Is it OK to plug a regular heavy duty extension cord (with appropriate plug adapter) into a household outlet if all you want is to be able to use a couple of lights (but no AC/fridge/tv etc)? Don't want to damage the power center when visiting the in-laws.

__________________
2007 Winnebago 26P

Jeep Wrangler
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-03-2006, 10:02 AM   #2
Gary the Wombat is offline
Senior Member
Gary the Wombat's Avatar


Join Date: Jun 2006
Location: Lake Berryessa, CA
Posts: 503
Is it OK to plug a regular heavy duty extension cord (with appropriate plug adapter) into a household outlet if all you want is to be able to use a couple of lights (but no AC/fridge/tv etc)? Don't want to damage the power center when visiting the in-laws.

__________________
2007 Winnebago 26P

Jeep Wrangler
  Reply With Quote
   
Old 08-03-2006, 10:30 AM   #3
ISLAPP is offline
Moderator Emeritus
ISLAPP's Avatar


Pond Piggies Club
Thor Owners Club
Join Date: Dec 2000
Location: NORTH CANTON OH USA
Posts: 1,946
Yea you will be fine. Basically all you will be running is the converter/charger unit. The lights are 12V. As needed, the converter/charger will come on to recharge your house batteries which is supplying the power to your lights. Anything more than that, you would be wise to have either a 20amp or 30amp rated extension cord and control your power thru your management system assuming you have an outlet at your families house capable of 20+ amps.
Mike
__________________
Mike And Debbie- Northeast Ohio
2011 Ford F150 Ecoboost engine- SWEET!!
2011 Jayco Eagle 322FKS TT
  Reply With Quote
   
Old 08-03-2006, 03:08 PM   #4
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
Absolutely! We've run refrigerator and lights on that kind of conneciton many times. during the night, we've run refrigerator and vent fans.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 08-03-2006, 04:04 PM   #5
GStream40 is offline
Senior Member
GStream40's Avatar
Join Date: Feb 2000
Location: Navarre, Ohio
Posts: 267
Just like Paul we have run the Frig, Lights and at times the TV also many times while visiting relatives with our RV's.
__________________
Gulf Stream RV Owners Forum www.gsowners.com

  Reply With Quote
   
Old 08-03-2006, 04:49 PM   #6
Renegades is offline
Senior Member
Renegades's Avatar
Monaco Owners Club
Join Date: Oct 2000
Location: Waverly, Tennessee
Posts: 184
Gary,
If your going to use an extension, get one from Lowes or Home Depot that is rated for 30amps, this is being on the safe side. It should be have 10/3 on the outer covering. This tells you that the wire is size 10 and has 3 conductors, black, white and green. Some come with a 20amp plug on the end which has one prong vertical and one prong horizontial and the round ground. Most outlets on the outside of home have an outlet that won't except that style of plug. Check and make sure. If your going to be less than 40 feet from the house, you can get away with a 12/3 cord, but I would get the 50' 10/3 and play it safe. I carry two around with all the time. The outlet should like either one of these diagrams, I hope....
1. |- | or 2. - |
O O

Hope those come out okay. Good luck. If it won't come out right, the 'O' is the ground.


Jim
__________________
Renegade (Jim) & Wrangler (Doreen)
& 4 attack cats, TJ, Shadow, Chessie, RJ
along with 2 who adopted us, Tom & puddy.
  Reply With Quote
   
Old 08-03-2006, 06:37 PM   #7
Gary the Wombat is offline
Senior Member
Gary the Wombat's Avatar


Join Date: Jun 2006
Location: Lake Berryessa, CA
Posts: 503
Thanks everyone. At least now I know I won't have to sleep on the plastic covered sofa--YUCK!!!
__________________
2007 Winnebago 26P

Jeep Wrangler
  Reply With Quote
   
Old 08-14-2006, 04:47 PM   #8
Jerry Wessel KA8MBK is offline
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 48
We volunteer a lot and sometimes we have to use 140 feet of cable and plug into a 15 amp receptical. We put the fridge and water heater on propane and we can run the a/c for two weeks. We turn off the air and run the microwave and never pop a breaker. All my cables are 10-3 extension (30 amp) and they are 50 feet apiece and the main cord which is 40 feet of 50 amp wire. NO PROBLEM while doing this we can run both tv sets and all lights. Wife and I also run electric blanket when needed. Yes with the air on. Nobody said I was normal.
__________________
Gerald Wessel
  Reply With Quote
   
Old 08-15-2006, 05:35 AM   #9
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
140 ft to a 15 AMP receptical is going to have voltage drop. Consider getting a meter and checking the voltage at your RV, with the appliance on. Then, following the instructions in the appliance owners manual, determine if you should be running the appliance. Appliances may run on low voltage, but it could be reducing the longevity of the appliance.
__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 08-15-2006, 10:28 AM   #10
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,606
There's no problem in using a 12 or 14 gauge extension cord toa 15/20 amp household outlet. You can't get 30A out of it anyway, so using a 30A power cord is overkill unless the distance is very far, e.g. the 140 feet mentioned earlier..

But the usual orange cords that everybody calls "heavy duty" mostly are not. They are typically only 16 gauge wiring. Read the label on the cord and get at least 14 gauge. Use 12 gauge if the distance is very long.
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 08-15-2006, 04:33 PM   #11
DonavonP is offline
Senior Member
DonavonP's Avatar


Workhorse Chassis Owner
Join Date: Jul 2004
Posts: 1,550
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by GaryKD:
140 ft to a 15 AMP receptical is going to have voltage drop. Consider getting a meter and checking the voltage at your RV, with the appliance on. Then, following the instructions in the appliance owners manual, determine if you should be running the appliance. Appliances may run on low voltage, but it could be reducing the longevity of the appliance. </div></BLOCKQUOTE>

My wire calculator says he's ok to run 15amp thru 10/3 copper for 140 feet.
__________________
  Reply With Quote
   
Old 08-19-2006, 08:20 AM   #12
Jerry Wessel KA8MBK is offline
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 48
The no load voltage at 140 feet was 117 at both ends of the wire. The loaded voltage was 114-115 and that includes loss in the MH wiring also. We were drawing @13-14 amps. 80% of the connectors are nickle plated and all are kept corrosion free. I could write a book on volunteering and the electrical available at many places. Monitoring power is not a option, but a necessity. Being a retired electrician I am very protective of my equipment. All voltages are monitored and checked with Fluke equipment.Actually if you have a long run with small wire, you will run low voltage long before you blow a breaker. I have more problem in some campgrounds with a regular cable and no extensions and supposidly a 30 amp plug. My 50-30 amp adaptor is all nickle plated and heavy duty.
__________________
Gerald Wessel
  Reply With Quote
   
Old 08-19-2006, 09:08 AM   #13
DonavonP is offline
Senior Member
DonavonP's Avatar


Workhorse Chassis Owner
Join Date: Jul 2004
Posts: 1,550
Jerry, I've been pricing 6/3 with ground UF for a 100 foot run and have found copper to be 3.00 to 3.60 per foot (just for the wire). I can buy 100 amp aluminum 4 wires underground for 1.50 per foot for all 4 wires combined but since there is an aluminum shortage this price won't last long.

Do you see any problem with aluminum wire (can't remember if it was # 2 or 4) fitting a 50amp circuit breaker and or any other problem? I know I have to use that electric grease stuff. (Sometimes my electrical work looks more like a Boris Karloff movie than I'd like - still alive though)

When you say nickel coated, is this something you did? how? or store bought.

Thanks in advance.
__________________
  Reply With Quote
   
Old 08-21-2006, 04:21 PM   #14
Jerry Wessel KA8MBK is offline
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 48
I myself do not care to use aluminum and in a lot of places it is banned. If you must use it be sure to check the connections regularly to make sure they are tight. I purchased two 50 foot extension cables for about 35 dollars apiece at a rally. Both are 10-3. I bought the connectors nickle plated. They are at rallies.

__________________
Gerald Wessel
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hi, another newbie with a question please :) linzatx New Member Check-In 3 12-21-2008 11:39 PM
Newbie here with Question Peabody Class A Motorhome Discussions 11 10-11-2008 05:06 AM
Newbie question vanxr Towing and Tow Vehicles Discussion 16 10-01-2007 03:56 AM
Newbie question aceisback Travel Trailer Discussion 6 02-25-2006 05:55 PM
Newbie Question New Member Check-In 44 12-31-1969 06:00 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 08:09 PM.