Onan generator problem

I have a Onan Micro Quiet 4000. It will only stay running as long as you hold the switch to the start position in the motor home or on the generator.
It's in a 2005 Coachmen Leprechaun if it matters.
Any one had this problem before and know the solution?
Also where can you source parts for these such as control boards etc?
Thanks in advance!
__________________
2005 Coachmen Leprechaun 292 with 2 slides.
Up North is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-12-2016, 05:20 PM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Here is a link to the current manual:

https://power.cummins.com/sites/defa.../F-1123-EN.pdf

It says low fluid level or call Cummins. Cummins now owns Onan. Your unit may pre date the aquistion so there may be a better manual around. Check the tag for the series number and use Google. Several sources have posted the pdf file for down load once you know the exact version you have. As an example I have a Microquiet KY manual I assume is the one I need. ;-)

There are many threads in this forum as well as many YouTube video's about the unit. Once you have nailed down what you have use the search or add to this thread.
nothermark is offline   Reply With Quote
Old 10-12-2016, 05:38 PM   #3
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
Quote:
Originally Posted by nothermark View Post
Here is a link to the current manual:

https://power.cummins.com/sites/defa.../F-1123-EN.pdf

It says low fluid level or call Cummins. Cummins now owns Onan. Your unit may pre date the aquistion so there may be a better manual around. Check the tag for the series number and use Google. Several sources have posted the pdf file for down load once you know the exact version you have. As an example I have a Microquiet KY manual I assume is the one I need. ;-)

There are many threads in this forum as well as many YouTube video's about the unit. Once you have nailed down what you have use the search or add to this thread.

Cummins has owned Onan since '86 so most units still on the road are Cummins/Onan units.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 10-12-2016, 05:40 PM   #4
Senior Member
 
Join Date: Nov 2014
Posts: 159
Thanks for getting me started!. I doubt low oil is the problem as I didn't run it much at all this season but I will give it a check.
I'm guessing the only parts source will be through Cummins therefore expensive!
__________________
2005 Coachmen Leprechaun 292 with 2 slides.
Up North is offline   Reply With Quote
Old 10-12-2016, 07:18 PM   #5
Senior Member
 
Join Date: Nov 2015
Posts: 335
If there is a l.e.d. on start/stop switch it can display fault codes narrowing your troubleshooting efforts.
Pretty sure your vintage micro quiet has the fault code feature. If so press stop three times and see what code it gives you, once it blinks a single digit code another press of stop will display the 2 digit fault code
https://www.google.com/url?q=https:/...WFBeZ5etwPRzgw
__________________
2016 Fleetwood Bounder 36E
pchuckie is offline   Reply With Quote
Old 10-13-2016, 06:20 AM   #6
Senior Member


 
Join Date: Jul 2006
Location: Anywhere I want to be.
Posts: 907
Quote:
Originally Posted by Up North View Post
Thanks for getting me started!. I doubt low oil is the problem as I didn't run it much at all this season but I will give it a check.
I'm guessing the only parts source will be through Cummins therefore expensive!
Not at all. When I had generator problems I called these people:

Onan Generator Voltage Regulator and Control Board Parts

They diagnosed the problem and had the parts I needed to get my generator up and running.

Kaye
__________________
1996 Newmar Mountain Aire. 3760 CA
2006 to 2015 Boxer named Cash (aka Cassius Clay)
2016 - Boxer named Chevy
Afubar is offline   Reply With Quote
Old 10-13-2016, 06:39 AM   #7
Senior Member
 
Join Date: Aug 2011
Posts: 258
Had the same problem on mine it was the control board.
__________________
Rich 1997 35' Dutch Star
jettyjock is offline   Reply With Quote
Old 10-14-2016, 06:46 AM   #8
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
You also want to check the oil pressure sensor switch. I have seen several reports of them failing with similar symptoms. No point in changing the control board until you know the inputs are good.
nothermark is offline   Reply With Quote
Old 10-14-2016, 06:56 AM   #9
Senior Member
 
Murf2u's Avatar
 
Join Date: Aug 2011
Location: Near Toronto, Canada
Posts: 1,842
I believe that vintage unit will still be the 'old school' version like mine, it generates in a voltage in / voltage out basis so i shuts down at unsafe levels.

You can start the engine with as little as 10 volts, but that would mean it would only have a 100 volt output.


Try charging the house battery, or use a known good battery temporarily to test.
__________________
Ted 'n' Laurie, plus Jackson (aka Deputy Dog, the Parson Russell Terrier 'fur kid') and, Rylie (who crossed the Rainbow Bridge June 14, 2012).
Murf2u is offline   Reply With Quote
Old 10-15-2016, 05:18 AM   #10
Senior Member
 
DAN L's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Sep 2007
Posts: 2,976
Afubar,
Just disconnect the wire at the oil switch to test it.
__________________
01 WINNEBAGO 35U W20.8.1L 5sp allison SW Wa,. Good Sam, SKP. RVM 198 AMSOIL fluids. BANKS ecm program. SCAN GAUGE II w/ Ally temp. 2 LIFELINE GPL-6CT AGM Batts on their sides. Michelins, TST tptts. K&N panel air filter. AERO mufflers. TAYLOR plug wires. ULTRA POWER track bar. KONI fsd shocks, toad '21MB GLA FWD on dolly
DAN L is offline   Reply With Quote
Old 10-16-2016, 04:54 PM   #11
Senior Member
 
Join Date: Nov 2014
Posts: 159
Thanks for the helpful replies everyone and thanks afubar for the link to the place where I can buy parts. Lots of helpful info on that site.
Haven't had the chance to mess with the gen much other than check the oil.
That was weird too. I pulled the dip stick and I swear it was on the add line. Thought I found my problem.
I looked up what weight oil to add and I didn't have any on hand.
The motor home needed gas anyhow so I took it to the gas station to fill it and buy the oil.
I got home to add the oil and pulled the dip stick again. Now it shows full and I can actually see the oil in the neck of the hole where the dip stick goes in.
So I thought by driving it it splashed the oil around. Waited a couple hours to let the oil all drain back in the pan and checked it again. Same thing it showed to be full. I don't know maybe I was seeing things the first time I checked it.

I will get a chance to look into it more this week. Just wanted to say thanks for all the helpful replies.
__________________
2005 Coachmen Leprechaun 292 with 2 slides.
Up North is offline   Reply With Quote
Old 10-17-2016, 01:18 AM   #12
Senior Member
 
DAN L's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Sep 2007
Posts: 2,976
Up north,
I have the Same experience with the oil dipstick multiple times. I expect this is normal.
__________________
01 WINNEBAGO 35U W20.8.1L 5sp allison SW Wa,. Good Sam, SKP. RVM 198 AMSOIL fluids. BANKS ecm program. SCAN GAUGE II w/ Ally temp. 2 LIFELINE GPL-6CT AGM Batts on their sides. Michelins, TST tptts. K&N panel air filter. AERO mufflers. TAYLOR plug wires. ULTRA POWER track bar. KONI fsd shocks, toad '21MB GLA FWD on dolly
DAN L is offline   Reply With Quote
Old 10-20-2016, 06:14 AM   #13
Junior Member
 
Join Date: May 2016
Posts: 23
Onan generator problem

One issue with Onan's, especially older ones is if the unit is shut down with load still on can cause voltage regulators to fail. Always remove as much load as possible first. Turn off Air Conditioners or any heavy loads before turning off the generator.
Maxwedge413 is offline   Reply With Quote
Old 10-20-2016, 06:09 PM   #14
Senior Member
 
Join Date: Nov 2014
Posts: 159
Haven't solved this issue yet. The trouble code I get is 4 flashes indicating cranking the motor for more than 30 seconds without a engine start.
Been waiting for a response from Flight Systems for a opinion from them before ordering a control board which is my suspicion of what the problem is.
They haven't returned my voice or email in 2 days.

This may wait until spring now.
__________________
2005 Coachmen Leprechaun 292 with 2 slides.
Up North is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan Generator Problem DCTENT Alpine Coach Owner's Forum 8 09-08-2007 03:51 PM
Onan Generator Problem Roam America RV Systems & Appliances 10 05-05-2007 08:19 AM
Onan Generator Problem jadams RV Systems & Appliances 2 03-30-2007 02:52 AM
Onan Generator / Wiring Problem Doggie MH-General Discussions & Problems 2 12-23-2006 11:04 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:09 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.