Onan generator shuts down after 1 minute
Old 03-10-2010, 07:18 AM   #1
bigeyes is offline
Junior Member
Join Date: Mar 2010
Posts: 4
I have an Onan 7.5 Quiet Diesel Generator on my 2004 Expedition. When I start the generator, it runs for about 1 minute and shuts down. The shut down code displayed is - primary 1, and secondary 33. The manual says that is a shut down code for overheating. Clearly it is not overheating in 1 minute. It will restart almost immediately but again runs for about a minute and shuts down. Have changed all filters and fluids. Any ideas on how to fix this problem would be appreciated.

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-10-2010, 09:16 AM   #2
Flagelpater is offline
Senior Member
Flagelpater's Avatar
Monaco Owners Club
Join Date: May 2009
Posts: 460
What does the manual state as a cause for code 33? Have you checked the cooling air inlet and outlet for blockage. How long since it did run okay? Do you have any electrical load on the GenSet? What is your ambient temperature?

__________________
2005 Monaco Knight, 3 Slide, 38' PST, Cummins 330 ISC, 34,000 miles on this one!
VMSpc, PressurePro, BrakeSwitch, DeLorme SA2010

2005 Honda CRV, Blue Ox, SMI Brake, TomTom Go 720
  Reply With Quote
   
Old 03-10-2010, 02:13 PM   #3
bigeyes is offline
Junior Member
Join Date: Mar 2010
Posts: 4
The manual says its an overheat problem. I put a new air filter in, but did not see anything in the inlet or outlet. It last ran about a month ago. temps have been in the 60s and 70s. No load on gen set.
__________________
  Reply With Quote
   
Old 03-10-2010, 02:36 PM   #4
Flagelpater is offline
Senior Member
Flagelpater's Avatar
Monaco Owners Club
Join Date: May 2009
Posts: 460
Did it run okay after you changed the filter? Are there birds or other nesting animals in your area that could have clogged the air inlet? Can you be sure nothing is blocking the cooling air? As you know, one minute is a very short time for it to overheat with the cooling system working properly. I would also expect it to run less than one minute on the second run if it was actually overheating, not taking the full minute the second time. Can you see if a wire may be shorting to ground on the temp sensor lead? as you can tell I am not an expert troubleshooting this unit. Hopefully an expert will chime in shortly.
__________________
2005 Monaco Knight, 3 Slide, 38' PST, Cummins 330 ISC, 34,000 miles on this one!
VMSpc, PressurePro, BrakeSwitch, DeLorme SA2010

2005 Honda CRV, Blue Ox, SMI Brake, TomTom Go 720
  Reply With Quote
   
Old 03-10-2010, 03:01 PM   #5
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,606
Since it probably didn't overheat that fast (UNLESS there is no coolant at all in the system - did you check?), I would suspect a failed coolant temp sensor. Or a disconnected wire to the sensor (but heaven's know where it might be!).
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 03-11-2010, 09:27 AM   #6
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
My Onan 7.5 did the same thing last April ...you said you changed "all fluids" ...I presume that includes coolant. I believe there is air in the coolant system. Here's what I did to cure mine, straight from my service records. It has run a lot since then with no problem.

"First time run since 13 Apr service, started generator, ran fine but no power output, found breaker on generator in OFF position, turned it on, generator died in less than one minute. Restarted. Ran less than one minute and died. First stage code 1 blink, "high temp." Restarted and again died in less than one minute with lots off gurgling sounds as it shut down. Checked air cleaner for proper installation, checked oil & coolant overflow levels, checked coolant level under pressure cap and found low, started and ran generator with cap off, ran fine, after a few minutes there was lots of spitting through overflow tube and coolant level dropped even further. Bought gallon of ethelyne glycol green coolant 50/50 mix, added apx 1 qt, then ran generator under load apx 30 min, worked as normal, checked & topped off coolant level after cooled down, replaced coolant fill tube in case."
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 03-12-2010, 10:37 AM   #7
bigeyes is offline
Junior Member
Join Date: Mar 2010
Posts: 4
Thanks for the replies. As soon as it stops raining here in the Tampa area I will go out and check the generator again for mentioned items.
__________________
  Reply With Quote
   
Old 03-14-2010, 08:32 AM   #8
caymann is offline
Senior Member
caymann's Avatar
Join Date: May 2003
Location: NH
Posts: 187
maybe your fan belt is broken..... check to see if it is blowing air
__________________
2001 Monaco Executive 43', CTD ISM
2004 Dodge Ram 3500 4WD Auto, CTD ISB
  Reply With Quote
   
Old 03-14-2010, 08:48 AM   #9
tquarles is offline
Member
tquarles's Avatar
Monaco Owners Club
Join Date: Nov 2007
Posts: 66
I had a similar problem with the 7.5 onan in my Endeavour the day before my warranty expired! Cummins pulled the generator out, pulled the cover off (5+ hours of labor on an '02 endeavour due to really poor design on holiday rambler's part), and changed the temp. sensor(5 minutes of labor) - no more problems. They said that if the temperature sensor fails to register any temp. increase after a minute of operation, it assumes the temperature sensor has failed and wouldn't be able to indicate an overtemp condition, so it shuts down immediately.
__________________
2002 HR Endeavor
  Reply With Quote
   
Old 03-14-2010, 01:22 PM   #10
bigeyes is offline
Junior Member
Join Date: Mar 2010
Posts: 4
Thanks for the responses. I'm taking it in to Onan this week and let you all know what the problem is. I believe its the fan belt or the sensor. Too much work for me to handle.
__________________
  Reply With Quote
   
Old 03-14-2010, 03:02 PM   #11
caymann is offline
Senior Member
caymann's Avatar
Join Date: May 2003
Location: NH
Posts: 187
If it is the fan belt, it is major work to take everything out before you can get to the fan belt.
The belt is located in the rear of the generator and you will have to take out all side covers
plus the fan belt protection/wind deflection cover
Use a genuine Onan fan belt (about $50 or so). Alternative belts such as from NAPA that costs a few bucks won't last more than a season and will wear off and you will have to do it again...speaking from experience...
__________________
2001 Monaco Executive 43', CTD ISM
2004 Dodge Ram 3500 4WD Auto, CTD ISB
  Reply With Quote
   
Old 08-04-2011, 08:25 PM   #12
RollngStones is offline
Junior Member
Join Date: Aug 2011
Posts: 5
Hi - I'm curious if you determined what the cause was. We appear to be having a very similar issue.
__________________
  Reply With Quote
   
Old 08-04-2011, 08:37 PM   #13
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,653
To replace the temp sensor on the ONAN 7.5 Quiet Diesel the top cover must be removed. The sensor is at the top of the top, over the fan blade where a coolant hose is connected. It's pretty obvious when you get the top cover off.

__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan diesel generator stops after about a minute Bob&AnnaMari MH-General Discussions & Problems 2 10-05-2009 02:38 PM
Onan 5.5 Marquis gold gas, shuts down at 15 min Shamong Shepherds MH-General Discussions & Problems 12 08-27-2008 05:39 PM
Onan Generator Quits On Start With No Load Birddog Pilot Alpine Coach Forum 26 08-11-2008 10:49 AM
Onan Problems Stretch Alpine Coach Forum 12 06-23-2005 06:02 PM
High dollar ONAN Quiet Diesel not worth it! Dale Tomlinson Winnebago Industries Owner's Forum 2 05-17-2005 06:24 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 04:59 PM.