Someone kindly posted the actual amps that can be drawn on 20 & 30 amp supplies as 16 & 24. How about from a 50 amp plug in? Someone else put up a list of typical power needs of various appliances. I'm building our chart of what we can use in combination.

__________________
Rexhall T-Rex Aerbus 36' May/2004 build

8.1 Vortec 5 spd Allison
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-23-2006, 08:25 PM   #2
eandy is offline
Senior Member
Workhorse Chassis Owner
Join Date: May 2006
Location: Belen, NM
Posts: 338
Someone kindly posted the actual amps that can be drawn on 20 & 30 amp supplies as 16 & 24. How about from a 50 amp plug in? Someone else put up a list of typical power needs of various appliances. I'm building our chart of what we can use in combination.

__________________
Rexhall T-Rex Aerbus 36' May/2004 build

8.1 Vortec 5 spd Allison
  Reply With Quote
   
Old 07-23-2006, 11:15 PM   #3
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,263
National Electrical Code dictates that a circuit should only be loaded to 80% of overcurrent protection device for constant use. Each leg should only be loaded to about 46 amps maximum, however the circuit is protected to hold to 50 amps and if eveything is balanced the neutral will carry the difference of the two legs.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Old 07-24-2006, 09:40 AM   #4
eandy is offline
Senior Member
Workhorse Chassis Owner
Join Date: May 2006
Location: Belen, NM
Posts: 338
RV Wizard, I'm elec challenged. What's that in English? While I'm speaking to the Wiz, how many watts = 1 amp? my conversion prog doesn't do elec. Ask Jeeves says 120 be that doesn't agree with some appliance suppliers.
__________________
Rexhall T-Rex Aerbus 36' May/2004 build

8.1 Vortec 5 spd Allison
  Reply With Quote
   
Old 07-24-2006, 10:39 AM   #5
DriVer is offline
iRV2 Marketing
DriVer's Avatar


Winnebago Owners Club
Workhorse Chassis Owner
Coastal Campers
Carolina Campers
Join Date: Jan 2000
Location: Conway, SC
Posts: 20,595
Blog Entries: 66
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by eandy:
While I'm speaking to the Wiz, how many watts = 1 amp? </div></BLOCKQUOTE>Here is the formula for Watts: P=IE Where Power in Watts is equal to the voltage (110 volts) (X times X) the Amperage (46 amps). Therfore, you can expect the total watts to be equivalent or close to 5060 Watts per leg OR 10,120 Watts total from a 50 Amp shore power receptacle.

Ya sure can cook up a bag of pop corn with that much juice for sure.
  Reply With Quote
   
Old 07-24-2006, 10:41 AM   #6
Bob Hatch is offline
Senior Member
Join Date: Oct 2003
Location: Fulltiming. Living wherever the jacks hit the ground.
Posts: 138
eandy. volts times amps = watts.

Therefore, 1 volt times 1 amp = 1 watt.

120 volts times times 50 amps = 6000 watts, which is 1 leg of the 59 amp service. Total max watts from both legs would be 12,000.

A 50 amp service, loaded to 80% of overcurrent protection, or as Mike posted, 46 amps "should" be safe to 46 times 240 = 11,040 watts, or 92 times 120 = 11,040 watts. A "perfectly" balanced 50 amp service could/should, have as high as 12,000 +/- watts available.
__________________
Bob Hatch
  Reply With Quote
   
Old 07-24-2006, 11:15 AM   #7
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,606
OK, I'll bite. How does 80% of a 50A circuit breaker yield a sustained capacity of 46 amps? .80 x 50 = 40, doesn't it?
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 07-24-2006, 04:51 PM   #8
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,177
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">actual amps that can be drawn on 20 & 30 amp supplies as 16 & 24 </div></BLOCKQUOTE>
So how is it that my power mgt system tells me I routinely draw 28 amps from a 30 amp service when running both ac compressors??? It's 30 amp service ...not 24 amp service!
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 07-24-2006, 05:11 PM   #9
GStream40 is offline
Senior Member
GStream40's Avatar
Join Date: Feb 2000
Location: Navarre, Ohio
Posts: 267
Paul,

As stated above, 80% of overcurrent protection device for constant use.
80% of 20 amp ciruit is 16 amps, 80% of 30 amp circuit is 24 amps.

Ron
__________________
Gulf Stream RV Owners Forum www.gsowners.com

  Reply With Quote
   
Old 07-24-2006, 05:52 PM   #10
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,630
With all said open your service load box and check to see if you have both AC's on same leg of ckt panel. Some have found such and it causes problems with surge protector and EMS panels. Try to balance loads on both sides of load panel.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 07-24-2006, 06:21 PM   #11
JRP is offline
JRP
Member
Join Date: Jun 2005
Location: SD, NM
Posts: 97
AFChamp,

The 80% load limitation(the 16 out of 20, or 24 out of 30), is a "Design" safety factor used in the circuit component sizing. the point being to assure the circuit breaker/fuse pops before the wire melts and starts a fire, when an overload occurs. so its not the actual amps that can be drawn, its the code required design & sizing limit.
ie. an engineer or licensed electrician should not use a 30 amp breaker and its corresponding #10 wire size on any circuit where the expected load is more than the 80% of 30 amp brkr rating. the actual limit on the circuit current in use is the circuit breaker itself. if the end user plugs more than the expected load into that circuit, the circuit will carry the load up to the point the circuit breaker/fuse trips. a 30 amp breaker will usually trip between 28-32 amps, depending on the type of breaker, type of load and ambient temp.

Jim
__________________
  Reply With Quote
   
Old 07-25-2006, 10:04 AM   #12
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,606
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">o how is it that my power mgt system tells me I routinely draw 28 amps from a 30 amp service when running both ac compressors??? </div></BLOCKQUOTE>


The key word here is "sustained". If you are in a climate where both a/c's run much of the time (all afternoon on a hot day), you are indeed overloaded at a continuous 28 amps on a 30A circuit. But if it is occasionally reaching 28 amps for short (undefined) periods when both a/c's happen to be cycling at the same time, you are not. Obviously the designer considered there would not be any "sustained" loads above 24 amps, cause he would be violating the NEC if he did.

In practice, it depends on how other parameters of the NEC were employed in the wiring. Heat is the main problem and if the junction boxes and cable runs do not have the max allowed conductors crowded together in a small airless space, there is no reason the circuits cannot safely run at the full 30 amps.
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 07-25-2006, 10:51 AM   #13
eandy is offline
Senior Member
Workhorse Chassis Owner
Join Date: May 2006
Location: Belen, NM
Posts: 338
Had the ans long ago but glad you kept it up. JRP & Roamer added the heat stuff, thanks. This will help when I do the elec layout on my res deisgns. There are places I like to have junction boxes accessable. That also explains the radical power available at Salton Sea state park. We were the only rig there when reported temp was 106, not in the sun. Another rig came in and power probs came on. No idea how they managed a full park. Thanks for the lesson

__________________
Rexhall T-Rex Aerbus 36' May/2004 build

8.1 Vortec 5 spd Allison
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 Amp to 50 Amp garrage circuit Band Buds RV Systems & Appliances 5 08-17-2008 02:41 PM
Electrical Question - Two 30 amps into One 50 amp Eusefull MH-General Discussions & Problems 10 05-29-2008 08:59 PM
Getting 50 amps to a 30 amp RV bjbkkb RV Systems & Appliances 5 03-15-2008 07:20 PM
Power Line One Panel Limits One Leg 50 Amp circuit to 30 Amps SteveG Winnebago Industries Owner's Forum 17 03-05-2008 04:43 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 12:49 AM.