New valve in propane tank - purge air or fill the tank ?

I am going to have the valves replaced in two 100 lb propane tanks. I have read on the internet somewhere that the air needs to be purged from a tank when the new valve is installed or there will be diminished performance from the fresh filling.

My thoughts are: 1) When the tank gets filled, the operator always cracks the bleed valve open until the liquid propane comes out, then the tank is full of liquid.
2) As the liquid propane enters the tank, it will not only displace air (which goes out the bleed valve, and is also producing vapor, which is heavier than air and will also displace air.

So, do I need to be concerned with asking the technician about bleeding the air out at the risk of looking stupid, or do I just get the tanks filled as normal and go with it ?
__________________

__________________
If you can't fix it with a hammer, it must be an electrical problem.
1978 Executive 29' class A MH that might be worth fixing up to drive and use. Three four wheel drives, an off grid rock house, some chainsaws, and a screwball cat.
mtnmankev is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-30-2013, 08:03 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 14,970
The shop installing the new valves should be able to tell you if the purge is necessary.
The shop that changed my valves , always filled the tanks at the same time .
Remember the only stupid question is the one you don't ask.
__________________

__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-30-2013, 08:23 PM   #3
Member
 
Join Date: May 2013
Location: Northern Arizona
Posts: 60
The biggest problem I have is my fixed income budget.

The shop replacing the valves charges almost 2 bucks a gallon and there is a place not far from there I can buy for a buck and a half a gallon. I am thinking of asking them (after they replace the valves and do the recert stamp on the tanks) if they will price match the other place.

Every bit of money I can save helps.
__________________
If you can't fix it with a hammer, it must be an electrical problem.
1978 Executive 29' class A MH that might be worth fixing up to drive and use. Three four wheel drives, an off grid rock house, some chainsaws, and a screwball cat.
mtnmankev is offline   Reply With Quote
Old 05-31-2013, 07:30 AM   #4
Senior Member
 
Join Date: Nov 2005
Posts: 3,332
Most distributors put a vacuum pump on the tank for several minutes when a valve is replaced or on the initial fill of the tank. Many times there's moisture in the air remaining in the tank. If it's not removed (by using a vacuum pump) it will condense to liquid form when the cold propane is added. It can then work it's way into the valve and possibly all the way to the regulator. The cold prpoane vapor can cause it to freeze stopping all flow.

Years ago you could just fill the tank to the top forcing out the moisture. Now that we have the OPD valves the tank can only be filled to 80% so you can't purge all the air from the tank. When putting a vacuum on the tank you cause the moisture in the air to boil at room temperature. It's then removed as a gas so it can't mix with the gas or freeze in the tank.
__________________
Hikerdogs
2013 Adventurer 32H
Hikerdogs is offline   Reply With Quote
Old 05-31-2013, 08:04 AM   #5
Senior Member
 
Join Date: Feb 2011
Location: Snowbird - Waterford Mi and Citrus Springs Fl.
Posts: 3,608
Quote:
Originally Posted by mtnmankev View Post
I am going to have the valves replaced in two 100 lb propane tanks. I have read on the internet somewhere that the air needs to be purged from a tank when the new valve is installed or there will be diminished performance from the fresh filling.

My thoughts are: 1) When the tank gets filled, the operator always cracks the bleed valve open until the liquid propane comes out, then the tank is full of liquid.
2) As the liquid propane enters the tank, it will not only displace air (which goes out the bleed valve, and is also producing vapor, which is heavier than air and will also displace air.

So, do I need to be concerned with asking the technician about bleeding the air out at the risk of looking stupid, or do I just get the tanks filled as normal and go with it ?
On the bold, no, that's not true. That bleed valve is attached to a stem fasten to the bottom of the valve that reaches down to the 80% full mark within the tank. So when filling, you'll see liquid appear when the tank is 80% full. Any air in the tank will be trapped in the area above that.

To purge the tank, normally you would put a gallon or so of propane in it, then turn it upside down and open the valve - releasing that gallon of propane as well as any air.

I've never seen a tank pumped down using vacuum, but it seems like that would work fine as well. Not sure how many propane stations are equipped with those though - or the potential for trouble pumping propane vapors through a vacuum pump?

Assuming you're on a budget, have the valves replaced when the tanks have emptied. Then take them to have them purged (as described above) at the inexpensive propane supplier. -Al
__________________
1997 37' HR Endeavor, 275hp Cat, Freightliner
03 CR-V Blue Ox, Ready Brake
ahicks is offline   Reply With Quote
Old 05-31-2013, 09:54 AM   #6
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 13,686
Quote:
Originally Posted by Hikerdogs View Post
Most distributors put a vacuum pump on the tank for several minutes when a valve is replaced or on the initial fill of the tank. Many times there's moisture in the air remaining in the tank. If it's not removed (by using a vacuum pump) it will condense to liquid form when the cold propane is added. It can then work it's way into the valve and possibly all the way to the regulator. The cold prpoane vapor can cause it to freeze stopping all flow.

Years ago you could just fill the tank to the top forcing out the moisture. Now that we have the OPD valves the tank can only be filled to 80% so you can't purge all the air from the tank. When putting a vacuum on the tank you cause the moisture in the air to boil at room temperature. It's then removed as a gas so it can't mix with the gas or freeze in the tank.
A frozen regulator is a real pain in the keester.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 05-31-2013, 12:58 PM   #7
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 4,382
When the law was changed and the portable tanks had to go to 80% valve, we changed all the tank valves at our lot. We changed on a non rainy, non cloudy day. We removed the old valve and immediately installed the new valve. We had no problems with the tanks.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2012 Honda Civic toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is offline   Reply With Quote
Old 05-31-2013, 03:59 PM   #8
Senior Member
 
Join Date: Nov 2012
Location: bis. nd
Posts: 687
when they purge tanks here they open the release valve and add gas then after a minute or so they close it and the air is mostly gas then ....jeff
__________________
London Aire..350hp Sparton chassis... with all the good stuff from the time.
2007 Alfa Gold!! model 1008. 400hp Freightliner, now in use!!
beenthere is offline   Reply With Quote
Old 05-31-2013, 04:08 PM   #9
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
Propane is heavier than air and under pressure so once the tank is filled when the
main valve is opened for a few seconds the small amount of air is released.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Old 05-31-2013, 04:43 PM   #10
Senior Member
 
Bobs911's Avatar
 
Winnebago Owners Club
Join Date: Apr 2010
Location: Pismo Beach, California
Posts: 174
During the initial fill, leave bleed closed, pump 1 gallon, stop pumping, open the bleed for 30 seconds, close the bleed. Repeat 3 times, then fill normally.

Former propane pumper.......
__________________

__________________
Bob & Kathy
2016 Itasca Navion 24V
BPOE #2504
Bobs911 is offline   Reply With Quote
Reply

Tags
propane, tank



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:56 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.