|
|
08-03-2006, 10:02 AM
|
#1
|
Senior Member
Join Date: Jun 2006
Location: Pahrump, NV
Posts: 528
|
Is it OK to plug a regular heavy duty extension cord (with appropriate plug adapter) into a household outlet if all you want is to be able to use a couple of lights (but no AC/fridge/tv etc)? Don't want to damage the power center when visiting the in-laws.
__________________
2007 Winnebago 26P
Jeep Wrangler
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-03-2006, 10:02 AM
|
#2
|
Senior Member
Join Date: Jun 2006
Location: Pahrump, NV
Posts: 528
|
Is it OK to plug a regular heavy duty extension cord (with appropriate plug adapter) into a household outlet if all you want is to be able to use a couple of lights (but no AC/fridge/tv etc)? Don't want to damage the power center when visiting the in-laws.
__________________
2007 Winnebago 26P
Jeep Wrangler
|
|
|
08-03-2006, 10:30 AM
|
#3
|
Moderator Emeritus
Thor Owners Club Pond Piggies Club
Join Date: Dec 2000
Location: NORTH CANTON OH USA
Posts: 1,926
|
Yea you will be fine. Basically all you will be running is the converter/charger unit. The lights are 12V. As needed, the converter/charger will come on to recharge your house batteries which is supplying the power to your lights. Anything more than that, you would be wise to have either a 20amp or 30amp rated extension cord and control your power thru your management system assuming you have an outlet at your families house capable of 20+ amps.
Mike
__________________
Mike And Debbie- Northeast Ohio
2011 Ford F150 Ecoboost engine- SWEET!!
2011 Jayco Eagle 322FKS TT
|
|
|
08-03-2006, 03:08 PM
|
#4
|
Senior Member
Forest River Owners Club
Join Date: Aug 2002
Location: ...East Texas
Posts: 5,325
|
Absolutely! We've run refrigerator and lights on that kind of conneciton many times. during the night, we've run refrigerator and vent fans.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
2022 Coachmen Leprechaun 319MB
towing 2017 Jeep Grand Cherokee Limited
|
|
|
08-03-2006, 04:04 PM
|
#5
|
Senior Member
Join Date: Feb 2000
Location: Navarre, Ohio
Posts: 262
|
Just like Paul we have run the Frig, Lights and at times the TV also many times while visiting relatives with our RV's.
__________________
Gulf Stream RV Owners Forum www.gsowners.com
|
|
|
08-03-2006, 04:49 PM
|
#6
|
Senior Member
Monaco Owners Club
Join Date: Oct 2000
Location: Waverly, Tennessee
Posts: 184
|
Gary,
If your going to use an extension, get one from Lowes or Home Depot that is rated for 30amps, this is being on the safe side. It should be have 10/3 on the outer covering. This tells you that the wire is size 10 and has 3 conductors, black, white and green. Some come with a 20amp plug on the end which has one prong vertical and one prong horizontial and the round ground. Most outlets on the outside of home have an outlet that won't except that style of plug. Check and make sure. If your going to be less than 40 feet from the house, you can get away with a 12/3 cord, but I would get the 50' 10/3 and play it safe. I carry two around with all the time. The outlet should like either one of these diagrams, I hope....
1. |- | or 2. - |
O O
Hope those come out okay. Good luck. If it won't come out right, the 'O' is the ground.
Jim
__________________
Renegade (Jim) & Wrangler (Doreen)
& 4 attack cats, TJ, Shadow, Chessie, RJ
along with 2 who adopted us, Tom & puddy.
|
|
|
08-03-2006, 06:37 PM
|
#7
|
Senior Member
Join Date: Jun 2006
Location: Pahrump, NV
Posts: 528
|
Thanks everyone. At least now I know I won't have to sleep on the plastic covered sofa--YUCK!!!
__________________
2007 Winnebago 26P
Jeep Wrangler
|
|
|
08-14-2006, 04:47 PM
|
#8
|
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 51
|
We volunteer a lot and sometimes we have to use 140 feet of cable and plug into a 15 amp receptical. We put the fridge and water heater on propane and we can run the a/c for two weeks. We turn off the air and run the microwave and never pop a breaker. All my cables are 10-3 extension (30 amp) and they are 50 feet apiece and the main cord which is 40 feet of 50 amp wire. NO PROBLEM while doing this we can run both tv sets and all lights. Wife and I also run electric blanket when needed. Yes with the air on. Nobody said I was normal.
__________________
Gerald Wessel
|
|
|
08-15-2006, 05:35 AM
|
#9
|
Senior Member
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 13,599
|
140 ft to a 15 AMP receptical is going to have voltage drop. Consider getting a meter and checking the voltage at your RV, with the appliance on. Then, following the instructions in the appliance owners manual, determine if you should be running the appliance. Appliances may run on low voltage, but it could be reducing the longevity of the appliance.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
|
|
|
08-15-2006, 10:28 AM
|
#10
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
|
There's no problem in using a 12 or 14 gauge extension cord toa 15/20 amp household outlet. You can't get 30A out of it anyway, so using a 30A power cord is overkill unless the distance is very far, e.g. the 140 feet mentioned earlier..
But the usual orange cords that everybody calls "heavy duty" mostly are not. They are typically only 16 gauge wiring. Read the label on the cord and get at least 14 gauge. Use 12 gauge if the distance is very long.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
08-15-2006, 04:33 PM
|
#11
|
Senior Member
Jayco Owners Club
Join Date: Jul 2004
Posts: 2,199
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by GaryKD:
140 ft to a 15 AMP receptical is going to have voltage drop. Consider getting a meter and checking the voltage at your RV, with the appliance on. Then, following the instructions in the appliance owners manual, determine if you should be running the appliance. Appliances may run on low voltage, but it could be reducing the longevity of the appliance. </div></BLOCKQUOTE>
My wire calculator says he's ok to run 15amp thru 10/3 copper for 140 feet.
__________________
DonavonP
2016 Jayco White Hawk 27dsrl
US Army 1968-70 SETAF 559th Vicenza Italy
|
|
|
08-19-2006, 08:20 AM
|
#12
|
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 51
|
The no load voltage at 140 feet was 117 at both ends of the wire. The loaded voltage was 114-115 and that includes loss in the MH wiring also. We were drawing @13-14 amps. 80% of the connectors are nickle plated and all are kept corrosion free. I could write a book on volunteering and the electrical available at many places. Monitoring power is not a option, but a necessity. Being a retired electrician I am very protective of my equipment. All voltages are monitored and checked with Fluke equipment.Actually if you have a long run with small wire, you will run low voltage long before you blow a breaker. I have more problem in some campgrounds with a regular cable and no extensions and supposidly a 30 amp plug. My 50-30 amp adaptor is all nickle plated and heavy duty.
__________________
Gerald Wessel
|
|
|
08-19-2006, 09:08 AM
|
#13
|
Senior Member
Jayco Owners Club
Join Date: Jul 2004
Posts: 2,199
|
Jerry, I've been pricing 6/3 with ground UF for a 100 foot run and have found copper to be 3.00 to 3.60 per foot (just for the wire). I can buy 100 amp aluminum 4 wires underground for 1.50 per foot for all 4 wires combined but since there is an aluminum shortage this price won't last long.
Do you see any problem with aluminum wire (can't remember if it was # 2 or 4) fitting a 50amp circuit breaker and or any other problem? I know I have to use that electric grease stuff. (Sometimes my electrical work looks more like a Boris Karloff movie than I'd like - still alive though)
When you say nickel coated, is this something you did? how? or store bought.
Thanks in advance.
__________________
DonavonP
2016 Jayco White Hawk 27dsrl
US Army 1968-70 SETAF 559th Vicenza Italy
|
|
|
08-21-2006, 04:21 PM
|
#14
|
Member
Join Date: Jul 2003
Location: Dundee Mi.
Posts: 51
|
I myself do not care to use aluminum and in a lot of places it is banned. If you must use it be sure to check the connections regularly to make sure they are tight. I purchased two 50 foot extension cables for about 35 dollars apiece at a rally. Both are 10-3. I bought the connectors nickle plated. They are at rallies.
__________________
Gerald Wessel
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|