I'm assuming you have disconnected shorepower when you are doing this test. And for the sake of this test you should turn off high current demand devices (like A/C's, hotwater heater, converter, etc).
I speculate that your generator has a problem, and although is showing 120vac, that's under a no-load situation. Could be when a load is put on it, the voltage drops.
I normally would have thought your transfer switch was bad, but you swapped that and still have the same symptom.
So given this situation, what I would do to prove the problem, is to unhook the generator from the switch, and wire in a 20amp cable that I would build to plug into home garage socket. [Make sure you get polarities correct (black power, white neutral, green/bare ground}]
- If you still have the same problem, then you've proved the 2nd transfer switch is also bad, and I would choose a different mfgs switch.
- If the switch works, then that proves the problem is with your generator, and you begin trouble shooting that.
Good luck