I'm getting ready to install a Xantrex Xpower 1500 inverter. The instructions require a 200 amp circuit breaker and I want to also install a Perko disconnect switch. I know the inverter needs to be installed in an area separate from the batteries but my question is: can the Perko switch and the circuit breaker be installed in the battery compartment? If so, which one goes closest to the batteries? I have two Trojan 105s.
__________________

__________________
2001 Condor by R-Vision 33' 6" w/galley slide
CYOUL8R is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-25-2005, 11:55 AM   #2
Member
 
CYOUL8R's Avatar
 
Join Date: Aug 2002
Location: Phoenix, AZ
Posts: 34
I'm getting ready to install a Xantrex Xpower 1500 inverter. The instructions require a 200 amp circuit breaker and I want to also install a Perko disconnect switch. I know the inverter needs to be installed in an area separate from the batteries but my question is: can the Perko switch and the circuit breaker be installed in the battery compartment? If so, which one goes closest to the batteries? I have two Trojan 105s.
__________________

__________________
2001 Condor by R-Vision 33' 6" w/galley slide
CYOUL8R is offline   Reply With Quote
Old 06-25-2005, 01:56 PM   #3
Senior Member
 
Kirk's Avatar
 
Join Date: Jan 2000
Location: Livingston, Tx., US
Posts: 162
The Perko would be fine located with the batteries, but I would not put the circuit breaker there because of the possibility of gassing of the batteries when under very heavy load, which is when the breaker would open. There is a small chance that the arc created by the breaker opening could ignite the hydrogen from the gassing. I would put the circuit breaker in the same area sa the inverter. That is just my opinion, but I always err to the safety side of things. That served me well for 40 years of electrical work.
__________________
Good travelin! ......Kirk
URL: www.1tree.net/adventure/
Kirk is offline   Reply With Quote
Old 06-25-2005, 03:43 PM   #4
Member
 
CYOUL8R's Avatar
 
Join Date: Aug 2002
Location: Phoenix, AZ
Posts: 34
Thanks for the reply Kirk. That makes sense about the possibility of an arc situation from the circuit breaker. If the circuit breaker is near the inverter in a separate compartment from the batteries and the Perko diconnect switch is in the battery compartment, that would make the disconnect switch the first thing connected to the battery line (out). Would there be a problem with this arrangement?
__________________
2001 Condor by R-Vision 33' 6" w/galley slide
CYOUL8R is offline   Reply With Quote
Old 06-26-2005, 04:23 AM   #5
Senior Member
 
Renegades's Avatar
 
Monaco Owners Club
Join Date: Oct 2000
Location: Waverly, Tennessee
Posts: 184
Instead of using a breaker, when I do installs of inverters, I use a fuse and locate it right close to the battery. Even the manfactures who put inverters in a coach will put the inverter fuse on the wall and wire directly to the battery. What size wire were you planning on using? Because size will depend on how far from the batteries you are putting the inverter. Is this just an inverter or does it also have a 3-stage charger built in? If it has the charger, remember to disconnect your old converter, (i.e just unplug it from the ac line) it can be left connected to the dc side.

On the output side of the inverter, how many circuits are you planning to have connected to the inverter? Does the inverter have it's own output breaker? If not, then put a small service panel of 2 or 4 breakers to protect the load side of the inverter.

Hope some of this info helps and didn't confuse you. Good luck.

Jim
RV Tech
__________________
Renegade (Jim) & Wrangler (Doreen)
& 4 attack cats, TJ, Shadow, Chessie, RJ
along with 2 who adopted us, Tom & puddy.
Renegades is offline   Reply With Quote
Old 06-26-2005, 01:51 PM   #6
Senior Member
 
cvrvr's Avatar
 
Workhorse Chassis Owner
Join Date: Dec 2003
Location: La Crescenta, CA USA
Posts: 270
I would use a 200a Class "T" fuse instead of a circuit breaker. Much cheaper and much smaller and easier to install.

George
__________________

__________________
George & Karen Wharton
2004 Allegro 30DA W-20
2000 Jimmy toad
cvrvr is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inverter installation problem Max Hubrich MH-General Discussions & Problems 27 05-18-2008 10:46 AM
Inverter Installation Provelogear Damon 16 05-08-2008 04:46 PM
Inverter installation in a 2003 Scottsdale park_ridge_dave Newmar Owner's Forum 7 06-14-2007 04:15 AM
Inverter installation? Ultrastryk RV Systems & Appliances 4 03-07-2007 07:52 AM
Simple Inverter Hook Up? Plug my 50 amp to the inverter? E Z Livin MH-General Discussions & Problems 7 12-19-2005 03:59 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.