeps it in the ordered position when the LG/LH power is removed. That's why it is called a latching solenoid.

Dave
__________________
Dave in Virginia
1978 Winnebago Chieftain
Dodge M400 - 440-3
Classic Winnebago Site: http://www.classicwinnebagos.com/forum/index.php
Dave78Chief is offline   Reply With Quote
Old 03-05-2014, 01:00 PM   #7
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by Dave78Chief View Post
Am i reading this correctly that you ended up replacing the ST80 from NAPA with the Intellitec Battery Disconnect solenoid? That's good if you did as the ST80 relay is not designed to be used as a Battery Disconnect relay. The ST80 is designed for continuous operation required for the Battery Mode relay only.
Dave
You misread his post. He said he replaced both the ST80 and the BD solenoid.

I'd say he was a bit unlucky with the new part, but has a good understanding of the system.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 03-05-2014, 07:04 PM   #8
Junior Member
 
Join Date: Mar 2014
Posts: 6
Quote:
Originally Posted by Gary RVRoamer View Post
Glad to hear it was a simple problem. At worst it's a new connector and/or fuse holder.
Well the spade is supposed to slip into the fuse slot ON the Intellitec BD. That wire goes to the switch on the wall.

The spade fits the 5 amp fuse like a glove when I pull the fuse. And it fits into the slot on the BD. But inside there is not making connection between spade and fuse. I'm sure you are familiar with the two 5 amp fuses on the Intellitec BD, right?

Not sure how I am going to remedy that yet, but for now I have the connector wire tied so it just touches the lug on the coach battery side of the BD, because this is highly temporary fix for the problem. I suspect I shall be in search of a longer spade of the same type?
BrassBelle is offline   Reply With Quote
Old 03-05-2014, 07:17 PM   #9
Junior Member
 
Join Date: Mar 2014
Posts: 6
Talking

Quote:
Originally Posted by loulong View Post
You misread his post. He said he replaced both the ST80 and the BD solenoid.

I'd say he was a bit unlucky with the new part, but has a good understanding of the system.
"girl here"

Yeah I replaced the old Trombetti with an ST80 and also got a new Intellitec BD of the same type that was installed OEM. Bypassing the 5 amp fuse on top of the Intellitec BD with the wire that goes to the switch on the wall enabled me to get everything working as it should.

The ST80 seems to be working fine in place of the old Trombetti.
BrassBelle is offline   Reply With Quote
Old 03-06-2014, 02:28 AM   #10
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
Quote:
Originally Posted by BrassBelle View Post
Well the spade is supposed to slip into the fuse slot ON the Intellitec BD. That wire goes to the switch on the wall.

The spade fits the 5 amp fuse like a glove when I pull the fuse. And it fits into the slot on the BD. But inside there is not making connection between spade and fuse. I'm sure you are familiar with the two 5 amp fuses on the Intellitec BD, right?

Not sure how I am going to remedy that yet, but for now I have the connector wire tied so it just touches the lug on the coach battery side of the BD, because this is highly temporary fix for the problem. I suspect I shall be in search of a longer spade of the same type?
The fuses are wired to the disconnect lugs. The female spade connector should have a 16 gage solid wire wrapped around the cable lug and may have broken short. Installing a new connector and wired to the lug should solve your issue.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 03-06-2014, 08:49 AM   #11
Senior Member
 
Old Bounder's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Mar 2009
Posts: 1,636
Quote:
Originally Posted by BrassBelle View Post
"girl here"

Yeah I replaced the old Trombetti with an ST80 and also got a new Intellitec BD of the same type that was installed OEM. Bypassing the 5 amp fuse on top of the Intellitec BD with the wire that goes to the switch on the wall enabled me to get everything working as it should.

The ST80 seems to be working fine in place of the old Trombetti.
Sorry 'bout dat. I'll be more careful in the future.

Welcome to the forum.
__________________
'97 Bounder 34V, F53 7.5L-460
Old Bounder is offline   Reply With Quote
Old 03-10-2014, 11:49 AM   #12
Junior Member
 
Join Date: Mar 2014
Posts: 6
Quote:
Originally Posted by RV Wizard View Post
The fuses are wired to the disconnect lugs. The female spade connector should have a 16 gage solid wire wrapped around the cable lug and may have broken short. Installing a new connector and wired to the lug should solve your issue.
It needs a different size spade to fit in there than what I currently have. "flatter and taller" than what I think of as a standard spade connector. I think I can get them on amazon.com
BrassBelle is offline   Reply With Quote
Old 03-11-2014, 03:47 AM   #13
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
You can instal any kind of overcurrent protection device rated for 5 amps. In other words, an inline fuse holder with 5 amp fuse by-passing the original is fine.
__________________

__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hadley problem Dave999 Class A Motorhome Discussions 1 01-12-2014 03:57 PM
Fridge Problem Rossi6998 Winnebago Industries Owner's Forum 22 01-10-2014 08:02 AM
Electrical problem MsSkeeter Class A Motorhome Discussions 15 01-07-2014 05:02 PM
Please help! New fulltimer with distressing electrical problem! ocipura Class A Motorhome Discussions 67 09-18-2013 01:41 PM
Front AC Vent Problem... Damon Diva Damon 3 09-10-2013 09:47 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:13 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.